Home / Technical Articles / IEC and NEMA/IEEE ratings of current transformers (CTs) in medium voltage applications
Metering and protection purpose
First, let’s remind ourselves of the basics in a few sentences. That is something you must know. A current transformer (CT) is designed to produce a secondary current which is accurately proportional to the primary current. It consists of a single primary winding, which an external busbar or cable runs through, or it can have a single primary bar, brought out to two ends for termination.
IEC and NEMA ratings of current transformers (CTs) for a medium voltage switchgear
IEC and NEMA ratings of current transformers (CTs) for a medium voltage switchgear (photo credit: Energie Technik Becker GmbH)
A medium voltage current transformer can have up to three independent secondary winding sets. The entire current transformer assembly is encapsulated in resin, inside an insulated casing. Current transformers are used for metering or protection purposes.
The accuracy class and size depends on the individual application – for example, revenue metering would use high accuracy metering CTs.
Just to note, it’s very important to never leave the secondary winding of a CT open circuit. This creates extremely high voltages which pose a real danger to personnel.
Ok, let’s get on the IEC and later NEMA ratings of a current transformer. Some rating explanations have exercises and real examples, which I hope it will help for better understanding.
  1. IEC  ratings of current transformer
    1. Rated primary current
    2. Rated secondary current: Isr
    3. Transformer ratio: Kn
    4. Rated thermal short-time withstand current: Ith (kA)
    5. Overcurrent coefficient: Ksi
    6. Rated primary circuit voltage: Up (kV)
    7. Rated frequency
    8. Rated real output power (VA)
      1. Exercises
    9. Metering class CT
    10. Protection class CT
      1. Example
    11. Selection of current transformers
      1. Exercise to select appropriate CTs
        1. Exercise #1
        2. Exercise #2
        3. Exercise #3
  2. NEMA/IEEE ratings of current transformer
    1. Accuracy class
    2. Class rating
    3. Burden
    4. Examples
1. IEC Ratings
1.1 Rated primary current: Ipr (A)
The primary current rating of a CT must be greater than the expected maximum operating current it is monitoring.
Metering CT’s primary current rating should not exceed 1.5 times the maximum operating current. Protection CT’s primary current rating needs to be chosen so that the protection pick-up level is attained during a fault.
Standard values for Ipr are: 10, 12.5, 15, 20, 25, 30, 40, 50, 60, 75 A, and decimal multiples of these values (source: IEC 60044-1)
1.2 Rated secondary current: Isr
The secondary current rating of a CT is either 1 A or 5 A. CTs with a 5 A secondary rating are becoming less common as more CT driven equipment becomes digital. For long secondary cable runs, CTs with 1 A secondary windings can minimize the transformer and secondary cable size.
1.3 Transformer ratio: Kn
This is the ratio of secondary to primary winding turns: Kn = Ns/Np = Ipr/Isr
Current transformer nameplate
Figure 1 – Current transformer nameplate
1.4 Rated thermal short-time withstand current: Ith (kA)
This is the highest level of rms primary fault current which the CT can endure, both thermally and dynamically, for 1 second without damage. When used in a medium voltage enclosure, the Ith rating should match the short-time withstand rating of the entire switchgear.
1.5 Overcurrent coefficient: Ksi
This is the ratio of a CT’s short-time withstand current rating to its primary current rating:
Ksi = Ith/Ipr
This coefficient indicates how difficult it would be to manufacture a CT. A higher coefficient means a physically larger CT, which is more difficult to manufacture.
  • If Ksi < 100 it’s easy to manufacture
  • If Ksi 100 ~ 500 it’s difficult to manufacture, with certain limitations
  • If Ksi > 500 it’s  extremely difficult to manufacture
1.6 Rated primary circuit voltage: Up (kV)
The primary circuit voltage rating indicates the level on insulation provided by the CT. If a ring type CT is installed around a cable or bushing, the insulation level can be provided by the cable or bushing.
Rated primary voltage
Upr (kV)
Suitable operation range
U (kV)
Power frequency withstand voltage
(kV) rms for 1 minute
Lightning impulse withstand voltage
(kV) peak, 1.2/50μs
7.233-7.22060
126-122875
17.510-17.53895
2412-2450125
3620-3670170
Source: IEC 62271-1
1.7 Rated frequency: fr (Hz)
This rating must match the system’s operating frequency. Standard frequencies are 50 Hz and 60 Hz. It’s very important to be cautios, because a 50 Hz CT can be used on a 60 Hz system, but a 60 Hz CT cannot be used on a 50 Hz system.
1.8 Rated real output power (VA)
The maximum power a CT secondary can deliver, to guarantee its accuracy and performance. The total sum VA (including cable, connectors and load) must not exceed the rated real output power of the CT. Standard values are: 1, 2.5, 5, 10, 15 VA.
Cable burden can be calculated the following way: VAcable = k × L/S, where:
  • k = 0.44 for 5 A secondary, = 0.0176 for 1 A secondary
  • L = total feed/return length of cable (m)
  • S = cross sectional area of copper cable (mm2)
Metering instrument burden:
  • Metering instrument (digital) = 1 VA (approx.)
  • Metering instrument (electromagnetic or induction) = 3 VA (approx.)
  • Transducer (self powered) = 3 VA (approx.)
Protection instrument burden:
  • Protection instrument (digital) = 1 VA (approx.)
  • Protection instrument (electromagnetic overcurrent) = 3-10 VA (approx.)
Medium voltage current transformers
Figure 2 – Medium voltage current transformers
1.8.1 Exercises
Exercise #1 – A CT with a 1 A secondary is connected to an electromagnetic ammeter located 10 m away, using 2.5 mm2 copper cable.
Calculate the minimum required VA rating of the CT.
  • VAcable = k × L/S = 0.0176 × 20/2.5 = 0.14 VA
  • VAammeter = 3 VA
  • VAtotal = 0.14 + 3 = 3.14 VA
The total burden is 3.14 VA. Use a 5 VA CT.
Exercise #2 – A CT with a 5 A secondary is connected to a digital protection relay located 2 m away, using 1.5 mm2 copper cable.
  • VAcable = k × L/S = 0.44 × 4/1.5 = 1.17 VA
  • VAammeter = 1 VA
  • VAtotal = 1.17 + 1 = 2.17 VA
The total burden is 2.17 VA. Use a 2.5 VA CT.
1.9 Metering class
A metering class indicates the accuracy of the CT secondary current at 5 to 125% of rated primary current. Above this level, the CT starts to saturate and the secondary current is clipped to protect the inputs of a connected metering instrument.
  • General metering CT would use a metering class CL 0.5 – 1.0
  • Revenue metering CT would use a metering class CL 0.2 – 0.5
Operating range for metering class current transformer
Figure 3 – Operating range for metering class current transformer
  1. Saturation
  2. Linear operating range, at accuracy class tolerance
1.10 Protection class CT
A protection class CT provides a linear transformation of the primary to secondary current at high overload levels. This characteristic makes them suitable for use with overcurrent protection relays.
A relay trip setting is normally 10~15 times the maximum load current and this level should fall on the linear part of the CT secondary current curve. If a CT saturates before the relay trip level is reached, the fault will remain undetected, leading to equipment damage and serious danger to personnel.
The most commonly used protection class is a 5PX, where X is the accuracy limit factor (ALF) or multiplication factor of the rated primary current. The secondary current is +/-1% accurate at rated primary current and +/-5% accurate at X times rated primary current.
Typical protection class CT ratings are 5P10, 5P15, 5P20.
Operating range for protection class current transformer
Figure 4 – Operating range for protection class current transformer
  1. Saturation
  3. Ideal protection setting trip zone 50%~100% ALF
1.10.1 Example
A 200/1 A CT has a protection class rating of 5P15. The secondary current is guaranteed to be linear up to 15 times the rated primary current. The secondary current will be 1 A (+/-1%) at 200 A primary current and 15 A (+/-5%) at 3000 A primary current.
For guaranteed operation, any overcurrent trip setting should be between 7.5 ~ 15 A secondary current.
1.11 Selection of current transformers
The main considerations for selecting a CT are the primary and secondary current ratio, real output power rating (VA) and accuracy class. Secondary selection considerations are rated primary voltage, frequency and thermal short-time withstand current.
1.11.1 Primary and secondary current ratio
SourceRated primary current Ipr (A)
Incomer from transformerIpr ≥ 1.0-1.25 of nominal source current
Feeder to transformerIpr ≥ 1.0-1.25 of transformer’s rated primary current
Feeder to motorIpr ≥ 1.0-1.5 of motor full load current
Feeder to capacitor bankIpr ≥ 1.3-1.5 of nominal capacitor current
Rated secondary current: Isr (A)
  • Use 1 A and 5 A for local installation
  • Use 1 A for remote installation
1.11.2 Real output power (VA)
The real output rating of the CT must be the next highest nominal size above the expected total burden on the CT secondary. Total burden is the sum of output cable, connectors and instruments.
1.11.3 Class type
Use a metering class CT for metering and indication. A higher class CT gives greater accuracy between the primary and secondary currents.
Use a 5PX protection class CT for current based protection relay inputs. The ALF must be selected so that the relay trip point lies on the linear part of the secondary current curve, between 50% and 100% of the ALF.
1.11.4 Exercise
Select appropriate CTs for the following transformer incomer and feeder circuits.
Example transformer incomer and feeder for selection of appropriate CTs
Figure 5 – Example transformer incomer and feeder for selection of appropriate CTs
1. Transformer Incomer:
  • MV/MV transformer (TXR1): 5 MVA, 36/11 kV, 10% Z
  • Instantaneous overcurrent trip setting = 15 × In for digital protection relay (OC1) driven off CT1-2
  • Electromagnetic ammeter (A) is driven off CT1-1
2.Transformer Feeder:
  • MV/LV transformer (TXR2): 2 MVA, 11/0.4 kV, 5% Z
  • Instantaneous overcurrent trip setting = 10 × In for digital protection relay (OC2) driven off CT2
Exercise 1 – Metering CT1-1 for transformer incomer circuit:
Step 1 – Calculate transformer TXR1 nominal secondary current: In (A)
  • In = S/(√3 × U) = 5000/(√3 × 11) = 262 A
  • The secondary current for TXR1 is 262 A
Step 2 – Calculated max. expected short circuit current at CT1 installation: Isc (A)
  • Ignoring any power cable or busbar impedances:
  • Isc = In × 100/Z = 262 × 100/10 = 2620 A
  • The maximum expected short circuit current at CT1 is 2620 A
Step 3 – Select metering CT1-1 ratings:
  • Primary rated current: Ipr = (1.0-1.25) × In = (1.0-1.25) × 262 A
    Use a rating of 300 A
  • Secondary rated current: Isr
    Use a rating of 1 A
  • Short-time withstand rating: Ith ≥ Isc
    Use a rating of 10 kA
  • Primary circuit voltage: Up ≥ U
    Use a rating of 12 kV
  • Real output power: Typically > 3 VA for electromagnetic type meter
    Use 5 VA (this allows 2 VA for cable burden, etc.)
  • Accuracy Class
    Use Class 1.0 (common class for general metering)
Exercise 2 –  Protection CT1-2 for transformer incomer circuit:
Step 1 – Select ratings common to both the metering and protection CTs
  • Primary/secondary rated current: Use 300/1 A
  • Short-time withstand rating [Ith]: Use 10 kA rating
  • Primary circuit voltage [Up]: Use 12 kV rating
Step 2 – Select real output power
  • Real output power: typically > 1VA for digital type protection relay
  • Use 2.5 VA (this allows 1.5 VA for cable burden, etc.)
Step 3 – Calculate protection class 5PX
  • The instantaneous trip current level of protection relay OC1 is set to 15 × In.
  • ITRIP = 15 × 262 = 3930 A (primary current)
Note: In most digital protection relays, the trip current levels are set with respect to the secondary current. In this case
  • ISEC = 3900/300 × 1 = 13.1 A
  • The instantaneous trip current level for the CT secondary is 13.1 A
The trip current level should fall between 100 to 50% of the accuracy limit factor (ALF). Using an ALF of 10 (5P10), the trip current level of 3930 A falls outside the range 100% to 50% ALF, so a 5P10 protection class CT is not suitable.
  • 100%(ALF) = 1.0 × 10 × 300 = 3000 A
  • 50%(ALF) = 0.5 × 10 × 300 = 1500 A
We may notice that 1500 ≤ 3930 ≥ 3000 A. Using an ALF of 15 (5P15), the trip current level of 3930 A falls within the range 100% to 50% ALF so a 5P15 protection class CT is suitable.
  • 100%(ALF) = 1.0 × 15 × 300 = 4500 A
  • 50%(ALF) = 0.5 × 15 × 300 = 2250 A
We may notice that 2250 ≤ 3930 ≤ 4500 A. Use protection class 5P15
Exercise 3 –  Protection CT2 for transformer feeder circuit:
Step 1 – Calculate transformer TXR2 nominal primary current: In (A)
  • In = S/(√3 × U) = 2000/(√3 × 11) = 105 A
  • The primary current for TXR2 is 105 A
Step 2 – Calculated maximum expected short circuit current at CT2 installation: Isc (A)
  • Isc = In × 100/Z = 105 × 100/5 = 2100 A
  • The maximum expected short circuit current at CT2 is 2100 A
Step 3 – Select protection CT2 ratings
  • Primary rated current Ipr = (1.0 – 1.25) × In = (1.0 – 1.25) × 105
    Use a rating of 150 A
  • Secondary rated current Isr
    Use a rating of 1 A
  • Short-time withstand rating, Ith ≥ Isc
  • Primary circuit voltage Up ≥ U
    Use a ratings of 12 kV
  • Real output power: Typically > 1 VA for digital type protection relay.
Step 4 – Calculate protection class 5PX
  • The instantaneous trip current level of protection relay OC2 is set to 10 × In
  • ITRIP = 10 × 105 = 1050 A (primary current)
  • The instantaneous trip current level for the CT secondary is 7 A
The trip current level should fall between 100 to 50% of the accuracy limit factor (ALF). Using an ALF of 10 (5P10), the trip current level of 1050 A falls within the range of 100% to 50% ALF so a 5P10 protection class CT is suitable.
  • 100%(ALF) = 1.0 × 10 × 150 = 1500 A
  • 50%(ALF) = 0.5 × 10 × 150 = 750 A
  • We may notice that 750 ≤ 1050 ≤ 1500 A
  • Use protection class 5P10
2. NEMA/IEEE Ratings
These ratings are typically used for current transformers manufactured or used in North American installations. As well as a stated primary to secondary nominal current ratio, the device also carries an overall accuracy rating in the format.
AC-CR-BU
  • AC = accuracy class
  • CR = class rating
  • BU = maximum burden (ohms)
2.1 Accuracy class
Designates the accuracy of the secondary current with respect to the primary rated current. This accuracy is only guaranteed provided the maximum burden is not exceeded.
Accuracy classTolerance at 100% primary current
1.2±1.2 %
0.6±0.6 %
0.5±0.5 %
0.3±0.3 %
2.2 Class rating
Designates the intended application of the device.
  • B = for metering applications
  • H = for protection applications. The CT secondary accuracy is guaranteed at 5 to 20 times the nominal primary rated current
2.3 Burden
The maximum load allowed to be connected to the current transformer secondary, to guarantee the accuracy class. The maximum burden includes secondary cable/wire, connectors and the load.
The following table converts burden in ohms to VA, for a 5 A secondary.
Ω0.040.060.080.120.160.200.240.280.320.360.400.480.560.640.720.80
VA11.523456789101214161820
tabela
2.4 Examples
0.5-B-0.1
This example indicates a current transformer with an accuracy of ±0.5%, and a maximum allowable secondary burden of 0.1 Ω (or 2.5 VA on a 5 A secondary CT). This is a metering class rated current transformer.
1.2-H-0.2
This example indicates a current transformer with an accuracy of ±1.2%, and a maximum allowable secondary burden of 0.2 Ω (or 5 VA on a 5 A secondary CT). This is a protection class rated current transformer.
Sources:
  1. Medium Voltage Application Guide by Aucom
  2. Electric Power Substations Engineering By James C. Burke
  3. Selection of current transformers and wire sizing in substations – Sethuraman Ganesan; ABB Inc.
17 Comments
  1. Said Gabr
    Mar 14, 2022
    Which standard is used for the insulation resistance test?
  2. Mojtaba
    Jan 24, 2022
    Hello
    Is it possible to use a 10VA CT with 1500 m copper cable and 1VA digital ammeter?
    Our cross section could be 2.5 mm2 or 4 mm2.
  3. sridhar
    Oct 01, 2021
    Thank you it is really very good.
    thanks again.
  4. Hakan DAGHAN
    Sep 23, 2021
    Hello Guys,
    Woul someone please explain me the relation between burden and accuracy class of CTs? And as far as I know, you should provide the secondary burden at least 25 % of nominal ratings burden written on the CTs plate. If yes, what is the reference for this information? can you give me a link or standart name or etc.
    to illustrate my question better..;
    for example on a CT’s plate it is written that: metering terminal burden 10 VA;
    So I need to install and use longer cable to ensure my secondary load (burden) to be higher than 25 % of 10 VA = 2,5 VA.. so .
    what do you think about this application? right or wrong?
    if right can you show me the reference to do so??
    Thank you so much? I’m looking forward to hearing from you..
    We confront this problem frequently while installing electrical meter circuit in substations. and we use very long cables without knowing whether the information atrribute something on a IEC standarts or anyplace??
    okey thanks again..
    urgent answer please!!!
  5. Dang Tuan Khanh
    Sep 02, 2021
    Hi Rodney Hughes,
    After reading the link as well as read your explanation above, I can know that using CTs of 1 A is better than CTs of 5 A nowadays because of using numerical relays today.
    Thanks a lot !
  6. Rodney Hughes
    Aug 01, 2021
    A couple of things wrong with the article.
    First about CT shorting. If there are multiple secondary windings on the same core, as long as one pair of terminals are connected or shorted, the other terminals MUST be left open
    Refer https://ideology.atlassian.net/l/c/Zka2eGRo
    Protection trip settings are NOT 10-15x rated.
    Trip is generally ~120% of rated (give or take according to requirements).
    There are “high-set” instantaneous elements which are set at such multiples, but it depends on grading requirements and maximum fault currents at the downstream protection devices.
  7. SUKANTA DEY
    Jul 01, 2021
    Dear sir ,
    Would you please explain the in case of
    CT , class = PS (Differencial Protection).
    Why do we recommend replacing the 6(six) NOS CT (3 for income & 3 for outgoing)?
    Where RCT (secondary winding resistance ) & Vk (knee point voltage) has to be the identically same?
    What is the basic method to cheek the knee point voltage, and how to identify the saturation level, & what amount of voltage should be applied, where no systems voltage is mentioned on the nameplate? I would be much obliged if you kindly let me know through my mail.
    With regards,
    Sukanta Dey
    • Rodney Hughes
      Aug 01, 2021
      Hi Sukanta
      PS is an old class designation .. now PX
      Diff applications need the CTs to all behave the same way for all through current conditions (load or external fault) so that there is no “false differential” created in the secondary for the same primary current .. hence class PX because we are looking for the same behaviour, i.e. same volts v excitation current on the mag curve. We don’t really care how saturated they may become, as long as they both become saturated to the same extent keeping false differential very low.
      P class only specifies what you can connect to the CTs to stay within accuracy, whereas PX effectively specifies how it is constructed and how it performs.
      refer https://ideology.atlassian.net/l/c/Gn6YA1jq
      https://ideology.atlassian.net/l/c/u9EHnAPu
      and https://ideology.atlassian.net/l/c/hxGebPK0
  8. noreldaim hamed
    Mar 13, 2021
    Hello,
    We installed the CT as below:
    MCC Bucket feeding pump motor then, the current in MCC is showing 37 A, while the analog Ammeter at the field near the pump shows very low reading, the CT is 100:5, the analog Ammeter is range 0 to 100, and it is 100:5, 2 VA. , The motor full load current is 53.2 A. . . It is in the local control station (LCS) near the motor which both are around 500 meters away from the substation the cable is directly buried. The CT is in the MCC Bucket in the substation. But the Ammeter is not reading
    Kindly advice on above-mentioned case,
  9. Dang Tuan Khanh
    Nov 04, 2020
    Can you explain for me this:
    Why do we use 1 A (Isr of CT) for remote installation instead of 5 A ?
    Thanks a lot !
    • Rodney Hughes
      Aug 01, 2021
      @ Dang Tuan Khanh
      re 1 A vs 5 A …
      a useful reference is
      https://www.linkedin.com/pulse/current-transformers-secondary-rating-1a-5a-what-choose-sivakumar-k/
    • Rodney Hughes
      Aug 04, 2021
      @Dang Tuan Khanh
      I have been thinking further about your query re choosing 1 A or 5 A CTs.
      The link I posted earlier is useful … but I think it is a bit misleading as well, and doesn’t “hit the mark” with the real reason we stopped using 5 A CTs
      I also don’t agree with that author’s statement
      “ALL BOARD MOUNTED CTs SHALL BE WITH A 5A SECONDARY CURRENT
      and
      ALL YARD MOUNTED CTs SHALL BE WITH A 1A SECONDARY CURRENT”.
      That is not the reason at all!!
      So I have gone back to my earliest days in protection engineering … it is an issue associated with the burden presented and hence minimum kneepoint requirements for CDG induction disc relays.
      Suffice to say a 5 A CDG11 OC+EF scheme 100 m between relay and CT would require minimim kneepoint 414 V
      The same using 1 A CTs would require minimum 1299 V
      5 A CTs with just 5 m distance would require 273 V, whilst 1 A requires 1271 V
      So 1 A was not a good proposition for electromechanical relays.
      But when electronic relays came along such as MCGG
      5 A CTs 100 m requires min kneepoint 153 V (0.765 V/Turn)
      1 A CTs 100 m requires min kneepoint 31 V (0.031 V/Turn)
      5 A CTs 5 m requires min kneepoint 12 V (0.060 V/Turn)
      1 A CTs 5 m requires min kneepoint 3 V (0.003 V/Turn)
      So as you can see, it is almost irrelevant choice for electronic relays.
      But when you then look at Volts per Turn, we are now considering the physical construction of the CT itself.
      A lower Volt per Turn means lower cross sectional area of the CT core.
      So a 1 A CT is less iron, although 5 x the turns and length of wire … and in theory we could get away with thinner wire. Hence we would expect to be cheaper and less weight to mount.👍👌✨
      Its all a bit difficult to explain step-by-step, but I have given it a good shake here:
      https://ideology.atlassian.net/l/c/H8vU0VoU
      I hope it helps
  10. Geoffrey Okyere Broni
    May 02, 2020
    Primary rated current Ipr for CT2 = (1.0 – 1.25) × In = (1.0 – 1.25) × 105
    This gives a value between 105A and 131.25A. Kindly help me understand why you used 150A for Ipr
    • Karthikeyan
      Nov 03, 2020
      Selected next standard size for CT
    • Rodney Hughes
      Aug 01, 2021
      @Geoffrey Okyere Broni
      Sometimes selections and settings seem a bit “arbitrary” .. it is the skill of the engineer in taking into account ALL the influencing factors.
      Yes, in this case a 2 MVA transformer would have 105 A rated current at 11 kV.
      The standard primary ratings are as stated multiples of 10, 12.5, 15 etc
      So you probably should not choose 100 A rated primary as then you are already setting the relay above 105% of rated CT
      It could be possible to choose therefore a 125 A primary rated CT as 119% of TF 105 A rated current, i.e. your protection has to be set > 105/125 = 84% of relay rated current
      Choosing 150 A rated primary is 143% of 105 A, and your relay setting has to be >70% of relay rated current
  11. Sandeep Sharma
    Jan 22, 2020
    Really practical information, really like
    Please mail wright up on MV/LV Switchgears Panel Designing.
  12. Md shariful islam
    Jan 20, 2020
    I’m md shariful islam I’m working qatar MHM- al muftah company
Leave a Reply to Rodney Hughes