Home / Technical Articles / Example for Coordination of Cascaded Circuit Breakers
Inputs for Coordination Calculation
A 440 V 60 Hz switchboard feeds a 4-wire distribution board for small loads such as socket outlets. The switchboard has a fault making capacity of 100kA rms. After applying diversity factors to the loads the total load current is 90 A. Moulded case circuit breakers (MCCBs) rated at 16 A and 32 A are to be used for the loads.
Example for Coordination of Cascaded Circuit Breakers (on photo: Low voltage SIEMENS SIKUS 1600 power distribution board; credit: DirectIndustry.com)
The installation will use cables having copper conductors and XLPE insulation. The cable from the switchboard to the distribution board is 20 metres in length.
A typical load cable is 15 metres in length and will carry a current of 29 A at a power factor of 0.85 lagging.
Let’s dive into solution!
1. Choose the upstream MCCB at the switchboard and its settings
From a manufacturer’s data sheet a 125 A MCCB with an adjustable 100 A thermal release is chosen. The thermal release is set to 90 A to match the total load.
2. Choose the incoming feeder cable
From a manufacturer’s data sheet several cables can be compared for the same ambient conditions and laying arrangements. Their details are:
  • 50 mm2 cable, maximum current 124 A, R = 0.492, X = 0.110 ohms/km.
  • 70 mm2 cable, maximum current 159 A, R = 0.340, X = 0.106 ohms/km.
  • 95 mm2 cable, maximum current 193 A, R = 0.247, X = 0.093 ohms/km.
The 70 mm2 cable is chosen since the rating of the 50 mm2 cable is just too low.
Go back to Index ↑
3. Choose the downstream load MCCB and its settings
From a manufacturer’s data sheet a 32 A MCCB with an adjustable 32 A thermal release is chosen. The thermal release is set to 29 A to match its load.
4. Find the upstream fault source impedance
For a prospective symmetrical fault current of 100 kA rms the upstream fault source impedance Zup is:
Upstream fault source impedance
Go back to Index ↑
5. Find the cut-off, or let-through, current from the switchboard
From a manufacturer’s data sheet a 125 A MCCB has a let-through current Ip of 25 kA peak for a prospective fault current Is of 100 kArms.
6.  Find the impedance of the incoming cable
The impedance Zc1 of the incoming cable is:
Impedance of the incoming cable
Go back to Index ↑
7. Find the impedance of the load cable
The impedance Zc2 of the incoming cable is:
  • 6 mm2 cable, maximum current 33.8 A, R = 3.91, X = 0.130 ohms/km.
  • 10 mm2 cable, maximum current 46.7 A, R = 2.31, X = 0.126 ohms/km.
The 6 mm2 cable is chosen provisionally, since its rating is above the 32 A rating of the MCCB that feeds it.
The impedance Zc2 of the load cable is:
Impedance of the load cable
Go back to Index ↑
8. Find the fault current at the distribution board, point B
From a manufacturer’s data sheet the contact impedance data for low voltage MCCBs are:
MCCB
(Rating in Amps)
Resistance
(in Ohms)
Reactanse
(in Ohms at 60Hz)
160.01neglect
200.008neglect
250.0065neglect
320.0050.000009
500.00270.000016
630.0020.000025
800.00140.000042
1000.00110.00007
1250.00080.0001
1600.000550.00015
2000.00040.0002
2500.000290.00027
3200.00020.0004
Hence the upstream MCCB impedance Zm1 is 0.0008 + j 0.0001 ohms. Therefore the fault impedance Zfb is:
Fault impedance
The fault making current Ifb is:
Fault making current
Where Vp is the line-to-neutral voltage. Locate the point R for 26,195 A on the prospective curve in Figure 1.
Go back to Index ↑
9. Find the fault current at the beginning of the load cable, point C
Hence the downstream MCCB impedance Zm2 is 0.005+j0.000009 ohms. Add this to Zfb to give the fault impedance Zfc as:
Fault current at the beginning of the load cable
The fault making current Ifc is:
Locate the point S for 17,443 A on the prospective curve in Figure 1.
Go back to Index ↑
10. Find the fault current at the end of the load cable, point D
Coordination of MCCBs at a distribution board
Figure 1 – Coordination of MCCBs at a distribution board
Add Zc2 to Zfc to give the fault impedance Zfd as:
Fault impedance
The fault making current Ifd is:
Locate the point U for 3473 A on the prospective curve in Figure 1.
Go back to Index ↑
11. Check the peak making capacity and peak let-through capacity of the MCCBs chosen above
The following manufacturer’s data are typical for 125 A and 32 A MCCBs:
MCCB RatingMaking capacityLet-through capacity
kApeak (cut-off)
kArmskApeak
 32 A95209 ***6.0
 125 A132 290 ***25.0
*** Approximate values of the doubling factor taken to be 2.2
Hence the peak making capacity of the 32 A MCCB is well in excess of the let-through peak current of the 125 A MCCB.
Go back to Index ↑
12. Find the highest I2t value for the upstream MCCB
Locate two points P and Q on the curve of the upstream MCCB as follows,
PointCurrent in p.u.Current in AmpsTime in secondsI2t
P144066989016.0
Q60217,4500.0016487204.0
Hence I2t at P exceeds that at Q.
13. Calculate a suitable size for the load cable to satisfy the I2t duty
For XLPE cables the ‘k factor’ for the I2t is 143. The cross-sectional area A is:
Suitable size for the load cable
The next standard cross-sectional area is 10 mm2.
Go back to Index ↑
14. Calculate the volt-drop in the load cable
The usual limit to volt-drop in three-phase cables feeding static loads is 2.5% at full load.
Volt drop
Where, Iflc = 29 A, L = 15 m and φ = 54.5495 degrees. For a 6 mm2 cable the volt-drop is found to be:
Volt drop
which is well within the limit of 2.5%.
Go back to Index ↑
15. Select the largest conductor size from the above calculations
Comparing the conductor sizes found in 13. and 14. gives the larger as 10 mm2, and this size should be used. Revise the calculation of the fault current IfdThe impedance Zc2 of the load cable is:
Impedance Zc2
Fault impedance
Go back to Index ↑
16. Plot the results
The results are plotted in Figure 1.
Refrence // Switchgear and Motor Control Centres – Handbook of Electrical Engineering: For Practitioners in the Oil, Gas and Petrochemical Industry by Alan L. Sheldrake (Download here)
  1. Ismail
    Jul 22, 2015
    Hello, just a small question, in the introduction the main cable size is given as 20m so why was it used as 25m to calculate the impedance in number 6 ?
Leave a Reply to Ismail
ninety  ⁄    =  15