Logic Behind the Operation Interlocks

This guide attempts to clarify the logic underlying the operational interlocks of various switch types, including disconnectors, earth switches, and circuit breakers, within one-and-a-half circuit breaker and double bus single circuit breaker schemes.

A Guide to the GIS Operation and Interlocking Schemes Design
A Guide to the GIS Operation and Interlocking Schemes Design

It should be noted that this manual should not be used solely to design an interlocking scheme or to compare an already designed interlocking scheme for any differences. The reason being that it is quite possible that a given interlock can be achieved by more than one method.

And the methods discussed in this manual may differ from some schemes.This manual shall only be used to develop and understanding of the necessary conditions that govern the interlocks for switches.


1. What is the One and Half Breaker Scheme?

Consider the Single Line Diagram arrangement shown in Figure-7 .As we can see that there are three circuit breakers: ‘Upper CB’ , ‘Middle CB’ and ‘Lower CB’. And using these breakers, two feeders can be connected to the Bus.

One line feeder going to remote end station and one transformer feeder.

Single Line Diagram of a one and half breaker scheme bay
Figure 1 – Single Line Diagram of a one and half breaker scheme bay

The Transformer feeder can be connected to the Bus by two methods:

  1. Close ‘Upper CB’
  2. Close ‘Lower CB and Middle CB’

Similarly the line feeder can also be connected to the Bus by two methods:

  1. Close ‘Lower CB’
  2. Close ‘Upper CB and Middle CB’

So we can see that three CBs are used to connect two feeders to the bus inside the substation. In other words , one and half CB per feeder is required in this arrangement. Hence it is called one and half circuit breaker scheme.


2. Interlocks of one and half circuit breaker system

In the last chapter we discussed the general rules for designing interlocks of different types of switches. Here we will see the actual interlocks for each and every switch in the one and half circuit breaker arrangement shown in Figure-1.

All switches are labelled for the same purpose , e.g. DS.1, ES.3. The interlocks are shown in equation for easy understanding.

It is to be noted that the general conditions for CB that are not related to switches e.g. All Lock out relays reset, Synchro check OK, CB spring charged, SF6 pressure normal,have not been mentioned here. It is assumed that the reader is familiar with these conditions.

For easy understanding, we will break down the single line diagram into 6 portions:

  1. The upper CB and its related disconnectors and earth switches or the ‘Upper portion’.
  2. The Transformer feeder.
  3. The middle CB and its related switches or the ‘Middle portion’.
  4. The line feeder.
  5. The lower CB and its related disconnectors and earth switches or the ‘Lower portion’.
  6. Bus Section.

DS.1

TEST = BUS1 ES CLOSE + ES1 CLOSE
SERVICE = BUS1 ES OPEN + ES1 OPEN + ES2 OPEN + UPPER CB OPEN


ES.1

DS1 OPEN + DS2 OPEN

[ve]

Upper CB

TEST = DS1 OPEN + DS2 OPEN
SERVICE = DS1 CLOSE + DS2 CLOSE + SYNCH CHECK OK + CLOSE BLOCK OK + CLOSE AUTH OK


DS.2

TEST = ES2 CLOSE + ES3 CLOSE
SERVICE = ES3 OPEN + ES1 OPEN + ES2 OPEN + UPPER CB OPEN


ES.2

DS1 OPEN + DS2 OPEN


2.1 Case Study- Upper Portion : (DS.1 Service Position Interlock)

As it is described in the previous section , the interlock of DS is with ES and CB. So logically the interlock of DS.1 should exist with all the earth switches and Circuit Breakers that are directly connected to DS.1.

In this case, the service condition of DS.1 should be:

SERVICE = BUS1 ES OPEN + ES1 OPEN + UPPER CB OPEN

But the actual service condition is:

SERVICE = BUS1 ES OPEN + ES1 OPEN + ES 2 OPEN + UPPER CB OPEN

So the question arises that what is the reason to include ‘ ES.2 OPEN’ status in the interlock when the remaining statuses were enough to fulfill the interlock condition. The reason is that , every switch is provided with several auxiliary contacts (Normally open and Normally Closed). These contacts are used wherever the status of the switch is required in the scheme.

An interlock circuit is one example. The switch and its auxiliary contacts are tested during the commissioning of the substation. However, the possibility cannot be over ruled that with the passage of time, there can be a slight chance of any of the contacts of one switch to malfunction. The possibility is very less but it cannot be established that it will never happen.

Now let’s consider that in the given case, one (52-B) auxiliary contact of Upper CB gets stuck in closed position. This means that its interpreting that the CB is Open. Now even if the CB is closed, this particular contact is giving the status that the CB is open. So if the same faulty auxiliary contact is used in this DS.1 interlock, and the general rule is used to design interlock . i.e.

SERVICE = BUS1 ES OPEN + ES1 OPEN + UPPER CB OPEN

Then DS.1 will be allowed to close only if ‘Bus ES’ and ‘ES.1 ‘are open regardless of CB status. It means that if CB is closed, and ES.2 is also closed , the system will think that CB is open and hence it will allow DS.1 to close the connect the live bus bar to earth.

To cope with this kind of situation, the interlock is made more efficient by including ES.2 open status.

Title:A Guide to the Logic Behind the GIS Operation Interlocks – Omer Nawaz Malik
Format:PDF
Size:5.10 MB
Pages:117
Download:Here 🔗 (Get Premium Membership) | Video Courses | Download Updates

Suggested Study – Learn how to interpret interlocking schemes between MV cubicles (single line and wiring diagrams)

Learn how to interpret interlocking schemes between MV cubicles (single line and wiring diagrams)

Premium Membership

Get access to premium HV/MV/LV technical articles, advanced electrical engineering guides, papers, and much more! It will help you to shape up your technical skills in your everyday life as an electrical engineer.
50% Discount - Save 50% on all 110+ video courses with Enterprise Membership plan.

More Information

Learn How to Design Power Systems

Learn to design LV/MV/HV power systems through professional video courses. Lifetime access. Enjoy learning!

EEP Hand-Crafted Video Courses

Check more than a hundred hand-crafted video courses and learn from experienced engineers. Lifetime access included.
Experience matters. Premium membership gives you an opportunity to study specialized technical articles, online video courses, electrical engineering guides, and papers written by experienced electrical engineers.
Whitepaper: How to Improve Risk Decisions for Power Systems - Prioritizing vulnerabilities with full operational context