Operational substation simulation

Designing and operating a substation is a tiresome and challenging task, which requires hefty capital, a well-trained workforce, and lots of time. With the ever-expanding nature of electricity distribution, the MV/LV power distribution substations are mushrooming everywhere. Sometimes, they are even installed in bulk numbers with preset design and loading conditions.

Load flow and short circuit analysis of a MV substation (case study 33/11 kV substation in ETAP)
Figure 1 - Load flow and short circuit analysis of a MV substation (case study 33/11 kV substation in ETAP)

While doing so, the equipment selection is done based on the general design criteria rather than customized sizes and specifications. For instance, in most of the MV substations, the VCBs, isolators, and other active components are oversized and maintain uniformity as far as possible.

This comes often in practice to cut the cost of customized manufacturing of components. It is a common practice for OEMs to manufacture the equipment in standard sizes and ratings to allow mass production. In between all these, the designers and technicians are left to choose from the available standard sizes and specifications.

It is even a possibility that the technicians may not be aware of exact technical requirements. There are many reliable software and platforms to design and check the technical requirement in the power system. The engineers and designers must be familiar with the actual technique and methods.

This article primarily focuses on the simulation of an operational MV substation for approximating the load flow and short-circuit currents and recommending improvements and equipment selection or replacement, based on the findings of the simulation.

This article familiarizes its reader with the perks of technical analysis of a substation, either in the design phase or in operation, based on a real-world case study performed in ETAP.

Table of Contents:

  1. Load flow analysis
  2. Short circuit analysis
  3. A case study: 33/11 kV substation for power distribution
    1. Preparatory data for simulation
    2. Result of load flow simulation
    3. Simulation result for Short circuit analysis and protection coordination
  4. Making use of simulation results
  5. BONUS – Etap project of case study
  6. Video tutorials

1. Load flow analysis

Load flow analysis is a steady-state analysis of any power system network to determine the operating condition and parameter (Voltage, phase angle, and branch current) for a set of loading conditions. It uses a technique to solve a set of non-linear algebraic equations to approximate the unknown variables of power systems.

Most of the modern-day power utility software: ETAP, Power world simulator, PSS-E, etc. are based on the fast and accurate Newton-Raphson or fast decoupled numerical algorithm to solve the power flow equations. It helps to determine the power or current flow for each branch or bus in the network, once the most accurate value of voltage is obtained.

Theoretically, this includes the conversion of the network into an admittance matrix, making the initial guess of all unknown voltage, and solving the power balance equation in loop reusing the most recent value of voltage acquired at the end of each iteration.

In the MV or any other radial substation, the load flow calculation is essential to cross-check the system for its adequacy to withstand the maximum connected load. This will give the idea of maximum voltage drop, maximum current, and power factor in the live components like busbar, circuit breakers, etc. for a particular loading condition.

Suggested course – Power System Analysis, Modelling, Load Flow and Fault Studies for True Engineers

Power System Analysis, Modelling, Load Flow and Fault Studies for True Engineers
Power System Analysis, Modelling, Load Flow and Fault Studies for True Engineers

Go back to the Contents Table ↑


2. Short circuit analysis

Short circuit analysis is a procedure that calculates the fault current at each point in a network upon an occurrence of a fault in a certain section of the network, which is essential to approximate the breaking capacity and fine-tuning of current interrupting devices and protective devices.

The output of short circuit analysis helps predict the incident energy levels and planning protection coordination. It involves the conversion of the network into a combination of equivalent impedance and a voltage source to approximate the fault current at the moment of fault. For MV substation, the internal resistance of cables, transformer impedance, etc. contributes to the calculation of equivalent impedance.

This article illustrates a case study of one such instance of short circuit current approximation of an MV substation, in ETAP. Usually, the substations are analyzed for their short circuit capacity in the design phase.

However, it is equally essential to periodically maintain the short circuit analysis data over time to refine the settings of protection elements and replace them if required.

Suggested read – How to reduce short-circuit currents in MV applications

How to reduce short-circuit currents in medium voltage applications

Go back to the Contents Table ↑


3. A case study: 33/11 kV substation for power distribution

This article uses a 33/11 kV, 11 MVA power distribution substation for a case study. The substation is functional since 2001, and most of the design documents are misplaced already. Some equipment is replaced during multiple periodic and breakdown maintenance.

The single line diagram in Figure 2 provides most of the details required for the ETAP modeling of the substation for load flow and short circuit analysis. The analysis will serve as a reference to cross-check the operating condition for recent loading conditions obtained from the load curve data in the substation logbook.

Figure 2 – Single line diagram of a 33/11, 11 MVA Power distribution substation

Single line diagram of a 33/11, 11 MVA Power distribution substation
Figure 2 – Single line diagram of a 33/11, 11 MVA Power distribution substation

Go back to the Contents Table ↑


3.1 Preparatory data for simulation

Figure 3 illustrates an ETAP model of the case substation of this article. A major factor for the accuracy of simulation output is the right selection of parameters and equipment, and the major focus should be to replicate the real-world case as far as possible.

In this case, the Short circuit MVA for the incoming grid is defined based on the capacity and percentage impedance of a power transformer in the source. The impedance of the transmission line from the source to the substation may or may not be included in the simulation.

Normally, to emulate the most pessimistic scenario, the designers and engineers can sometimes opt to neglect the impedance of the live parts like cable, line conductors, etc.

Figure 3 – ETAP simulation conversion of available SLD of the substation (click to zoom)

ETAP simulation conversion of available SLD of the substation
Figure 3 – ETAP simulation conversion of available SLD of the substation (click to zoom)

The sizing and ampacity of the busbar, breakers, switches, etc. are kept identical to the actual case. Likewise, the percentage impedance of power transformer and station transformer in the substation are of prime importance too, which can be obtained from datasheets of respective components.

Membership Upgrade Required

This content is not available in your premium membership plan. Please upgrade your plan in order to access this content. You can choose an annually based Basic, Pro, or Enterprise membership plan. Subscribe and enjoy studying specialized technical articles, online video courses, electrical engineering guides, and papers.

With EEP’s premium membership, you get additional essence that enhances your knowledge and experience in low- medium- and high-voltage engineering fields.

Good to know: – Save 50% on all video courses with Enterprise plan.

Upgrade

Already a member? Log in here

Premium Membership

Get access to premium HV/MV/LV technical articles, electrical engineering guides, research studies and much more! It helps you to shape up your technical skills in your everyday life as an electrical engineer.
More Information
Bishal Lamichhane - Author at EEP-Electrical Engineering Portal

Bishal Lamichhane

Electrical Engineer (B.E Electrical, M. Sc Engineering) with specialization in energy systems planning. Actively involved in design and supervision of LV/MV substations, power supply augmentations and electrification for utilities and bulk consumers like airports and commercial entities. An enthusiast and scholar of power systems analysis.
Profile: Bishal Lamichhane

Leave a Comment

Tell us what you're thinking. We care about your opinion! Please keep in mind that comments are moderated and rel="nofollow" is in use. So, please do not use a spammy keyword or a domain as your name, or it will be deleted. Let's have a professional and meaningful conversation instead. Thanks for dropping by!

Learn How to Design Power Systems

Learn to design LV/MV/HV power systems through professional video courses. Lifetime access. Enjoy learning!

EEP Hand-Crafted Video Courses

Check more than a hundred hand-crafted video courses and learn from experienced engineers. Lifetime access included.
Experience matters. Premium membership gives you an opportunity to study specialized technical articles, online video courses, electrical engineering guides, and papers written by experienced electrical engineers.
Whitepaper: How to Improve Risk Decisions for Power Systems - Prioritizing vulnerabilities with full operational context