66/33 KV Olakha Substation
This report describes about the various testing that are required to be done before commissioning of 66/33 KV substation. Primary goal of this report is to provide in a simple and more of conventional way of conducting the testing of various switchgears and the system.
It contains in a lucid way, a concise presentation of various technical data and parameters that were obtained while in field testing.
This report intends to serve as a history of Olakha substation in terms of its technical data and could be used as future reference while testing however the data may vary with different instruments used and the way it is conducted.
The materials presented in this report are intended to serve as a platform from where young and enthusiastic technical people could enhance their learning and explore in the area of testing and commissioning.
However it could be used as reference by the one who already have the experience.
Testing and commissioning procedures:
- Checking the winding resistance of CT, PT and CVT
- CT ratio check
- Ratio test of CVT and PT
- Knee point voltage test (KPV Test) of current transformer
- Surge monitor testing
- SF6 circuit breaker testing
- Transformer winding resistance
- Transformer testing
- Transformer oil testing
- Winding resistance and ratio check of 33kv CT and PT
- High Pot test (Cable HV test)
- Relay testing (Overcurrent protection)
- Stability testing report
SF6 Circuit Breaker Testing
Objectives:
- To find out the Alarm ‘Loss of SF6’ at 20ºC.
- To find out the General Lock out SF6 at 20ºC.
- To find the closing and opening time of SF6 Circuit Breaker.
Tested circuit breakers:
- CB#1 : Circuit Breaker on Incomer#1 (Tie Line)
- CB#2 : Circuit Breaker on Transformer#1 side
- CB#3 : Circuit Breaker on Bus Coupler Side
- CB#4 : Circuit Breaker on Incomer#2 (Jemina Line)
- CB#5 : Circuit Breaker on Transformer#2 side
Theory:
The Nominal pressure of SF6 gas at 20ºC is 6.0 bars. When the loss of SF6 gas occurs below certain set value it gives an alarm indicating less SF6 gas.
So we need to attend to it by refilling.
If we fail to attend to the alarm, then when the pressure of SF6 gas falls further, then Lock out of SF6 occurs. At this point the circuit breaker neither opens nor closes i.e. it remains in deadlock position.
| Title: | Testing and commissioning of 66/33 KV substation – Cheten Tshering, Olakha Sub-Station, SMD Semtokha (Transmission Department Bhutan Power Corporation Limited Thimphu) |
| Format: | |
| Size: | 5.40 MB |
| Pages: | 130 |
Presentation should be more elaborate with details testing figures and details of standard followed during commissioning.
What is instantaneous current for 33KV in power system
What will be the maximum current rate for 33KV?
What are the possible courses of 33kva line failure after new installation