Transformer Performance Ratings
Assuming that you have a general understanding of transformer parameters and IEC Standards in use, this technical article is aimed at providing a variety of tools and data to make an educated assessment of the principal transformer performance ratings.
Derived from transformer design tools, curves, formulae, etc., this technical article should allow the reader to produce a credible estimate of a potential transformer’performances characteristics, including weights ond dimensions, losses, magnetizing currents, relative variations in impedance across the tapping range, and a basic estimation of sound level.
It should be emphasized that this is on educated estimate.
  1. Sizing Transformer Power Definition:
    1. Transformers with More Than Two Windings
    2. Aufotransformers with Tertiary Windings
    3. Transformers with Taps
    4. Phase-Shifting Transformers (PSTs)
  2. Transformer Mass Estimation:
    1. Transport Mass
    2. On Site Mass
    3. Oil Mass
  3. Transformer Dimensions Estimation:
    1. Transport Dimensions
    2. On Site Dimensions:
      1. ONAF Cooled with Tank Mounted Radiators
      2. Cooling Having Separate Radiator Bank
      3. ODAF Cooled Based on Air Blast Coolers
      4. ODWF Cooled Based on Water Coolers
    3. Clearances for Cooling Purposes:
      1. Clearance to Walls for Transformers Having Cooling with Radiators
      2. Clearance to Walls for Transformers Having Cooling with Air Blast Coolers
  4. Transformer Losses and No-Load Current:
    1. Typical Load and No-Load Losses
    2. Typical No-Load Current
    3. Typical Inrush Current
    4. Typical Cooling Losses
  5. Transformer Impedances:
    1. Preferred Impedances
    2. Variation of Impedance Across Tapping Range
    3. Effects of Impedance Variation
  6. Estimation of Transformer Sound Levels:
    1. No-Load Sound Level
    2. Load Sound Level
  7. Attachment (PDF) 🔗 Download ‘Transformer Design and Calculations Handbook’
The prescribed way of defining the throughput capabitity of a transformer is to use the rated power. This rated power is well defined in the standards and is one of the main parameters of sizing a transformer. However, this essential parameter does not always give a clear identification of the physical size of the transformer.
In order to overcome this particular difficulty, it has becomea well known practice in the transformer industry to introduce a sizing power definition, which better determines the physical size of the unit in “Sizing MVA“.
This “SizingMVA” not only is a more meaningful indicator of the physical weight and dimensions but is also better correlated to the man-hours required to manufacture the unit and to its price.
As an initial demonstration of the application, reference is made to the simplest feasible transformer, which has only two windings and neither winding is provided with tappings. In this simple case, the rated power of each of the separate windings is equal to the transformer rated power.
The higher voltage (HV) winding is dimensioned to carry the rated load (Sn MVA) and the same applies to the lower voltage (LV) winding. In other words the transformer has two windings each designed to have the number of turns and conductor cross-sectional area for Sn MVA rated power.
Its Sizing MVA (Ssizing) is defined as half the sum of the rated powers of all windings i.e. (Sn+ Sn)/2 which in this case equals Sn.
The simple case sets the base for other more interesting applications. For instance, applying this sizing definition to a simple shunt reactor of 100 MVAr containing only one winding of 100 MVA capability, leads to the conclusion that its sizing power is only (100 + 0) MVA / 2 = 50 Sizing MVA.
Most types of transformers have two or more windings, for example; autotransformers, transformers with a tapping winding, and phase-shifting transformers.
This technical article will givethe basic calculations of the physical transformer sizea nd use this to develop assessments of other parameters for the main types of transformers that are normally encountered.
Watch Lesson – Transformer MVA sizing
1.1 Transformers with More Than Two Windings
Applying the definition given aboveto a transformer having 3 windings, we havefor example:
  • Rated power of high voltagewinding (SHV) = 100 MVA
  • Rated power of low voltage winding (SLV) = 100 MVA
  • Ratedpower of tertiary winding (STV) = 30 MVA
  • Ssizing = (SHV+ SLV+ STV) / 2
  • Ssizing = (100 MVA + 100 MVA + 30 MVA) / 2
  • Ssizing = 115 SizingMVA
1.2 Autotransformers with Tertiary Windings
A two winding auto-transformer has a winding that is common to both the HV and LV circuits and so all of the power is not actually transformed. It is necessary,in this instance,to correct the rated power to a transformed power before adding the effect of the Tertiary.
As an example we see:
  • Rated Power of high voltage winding (SHV)= 100 MVA
  • Voltage of high voltage winding (UHV) = 400 kV
  • Rated Power of low voltage winding (SLV)= 100 MVA
  • Voltage of low voltage winding (ULV)= 1l0 kV
  • Rated Power of tertiary winding (STV) = 30 MVA
  • Voltage of tertiary winding (UTV) = 13 kV (does not affect the calculation)
  • Ssizing = (2 × (1 − ULV/UHV) × SHV + STV) / 2
  • Ssizing = (2 × (1 − 110kV/400kV) × 100 MVA + 30 MVA) / 2
  • Ssizing = 87.5 SizingMVA
Further Study – Transformers in plant power distribution: The bigger picture
1.3 Transformers with Taps
As an example, we consider a transformer with 2 windings and with a tapping (regulating) winding on the high voltage side. The rating must be corrected to take into account the highest values of both voltage and current that are applicable to any tapping.
  • Rated power of high voltage winding (SHV) = 100 MVA
  • Tapping range of the HVwinding is (Rpos) positive 12% and.(Rneg) negative 12%
  • Rated power of the untapped low voltage winding (SLV) = 100 MVA
  • Ssizing = (SHV × [(1 + Rpos) / (1 − Rneg)] + SLV)  / 2
  • Ssizing = (100 MVA × [(1 + 0.12) / (1 − 0.12)] + 100 MVA)  / 2
  • Ssizing = 113.6 SizingMVA
Learn more – What is a Load Tap Changer (LTC)?
1.4 Phase-Shifting Transformers (PSTs)
The RatedEquivalentSizingMVAis calculatedas follows:
√3 × Rated Voltage between Lines × Line Amps × function (No-Load PhaseAngle)
where function (No-Load PhaseAngle) is determined in a number of ways, dependant upon the type of Phase-Shifting Transformer required
See Figures 1, 2 and 3.
NOTE: The value of √3 is the phase factor that is appropriate to a 3-phase system in which line values are used to define voltage and current ratings. For single-phase units, it is usual to refer to phase values and the phase factor is therefore 1.
Figure 1 – Vector diagram for assymetrical phase shifting transformer (PST)
Vector diagram for assymetrical phase-shifting transformer (PST)
Figure 2 – Vector diagram for symmetrical phase shifting transformer (PST)
Figure 3 – Vector diagram for hexagonal connection phase shifting transformer
Vector diagram for hexagonal connection phase shifting transformer (PST)
Figure 3 – Vector diagram for hexagonal connection phase shifting transformer (PST)
The actual masses relating to a transformer depend upon a wide range of specified requirements, such as transformer type, cooling types, cooler location, loss capitalization rates, impedance, transportation or site access constraints, mounting inside an enclosure, and, to some extent, on the relative costs of the active part materials
Long before the transformer design has been completed, however, it is often convenien to make estimations of key weights for planning or cross-checking  purposes. Only the final complete design can take into account all of the many specified requirements, but a selection of curves covering some key parameter estimations are presentedin this article.
Some mass differences exist between 50 and 60 Hz transformers, because for the same flux density the 50Hz transformer core has a larger cross-sectional area and hence a greater mass than a 60 Hz core.
This characteristic has an effect on all masses: transport, on site and oil masses.
Despite the mass differences between 50 and 60Hz transformers, the variance on the dimensionsis of second order effect in comparison with the variances due to capitalization rates, cooler type etc.
2.1 Transport Mass
The first of these key parameters is the mass of the heaviest package, which is usually the active part enclosed within the tank. The figure below provides estimates of typical transport masses of this heaviest part based upon the SizingMVA as derived in Section 3.1above.
When using this curve (Figure 4), cognizance must be given to the fact that more onerous transport constraints will probably give rise to a lighter package than indicated here.
On the other hand, a transformer that has very high capitalization cost values will probably be heavier than the curve might show.
Of course, if knowledge of another transformer having a rating within about 150%, the same general specification, similar impedance, and similar capitalization rates exists, extrapolation to the new designis possible by plotting the known point on the graph and drawing a new curve parallel with that shown in the figure.
Figure 4 – Typical variation of transport mass with SizingMVA
2.2 On Site Mass
Another parameter that is of considerable interest at the planning stage is the total site mass of the complete transformer, shown in Figure 5.
Knowledge of this parameter, even considering a limited range of validity as exlained in the opening remarks of Section 2 (Transformer Mass Estimation), will permit some initial estimates to be made in terms of plinth strength.