Relay protection circuitry
This handbook covers the code of practice in protection circuitry including standard lead and device numbers, mode of connections at terminal strips, colour codes in multicore cables, dos and donts in execution. Also principles of various protective relays and schemes including special protection schemes like differential, restricted, directional and distance relays are explained with sketches.
Practical handbook for relay protection engineers
The norms of protection of generators, transformers, lines and capacitor banks are also given. The procedures of testing switchgear, instrument transformers and relays are explained in detail. The close and trip, indication and alarm circuits for variety of circuit breakers indicating ferrule numbers are also included.
All relevant information and circuit diagrams necessary for troubleshooting are also given.
Relay protection
The objective of relay protection is to quickly isolate a faulty section from both ends so that the rest of the system can function satisfactorily.
The functional requirements of the relay:
Reliability
The most important requisite of the protective relay is reliability since they supervise the circuit for a long time before a fault occurs. If a fault then occurs, the relays must respond instantly and correctly.
Selectivity
The relay must be able to discriminate (select) between those conditions for which prompt operation is required and those for which no operation, or time delayed operation is required.
Sensitivity
The relaying equipment must be sufficiently sensitive so that it operates reliably when required under the actual conditions that produces least operating tendency.
Speed
The relay must operate at the required speed. It should neither be too slow which may result in damage to the equipment nor should it be too fast which may result in undesired operation.
Basic connections of protectiverelay
Important elements used in protection relaying
Switchgear
Circuit breaker bulk oil, minimum oil, SF6, airblast, vacuum etc. depending on medium used for quenching the arc. Different operating mechanisms such as solenoid, spring, pneumatic, hydraulic etc. are employed.
Protective gear
Relays (current, voltage, impedance, power, frequency, etc.) based on operating parameter, definite time, inverse time, stepped etc. as per operating characteristic, logic wise such as differential, over fluxing etc.
Station Battery
A Station battery containing a number of cells accumulate energy during the period of availability of A.C supply and discharge at the time when relays operate so that relevant circuit breaker is tripped.
Station battery connection scheme
Table of handbook contents:
  1. Code of Practice:
    1. Standard number for devices
    2. Types of panels
    3. Protective relay – connection and zones of protection
    4. Norms of protection for generator, transformers and lines
    5. Current transformers
    6. Voltage transformers
    7. Energy meters
    8. Synchronising panel
  2. Generator and their protection
  3. Transformers and their protection
  4. Distance relays in A.P. system, relay indications and their meanings
  5. Busbars – arrangements and protection
  6. O/L & E/F relays
  7. Circuit breakers
  8. Station battery
  9. Earthing practices
  10. Excitation and voltage regulation
Title:Practical handbook for relay protection engineers – Mohammed Fasil
Pages:127
Recommended – Testing and Commissioning Procedures for Substation Equipment
17 Comments
  1. Olebogeng
    Feb 13, 2023
  2. Ranvir Kumar
    Sep 03, 2022
    There are very good topics and lots to lean.
  3. Adil
    Nov 03, 2021
    Very useful book & practical, thanks a lot
  4. Hari
    Jun 22, 2021
    Wonderful and informative .pdf i have ever read about protection. Thank you very much.
  5. Shaik.Gudubhai
    Feb 13, 2021
    Nandyal,kurnool(dt)AP, India.EEP is most valuable journal published for electrical engineer and technicians.Hat’s up you.
  6. Evans Chadili Mhango
    Feb 12, 2021
    Thank you very for the information and the narrative way of the book.
  7. MOHAMED idris
    Feb 11, 2021
    I am Electrical technician I want basic
  8. Noubatoide
    Feb 11, 2021
    It is a real pleasure for me to leave a comment in this site ,because of your publication, i improve so much my understanding of electricity. All my regard
  9. MOHAMMEDAYAZ MOHAMMEDSHARIF SHAIKH
    Oct 08, 2020
    Nice Book. This is a good hand book for understanding the basics of protection system.
  10. Madhav
    Jan 18, 2020
    This is a good hand book for understanding the basics of protection system. Although references are drawn from the practice followed in AP Electricity Distribution(In southern India) system, the protection protocol for feeders is generally the same elsewhere in India. However, we in Maharashtra (Central India) often have to adopt very low settings as far as Earth Fault Protection is concerned.. e.g. for a typical 11kV feeder with connected CT ratio of 200/5A having 3 O/C and 1 E/F IDMT relay we have the adopted relay settings as follows:
    IDMT curve: 1.3 sec.
    O/C settings: Plug setting (current setting) 80%, Time Dial (TMS) setting 0.07
    E/F settings: Plug setting (current setting) 10%, Time Dial (TMS) setting 0.07
    and the Instantaneous or High Fault settings for O/C and E/F are set to 300% for both. In Numerical relays we also use the Cold Load Pickup feature in order to block the relay from mal-operating at the time of charging a feeder.
  11. CHEVITI SUDHEER
    Jan 16, 2020
    SV UNIVERSITY COLLEGE OF ENGINEERING
  12. garba mohd
    Jan 16, 2020
    I am very excited, as on a project of installing relay today.
  13. Jerry Padayhag
    Jan 16, 2020
    Thanks a lot.!
    • ariel balcos
      Jan 16, 2020
      Jerry, you know Nono Padayhag?
  14. NguyenCao Ky
    Jan 16, 2020
    Thanks so much!
  15. Davis Mwakyusa
    Jan 15, 2020
    The various articles have been very useful to me.