Ground source issues

The term “ground source”, as it is commonly used, implies a source for zero sequence current from a grounded neutral connection during faults or other system unbalance conditions. The term is a bit of a misnomer in that a grounded neutral is indeed not a source of zero sequence current, but rather a path for zero sequence current.

Applying directional overcurrent relays in ground fault protection of transmission lines
Applying directional overcurrent relays in ground fault protection of transmission lines

Even as a ground current path, the grounded neutral is not necessarily a ground source as it will be herein defined. The real source for ground fault current is the combination of the power system positive sequence generation to provide the fault current and the unbalanced fault condition.


Ground source importance towards the contribution of fault current

Figure 1(a) shows a generator or an equivalent source on the primary side of a transformer with the primary windings connected in delta and secondary windings connected grounded-wye. With a phase-to-ground fault on the primary side of the transformer the generator (source) will provide the current that must flow through the generator grounded neutral connection, which is usually a high impedance connection.

The delta winding is an open circuit in the primary ground fault loop (zero sequence circuit), but allows I0 to flow in the secondary ground fault loop providing a shunt impedance path in the transformer’s zero sequence circuit.
Figure 1(a) – Transformer Connections with Zero Sequence Circuits: The delta winding is an open circuit in the primary ground fault loop (zero sequence circuit), but allows I0 to flow in the secondary ground fault loop providing a shunt impedance path in the transformer’s zero sequence circuit.

This is indeed a ground current path that meets the definition of a ground source. Ground (zero sequence) current cannot, however, be provided from the secondary system for this fault because there is no primary ground connection at the transformer to provide phase-to-ground amp-turn coupling through the transformer.

For a phase-to-ground fault on the transformer secondary side a fault current (3I0) will be allowed to flow as there is a path for zero sequence current I0, to flow in each phase of the delta connected primary winding satisfying the transformer’s ampturn coupling requirements, i.e., nPI0P + nSI0S = 0, where nP is the number of primary turns and ns is the number of secondary turns.

This coupling sets up the shunt ground path in the transformer equivalent zero sequence circuit.

Figure 1(b) shows the same configuration except the transformer is provided with wye-grounded windings on both the primary and secondary. The primary side, however, now has the ground connection to allow phase-to-ground amp-turn coupling through the transformer, i.e., nPI0P + nSI0S = 0.

I0 in the primary wye-grounded winding is coupled by amp-turns to the secondary wye-grounded winding and is equal in per unit value, thus providing a series impedance in the transformer’s zero sequence circuit. 
Figure 1(b) – Transformer Connections with Zero Sequence Circuits: I0 in the primary wye-grounded winding is coupled by amp-turns to the secondary wye-grounded winding and is equal in per unit value, thus providing a series impedance in the transformer’s zero sequence circuit.

Therefore, the per unit ground current is the same on both sides of the transformer regardless of the location of the fault. This results in a series coupled zero sequence current path through the transformer from the primary system to secondary system.

Although ground current is flowing in the transformer grounded neutral this connection is not a “ground source.” It does, however, allow adjacent ground sources to be available for faults on the opposite side of the transformer. This can be referred to as a “passing” ground source.

Figure 1(c) shows the configuration with a three winding transformer with two wye-grounded and one delta windings. This configuration provides both a series path to the primary source and a shunt path at the transformer for zero sequence current that will flow through the neutral during secondary ground faults.

I0 in the primary wye-grounded winding is coupled by amp-turns to the secondary wye-grounded winding and is equal in per unit value, thus providing a series impedance in the transformer’s zero sequence circuit.
Figure 1(c) – Transformer Connections with Zero Sequence Circuits: I0 in the primary wye-grounded winding is coupled by amp-turns to the secondary wye-grounded winding and is equal in per unit value, thus providing a series impedance in the transformer’s zero sequence circuit.

Considering the above discussion a ground source is therefore defined as a three-phase transformer or generator configuration with a grounded neutral connection that provides a shunt path in the zero sequence circuit for zero sequence current.

For the transmission system, ground sources are provided with either delta-wye or a zigzag transformer winding connections.


Distributed generation influence on transmission system ground sources

Distributed generation in the power system influences fault current and fault current distribution in a power system. The focus is how the distributed sources affect the magnitude of the ground fault current in the power system during a ground fault condition, so that proper coordination between ground overcurrent devices can be maintained.

Take the example system shown in Figure 2.

Simplistic Power System
Figure 5.10.2 – Simplistic Power System

For a ground fault at the location shown in Figure 2 the zero sequence diagram is drawn as shown in Figure 3:

The distributed sources can be switched in and out of the system depending on the generation requirements of the power system. The conventional source will be considered as being in the circuit for the purpose of this discussion. Note that for this example the distributed sources have relatively high positive and negative sequence impedance when compared to the conventional sources.

In other words, the distributed sources contribute very little to the overall fault current whether they are in or out of service, and as such we can ignore them.

Zero Sequence Impedance of the Simplistic Power System
Figure 3 – Zero Sequence Impedance of the Simplistic Power System

However, the distributed sources have relatively low impedance in the zero sequence network because of the wye-delta transformers used to connect them to the grid. Therefore, they have to be considered in the zero sequence circuit. Hence, the magnitude of I0Total is dependent on whether the distributed source is in or out of service.

The more distributed sources that are in service, the lower the overall impedance of the zero sequence circuit, and therefore, the higher the magnitude of I0Total.

Title:Applying directional overcurrent relays in ground fault detection for protection of transmission lines – Working Group D24 members: Don Lukach (Chairman), Rick Taylor (Vice-Chairman), Jeffrey Barsch, Ken Behrendt, Martin Best, Mike Bloder, Randy Crellin, Randy Cunico, Alla Deronja, Normann Fischer, Dom Fontana, Rafael Garcia, Gene Henneberg, Meyer Kao, Walter McCannon, Bruce Mackie, Alexis Mezco, John Miller, Dean Miller, Jim O’Brien, Cristian Paduraru, Manish Patel, Claire Patti, Elmo Price, Alejandro Schnakofsky, Mark Schroeder, Don Sevcik, Steve Turner, Karl Zimmerman,
Format:PDF
Size:459.7 KB
Pages:30
Download:Here đź”— (Get Premium Membership) | Video Courses | Download Updates

Suggested Reading – Three most common SCADA applications in MV/LV distribution systems you SHOULD know

Three most common SCADA applications in MV/LV distribution systems you SHOULD know

Premium Membership

Get access to premium HV/MV/LV technical articles, advanced electrical engineering guides, papers, and much more! It will help you to shape up your technical skills in your everyday life as an electrical engineer.
50% Discount - Save 50% on all 110+ video courses with Enterprise Membership plan.

More Information

Leave a Comment

Tell us what you're thinking. We care about your opinion! Please keep in mind that comments are moderated and rel="nofollow" is in use. So, please do not use a spammy keyword or a domain as your name, or it will be deleted. Let's have a professional and meaningful conversation instead. Thanks for dropping by!

Learn How to Design Power Systems

Learn to design LV/MV/HV power systems through professional video courses. Lifetime access. Enjoy learning!

EEP Hand-Crafted Video Courses

Check more than a hundred hand-crafted video courses and learn from experienced engineers. Lifetime access included.
Experience matters. Premium membership gives you an opportunity to study specialized technical articles, online video courses, electrical engineering guides, and papers written by experienced electrical engineers.
Whitepaper: How to Improve Risk Decisions for Power Systems - Prioritizing vulnerabilities with full operational context