Home / Technical Articles / My practical experience in the electrical protection system of industrial generators
Estimated Study Time: 15 minutes
Detect, discriminate & disconnect fault
A functional protection system installed, commissioned, and maintained on critical equipment like an industrial generator is of high importance. As such, every protection system must have the ability to: accurately detect, discriminate and isolate, and timely disconnect any fault.
My practical experience in the electrical protection system of industrial generators (photo credit: EEP)
Each of the named ability that protection system must-have can be described in a sentence:
  1. Detect: Accurately pick-up any abnormal fault condition in the electrical network.
  2. Discriminate: Isolate abnormal electrical conditions from a point (i.e., circuit breaker or switchgear) closest to the fault location.
  3. Disconnect: Clear fault conditions by the timely disconnection of abnormal circuits to limit the extent of prospective damage to equipment and personnel to a level that is as low as reasonably practicable.
The scope of this technical article is limited to the best practices of electrical protection systems as applied in industrial generator sets. Compulsory protection schemes and a case-study of a successful troubleshooting effort on a generator protection system will be discussed.
Table of contents:
  1. Components of an electrical protection system
    1. Power supply
    2. Sensors
    3. Logic
    4. Output
  2. Compulsory protection schemes for industrial generator-sets
    1. Overcurrent protection
      1. Instantaneous overcurrent protection (ANSI Code 50)
      2. Timed overcurrent (ANSI Code 51)
  3. Case Study
    2. Timed overcurrent protection
    3. Undervoltage and overvoltage protection (ANSI 27 and 59)
    4. Synchronization protection (ANSI 25)
    5. Differential protection (ANSI Code 87)
  4. My troubleshooting experience
A reliable protection system must comprise of the following components which are pre-selected and configured to achieve a protection philosophy that is well suited for its intended application. They are:
Ezeala Winner - Author at EEP-Electrical Engineering Portal
Ezeala Winner
I'm an electrical and controls engineer with core strengths in electrical protection and PLC-based control systems. My excellent performance in design, commissioning, maintenance, and troubleshooting of HV/LV switchboard controls and power equipment positions me as a valuable asset to an industrial environment.
Profile: Ezeala Winner