Home / Technical Articles / Dry-Type Transformer Installation and Ventilation Requirements
Dry-Type Transformer Installation and Ventilation Requirements (On photo dry-type transformer placed and connected)
Installation
Dry-type transformers should be installed over foundations that are properly leveled and capable to withstand their weight.
When a transformer is fitted with wheels, make sure the equipment will be equally supported on its base points in order to assure its stability and to prevent any deformation.
When installing the transformer, the following factors should be carefully taken in account:
1. There should be a minimum spacing of 0,5 m between one transformer and another, and between the transformer and any adjacent wall in order to facilitate the access for inspection and ventilation, depending, however, on the project dimensions and the voltages;
2. The room where the transformer will be installed should be well ventilated as to assure proper natural ventilation, since this is an essential parameter for a proper performance of a dry transformer.
In this regard, it is important that the air inlets are located at the front part of the transformer near the bottom and the air outlets are located at the back part of the transformer, with near the top openings large enough to allow for a circulation of approx. 2,5 cubic meters of air per minute/kW of loss. (See the example calculation below).
Proper ventilation in the transformer room will grant the expected useful life and stable operation either on continuous regime or under momentary overloads.
Natural transformer ventilation
Figure 1 – Natural transformer ventilation
As normally the natural ventilation is not sufficient, fans can be installed to increase the air flow i n the room according to Figure 2 or, preferably, adopt the refrigeration o f the room where the transformer will operate .
Danger! If the transformer room is going to be air conditioned, make sure the conditioned air will not be directly blown on the transformer, otherwise water condensation can be built on it and can result in the transformer’ s burning.
Forced transformer Room Ventilation
Figure 2 – Forced transformer Room Ventilation
To calculate the approximate size of the openings or the airflow necessary in the room the following expressions cab be used, considering a difference of 15ºC between the inlet air and the outlet air.
Approximate size of the openings or the airflow
where:
Pt = total transformer losses sinked at 115°C [kW]
S = lower opening surface [m2]
S’ = upper opening surface [m2]
H = distance measured between the middle of the height of the transformer and the middle of the upper opening for air outlet [m]
V = cooling air volume[m3/min]
Example: Installation of two 2.000 kVA dry-type transformers
  • Typical total losses PT for 2 MVA dry-type transformer at 115ºC = 27kW
  • Distance H between the middle of the transformer height and the middle of the air upper outlet opening: 1,5m
Calculated area
From the calculated area we know that the installation of forced ventilation in the room will be necessary.
The minimum flow of the fans will be:
Minimum flow of the fans
This example does not consider the presence of a protection cabinet, wich would be put in questi on in the case of a proper room for the transformer installation.
Warning! If the transformer is fitted with protective cubicle, do not replace that Box with another because its ventilation might not be enough for a proper operation of the equipment.
Reference: Instruction Manual For Dry-type Transformers – WEG
10 Comments
  1. Lesley Mahole
    Feb 17, 2024
    Hi Guys
    The formulars for determining the inlet and outlet opening surfaces are they only applicable on natural airflow, can I use them still for forced airflows
  2. Benjamin
    May 21, 2023
    Send me notificatios of new technical articles and guides
  3. Raghavan Parthasarathy
    Apr 19, 2022
    In the example, S is calculated as S=0.3*27*2/sqrt(1.5); why the factor 2 and not just S = 0.3*27/sqrt(1.5) as in the formula.
    • Lasha
      Jun 23, 2022
      Because there are 2 transformers not just one .
  4. rajput yogesh
    Feb 18, 2021
    > Can share the calculation for the enclosure IP23 Class
  5. Harshit Pant
    Apr 16, 2018
    Is there any standard or compliance for height of foundation for dry type transformer to be kept in a room?
  6. Jan
    Jan 04, 2017
    Well, you said that airflow could be “2,5 cubic meters of air per minute/kW of loss.” But fundamental question is why 2,5? Why not 2 or 3? Or 2,75? Is there some technical requirement? I am asking because I do not know about any. In IEC 61936-1:2010/Cor.1:2011 there is nothing about.
    • Vilas Tamhane
      Apr 18, 2023
      You are right. Actually you will have to calculate amount of air required to drain off the heat. You will have to assume outlet temperature of air. Then velocity will depend on this volume. Each fan can impart fixed velocity to the air or it can drain fixed amount of air. Hence velocity will depend on the type of the.fan
  7. RAMI REDDY
    Jun 10, 2015
    Good Article!
  8. Behnam Khojir
    Aug 05, 2014
    Great Article, thanks for sharing. In your example the calculation for the fresh air volume it should be 2.5 x 27 x 2 according to the text in the installation section.
Leave a Reply to Raghavan Parthasarathy
  ⁄  1  =  three