Save 15% on Pro Premium Plan with discount code: UX226 (expires on July 31, 2021). Study specialized LV/MV/HV technical articles and papers.
Home / Technical Articles / How to calculate voltage regulation of distribution line
Voltage regulation
  1. Introduction to voltage regulation
  2. Voltage Regulation for 11KV, 22KV, 33KV Overhead Line
  3. Permissible Voltage Regulation (As per REC)
  4. Voltage Regulation Values
  5. Required Size of Capacitor
  6. Optimum location of capacitors
  7. Voltage Rise due to Capacitor installation
  8. Calculate % Voltage Regulation of Distribution Line
How to calculate voltage regulation of distribution line (on photo: Distribution Lines – Oaxaca, Mexico, 2013 via FlickR)
Voltage (load) regulation is to maintain a fixed voltage under different load.Voltage regulation is limiting factor to decide the size of either conductor or type of insulation.
In circuit current need to be lower than this in order to keep the voltage drop within permissible values. The high voltage circuit should be carried as far as possible so that the secondary circuit have small voltage drop.
Go to Content ↑
% Voltage Regulation = (1.06 x P x L x PF) / (LDF x RC x DF)
P – Total Power in KVA
L –  Total Length of Line from Power Sending to Power Receiving in KM.
PF – Power Factor in p.u
RC – Regulation Constant (KVA-KM) per 1% drop.
RC = (KV x KV x 10) / ( RCosΦ + XSinΦ)
LDF – Load Distribution Factor.
LDF = 2 for uniformly distributed Load on Feeder.
LDF > 2 If Load is skewed toward the Power Transformer.
LDF = 1 To 2 If Load is skewed toward the Tail end of Feeder.
DF – Diversity Factor in p.u
Go to Content ↑
Maximum  Voltage Regulation at any Point of Distribution Line
Part of Distribution SystemUrban Area (%)Suburban Area (%)Rural Area (%)
Up to Transformer2.52.52.5
Up to Secondary  Main320.0
Up to Service Drop0.50.50.5
Total6.05.03.0
Go to Content ↑
The voltage variations in 33 kV and 11kV feeders should not exceed the following limits at the farthest end under peak load conditions and normal system operation regime.
  • Above 33kV (-) 12.5% to (+) 10%.
  • Up to 33kV (-) 9.0% to (+) 6.0%.
  • Low voltage (-) 6.0% to (+) 6.0%
In case it is difficult to achieve the desired voltage especially in Rural areas, then 11/0.433 kV distribution transformers(in place of normal 11/0.4 kV DT’s) may be used in these areas.
Go to Content ↑
Size of capacitor for improvement of the Power Factor from Cos ø1 to Cos ø2 is:
Required size of Capacitor (Kvar) = KVA1 (Sin ø1 – [Cos ø1 / Cos ø2] x Sin ø2)
Where KVA1 is Original KVA.
Go to Content ↑
L = [1 – (KVARC / 2 KVARL) x (2n – 1)]
L – distance in per unit along the line from sub-station.
KVARC – Size of capacitor bank
KVARL – KVAR loading of line
n – relative position of capacitor bank along the feeder from sub-station if the total capacitance is to be divided into more than one Bank along the line. If all capacitance is put in one Bank than values of n=1.
Go to Content ↑
Voltage Rise due to Capacitor installation:
% Voltage Rise = (KVAR(Cap) x Lx X) / 10 x Vx2
KVAR (Cap) – Capacitor KVAR
X – Reactance per phase
L – Length of Line (mile)
V – Phase to phase voltage in kilovolts
Go to Content ↑
Calculate Voltage drop and % Voltage Regulation at Trail end of following 11 KV Distribution system:
  • System have ACSR DOG Conductor (AI 6/4.72, GI7/1.57)
  • Current Capacity of ACSR Conductor = 205Amp,
  • Resistance = 0.2792Ω and Reactance = 0 Ω,
Permissible limit of % Voltage Regulation at Trail end is 5%.
Calculate percentage of Voltage Regulation of Distribution Line
Method-1 (Distance Base)
Voltage Drop  = ( (√3x(RCosΦ+XSinΦ)x I ) / (No of Conductor/Phase x1000))x Length of Line
Voltage drop at Load A
  • Load Current at Point A (I) = KW / 1.732xVoltxP.F
  • Load Current at Point A (I) =1500 / 1.732x11000x0.8 = 98 Amp.
  • Required No of conductor / Phase =98 / 205 =0.47 Amp =1 No
  • Voltage Drop at Point A = ( (√3x(RCosΦ+XSinΦ)xI ) / (No of Conductor/Phase x1000))x Length of Line
  • Voltage Drop at Point A =((1.732x (0.272×0.8+0×0.6)x98) / 1×1000)x1500) = 57 Volt
  • Receiving end Voltage at Point A = Sending end Volt-Voltage Drop= (1100-57) = 10943 Volt.
  • % Voltage Regulation at Point A = ((Sending end Volt-Receiving end Volt) / Receiving end Volt) x100
  • % Voltage Regulation at Point A = ((11000-10943) / 10943 )x100 = 0.52%
  • % Voltage Regulation at Point A =0.52 %
Voltage drop at Load B
  • Load Current at Point B (I) = KW / 1.732xVoltxP.F
  • Load Current at Point B (I) =1800 / 1.732x11000x0.8 = 118 Amp.
  • Distance from source= 1500+1800=3300 Meter.
  • Voltage Drop at Point B = ( (√3x(RCosΦ+XSinΦ)xI ) / (No of Conductor/Phase x1000))x Length of Line
  • Voltage Drop at Point B =((1.732x (0.272×0.8+0×0.6)x98) / 1×1000)x3300) = 266 Volt
  • Receiving end Voltage at Point B = Sending end Volt-Voltage Drop= (1100-266) = 10734 Volt.
  • % Voltage Regulation at Point B= ((Sending end Volt-Receiving end Volt) / Receiving end Volt) x100
  • % Voltage Regulation at Point B= ((11000-10734) / 10734 )x100 = 2.48%
  • % Voltage Regulation at Point B =2.48 %
Voltage drop at Load C
  • Load Current at Point C (I) = KW / 1.732xVoltxP.F
  • Load Current at Point C (I) =2000 / 1.732x11000x0.8 = 131 Amp
  • Distance from source= 1500+1800+2000=5300 Meter.
  • Voltage Drop at Point C = ( (√3x(RCosΦ+XSinΦ)xI ) / (No of Conductor/Phase x1000))x Length of Line
  • Voltage Drop at Point C =((1.732x (0.272×0.8+0×0.6)x98) / 1×1000)x5300) = 269 Volt
  • Receiving end Voltage at Point C = Sending end Volt-Voltage Drop= (1100-269) = 10731 Volt.
  • % Voltage Regulation at Point C= ((Sending end Volt-Receiving end Volt) / Receiving end Volt) x100
  • % Voltage Regulation at Point C= ((11000-10731) / 10731 )x100 = 2.51%
  • % Voltage Regulation at Point C =2.51 %
Here Trail end Point % Voltage Regulation is 2.51% which is in permissible limit.
Go to Content ↑
Method-2 (Load Base)
% Voltage Regulation =(I x (RcosǾ+XsinǾ)x Length ) / No of Cond.per Phase xV (P-N))x100
  • Distance from source= 1.500 Km.
  • Voltage Drop at Point A = (I x (RcosǾ+XsinǾ)x Length ) / V (Phase-Neutral))x100
  • Voltage Drop at Point A =((98x(0.272×0.8+0×0.6)x1.5) / 1×6351) = 0.52%
  • Distance from source= 1500+1800=3.3Km.
  • Required No of conductor / Phase =118 / 205 =0.57 Amp =1 No
  • Voltage Drop at Point B = (I x (RcosǾ+XsinǾ)x Length ) / V (Phase-Neutral))x100
  • Voltage Drop at Point B =((118x(0.272×0.8+0×0.6)x3.3)/1×6351) = 1.36%
  • % Voltage Regulation at Point A =1.36 %
  • Load Current at Point C (I) =2000 / 1.732x11000x0.8 = 131Amp.
  • Distance from source= 1500+1800+2000=5.3Km.
  • Required No of conductor / Phase =131/205 =0.64 Amp =1 No
  • Voltage Drop at Point C = (I x (RcosǾ+XsinǾ)x Length ) / V (Phase-Neutral))x100
  • Voltage Drop at Point C =((131x(0.272×0.8+0×0.6)x5.3)/1×6351) = 2.44%
  • % Voltage Regulation at Point A =2.44 %
Here Trail end Point % Voltage Regulation is 2.44% which is in permissible limit.
Go to Content ↑
Jignesh Parmar
25 Comments
  1. Bukar
    May 25, 2021
    I want to design a 33kV single circuit radiating using 100mm AAC from a 60MVA 132/33kV to a distance of 140km.
    I have the problem of controlling the Voltage Regulation of this 33kV line.
  2. ozi
    Dec 02, 2020
    how do I determine the capacity of voltage regulator to use on the secondary side [11kV] of a transformer which is 15MVA capacity
  3. Ajay gothwal
    Sep 15, 2020
    Sir what is VR constant of dog conductor
  4. Mokhoele Mahao
    Jan 07, 2020
    Good day,
    1. If I am pulling the 5600 MVA @ 0.98 PF on 11kV system and the distance from main sub to my MV sub is around 1.5KM what size of voltage regulators do I need to install to balance my incoming voltage to the plant
  5. Ghazanfar Ali Khan
    Aug 01, 2017
    How 3rd harmonics are mitigated in tertiary winding, delta connected.
    The answer is pending since 2015. Why no body has turned back with a comprehensive reply,including Jignesh Parmar.
  6. NP Singh
    Feb 08, 2017
    One 11 KV HT line feeder is required to provide power supply to the sub divided 85 Nos. industrial plots. Though these plots are not yet sold but considering the futuristic requirement of the power supply of the individual plot holder, an electrification scheme is required to be passed from DHBVN as it is technically not feasible to get power supply from the DHBVN. The total minimum load as per the norms of the dhbvn is 3915 kv, hence we need to apply for the sanctioning of the load. Could anyone suggest, how the demand factor / diversification factor is taken and what would be the load required for applying.
    As per my calculation the load is : 3910 divided by 0.9 = 4344 kva
    Demand factor would = 3910 x .625 = 2443.75 kva or 2.45 mva approx.
    Request confirm whether the demand factor 0.625 will be divided or multiplied to get the total load?
  7. Engr. Ghazanfar Ali Khan
    Oct 01, 2016
    How third harmonics are mitigated by tertiary winding?
  8. Narendrasinh Desai
    Aug 05, 2016
    sir
    i am working in Electricity Department Silvassa. recently i have made calculation as per above method which is as under . kindly guide me is it true?
    A
    66/11KV Athal s/s end Load 250KVA=225KW at PF.-09
    • System have ACSR DOG Conductor (AI 6/4.72, GI7/1.57) ATHAL FEEDER II
    • Current Capacity of ACSR Conductor = 300Amp,
    Load at point A=250KVA
    Taking P.F-0.9 of system factor
    Load =250 X 0.9=225KW
    Length of Load Point from Athal S/s=1.5KM=1500Mtr
    Method- (Distance Base)
    • Load Current at Point A (I) =225 / 1.732x11000x0.99 = 13.12 Amp.
    • Required No of conductor / Phase =13.12 / 300 =0.044 Amp =1 No
    • Voltage Drop at Point A =((1.732x (0.272×0.99+0×0.141)x13.12) / 1×1000)x1500) = 9.21 Volt
    • Receiving end Voltage at Point A = Sending end Volt-Voltage Drop= (11000-9.21) = 10990.79 Volt.
    • % Voltage Regulation at Point A = ((11000-10990.79) / 10990.79 )x100 = 0.084%
    • % Voltage Regulation at Point A =0.084 %