Home / Technical Articles / Performing power factor test on dry-type transformer during commissioning
Power factor test
The power factor test is a maintenance test used to determine the insulation system dielectric power loss by measuring the power angle between an applied AC voltage and the resultant current. Power factor is defined as the ratio of the power dissipated divided by the input volt-ampere multiplied by 100%.
Performing power factor test on dry-type transformer during commissioning (photo credit: sgb-smit.com)
This test may be required to be performed during the acceptance testing stage to establish a baseline reading for future test comparison.
Insulation System Equivalent Circuit and Power Factor Vector Diagram
Figure 1 – Insulation System Equivalent Circuit and Power Factor Vector Diagram
Dielectric losses in and power factor can be calculated by:
Watts = E × IT × Cosine Ө
Power factor = Cosine Ө = Watts / (E × IT)
Power factor test is performed for detecting insulation deterioration or degradation usually caused by moisture, carbonization or other forms of contaminants of the winding and bushing. Winding distortions results in a change in winding capacitance and short-circuited and partially short-circuited turns result in abnormally high excitation current.
Types of transformers that are normally subjected to the power factor test are:
  1. Two winding transformers
  2. Three winding transformer
  3. Auto-transformers
  4. Instrument transformers
Other test names synonymous with the power factor test are dielectric loss angle, dissipation factor test, tan delta or doble test.
General conditions required for testing transformers are:
  1. The unit must be de-energized and isolated from the power system including the neutral connection from ground.
  2. Transformer enclosure must be properly grounded and applicable to when testing spare units.
  3. All terminal of each winding are short-circuited together including the neutral terminals. This will minimize the effect of winding inductance
    during testing.
  4. Load tap changer (LTC) should be set of neutral if it has arrester-type elements that are not effectively short circuited in the neutral position.
The power factor test typically applies a test voltage less than the stress working levels of the equipment. Refer to Table 1.
Table 1 – Recommended power factor test voltage for dry-type power transformer connected in delta and ungrounded-wye
Winding rating
Line-to-line, kV
Test Voltage
Line-to-ground, kV
Above 14.42 and 10
12 to 14.42, 10 and at operating line-to-ground voltage
5.04 to 8.722 and 5
2.4 to 4.82
Below 2.41
Note // Transformer windings provided with neutral insulation rating which is less than the line insulation rating should be tested below the neutral insulation rating level.
The required tests are noted in Table 2 and its connection is shown in Figure 2 and Figure 3. The difference between the high voltage winding tests and the low voltage winding tests are the placement of the test leads and the test voltage levels. Test 3 and test 8 of Table 2 should generate the same value as they both measure the same capacitance between the windings.
Table 2 – Power Factor test connection for two winding dry-type transformer
Test numberTest modeEnergized windingGroundGuardUSTMeasure
1GSTHighLowCH+CHL
2GSTHighLowCH
3USTHighLowCHL
4Calculate Test 1 minus Test 2CHL
5GSTLowHighCL+CHL
6GSTLowHighCL
7USTLowHighCHL
8Calculate Test 5 minus Test 6CHL
HV winding power factor test
  1. Isolate transformer
  2. Isolate Neutral Connection
  3. Install shorting jumpers on H1, H2 and H3
  4. Install shorting jumpers on X1, X2, X3 and X0
  5. Apply Specified test voltage at ramp rate in 15 seconds
  6. Test at specified voltage for 1 minute
  7. Reduce test voltage to zero at ramp rate in 5 seconds
Power Factor High Voltage Winding Test Connection
Figure 2 – Power Factor High Voltage Winding Test Connection
LV winding power factor test
  5. Perform a GST test
  6. Perform a Guard test
  7. Perform an UST test
  8. Confirm capacitance value from GST test minus Guard test equal UST test
Power Factor Low Voltage Winding Test Connection
Figure 3 – Power Factor Low Voltage Winding Test Connection
Caution //
Always ground to the previously energized terminal with a grounding stick before making any connection changes to bleed off any electrical charge that may be present. Leave the grounding connected until connection changes is completed and before the start of the next test.
Power factor test procedure (Two winding dry-type transformer)
  1. Isolate the equipment, apply working grounds to all incoming and outgoing cables and disconnect all incoming and outgoing cables from the transformer bushing terminals. Disconnected cables should have sufficient clearance from the switchgear terminals greater that the phase spacing distance.
    Use nylon rope to hold cable away from incoming and outgoing terminals as required.
  2. Isolate the neutral bushing connection if applicable from the transformer grounding bar.
  3. Short-circuit all high voltage bushing terminals together.
  4. Short-circuit all low voltage bushing terminals and the neutral bushing terminal together.
  5. Connect the power factor test set. Refer to Table 2 for the test measuring mode and associated test number.
  6. Apply the specified test voltage levels as noted in Table 2.
  7. Record power factor and watts loss values.
  8. Repeat step 5 to 7 until all tests are completed
Table 2 -Standard kVA Ratings for Dry-Type Transformers
Single phaseThree phaseSingle phaseThree phase
263331000
395001500
5156672000
10308332500
154510003000
257512503750
3711216675000
5015025007500
752253333open-ended
1003005000
450open-ended
167500
250750
Measuring capacitance and power factor or dissipation factor
The condition of the bushings and the overall insulation of power transformers can be investigated by measuring the capacitance and dissipation factor, also known as the tangent delta, or power factor.
Aging and decomposition of the insulation, or the ingress of water, increases the losses and thus more energy is turned into heat in the insulation. The level of this dissipation is expressed by the dissipation factor or power factor.
Power factor testing
In this video you will learn about means to measure the quality of the insulation of power transformers and bushings, such as power factor or dissipation factor measurement, and measuring capacitance.
Possible causes for a reduction in insulation quality are also explained.
TanDelta/Power Factor Testing
Reference // Substation commissioning course – Dry-type transformers by Raymond Lee, Technical Trainer
  1. Hugh Garvey
    May 16, 2021
    Can you share what are typical acceptable power factor results for oil type instrument transformers and dry type instrument transformers rated for 69kv and 138kv voltages. The IEEE guidelines are not clear in terms of what the acceptable result should be especially for dry type resin encapsulated type units.
  2. Iftikhar
    Jan 03, 2020
    excellent article alongwith videos . Need some detail about how to improve energy efficiency at HV and LV levels ( Grid Station , distribution system and at home)
  3. Ezzo Abbas
    Jan 31, 2018
    oil test transformar –(25kva—–5000kva) –evry think abaut it
  4. jose
    Jul 09, 2017
    The tip-up test does not mention it in dry transformers, why?
Leave a Reply to Hugh Garvey
forty  ⁄    =  five
