Home / Technical Articles / Inspection and test procedures for Rotating Machinery, Synchronous Motors and Generators
Testin Procedures
  1. Visual and Mechanical Inspection
  2. Electrical Tests
  3. Test Values
    1. Visual and Mechanical Tests
    2. Electrical Tests
  4. Pictures:
    1. Electrical machine wired for electrical testing
    2. The Electrical Machines Laboratory
  5. TABLE 100.10 – Maximum Allowable Vibration Amplitude
  6. TABLE 100.12 – US Standard Fasteners
Inspection and test procedures of Rotating Machinery, Synchronous Motors and Generators
Inspection and test procedures of Rotating Machinery, Synchronous Motors and Generators (On photo: Small machine test set – ee.polyu.edu.hk)
  1. Compare equipment nameplate datawith drawings and specifications.
  2. Inspect physical and mechanical condition.
  3. Inspect anchorage, alignment, and grounding.
  4. Inspect air baffles, filter media, cooling fans, slip rings, brushes, and brush rigging.
  5. Inspect bolted electrical connections for high resistance using one or more of the following?methods:
    1. Use of low-resistance ohmmeter?in accordance with procedure for LR ohmmeter?usage.
    2. Verify tightness of accessible bolted electrical connections by calibrated torque-wrench?method in accordance with manufacturer?s published data or Table 100.12?(see below).
    3. Perform thermographic survey.
  6. Perform special tests such as air-gap spacing and machine alignment.
  7. Verify the application of appropriatelubrication and lubrication systems.
  8. Verify that resistance temperature detector (RTD) circuits conform to drawings.
Go to Index ↑
2. Electrical Tests
  1. Perform resistance measurements through bolted connections with a low-resistance ohmmeter,?if applicable.
  2. Perform insulation-resistance tests inaccordance with ANSI/IEEE Standard 43.
    1. Machines larger than 200 horsepower (150 kilowatts):
      Test duration shall be for ten minutes. Calculate polarization index.
    2. Machines 200 horsepower (150 kilowatts) and less:
      Test duration shall be for one minute. Calculate dielectric-absorption ratio.
  3. Perform dc dielectric withstand voltage tests on machines rated at 2300 volts and greater in?accordance with ANSI/IEEE Standard 95.
  4. Perform phase-to-phase stator resistance test on machines 2300 volts and greater.
  5. ** Perform insulation power-factoror dissipation-factor tests.
  6. ** Perform power-factor tip-up tests.
  7. ** Perform surge comparison tests.
  8. Perform insulation-resistance test on insulated bearings in accordance with manufacturer?s?published data, if applicable.
  9. Test surge protection devices.
  10. Test motor starter.
  11. Perform resistance tests on resistance temperature detector (RTD) circuits.
  12. Verify operation of machine space heater, if applicable.
  13. ** Perform vibration test.
  14. Perform insulation-resistance tests on the main rotating field winding, the exciter-field winding, and the exciter-armature winding in accordance with ANSI/IEEE Standard 43.
  15. ** Perform an ac voltage-drop test on all rotating field poles.
  16. ** Perform a high-potential test on the excitation system in accordance with ANSI/IEEE Standard?421.3.
  17. Measure resistance of machine-field winding, exciter-stator winding, exciter-rotor windings,?and field discharge resistors.
  18. ** Perform front-to-back resistance tests on diodes and gating tests of silicon-controlled rectifiers?for field application semiconductors.
  19. Prior to re-energizing, apply voltage to the exciter supply and adjust exciter-field current to?nameplate value.
  20. Verify that the field application timer and the enable timer for the power-factor relay have been?tested and set to the motor drive manufacturer?s recommended values.
  21. ** Record stator current, stator voltage, and field current for the complete acceleration period?including stabilization time for a normally loaded starting condition. From the recording?determine the following information:
    1. Bus voltage prior to start.
    2. Voltage drop at start.
    3. Bus voltage at machine full-load.
    4. Locked-rotor current.
    5. Current after synchronization but before loading.
    6. Current at maximum loading.
    7. Acceleration time to near synchronous speed.
    8. Revolutions per minute (RPM) just prior to synchronization.
    9. Field application time.
    10. Time to reach stable synchronous operation.
  22. ** Plot a V-curve of stator current versus excitation current at approximately 50 percent load to?check correct exciter operation.
  23. ** If the range of exciter adjustment and machine loading permit,reduce excitation to cause power?factor to fall below the trip value of the power-factor relay. Verify relay operation.
** OPTIONAL
Go to Index??
3. Test Values
3.1 Visual and Mechanical Test Values
  1. Inspection:
    1. Air baffles shall be clean and installed in accordance with manufacturer?s published?data.
    2. Filter media shall be clean and installed in accordance with manufacturer?s published?data.
    3. Cooling fans shall operate.
    4. Slip ring alignment shall be within manufacturer?s published tolerances.
    5. Brush alignment shall be within manufacturer?s published tolerances.
    6. Brush rigging shall be in accordance with manufacturer?s published data.
  2. Compare bolted connection resistance values to values of similar connections. Investigate any?values that deviate from similar bolted connections by more than 50 percent of the lowest?value.
  3. Bolt-torque levels should be in accordance with manufacturer?s published data. In the absence?of manufacturer?s published data, use Table 100.12 (see below)
  4. Results of thermographic survey to be analysed.
  5. Air-gap spacing and machine alignment shall be in accordance with manufacturer?s published?data.
Go to Index??
3.2 Electrical Test Values
  1. Compare bolted connection resistance values tovalues of similar connections. Investigate any?values that deviate from similar bolted connections by more than 50 percent of the lowest?value.
  2. The dielectric absorption ratio or polarization index shall not be less than 1.0. The?recommended minimum insulation resistance (IR 1 min) test results in megaohms shall be?corrected to 40? C and read as follows:
    1. IR 1 min = kV + 1 for most windings made before 1970 (kV is the rated machine terminal-to-terminal voltage in rms kV)
    2. IR 1 min = 100 megohms for most dc armatureand ac windings built after 1970 (form-wound coils).
    3. IR 1 min = 5 megohms for most machines and random-wound stator coils and form-wound coils rated below 1 kV.
      NOTE: Dielectric withstand voltage and surge comparison tests shall not be performed?on machines having values lower than those indicated above.
  3. If no evidence of distress or insulation failure is observed by the end of the total time of voltage?application during the dielectric withstand test, the test specimen is considered to have passed?the test.
  4. Investigate phase-to-phase stator resistance values that deviate by more than five percent.
  5. Power-factor or dissipation-factor values shall be compared to manufacturer?s published data.?In the absence of manufacturer?s published data these values will be compared with previous?values of similar machines.
  6. Tip-up values shall indicate no significant increase in power factor.
  7. If no evidence of distress, insulation failure, orlack of waveform nesting is observed by the end?of the total time of voltage application during the surge comparison test, the test specimen is?considered to have passed the test.
  8. Insulation resistance of bearings shall be within manufacturer?s published tolerances. In the?absence of manufacturer?s published tolerances, the comparison shall be made to similar?machines.
  9. Test results of surge protection devices shall be in accordance with procedures for testing of LV surge arresters.
  10. Test results of motor starter equipment shall be in accordance with?procedures for testing of motor starter equipment.
  11. RTD circuits shall be in accordance with system design intent and machine protection device?manufacturer?s published data.
  12. Heaters shall be operational.
  13. Vibration amplitudes of the uncoupled and unloaded machine shall not exceed values shown in?Table 100.10 (see below). If values exceed, perform complete vibration analysis.
  14. The recommended minimum insulation resistance (IR1 min) test results in megaohms shall be?corrected to 40? C and read as follows:
    1. IR 1 min= kV + 1 for most windings made before 1970, all field windings (kV is the rated machine terminal-to-terminal voltage in rms kV)
    2. IR 1 min= 100 megohms for most dc armature and ac windings built after 1970 (form-wound coils).
    3. IR 1 min= 5 megohms for most machines and random-wound stator coils and form-wound coils rated below 1 kV.
      NOTE: Dielectric withstand voltage, high-potential, and surge comparison tests shall?not be performed on machines having values lower than those indicated above.
  15. The pole-pole AC voltage drop shall not exceed 10 percent variance between poles.
  16. If no evidence of distress or insulation failure is observed by the end of the total time of voltage?application during the dielectricwithstand test, the winding is considered to have passed the?test.
  17. The measured resistance values of motor-field windings, exciter-stator windings, exciter-rotor?windings, and field-discharge resistors shall be compared to manufacturer?s published data. In?the absence of manufacturer?spublished data, the comparison shall be made to similar?machines.
  18. Resistance test results of diodes and gating tests of silicon-controlled rectifiers shall be in?accordance with industry standards and system design requirements.
  19. Exciter power supply shall allow exciter-field current to be adjusted to nameplate value.
  20. Application timer and enable timer for power-factor relay test results shall comply with?manufacturer?s recommended values.
  21. Recorded values shall be in accordance with system design requirements.
  22. Plotted V-curve shall indicate correct exciter operation.
  23. When reduced excitation falls below trip value for the power-factorrelay, the relay shall?operate.
Go to Index ↑
Electrical machine wired for electrical testing (photo credit: komel.katowice.pl)
Go to Index ↑
The Electrical Machines Laboratory (photo credit: ee.polyu.edu.hk)
Go to Index ↑
TABLE 100.10
Table 100.10 - Maximum Allowable Vibration Amplitude
Table 100.10 – Maximum Allowable Vibration Amplitude
Go to Index ↑
TABLE 100.12
US Standard Fasteners – Bolt-Torque Values for Electrical Connections
Table 100.12.1 - Heat-Treated Steel - Cadmium or Zinc Plated
Table 100.12.1 – Heat-Treated Steel – Cadmium or Zinc Plated
Table 100.12.2 - Silicon Bronze Fasteners
Table 100.12.2 – Silicon Bronze Fasteners
Table 100.12.3 - Aluminum Alloy Fasteners
Table 100.12.3 – Aluminum Alloy Fasteners
Table 100.12.4 - Stainless Steel Fasteners
Table 100.12.4 – Stainless Steel Fasteners
a. Consult manufacturer for equipment supplied with metric fasteners.
b. This table is based on bronze alloy bolts having a minimum tensile strength of 70,000 pounds per square inch.
c. This table is based on aluminum alloy bolts having a minimum tensile strength of 55,000 pounds per square inch.
d. This table is to be used for the following hardware types:
  • Bolts, cap screws, nuts, flat washers, locknuts (18?8 alloy)
  • Belleville washers (302 alloy).
Go to Index ↑
Reference:?ANSI/NETA Standard for Acceptance Testing Specifications for Electrical Power Equipment and Systems
6 Comments
  1. Engineer Samson
    Jul 20, 2022
    Perfect
  2. akula rama chandrudu
    May 19, 2021
    i want for preparation of AMIE SECTION B SO WE ARE REFERENCE YOUR PORTAL
  3. mohamed Elsayed
    Dec 24, 2019
    Very Very good
  4. TASHOKKUMAR
    May 12, 2016
    very good
  5. Israel E Tettey
    May 02, 2016
    Please can you give me the principles of operation of both syn.Motors and Generators?
  6. M.Thanupillai
    Sep 22, 2015
    very ***********Good
Leave a Reply to TASHOKKUMAR
seventy two  −    =  sixty three
