IEC MV Switchgear Rating Definitions

Standard IEC 62271-1 defines standard ratings for medium voltage switchgear. Full name of this standard is ‘High-voltage switchgear and controlgear – Part 1: Common specifications for alternating current switchgear and controlgear’. Ratings defined in this standard allow selection of equipment to match the electrical characteristics at the point of installation.

MV application guide for engineers to select and specify the right equipment
MV application guide for engineers to select and specify the right equipment (on photo: British Sugar 11kV switchgear upgrade; credit: Industrial Switchgear Services Ltd)

Voltage

Operating voltage, U (kV)

This is the system’s operating voltage at the point where the switchgear is installed. The operating voltage must always be less than or equal to the rated voltage of the switchgear equipment.

Rated voltage, Ur (kV)

This is the maximum rms voltage the switchgear equipment can continuously operate at, under normal conditions. The rated voltage is always higher than the systems operating voltage and determines the insulation levels of the equipment.

Medium voltage, metal-enclosed switchgear is defined for use on operating voltages from1 kV to 52 kV. Within this voltage range, IEC 62271-1 defines standard switchgear rated voltages as:

  • Series I equipment (used in European 50 Hz installations): 3.6, 7.2, 12, 17.5, 24, 36, 52 kV
  • Series II equipment (used in Non-European 60 Hz installations): 4.76, 8.25, 15, 15.5, 25.8, 27, 38, 48.3 kV

Insulation level voltages, Ud (kV rms 1 min) and Up (kV peak)

The defined levels are stated for phase-to-earth and phase-to-phase limits under standardized ambient conditions. For installations above 1000 metres, these insulation levels must be derated.

Power frequency withstand voltage, Ud

This is the maximum rms voltage that the equipment can withstand at mains frequency for 1 minute. It simulates power surges originated from within a power system from such events as switching transients, resonance, etc.

Power frequency withstand voltage, Ud
Power frequency withstand voltage, Ud
Lightning impulse withstand voltage, Up

This is the peak transient voltage that the equipment can withstand from power surges originating from atmospheric conditions such as lightning. It is simulated using a standard voltage waveform.

Lightning impulse withstand voltage, Up
Lightning impulse withstand voltage, Up

Table 1 – Standard values for insulation level voltages

Ur (kV)Ud (kV rms)Up (kV peak)
7.22060
122875
17.53895
2450125
3670170

Current

Operating current, I (A)

This is the maximum rms current expected to flow through the equipment. The operating current must always be less than or equal to the rated current of the equipment.

Rated current, Ir (A)

This is the maximum rms current the equipment can continuously operate at, under normal conditions. This rating is based on an ambient operating temperature of 40°C, within an allowable maximum temperature rise. For temperatures above 40°C, switchgear rated current must be derated.

IEC 62271-1 specifies standard ratings as base 10 multiples of 1, 1.25, 1.6, 2, 2.5, 3.15, 4, 5, 6.3, 8.

Table 2 – Maximum permissible temperature rise

Material and dielectric mediumMaximum permissible temperature (°C)Temperature rise above 40 °C ambient (°C)
Contacts, in air
Bare copper, bare copper alloy or bare aluminium alloy7535
Silver or nickel coated10565
Tin-coated9050
Bolted connection (or equivalent), in air
Bare copper, bare copper alloy or bare aluminium alloy9050
Silver or nickel coated11575
Tin-coated10565

Peak withstand current, Ip (kA)

This is the peak current the equipment can withstand in the closed position from the first loop of a short circuit fault. This current contains a symmetrical AC component, superimposed on a decaying DC component.

Peak withstand current is defined as 2.5 times the rated short-time withstand current for 50 Hz installations and 2.6 times the rated short-time withstand current for 60 Hz installations. The switchgear peak withstand current rating must be higher than the calculated peak dynamic current (Idyn) expected if a short circuit fault occurred at the point of installation.

NOTE – Switchgear peak withstand current rating is commonly referred to as rated short circuit making capacity.

Peak withstand current
Figure x – Peak withstand current

Short-time withstand current, Ik (kA)

This is the level of symmetrical rms fault current the switchgear can carry in the closed position for a short time period (typically 1 second), without temperature rise exceeding predefined levels. IEC 62271-1 specifies standard ratings as base 10 multiples of 1, 1.25, 1.6, 2, 2.5, 3.15, 4, 5, 6.3, 8

Short-time withstand duration, tk (seconds)

This is the period of time that the equipment is rated to carry the short-time withstand current. IEC 62271-1 specifies a standard rating of 1 second, although durations of 0.5, 2 and 3 seconds are allowed.

Frequency, fr (Hz)

This is the rated test frequency of the switchgear and must match the operating frequency of the installation. Two medium voltage mains supply frequencies are used globally:

  • 50 Hz in European systems
  • 60 Hz in American systems
Title:MV application guide for engineers to select and specify the right MV equipment – AuCom
Format:PDF
Size:4.4 MB
Pages:224
Download:Here 🔗 (Get Premium Membership) | Video Courses | Download Updates

Recommended – Voltage Drop Analysis and Calculation Essentials (MS Excel Sheet)

Voltage Drop Analysis and Calculation Essentials (MS Excel Sheet Bonus)

Premium Membership

Get access to premium HV/MV/LV technical articles, advanced electrical engineering guides, papers, and much more! It will help you to shape up your technical skills in your everyday life as an electrical engineer.
50% Discount - Save 50% on all 110+ video courses with Enterprise Membership plan.

More Information

5 Comments


  1. Firehiwot Geda
    May 18, 2023

    Thank you, useful information


  2. Workineh alemayehu
    Oct 02, 2022

    Thanks full


  3. Vasyl Savkin
    Sep 28, 2022

    Very interesting


  4. Ion Raileanu
    Nov 19, 2021

    Excellent information. You should do something for Europe 🇪🇺 too. Thanks.


  5. Frido Jimmy Tarigan
    Jul 23, 2020

    Thank you very much for this topic, very helpful

Leave a Comment

Tell us what you're thinking. We care about your opinion! Please keep in mind that comments are moderated and rel="nofollow" is in use. So, please do not use a spammy keyword or a domain as your name, or it will be deleted. Let's have a professional and meaningful conversation instead. Thanks for dropping by!

Learn How to Design Power Systems

Learn to design LV/MV/HV power systems through professional video courses. Lifetime access. Enjoy learning!

EEP Hand-Crafted Video Courses

Check more than a hundred hand-crafted video courses and learn from experienced engineers. Lifetime access included.
Experience matters. Premium membership gives you an opportunity to study specialized technical articles, online video courses, electrical engineering guides, and papers written by experienced electrical engineers.
Whitepaper: How to Improve Risk Decisions for Power Systems - Prioritizing vulnerabilities with full operational context