Eight rules to follow:
  1. Substation Capacity and Short Circuit Current Capacity (As per GERC)
  2. Substation Capacity and Short Circuit Current Capacity (As per Central Electricity Authority)
  3. Minimum Ground Clearance and Fault Clearing Time
  4. Busbar Ampere Rating
  5. Busbar Spacing
  6. Sound Level of Diesel Generator (ANSI 89.2 and NEMA 51.20)
  7. IR Value of Transformer
  8. Standard Size of MCB, MCCB, ELCB, RCCB, SFU and Fuse
As per GERC
Voltage Sub Station CapacityShort Circuit Current
400 KVUp to 1000 MVA40 KA  (1 to 3 Sec)
220 KVUp to 320 MVA40 KA  (1 to 3 Sec)
132 KVUp to 150 MVA32 KA  (1 to 3 Sec)
66 KVUp to 80 MVA25 KA  (1 to 3 Sec)
33 KV1.5 MVA to 5 MVA35 KA (Urban) (1 to 3 Sec)
11 KV150 KVA to 1.5 MVA25 KA (Rural) (1 to 3 Sec)
415 V6  KVA to 150 KVA10 KA  (1 to 3 Sec)
220 VUp to 6 KVA6 KA  (1 to 3 Sec)
Go back to Rules ↑
765 KV4500 MVA31.5 KA for 1 Sec
400 KV1500 MVA31.5 KA for 1 Sec
220 KV500 MVA40 KA for 1 Sec
110/132 KV150 MVA40 KA or 50 KA for 1 Sec
66 KV75 MVA40 KA or 50 KA for 1 Sec
Go back to Rules ↑
Voltage Min. Ground ClearanceFault Clear Time
400 KV8.8 Meter100 mille second
220 KV8.0 Meter120 mille second
132 KV6.1 Meter160 mille second
66 KV5.1 Meter300 mille second
33 KV3.7 Meter
11 KV2.7 Meter
Go back to Rules ↑
For Phase BusbarAluminium 130 Amp / Sq.cm or 800Amp / Sq.inch.
For Phase BusbarCopper 160 Amp / Sq.cm or 1000Amp / Sq.inch
For Neutral BusbarSame as Phase Busbar up to 200 Amp than Size of Neutral Busbar is at least half of Phase Busbar.
Go back to Rules ↑
5. Busbar Spacing
Between Phase and Earth26mm (Min)
Between Phase and Phase32mm (Min)
Busbar Support between Two Insulator250mm.
Go back to Rules ↑
KVAMax. Sound Level
<9 KVA40 DB
10 KVA to 50 KVA45 DB
51 KVA to 150 KVA50 DB
151 KVA to 300 KVA55 DB
301 KVA to 500 KVA60 DB
Go back to Rules ↑
Voltage30°C40°C50°C
>66KV600MΩ300MΩ150MΩ
22KV to 33KV500MΩ250MΩ125MΩ
6.6KV to 11KV400MΩ200MΩ100MΩ
<6.6KV200MΩ100MΩ50MΩ
415V100MΩ50MΩ20MΩ
Go back to Rules ↑
MCB, MCCB, ELCB, RCCB, SFU, Fuse – Standard Ratings
MCBUp to 63 Amp (80Amp and 100 Amp a    per Request)
MCCBUp to 1600 Amp (2000 Amp as per Request)
ACBAbove 1000 Amp
MCB Rating6A,10A,16A,20A,32A,40A,50A,63A
MCCB Rating0.5A,1A,2A,4A,6A,10A,16A,20A,32A,40A,50A,63A,80A,100A (Domestic Max 6A)
RCCB/ELCB6A,10A,16A,20A,32A,40A,50A,63A,80A,100A
Sen. of ELCB30ma (Domestic),100ma (Industrial),300ma
DPIC (Double Pole Iron Clad) main switch5A,15A,30 A for 250V
TPIC (Triple Pole Iron Clad) main switch30A, 60A, 100A, 200 A For 500 V
DPMCB5A, 10A, 16A, 32A and 63 A for 250V
TPMCCB100A,200A, 300Aand 500 A For 660 V
TPN main switch30A, 60A, 100A, 200A, 300 A For 500 V
TPNMCB16A, 32A,63A For 500 V, beyond this TPNMCCB: 100A, 200A, 300A, 500 A For 660 V
TPN Fuse Unit (Rewirable)16A,32A,63A,100A,200A
Change over switch (Off Load)32A,63A,100A,200A,300A,400A,630A,800A
SFU (Switch Fuse Unit)32A,63A,100A,125A,160A,200A,250A,315A,400A,630A
HRC Fuse TPN (Bakelite)125A,160A,200A,250A,400A.630A
HRC Fuse DPN (Bakelite)16A,32A,63A
MCB/MCCB/ELCB Termination Wire / Cable
Up to 20A MCBMax. 25 Sq.mm
20A to 63A MCBMax. 35 Sq.mm
MCCBMax. 25 Sq.mm
6A to 45A ELCB16 Sq.mm
24A to 63A ELCB35 Sq.mm
80A to 100A ELCB50 Sq.mm
Jignesh Parmar
13 Comments
  1. Praveen Kumar Yadav
    Aug 25, 2018
    What is Maximum sound level for
    1000 KVA and 1250 KVA DG Set’s
  2. NITIN
    Apr 19, 2018
    I want to install a bus bar. For total 6 rooms having 6 electric water gyser of 25 litres (2000 watt) and lighting.
    Which bus bar suits me.
    63 amp
    100 amp
  3. hari haran GKM
    Nov 21, 2017
    MCCB Max. 25 Sq.mm is it correct??
  4. Ghazanfar Ali Khan
    Nov 11, 2017
    How the maximum voltage is specified for 132-KV and 220-KV for Lightning arresters ?
    How Tertiary winding a transformer mitigate third harmonics? This question is pending since Feb.2015 to answer.
  5. uday desai
    Oct 23, 2015
    Excellent information, which will usefull in daily working.
  6. Joseph Auo
    Jul 08, 2015
    Dear Sir,
    the minimum Ground clearances to Ground for the voltages 11kV to 132kV seem to be too small. They should be 5.6 for 11kV and 22kV and 6.5 for 33kV and 6.7 for 66kV and 132kV. The condition should be @ he maximum operating temperature of 75 Deg. C.
  7. Y M Yacoob
    Jun 19, 2015
    Sorry Jignesh, I just found all the past copies, Thanks
  8. Y M Yacoob
    Jun 19, 2015
    Hello Jignesh, thank you for the very interesting info. Where can I find parts 1 ; 2 & 3 ?
  9. anuja
    Feb 20, 2015
    Its too useful n knowledgeable thanku
  10. bavya
    Dec 04, 2014
    You are a motivation for many of unsuccessful electrical engineers
  11. Manoj Badave
    Jun 02, 2014
    Hello dear,
    you have a grand collection of information, very useful one for the freshers as well as for practicing engineers
  12. hoss
    Mar 22, 2014
    Hi mr. Parmar.Please send to me your experiences via my email [email protected] regards.
  13. merksab
    Dec 01, 2013
    Excelleng
Leave a Reply to Ghazanfar Ali Khan
EEP Academy Video Courses