Commissioning Challenges

Commissioning of a power plant or an industrial plant is not that simple, on contrary, it’s full of hidden traps and logical challenges. In power plants, the generating units are substantial operational blocks, tested individually alongside the water or fuel pathways (input) and the electrical route from low-voltage switchgear to the high-voltage switchyard (output), in conjunction with the unit services and operational controls simultaneously. Station services are usually commissioned independently.

Blind Spots in Power Plant Commissioning: What You’re Overlooking
Blind Spots in Power Plant Commissioning: What You’re Overlooking (photo credit: Mohammad Aljohani vi Linkedin)

On the other hand, the facility operating system can be divided into smaller subsystems, such as crushing and milling, which can be precommissioned and commissioned independently.

Extreme caution is required at all times by anyone operating the equipment during testing and commissioning to prevent the accidental activation of circuit-breakers, disconnectors, motors, etc. Serious harm can be inflicted by released tensioned springs, rotating shafts, levers, and similar devices.

Consideration of the possibility of shocks and injuries caused by falling from ladders, etc., is also necessary.

Disconnecting electrically operated equipment’s control circuits and, if feasible, mechanically securing it helps prevent accidents like these.

Table of Contents:

  1. Precommissioning Activities:
    1. Secondary Injection to CTs & PTs Circuits
    2. Circuit Breakers (Drawn-in, Test and Drawn-out Conditions)
    3. Testing Cable Wiring
    4. Testing Transformer Oil
  2. Wet and Dry Commissioning:
    1. Primary Injection
  3. Checking the Reliability of Power Plant Systems (CR)
  4. Power Plant Grid Tests
  5. Commissioning Reports
  6. Attachment (PDF) 🔗 Download ‘Power Plant Commissioning Guide’

1. Precommissioning Activities

The precommissioning and commissioning of an industrial or power plant are distinct tasks. They must be treated differently, especially if the facility systems are totally automated.

Precommissioning involves the testing of equipment, including switchgear, Motor Control Centres (MCC), Variable Frequency Drives (VFD), and transformers, individually in an energized condition, while completely isolated from other operational equipment.

1.1 Secondary Injection to CTs & PTs Circuits

Meggering and high-pot testing of the switchgear are the initial steps. Next, in accordance with the protective relay setting sheets for every circuit breaker, the protective relays are tested by secondary injection (simulation) to trip the breakers caused by overloads or undervoltages.

The circuits of protective current transformers (CTs) and potential transformers (PTs) are supplied to the tester to simulate the operational condition.

A three-phase tester, depicted in Figure 1, conducts the secondary injection.

Figure 1 – Secondary injection test kit

Secondary injection test kit
Figure 4 – Secondary injection test kit

Go back to Content Table ↑


1.2 Circuit Breakers (Drawn-in, Test and Drawn-out Conditions)

Each circuit breaker in the switchgear can be tested for operation in its drawn-in (actually connected), test, and withdrawn (disengaged) positions. The switchgear is de-energized; however, the circuit breakers remain operable due to the electrically powered 125 V DC control circuits, enabling their functionality.

Additionally, an additional control circuit operating at 24 V AC or DC may be utilized for remote operation and communication with the plant control system. In each of the three positions, the switchgear and circuit breaker make their presence known and marked.

In the withdrawn state, one may test the breaker to charge the activating spring and to open or close without impacting the other breakers in the panel. The breaker test position is a half-drawn-out position. This position allows for comprehensive testing of the breaker in all control and interlock aspects, without impacting other components of the switchgear assembly. In the connected position (drawn-in), the breaker can be thoroughly checked if the incoming and tie breakers have been locked and maintained in a withdrawn position.

The test position is extremely helpful during the commissioning (energized) phase of plant testing that occurs prior to precommissioning.

Comparable precommissioning actions are conducted on MCCs for each motor or feeder circuit to facilitate the energization of the assembly and to supply power to motors and feeders for further testing. Each motor is being adjusted to synchronize its rotation with that of the pumps or conveyor movements, etc. The motors are decoupled from the pumps for this task.

Additionally, the motor branch circuit breakers undergo pretesting to determine their minimum instantaneous protection settings appropriate for the motor inrush currents.

Figure 2 – Technician drawing out the VCB trolley for testing

Technician drawing out the VCB trolley for troubleshooting
Figure 2 – Technician drawing out the VCB trolley for testing

Go back to Content Table ↑


1.3 Testing Cable Wiring

Extensive simulations will be necessary during precommissioning to evaluate the equipment and cable wiring. This requires bridging the connections and applying voltage or current from other sources to control the operation of the switchgear breakers or motor control center starters. All wiring and schematics of field devices and hardwired safety interlocks must be verified.

Wiring diagrams were previously verified during the precommissioning phase; however, they are now increasingly uncommon as they become outdated.

Wiring diagrams have been significantly simplified through the utilization of communication channels, including Ethernet, DeviceNet, Modbus, and others. The newest schematics have all the terminals labeled identically to the previously used wiring diagrams.

It appears to be a prevailing trend currently. While not yet evident in all industrial projects, it is undeniably a trend in large power plants.

Membership Upgrade Required

This content is not available in your premium membership plan. Please upgrade your plan in order to access this content. You can choose an annually based Basic, Pro, or Enterprise membership plan. Subscribe and enjoy studying specialized technical articles, online video courses, electrical engineering guides, and papers.

With EEP’s premium membership, you get additional essence that enhances your knowledge and experience in low- medium- and high-voltage engineering fields.

Good to know: – Save 50% on all video courses with Enterprise plan.

Upgrade

Already a member? Log in here

Premium Membership

Get access to premium HV/MV/LV technical articles, electrical engineering guides, research studies and much more! It helps you to shape up your technical skills in your everyday life as an electrical engineer.
More Information
Edvard Csanyi - Author at EEP-Electrical Engineering Portal

Edvard Csanyi

Hi, I'm an electrical engineer, programmer and founder of EEP - Electrical Engineering Portal. I worked twelve years at Schneider Electric in the position of technical support for low- and medium-voltage projects and the design of busbar trunking systems.

I'm highly specialized in the design of LV/MV switchgear and low-voltage, high-power busbar trunking (<6300A) in substations, commercial buildings and industry facilities. I'm also a professional in AutoCAD programming.

Profile: Edvard Csanyi

Leave a Comment

Tell us what you're thinking. We care about your opinion! Please keep in mind that comments are moderated and rel="nofollow" is in use. So, please do not use a spammy keyword or a domain as your name, or it will be deleted. Let's have a professional and meaningful conversation instead. Thanks for dropping by!

Learn How to Design Power Systems

Learn to design LV/MV/HV power systems through professional video courses. Lifetime access. Enjoy learning!

EEP Hand-Crafted Video Courses

Check more than a hundred hand-crafted video courses and learn from experienced engineers. Lifetime access included.
Experience matters. Premium membership gives you an opportunity to study specialized technical articles, online video courses, electrical engineering guides, and papers written by experienced electrical engineers.
Whitepaper: How to Improve Risk Decisions for Power Systems - Prioritizing vulnerabilities with full operational context