Home / Technical Articles / Electrical Safety Standards for LV/MV/HV (Part-1)
Electrical Safety Standards for LV/MV/HV (on photo Indonesia's state energy giant - High Voltage Switchyard)
Content
  1. Standard: Western Power Company
  2. Standard: New Zealand Electrical Code
  3. Standard: ETSA Utilities
  4. Standard: UK Power Networks – EI 02-0019
Water Safely Clearance on Electrical Fires
VoltageMinimum distances between a nozzle producing a fog stream of fresh water and a live conductor
Up to 750 V1.5 Meter
750 V to 15 KV4.0  Meter
15 KV to 230 KV5.0 Meter
Go to Content ↑
Minimum Approach Distance for Authorized Person
This is the minimum distance that must be maintained by a person, vehicle or mobile plant.
VoltageDistance (minimum)
Up to 1 KV0.7 Meter
1 V to 6.6 KV0.7 Meter
6.6 KV to 11 KV0.7 Meter
11 KV to 22 KV0.7 Meter
22 KV to 33 KV1.0 Meter
33 KV to 66 KV1.0 Meter
66 KV to 132 KV1.2 Meter
132 KV to 220 KV1.8 Meter
220 KV to 330 KV3.0 Meter
Go to Content ↑
Minimum Approach Distance for Ordinary Person
VoltageDistance  (min)
Up to 1 KV3.0 Meter
1 V to 6.6 KV3.0 Meter
6.6 KV to 11 KV3.0 Meter
11 KV to 22 KV3.0 Meter
22 KV to 33 KV3.0 Meter
33 KV to 66 KV3.0 Meter
66 KV to 132 KV3.0 Meter
132 KV to 220 KV4.5 Meter
220 KV to 330 KV6.0 Meter
Go to Content ↑
Minimum Approach Distance for Vehicle and Plant for Ordinary Person
Mobile PlantVehicle
Up to 1 KV3.0 Meter0.6 Meter
1 V to 6.6 KV3.0 Meter0.9 Meter
6.6 KV to 11 KV3.0 Meter0.9 Meter
11 KV to 22 KV3.0 Meter0.9 Meter
22 KV to 33 KV3.0 Meter0.9 Meter
33 KV to 66 KV3.0 Meter2.1 Meter
66 KV to 132 KV3.0 Meter2.1 Meter
132 KV to 220 KV3.0 Meter2.9 Meter
220 KV to 330 KV6.0 Meter3.4 Meter
Go to Content ↑
Min. Safe Distance between Buildings and Overhead Line
VoltagePoleTower
11 kV to 33 kV2 Meter2 Meter
33 kV to 66 kV6 Meter6 Meter
66 kV and Above8 Meter8 Meter
Go to Content ↑
Min. Safe Distance for excavation near Overhead Line
Description of ClearanceFrom Pole (Min)From Tower (min)
Excavation in land more than 750mm depth8 Meter12 Meter
Excavation in land up to750mm depth2.2 to 5 Meter6 to12 Meter
Excavation in land up to 300mm depth2.2 Meter6 Meter
Construction near 11KV to 33KV Line2.2 Meter6 Meter
Construction near 33KV to 66KV Line6 Meter9  Meter
Construction near 66KV and more8 Meter12 Meter
Wire Fence near 1KV to 66KV Line2.2 Meter2.2 Meter
Wire Fence near 66KV and more5 Meter5 Meter
Go to Content ↑
Min. Safe Distance for Tower Carin near Electrical Tower
Description of ClearanceDistance (Min)
Mobile Carin movement4.0 Meter
Tower Carin movement4.0 Meter
Moving Activity above height of Tower4.0 Meter
Hedge Cutter  movement4.0 Meter
Go to Content ↑
Min. Safe Vertical Distance above Railway Track
Earthed conductors5.5 Meter
Stay wires5.5 Meter
Conductors up to 33 kV6.5 Meter
Conductors above 33 kV to 220 kV7.5 Meter
Conductors above 220 kV.8 Meter
Go to Content ↑
Min. Distance between two Conductors on Same Supports
High Voltage CircuitHigh Voltage CircuitDistance  between circuits (min)
Up to 33 KVUp to 1KV1.0 Meter
Up to 33 KVMore than 1KV1.2 Meter
33 KV to 110 KVUp to 1KV1.5 Meter
33 KV to 110 KVMore than 1KV2.0 Meter
More than 110 KVAll2.5 Meter
Go to Content ↑
Min. Distance between two Conductors on Different Supports
High Voltage CircuitDistance (min)
Up to 1 KV0.6 Meter
1 KV to 33 KV1.2 Meter
33 KV to 66 KV1.8 Meter
110 KV2.4 Meter
More than 220 KV2.8 Meter
Go to Content ↑
Min. Safety Distance from Electrical Apparatuses
Description of ClearanceDistance (min)
Passage In front of Metal-Clad Switchgear (UP to HV)1.0 Meter wide 2.5 Height
Passage In rear or side of Metal-Clad Switchgear (UP to HV)1.0 Meter wide 2.2 Height
Passage at any side of Metal-Clad Switch gear containing Bare conductor (UP to HV)0.8 Meter wide 2.2 Height
Go to Content ↑
Min. Approach Distance for Non-Competent Person near exposed Live Parts
Below 110 kV4.0 Meter
220 kV and above6.0 Meter
Go to Content ↑
Min. Approach Distance for Competent Person near exposed Live Parts
Below 1 kV0.5 Meter
11 kV1.5 Meter
22 kV2.0 Meter
33 kV2.5 Meter
66 kV3.0 Meter
110 kV4.0 Meter
Go to Content ↑
Vertical Clearances between Services
ServiceLV CableHV Cable
Common Pipe0.100 Meter0.100 Meter
Gas Pipe0.200 Meter0.200 Meter
Sewer Pipe0.300 Meter0.300 Meter
Water Pipe0.600 Meter0.600 Meter
Go to Content ↑
Horizontal Clearances between Services
Sewer Pipe1.0 Meter1.0 Meter
Go to Content ↑
Cable Installation Depths
VoltageAreaDepth (min)
Low VoltageFootways, grass verges or private property0.450 Meter
Carriageways (including road crossings)0.600 Meter
Normal agricultural land (not deep ploughing)1.0 Meter
Agricultural land subject to deep ploughing1.2 Meter
11 KV to 20 KVFootways, grass verges or private property0.600 Meter
Carriageways (including road crossings)0.750 Meter
33 KV to 132 KVFootways, grass verges or private property0.9 Meter
Carriageways (including road crossings)0.9 Meter
Auxiliary Multi-core & Multi-pair CablesFootways, grass verges or private property0.450 Meter
On Cable Ladder for LV to HVThe Horizontal clearance between cables on cable ladders2X Dia of Cable of Largest Cable or min 150 mm
The clearance from a supporting wall20 mm
The vertical clearance between cables is greater150 mm
If the number of cables > 4, they are to be installed in a horizontal
Go to Content ↑
Minimum Approach Distance of Crane or Moving Part from Live Conductor
VoltageWithout Safety ObservationFor ordinary Person
Un insulated portionsInsulated portions
Up to 1KV2 Meter1.0 Meter3.0 Meter
11 KV2 Meter1.4 Meter3.0 Meter
22 KV2.4 Meter2 Meter3.0 Meter
33 KV2.4 Meter2 Meter3.0 Meter
66 KV2.8 Meter2 Meter3.0 Meter
132 KV3.0 Meter3.0 Meter3.0 Meter
220 KV4.8 Meter4.8 Meter6.0 Meter
330 KV6.0 Meter6.0 Meter6.0 Meter
500 KV8.0 Meter8.0 Meter8.0 Meter
Go to Content ↑
Minimum Fixed Clearances for Electrical Apparatus (Isolation Points)
VoltageFixed Clearance
Up to 11Kv0.320 Meter
11KV to 33KV0.320 Meter
33KV to 66KV0.630 Meter
66KV to 132KV1.1 Meter
Go to Content ↑
Jignesh Parmar
21 Comments
  1. Jamil Jadoon
    Nov 28, 2023
    Underground 6KV cable laid 700M. I want to Lay Fiber optic cable in same cable trench kind tell as per NEC standard how much minimum space keep between MV cable and Fiber Optic cable, while both cables in parallel .
  2. Suresha KJ
    Sep 22, 2023
    It’s it’s 66kV line it should be minimum 6mtrs clearance from building, if it’s 11kV it should be minimum 3mtrs
  3. Balamurali tharan
    Oct 31, 2021
    Sir, New petrol bunk construction means 11kv and 500kv line how much distance between petrol bunk.
  4. Ravindra Kumar Kahar
    Mar 22, 2021
    My land has an overhead transmission line of 110KV. We wanted to build a house on our house but one of the overhead wire is just above the back side of the house. Is it safe to build a house in that area?
    i have head that minimum clearance for a normal person to live is 50m away from 110KV transmission line.
  5. Saeed
    Jul 09, 2019
    Need to know minimum approach distance to a MV transformer(11kv,22kv) for ordinary persons,and can a technition touch the transformer body safely.
  6. Saad
    Mar 26, 2019
    Greeting…
    i am not sure you will advise my enquiry as I saw you not answer any comments .
    could you please advise that if there are any article in BS standard mention for the clearance between MV,LV & other utilities as mention here in this informative article.
    appreciation your helpful
  7. Rajib
    Dec 31, 2018
    I am looking for a flat. 66Kv line is just 5 miters away from balcony. is it safe?
    • pawan kumar sharma
      Apr 14, 2019
      no it is not safe ,minimum distanse shoud be 8 meter
  8. Hayder
    Aug 18, 2018
    It is a great article.
    Would you please refer to the standard that you got this information from, in order to be more specific when I negotiate with others.
  9. ali
    Aug 06, 2018
    what is the distance between underground HV(11kv) and LV(415 v) cable
  10. ABDUL MOHID SHEIKH
    Apr 25, 2018
    What should be the phase to phase and circuit to circuit distance between 380kV XLPE directly buried 1C cable in flat formation?
  11. Eng. Mostafa Elsheikh
    Feb 21, 2018
    Pls, What is the distance of 66 KV – O.H.T.L from tower to another ? Thanks
  12. Geetesh
    Jan 08, 2016
    Excellent article.
    Are there any regulations in India governing safe distance for construction activities ? How are they governed.
  13. Maureen Pumulo
    Nov 13, 2015
    Good Day,
    may send us a quote for tester live line 220/330kv as soon as possible.
    And for how long can it take for us to get it?
    My Regards
    Ms pumulo
    +260966497718
  14. rajkumar panwar
    Jun 06, 2015
    Safe distance between phase to phase &phase to earth& other arrival is best arrival. thank you.
  15. P.Shreehari
    Mar 30, 2015
    In a 33 KV feeder line , at what distance isolation needs to be provided
  16. nisar ahmed
    Mar 12, 2015
    What will be the permissible distance between high voltage tower and stone quarry and crushing unit please also suggest the related laws and information thanking you
  17. Gita
    Feb 15, 2015
    Hello Mr. Parmar,
    Very informative article. What is the safe distance between a High Voltage Power grid tower and a crushing unit as per law? It will be helpful if you can point me to any related Act or article for more information.
    • Gita
      Feb 15, 2015
      By crushing unit I meant a stone quarry
  18. sanilal
    Aug 29, 2014
    Respected sir,
    i would like to know easy way to trouble shoot a series aeronautical ground lighting circuit
  19. Gamili
    Aug 26, 2014
    I am looking for the safe distance between a person sitting 8 hours per day next to a medium voltage cable 10 kv