To protect persons and LV instalations

The prime function of an earth electrode is the protection of persons. That’s it. It is a fact that we live on Earth! And it is vital to earth exposed metal parts of electrical equipment to avoid electrocution by indirect contact should an insulation fault occur. This measure has been stipulated in the standards a long time ago, since 1923 (IEC 364; NF C 15-100).

What is the prime function of an earth electrode in power system
What is the prime function of an earth electrode in power system (photo credit: stationproject.wordpress.com)

The fault current varies in strength according to the earthing system used, and measures are taken to ensure that contact voltage does not exceed conventional safety voltage for a stipulated time: UL (50 V in AC). The exposed metal parts of electrical equipment are connected to the PE protective conductors in turn connected to the earth, thus forming the earthing arrangement.

The second function of an earth electrode is to minimize common mode disturbances external to the LV installation. An example is 50/60 Hz overvoltage in the event of:

  • MV/LV transformer breakdown (see figure 1) or
  • Overvoltage due to lightning (see figure 2).

MV/LV breakdown – The power system potential rises with respect to the earth: U = RN × Ih resulting in risk for the equipment in TT system or for persons in TN system if the building is not completely equipotentially bound.

MV/LV breakdown
Figure 1 – MV/LV breakdown

Lightning surge – The power system is subjected to pulsating overvoltage on all live conductors, resulting in a high EMC risk. Requires use of lightning arresters whatever the earthing system used.

Lightning surge
Figure 2 – Lightning surge

With reference to the above, NF C 13-100 has laid down limit earth electrode values in France. Lightning, MV/LV faults and safety of persons call for use of low impedance earth electrodes (IhMV can reach 1000 A and the insulating voltage of sensitive devices is 1500 V !). This problem particularly needs to be managed in TT earthing systems.

Beware, naturally multiple earth electrodes should be avoided unless they are interconnected! The earth electrode may be one or more spikes pressed into the ground or a foundation ditch loop, or a combination of both.

For a spike: Rp = ρ / L

For the foundation ditch loop: RFF = 2ρ / L

where L is the length of the spike or the perimeter of the loop.

The earth electrode must be a solid copper or stainless steel conductor so as to limit oxidation. Ground resistivity (ρ) is an important parameter, varying considerably with ground humidity and nature from 1 to 5000 Ω/m. It is vital to place the ‘right’ earth at the bottom of the foundation ditch around the loop conductor (see figure 3).

Earth electrode: creating a loop in the foundation ditch
Figure 3 – Earth electrode: creating a loop in the foundation ditch

The impedance of an earth electrode varies only slightly between 50 Hz and 500 kHz. If the building is equipped with lightning rods, the rod downcomers must be connected to earth electrodes in triangular crossbracing.

All conductors which might be required to convey lightning currents must be flat conductors in order to reduce the self-induction factor and skin effect and consequently the drop in linear voltage (see figure 3).


Calculation

Continuous resistance of a conductor

Continuous resistance of a conductor is RC = ρ l / s , i.e. RC = 1.7 mΩ for a 10 m long cylindrical copper conductor with a 100 mm2 cross-section. As frequency increases, the skin effect strengthens this resistance.

This is because high frequency currents are concentrated at the edges of the conductor over a depth of δ = (π f μ σ)-1/2 which decreases with frequency. δ is known as the skin depth.

For copper:

  • δ (50 Hz) = 9.3 mm,
  • δ (1 MHz) = 65.8 μm,
  • δ (10 MHz) = 21 μm.

As a result the real cross-section of the conductor decreases. The ratio between RHF and RC is given for a cylindrical conductor with a radius r by:

The ratio between RHF and RC is given for a cylindrical conductor with a radius r

This formula only applies if the radius r of the conductor is greater than the skin depth δ. Our copper conductor is such that:

  • at 50 Hz: RHF = RC = 1.7 mΩ,
  • at 1 MHz: RHF = 43.1 × RC = 73 mΩ,
  • at 10 MHz: RHF = 135 × RC = 230 mΩ.

The self-inductance L (μH) of a conductor

The self-inductance L (μH) of a conductor of a length l is:

  • For a cylindrical conductor:
    The self-inductance L (μH) for a cylindrical conductor
  • For a conductor with rectangular cross-section:
    The self-inductance L (μH) for a conductor with rectangular cross-section

Where l, d(diameter), δ, w (width), e (thickness) are expressed in meters.


Impedance of conductors depending on their geometry and frequency

Impedance of conductors depending on their geometry and frequency
Impedance of conductors depending on their geometry and frequency

Self-inductance and impedance of a 10 m long copper conductor with a 100 mm2 cross-section depending on its geometry.

(*) in the table the self-inductance of the cylindrical conductor is given at 50 Hz. In HF the term 100 μr, δ becomes negligible, and L ≈ 14.35 μH becomes, like the rectangular cross-section conductor, independant of frequency. Finally note that in HF the impedance Z = 2π×f×L becomes preponderant compared with the resistance RHF.

It is important for these conductors to be as short as possible!!

Let us take the example of an LV lightning arrester designed to limit common mode voltage to 1.5 kV. If it is connected between the protected phase and the earth strip by a 1 m long conductor with circular cross-section, a 5 kA current and a 8 μs rising edge, it will develop the following voltage:

Voltage

Hence a total overvoltage of 2.1 kV which is dangerous as many devices have an impulse voltage withstand of 1.5 kV. The solution is to connect the application directly to the terminals of the lightning arrester (see figure 4).

Optimum connection of a lightning arrester
Figure 4 – Optimum connection of a lightning arrester

[TP]

Lightning protection and earthing system design for Buildings

Reference // Cohabitation of high and low currents by R. Calvas and J. Delaballe

Premium Membership

Get access to premium HV/MV/LV technical articles, electrical engineering guides, research studies and much more! It helps you to shape up your technical skills in your everyday life as an electrical engineer.
More Information
Edvard Csanyi - Author at EEP-Electrical Engineering Portal

Edvard Csanyi

Hi, I'm an electrical engineer, programmer and founder of EEP - Electrical Engineering Portal. I worked twelve years at Schneider Electric in the position of technical support for low- and medium-voltage projects and the design of busbar trunking systems.

I'm highly specialized in the design of LV/MV switchgear and low-voltage, high-power busbar trunking (<6300A) in substations, commercial buildings and industry facilities. I'm also a professional in AutoCAD programming.

Profile: Edvard Csanyi

One Comment


  1. Manuel Bolotinha
    Apr 03, 2017

    It must also be considered the role of earth electrodes in touch and step potential.

Leave a Comment

Tell us what you're thinking. We care about your opinion! Please keep in mind that comments are moderated and rel="nofollow" is in use. So, please do not use a spammy keyword or a domain as your name, or it will be deleted. Let's have a professional and meaningful conversation instead. Thanks for dropping by!