Home / Technical Articles / Electrical Thumb Rules You MUST Follow (3)
Electrical Thumb Rules You MUST Follow (photo by megstewart via Flickr)
Continued from second part: Electrical Thumb Rules You MUST Follow (Part 2)
Size of Capacitor for Power Factor Correction
For Motor
Size of Capacitor = 1/3 Hp of Motor ( 0.12x KW of Motor)
For Transformer
< 315 KVA5% of KVA Rating
315 KVA to 1000 KVA6% of KVA Rating
>1000 KVA8% of KVA Rating
Earthing Resistance value
Earthing Resistance Value
Power Station0.5 Ω
Sub Station Major1.0 Ω
Sub Station Minor2.0 Ω
Distribution Transformer5.0 Ω
Transmission Line10 Ω
Single Isolate Earth Pit5.0 Ω
Earthing Grid0.5 Ω
As per NEC Earthing Resistance should be <5.0 Ω
Voltage Limit (As per CPWD & KEB)
Voltage Limit (As Per CPWD)
240V< 5 KW
415V<100 KVA
11KV<3  MVA
22KV<6 MVA
33KV<12 MVA
66KV<20 MVA
110KV<40 MVA
220KV>40 MVA
Voltage Variation
> 33 KV(-) 12.5% to (+) 10%
< 33 KV(-) 9% to (+) 6%
Low Voltage(-) 6% to (+) 6%
Insulation Class
InsulationTemperature
Class A105°C
Class E120°C
Class B130°C
Class F155°C
Class H180°C
Class N200°C
Standard Voltage Limit
VoltageIEC (60038)IEC (6100:3.6)Indian Elect. Rule
ELV< 50 V
LV50 V to 1 KV<=1 KV< 250 V
MV<= 35 KV250 V to 650 V
HV> 1KV<= 230 KV650 V to 33 KV
EHV> 230 KV> 33 KV
Standard Electrical Connection (As per GERC)
As per Type of Connection
ConnectionVoltage
LT Connection<=440V
HT connection440V to 66KV
EHT connection>= 66KV
As per Electrical Load Demand
Up 6W Load demand1 Phase 230V Supply
6W to 100KVA(100KW)3 Phase 440V Supply
100KVA to 2500KVA11KV,22KV,33KV
Above 2500KVA66KV
HT Connection Earthing
H.T Connection’s Earthing Strip20mmX4mm Cu. Strip
CT & PT bodies2Nos
PT Secondary1Nos
CT Secondary1Nos
I/C and O/G Cable+ Cubicle Body2Nos
Standard Meter Room Size (As per GERC)
Meter Box HeightUpper level does not beyond 1.7 meter and Lower level should not below 1.2 meter from ground.
Facing of Meter BoxMeter Box should be at front area of Building at Ground Floor.
Meter Room / Closed Shade4 meter square Size
Electrical Load as per Sq.ft Area (As per DHBVN)
Sq.ft AreaRequired Load (Connected)
< 900 Sq.ft8 KW
901 Sq.ft to 1600 Sq.ft16 KW
1601 Sq.ft to 2500 Sq.ft20 KW
> 2500 Sq.ft24 KW
For Flats :100 Sq.ft / 1 KW
For Flats USS /TC: 100 Sq.ft / 23 KVA
Contracted Load in case of High-rise Building
For Domestic Load500 watt per 100 Sq. foot of the constructed area.
For Commercial1500 watt per 100 Sq. foot of the constructed area
Other Common LoadFor lift, water lifting pump, streetlight if any, corridor/campus lighting and other common facilities, actual load shall be calculated
Staircase Light11KW/Flat Ex: 200Flat=200×11=2.2KW
Sanctioned Load for Building
Up to 50 kWThe L.T. existing mains shall be strengthened.
50 kW to 450 kW (500 kVA)11 kV existing feeders shall be extended if spare capacity is available otherwise, new 11 kV feeders shall be constructed.
450 kW to 2550 kW (3000 kVA)11 kV feeder shall be constructed from the nearest 33 kV or 110 kV substation
2550 kW to 8500 kW (10,000 kVA)33kV feeder from 33 kV or 110 kV sub station
8500 kW (10,000 kVA)110 kV feeder from nearest 110 kV or 220 kV sub-station
Jignesh Parmar
17 Comments
  1. Gorakh Doshi
    Sep 14, 2023
    Hello Sir,
    Can you explain me that thumb rule for the selection of APFCR panel Capacity in LT distribution.
  2. ismarezaazmi
    Oct 18, 2019
    Hi Sir. Can you help me with the formula on calculating motor thermal overload
  3. M.Krishnan
    Sep 01, 2019
    Hi Sir,
    Very Good Morning
    This is Krishna from Kuwait.I Want to Know about,How to calculate Voltage Drop and How to select Cable size with consider Ampere.Kindly give me a Example.
  4. vinayagamj
    Aug 07, 2018
    what will happen when i connect 300 kvar power factor correction capacitor to fully load 1500kva diesel generator (full load at 1950 amps) please help me to my mail
  5. HossamHamdy
    Mar 07, 2018
    Many mistakes inside, ,,,,
  6. VIJAY KUMAR SHARMA
    Sep 10, 2017
    THANKS FOR SPECIFICATIONS
  7. Ardelia Adair
    Jun 24, 2016
    Fantastic analysis ! I learned a lot from the details – Does someone know where my business could possibly access a blank a form version to fill in ?
  8. Anand
    Apr 11, 2016
    In voltage limit you have specified upto 100kVA i can use 415V supply and in sanction load for building you are telling for commercial building 11kV supply for 50kW – 450kW, which one is right here. If my MD is 80kVA can i still use 415V supply to avoid transformer and other high side equipments.
  9. Nitin W
    Aug 24, 2014
    Is there any thumb rule to decide total power load to be considered for commercial premises ie how much kva per sq.ft area can be taken as priliminery thumb rule.
  10. nilesh kulkarni
    May 11, 2014
    Thanks for this valuable information!!!
  11. jbuda54
    Nov 16, 2013
    @Tarekdia From a simple google search I returned the following assumptions:
    GERC = The Gujarat Electricity Regulatory Commission
    Dakshin Haryana Bijli Vitran Nigam, also known as DHBVN Limited is an Indian state owned electric utility company
  12. BG Tilak
    Nov 14, 2013
    The information, indeed is very useful. It would be much more useful, if you also indicate the corresponding code, where applicable.
  13. NParekh
    Oct 20, 2013
    In the para “Contracted Load in case of High-rise Building” there seems to be a typo error for Staircase lighting. Instead of 11KW/Flat Ex: 200Flat=200×11=2.2KW it should be 11W/Flat Ex: 200Flat=200×11=2.2KW. could you please verify?
  14. Vishnu
    Sep 23, 2013
    up to “6KW” load demand the connection should be 1phase 230V.It is “KW” not “W” .
  15. muazu
    Sep 05, 2013
    tank you very much
  16. sazali
    Sep 03, 2013
    yes, agree…because i am from malaysia, not so familiar with the short form as mention commentator above……thank you
  17. tarekdia
    Sep 02, 2013
    please write the legend for the appreviations like GERC and DHBVN
Leave a Reply to VIJAY KUMAR SHARMA