Home / Technical Articles / Eight fuse characteristics you must consider when designing protection circuits
Always reliable fuses…
Fuses were the first type of protection to be used, and they still have a place in numerous applications. Although they do not have the flexibility of adjustment and resetting capacity of a circuit breaker, they are nevertheless reliable, high performance devices in terms of their ability to break very high short-circuit currents.
The fuse cartridge is inserted in the circuit to be protected. If there is an overcurrent, the circuit is broken automatically by fusing of the conductive fuse element, which is specially rated, inside the cartridge.
The silica in the body of the cartridge absorbs very high energies by fusing and vitrification. Unlike a circuit breaker, the fuse cartridge is destroyed by the fault and must be replaced. Fuse cartridges comply with standard IEC 60269-1. They come in various shapes and sizes. In low voltage electrical installations cylindrical cartridges and blade type cartridges are mainly used, with ratings ranging from 0.5-1250 A.
Fuse cartridges are fitted in isolating switches, fuse carriers or simply on bases.
Table of contents:
  1. Fuse Type
  2. Rated Currents and Voltages
  3. Conventional Non-fusing And Fusing Currents
  4. Fuse Operating Zone
  5. Breaking Capacity
  6. Limitation Curve
  7. Limited Thermal Stress
  8. Selectivity
  9. Cylindrical cartridge fuses gG and aM types
  10. Blade cartridge fuses gG and aM types
Fuse characteristics
1. Fuse type
Fuses are identified by 2 letters, according to their application category. In low voltage installations gG and aM fuses are mainly used.
gG cartridges
gG cartridges are for general use and they protect the circuits against low and high overloads and, of course, against short circuits. gG cartridges are marked in black.
aM cartridges
aM cartridges are used with electric motors and they protect against high overloads and short circuits. They are calculated to resist certain temporary overloads (starting a motor).
These cartridges must therefore be used together with a thermal protection device to protect against low overloads. aM cartridges are marked in green.
Go back to Contents Table ↑
2. Rated currents and voltages
The rated current can cross a fuse indefinitely, without triggering either fusing or any excessive temperature rise. The rated voltage is the voltage at which this fuse can be used. Let’s explain the meanings of the letters used for the application categories.
Fuse ratings (example)
Figure 1 – Fuse ratings (example)
The first letter indicates the main operation:
  • a (associated) – The fuse must be associated with another protection device, because it cannot break faults below a specified level. It provides short-circuit protection only.
  • g (general) – It breaks all faults between the lowest fusing current (even if it takes 1 hour to melt the fuse elements) and the breaking capacity. It provides short-circuit and overload protection.
The second letter indicates the category of equipment to be protected:
  • G = Protection of cables and conductors
  • M = Protection of motor circuits
  • R = Protection of semiconductors
  • S = Protection of semiconductors
  • Tr = Protection of transformers
  • N = Protection of conductors according to North American standards
  • D = Time-delay fuse for protecting motor circuits according to North American standards
You should differentiate two conventional currents: non-fusing and fusing.
Conventional non-fusing current (Inf) – This is the current value that the fuse cartridge can withstand for a conventional time without melting.
Conventional fusing current (If) – This is the current value that causes the fuse cartridge to fuse before the conventional time has elapsed.
Ratings
(A)
Inf
Non-fusing current
If
Fusing current
t
Conventional time
In ≤ 41.5 In2.1 In1 h
4 < In ≤ 101.5 In1.9 In1 h
10 < In ≤ 251.4 In1.75 In1 h
25 < In ≤ 631.3 In1.6 In1 h
63 < In ≤ 1001.3 In1.6 In2 h
100 < In ≤ 1601.2 In1.6 In2 h
160 < In ≤ 4001.2 In1.6 In3 h
400 < In1.2 In1.6 In4 h
Fusing time / Fault current
Figure 2 – Fusing time / Fault current
In the above example (100 A gG cartridge):
  • Conventional time = 2 h
  • Inf = 1.3
  • If = 1.6 In
4. Operating zone
The operating zone defined by the standards is used to determine the operating time of the fuse according to the current crossing it. It is important to know the operating characteristics of the fuse in order to calculate the discrimination of the various protective devices installed in series.
Fuse operating zone
Figure 3 – Fuse operating zone
For a 100 A, 22 × 58 gG cartridge, an overload of 300 A will melt the cartridge in 40 s.
The breaking capacity must be at least equal to the prospective short-circuit current that may occur at the point at which the fuse is installed. The higher the breaking capacity, the more capable the fuse of protecting the installation against high intensity short circuits.
HBC (High Breaking Capacity) fuses limit short circuits that could reach more than 100 000 A rms.
6. Limitation Curve
The limitation of the current can vary according to the conditions of the short circuit (intensity, cos ϕ, short-circuit starting angle ψ). The limitation curves of cartridges represent the maximum limited current values that can be achieved under the most unfavourable conditions.
Example
For a prospective short circuit of 10 000 A rms (or 10 kA rms) in view of the maximum asymmetry of the current, the short circuit could reach a theoretical maximum value of 2.5 × Irms, i.e. 25 kA peak.
Fuse limitation curve
Figure 4 – Fuse limitation curve
The 100 A gG cylindrical fuse cartridge limits the first current wave to 8 000 A peak, i.e. approximately 30% of the prospective maximum value. The destructive electrodynamic effects are therefore reduced by a factor of 10 ( (8 000/25 000)2) of the maximum value.
The higher the prospective short-circuit current, the higher the limitation ratio. For example for a 100 000 A rms short circuit, i.e. 250 000 A peak, the 100 A gG cartridge limits this current to 15 000 A peak, i.e. limitation to 6% of the prospective maximum current and limitation to 0.36% of the prospective maximum electrodynamic effects.
Importance of the limitation capacity
A short circuit is dangerous, both in terms of its electrodynamic effects and its thermal effects:
The destructive electrodynamic effects depend on the square of the peak current reached during the short circuit, and cause mechanical damage to the insulation of the conductors.
The destructive thermal effects depend on the thermal energy dissipated during the short circuit, and could burn the insulation of the conductors. Fuse cartridges limit both these effects as much as possible.
Planning and installation of the low voltage switchgear – The devil is in the detail!
A short circuit triggers the release of a considerable amount of energy. The fuse cartridge limits this energy to a much lower value, conventionally known as the limited thermal stress, expressed in A2s.
Why must the thermal stress be limited?
If the energy released by the short circuit is not limited, it can quickly lead to total or partial destruction of the installation. Thermal stress is governed by two main parameters:
  • Cos ϕ: the lower this is, the greater the energy
  • Voltage: the higher the voltage, the greater the energy
Fuse cartridges significantly limit this energy. For example, for a 10 kA rms asymmetrical short circuit at 230 V, cos ϕ = 0.1, would develop if there were no cartridge, on several current waves. For the first wave only, the thermal stress could reach 4 000 000 A2s. Under the same fault conditions, a 100 A gG cartridge would limit the thermal stress to 78 000 A2s, i.e. 1.95% of the value on the first wave of the prospective current only.
Difference between pre-arcing and arcing thermal stresses
A fuse breaks a short circuit in two stages: pre-arcing, then arcing. Let’s say a word about each stage:
The pre-arcing thermal stress corresponds to the minimum energy necessary for the fuse element of the cartridge to start melting. It is important to know this thermal stress in order to determine the selectivity on a short circuit between several protection systems in series.
The arcing thermal stress corresponds to the energy limited between the end of pre-arcing and total breaking.
Figure 5 – Difference between pre-arcing and arcing thermal stresses
The sum of the arcing and pre-arcing thermal stresses gives the total thermal stress.
Total thermal stress
Figure 6 – Total thermal stress
8. Selectivity
A current generally crosses a number of protection devices in series. These devices are calculated and distributed according to the various circuits to be protected. There is selectivity when only the device protecting the faulty circuit operates.
Example
Only the 25 A cartridge has operated on a fault occurring on the line it is protecting. If the 100 A cartridge, or even the 400 A cartridge, had also operated (incorrect selectivity), the whole installation would have gone down.
An example of fuse selectivity
Figure 7 – An example of fuse selectivity
Rupture capacity curves
Rupture capacity curves for cylindrical cartridge fuses gG and aM types
Figure 8 – Rupture capacity curves for cylindrical cartridge fuses gG and aM types (click to expand)
Thermal stress (∫i2dt)
Thermal stress (∫i2dt) for cylindrical cartridge fuses gG and aM types
Figure 9 – Thermal stress (∫i2dt) for cylindrical cartridge fuses gG and aM types (click to expand)
Limitation curves
Limitation curves for cylindrical cartridge fuses gG and aM types
Figure 10 – Limitation curves for cylindrical cartridge fuses gG and aM types (click to expand)
Rupture capacity curves for blade cartridge fuses gG and aM types
Figure 11 – Rupture capacity curves for blade cartridge fuses gG and aM types (click to expand)
Thermal stress (∫i2dt) for blade cartridge fuses gG and aM types
Figure 12 – Thermal stress (∫i2dt) for blade cartridge fuses gG and aM types (click to expand)
Limitation curves
Limitation curves for blade cartridge fuses gG and aM types
Figure 13 – Limitation curves for blade cartridge fuses gG and aM types (click to expand)
Source: Breaking and protection devices by Legrand
  1. V S DEVANNA
    Jun 24, 2022
    I have been in Electrical maintenance activities for two decades and i felt my ignorance on type of curves to be verified for Fuses .
    Thank you very much for the clear cut explanation of their functioning.
  2. Edward
    Sep 22, 2020
    I want to learn
  3. Abieku Grant
    Sep 17, 2020
    Very interesting insight of how select a cartridge fuses. Good work done
  4. Olusiji Banjo, CEng
    Sep 16, 2020
    Edvard, THIS IS AN ARTICLE PER EXCELLENCE.
Leave a Reply to Olusiji Banjo, CEng
seven  ⁄    =  7
