Synchronization to the grid

Any power plant commissioning, from small industrial GTG (Gas-To-Gasoline) to nuclear facility, will converge to a very final step before (provisional) commercial operation, sometimes empathized as “first kW”: synchronization to the local or national grid. This is in fact a very critical phase of the installation, where mistakes in pre-commissioning or forced control variables to bypass that last permissive prevention to close the main MV breaker can easily lead to a disaster.

My experience in the first synchronization of the MV generator in an industrial plant
My experience in the first synchronization of the MV generator in an industrial plant (original photo by Francesco Becattini)

As common sense would suggest, synchronization of generator and grid implies that three key parameters of the two waveforms match within a certain window:

  1. Frequency
  2. Voltage
  3. Phase Angle

This condition is verified by a synchro check device, that may be integrated in the main IED protecting the generator as ANSI 25C function and obtained acting on governor and AVR either manually or via an automatic synchronization card, that will send the closing command to the MV switchgear control circuitry finally closing the main circuit breaker (52G).


Check on instrumentation and protection

Before initiating the synchronization sequence, regardless of the fact that all factory test reports, pre-commissioning, and commissioning certificates are available a final check of proper protective functions in the live condition is due.

To perform this key activity all the instrumentation connected to the protection relay including VT via (possibly) primary and secondary injection, and CT via polarity test must be rechecked. Obviously, all other subsystems including prime mover and driven skid shall be fully commissioned, hardwired control loops checked (with special focus on trip signals), communication (soft link) established.

All panels including the MV Switchgear station and excitation panel (AVR) shall be energized and ready.

Open circuit tests will be conducted at first possibly opening the earth switch (89) to test if it has been inserted for safety reasons, checking the expected behavior of voltage and frequency (ANSI 27, 59, and 81) trips, in accordance to the actions listed in the trip matrix, that may include apart from open breaker command lockout relay engage (either electromechanical or logical) and other actions.

In phase 2 earth switch is closed to start the short circuit tests, which will imply a soft ramping of excitation current and measuring armature currents at different field excitation current. An ANSI 87 (differential) protection is simulated changing the ratio of one CT.

In this phase, both proper excitation system functioning and actions of a differential system that is one of the cornerstone protections will usually trigger both a prime mover trip and a fast de-excitation of the generator.

Commissioning live tests on protective system
Figure 1 – Commissioning live tests on the protective system

Phase 3 will involve an unbalance of the three-phase system connecting to the ground one of the phases and obviously removing the shorting link, in this way 51G and 67N protection (via toroidal or ZCT) will be tested.

Phase 4 will finally check the phase sense of rotation after back feeding the system (closing 52G breaker after opening the star point link), phasor visualization of a digital protective relay will help to check that rotation is coherent. Finally, voltage waveforms (usually phase to phase, e.g. U to V secondaries) to synchro check system and automatic synchronization system are measured and visualized.

Now the synchronization system has all the inputs (and a working protective relay as a backup in case of troubles) to interconnect our system to the grid.


Voltage and frequency

Grid frequency is usually a very stable parameter, and definitely, it will be during a plant synchronization (you don’t want to connect a new unit to the grid during a thunderstorm!). For historical reasons, two main values coexist, 50Hz and 60Hz, and prime mover, usually after being duly commissioned, has no trouble reaching the revolutions per minute needed to match the grid value.

Matching the voltages is on the contrary a little trickier. For MV applications in fact it is unpractical to have a direct measuring of the voltage, a potential transformer (PT or VT) is hence interposed and readings are hence affected by the ratio and performance of the two devices used to measure the voltage upstream and downstream the breaker object of the synchronization.

Typical front commands of synchronization panel
Figure 2 – Typical front commands of synchronization panel

Since usually, the upstream VT is part of an existing MV equipment, unless the plant is totally a greenfield installation, accuracy versus the device downstream the (possibly new) MV breaker may differ significantly. The secondary value may differ, e.g. in Europe, the industry-standard moved from 100V line to line to 110V line to line during last year and upstream voltage may be affected by a tap changer position of an upstream transformer, possibly in a part of the plant that is not accessible for a CHP or other continuous cycle production plant.

Although standard pre-commissioning checks, in the particular primary injection of VT and reading of the measured voltages on the control panel, will help to prevent these errors, a very dangerous (as we will see also for the phasor angle displacement) is a potential double mistake that will make the system look like (not only to the operator but also to digital synchro check devices) ready to synchronize.

What will happen e.g. if the VT upstream is marked on the schematics as brand new 110V secondary, while actually is still the old 100V device and at the same time the upstream transformer tap changer is not in null position but it is raising the busbar voltage of exactly +10% (e.g. due to plant need, e.g. some operator may have acted on the tap to compensate a reactive power compensator bank temporary offline)?

In this scenario, you may have perfectly adjusted the automatic synchronizer and synchro check, but there is no possibility to avoid a breaker closure that will trigger a massive reactive power flow from the grid since the actual voltage difference is way above the permitted delta.

Typical generator capability (P-Q) curve, x-axis differentiates under and overexcited operation
Figure 3 – Typical generator capability (P-Q) curve, x-axis differentiates under and overexcited operation (click to expand)

In this scenario either the AVR increases the field (excitation) current, which is unlikely since due to the above double mistake the AVR is not aware to be in under excited state… and to increase field current will be against the overexcitation limiter logics, or a trip will happen.

Since you are affecting the reactive power flow from the grid this trip may occur at grid breaker level, that is what you do not what to experience in a CHP installation since a full outage will take hours to recover, apart from the mechanical stresses on the machines (especially a brand new prime mover like a gas turbine) due to a sudden trip.

Note that for this phase of the installation the current measuring (again via a current transformer or CT, being unpractical to directly measure a current of possibly thousands of Amps) is far less critical, even in case polarity has not been correctly tested, the typical trouble you will experience is a differential (ANSI 87) protection fault after synchronizing since relay will see a negative current flowing. In some way, you will experience solid testing of that fundamental protection.

Another source of trouble is the fact that due to cost considerations sometimes there is not a VT immediately upstream and downstream the breaker you have to synchronize, especially when a step-up transformer is included in the plant.

While voltage could be easily compensated via a different primary to secondary VT ratio, assuming that no tap-changer is installed, either on load or off-load, there is a more hidden risk associated with a transformer insertion. The Vector group of typical Dyn11 equipment will in fact add a 30° displacement between upstream and downstream waveforms.

Membership Upgrade Required

This content is not available in your premium membership plan. Please upgrade your plan in order to access this content. You can choose an annually based Basic, Pro, or Enterprise membership plan. Subscribe and enjoy studying specialized technical articles, online video courses, electrical engineering guides, and papers.

With EEP’s premium membership, you get additional essence that enhances your knowledge and experience in low- medium- and high-voltage engineering fields.

Good to know: – Save 50% on all video courses with Enterprise plan.

Upgrade

Already a member? Log in here

Premium Membership

Get access to premium HV/MV/LV technical articles, electrical engineering guides, research studies and much more! It helps you to shape up your technical skills in your everyday life as an electrical engineer.
More Information
Marco Bruschini - Author at EEP-Electrical Engineering Portal

Marco Bruschini

Chartered engineer with +10y of experience in electrical rotating and static equipment engineering procurement and installation, for renewables (hydroelectric) and natural gas plants. industrial and O&G markets (onshore and offshore). Genuine interest for energy transition and electrification, with a focus on integration of new energy sources in national grid and digitalization of control system and plant automation, including remote diagnostic.
Profile: Marco Bruschini

Leave a Comment

Tell us what you're thinking. We care about your opinion! Please keep in mind that comments are moderated and rel="nofollow" is in use. So, please do not use a spammy keyword or a domain as your name, or it will be deleted. Let's have a professional and meaningful conversation instead. Thanks for dropping by!

Learn How to Design Power Systems

Learn to design LV/MV/HV power systems through professional video courses. Lifetime access. Enjoy learning!

EEP Hand-Crafted Video Courses

Check more than a hundred hand-crafted video courses and learn from experienced engineers. Lifetime access included.
Experience matters. Premium membership gives you an opportunity to study specialized technical articles, online video courses, electrical engineering guides, and papers written by experienced electrical engineers.
Whitepaper: How to Improve Risk Decisions for Power Systems - Prioritizing vulnerabilities with full operational context