Home / Technical Articles / Example On How To Design a Low Voltage Switchboard
Low voltage switchboard construction
This technical article has the aim of helping the panel builder and the designer in the construction of ABB SACE ArTu low voltage switchboard. To this purpose, starting from the single-line diagram of a plant, it is possible to arrive – by selecting the suitable components – to the construction of an switchboard and to the relevant declaration of conformity with the Std. IEC 61439-2.
Example On How To Design a Low Voltage Switchboard (on photo: LV switchboard type 'MNS')
Characteristics of the low voltage switchboard, according to the specification:
  • “not separated” switchboard;
  • IP 65;
  • exposed wall-mounted.
Single-line diagram of LV switchgear
Figure 1 – Single-line diagram of LV switchgear
Single-line diagram
Let us suppose that realization of a main distribution switchboard is required, to be placed immediately on the load side of a 2000kVA MV/LV transformer. Three 850A outgoing feeders from this switchboard supply other distribution switchboard, but they are not dealt with.
Due to reasons of selectivity with other circuit breakers of switchboards on the load side, air circuit breakers have been chosen branched from the busbars. The main distribution busbar short-circuit current is 48 kA.
Selection of the circuit breakers and of the conductors external to the switchboard
Circuit breakers //
As shown in the single-line diagram, the circuit breakers chosen are:
  • 1 pc. of Emax E3N3200 PR121/P-LSI In 3200 (main circuit breaker of the switchboard QF1);
  • 3 pcs. of Emax E1N1250 PR121/P-LSI In 1250 (circuit breakers for the three outgoing feeders QF2, QF3, QF4).
Conductors //
  • Incoming, from the transformer:
    – 1 bus duct with Iz = 3150 A; L = 5 m
  • Outgoing from the switchboard, hypothesizing overhead installation on perforated trays, there are three low voltage cables:
    – 1 cable L = 20m 3 x (3 x 120) Iz = 876,3 A;
    – 1 cable L = 70m 3 x (3 x 120) Iz = 876,3 A;
    – 1 cable L = 100m 3 x (3 x 120) Iz = 876,3 A.
Switchboard front, distribution system and metalwork structure
With regard to the positioning of the equipment, it has been decided to locate the main circuit breaker in one column, and the three outgoing feeders in another one. Since the power supply comes from below, it has been decided to position the circuit breaker QF1 at the bottom.
The switchboard assembly is of “not-separated” type. A possible layout of the busbars and of the circuit breakers is shown in the following figure:
LV switchgear construction and devices
Figure 2 – LV switchgear construction and devices
Distribution system //
As regards the busbars inside the switchboard, by first approximation, they are selected according to the size of the circuit breaker:
Main distribution busbar system
Circuit breaker QF1
(From the “Distribution Switchgear – General catalogue”)
BA2000 In=3200 A (IP65); Icw max =100 kA
To get an Icw value suitable to the short-circuit current of the plant:
– 5 busbar holders PB3201 at a maximum distance of 425mm (Icw=50 kA) must be positioned.
Busbar holder 3200A - PB3201
Busbar holder 3200A – PB3201
Being in the presence of non-current limiting air circuit breakers, the Icw value of the distribution system shall be higher than the prospective Icp at the busbars.
Branch busbars of the circuit breakers
Circuit breakers QF2, QF3, QF4
BA1250 In= 1250 A (IP65) Icw max = 75 kA
1250A busbar
1250A busbar
– 5 busbar holders PB1601 at a maximum distance of 425mm (Icw=50 kA) must be positioned.
Busbar holder PB1601, max. 1600A
Joining pieces between circuit breakers and busbars
(circuit breakers QF2, QF3, QF4)
Table 11.2 of clause 11.4 of the Technical Application Paper shows the cross-sectional areas of the busbars for the connection of the circuit breakers:
  • E3N323200 – A cross-sectional area 3 x (100 x 10)
  • E1N121250 – A cross-sectional area 1 x (80 x 10)
Cross-sectional areas of the busbars for the connection of the circuit-breakers
Table 11.2 of clause 11.4 of the Technical Application Paper: Cross-sectional areas of the busbars for the connection of the circuit breakers
Moreover, according to the terminal types, the maximum anchoring distance of the first anchor plate, shown at clause11.3 of the Technical Application Paper, shall be respected.
Clause 11.3 - Emax air circuit breakers an example of the maximum distance in mm (D)
Clause 11.3 – Emax air circuit breakers an example of the maximum distance in mm (D) at which the first. Anchor plate of the busbars connecting to the circuitbreaker shall be positioned according to the type of terminal and making reference to the highest admissible value of short-circuit current and of its relevant peak.
Joints for busbars //
As indicated in the “Distribution switchgear. General catalogue” the following joints are necessary:
  • Joint from 3200 busbar to 3200 busbar, T joint, AD1073
  • Joint from 3200 busbar to 1250 busbar, AD1078
Busbar connection joints
Earthing busbar //
As shown on page 44 and 45 of this technical Application Paper, the earthing busbar shall have a minimum cross-sectional area equal to 1⁄4 of the cross-section of the main busbars. Therefore a bar 50×10 has been chosen.
Minimum cross-section of the corresponding protective conductor
Metalwork structure
As regards the metalwork structure, an ArTu K series switchboard with door (IP 65) is used. In order to house the circuit breakers, the vertical busbar system and the outgoing cables the following is used:
  • 2 columns for the circuit breakers;
  • 2 cable containers, one for the busbar system and one for the outgoing cables.
For a correct selection of the structure it is advisable to consult the “Distribution switchgear. General catalogue” where:
  • to house Emax E1-E2-E3 circuit breakers a switchboard assembly with 800mm depth and 600mm width and one installation kit KE3215 are required.
Kits for installing Emax circuit-breakers X1-E1-E2-E3-E4
Kits for installing Emax circuit breakers X1-E1-E2-E3-E4
The cable container has obviously 800mm depth and 300mm width. In the general catalogue for distribution switchgear the fixing crosspieces for busbars with shaped section can be found:
  • For the 3200 A horizontal busbars (BA2000) the selected type of installation is number 5, for which the correct choice is two components TV6221 and one TV8011;
  • For the 3200 A vertical busbars (BA2000) the selected type of installation is number 2, for which the correct choice is TV8101 component;
  • For the 1250 A horizontal busbars (BA1250) the selected type of installation is number 5, for which the correct choice is two components TV6221 and one TV8011.
Busbar horizontal at any height
Busbar horizontal at any height – TV6221 (24 DIN mod W=600mm), TV8011
As specified in the general catalogue for distribution switchgear, the metalwork structure shall be completed by the side-by-side kits (AD1014).
Completed by the side-by-side kits (AD1014)
References //
  1. Guidelines to the construction of a low-voltage assembly complying with the Standards IEC 61439 Part 1 and Part 2 – ABB
  2. Distribution switchgear General catalogue // ArTu K – ABB
25 Comments
  1. Hüseyin Güzel
    Aug 10, 2019
    Thanks Mr. Edvard
  2. alejandro markarian
    Aug 10, 2019
    There are a free software ABB-DOC, for construction switchhboard ABB- ARTU, I use that for my jobs.
  3. Mohammed salem
    Aug 10, 2019
    Thanks lot for the article it is well explained and informative can Ihave a copy on my mail direct.
    Thanks,
  4. Amita kumari
    Jul 03, 2019
    Thank you sir ,
    Can you share me 11kv & 33kv TD article on my mail.
  5. mohammed yousif
    Mar 07, 2019
    thank you
  6. khaled abdel rahman
    Jul 09, 2018
    Its very good effort please keep with.
  7. Makmun
    Jul 09, 2018
    Thank you Edvard, can i get the article by email
  8. Rogelio
    Jul 06, 2018
    thanks Edvard so Could you share this information by email?
  9. Bor
    Aug 25, 2017
    Need some advise I have a PFC bank when it engages the banks instead of improving power factor of the system it drops what could be the problem CT position is correct and right size
  10. mohammad
    Dec 12, 2016
    thank you for all
  11. Simon Oyuu egoriat
    Jul 18, 2016
    Thank you very much Edvard for such a well elaborated and educative article. Iwas requesting if possible if I get a soft copy of your articles direct on my email.