Home / Technical Articles / Maintenance Of SF6 Gas Circuit Breakers
SM6 10kV switchgear with circuit breakers by Schneider Electric
Sulfur Hexafluoride (SF6) is an excellent gaseous dielectric for high voltage power applications. It has been used extensively in high voltage circuit breakers and other switchgears employed by the power industry.
Applications for SF6 include gas insulated transmission lines and’gas insulated power distributions.
The combined electrical, physical, chemical and thermal properties offer many advantages when used in power switchgears.
Some of the outstanding properties of SF6 making it desirable to use in power applications are:
  • High dielectric strength
  • Unique arc-quenching ability
  • Excellent thermal stability
  • Good thermal conductivity
Properties Of SF6 (Sulfur Hexafuoride) Gas
a) Toxicity
SF6 is odorless, colorless, tasteless, and nontoxic in its pure state. It can, however, exclude oxy­gen and cause suffocation. If the normal oxygen content of air is re­duced from 21 percent to less than 13 percent, suffocation can occur without warning. Therefore, circuit breaker tanks should be purged out after opening.
b) Toxicity Of Arc Products
Toxic decomposition products are formed when SF6 gas is subjected to an elec­tric arc. The decomposition products are metal fluorides and form a white or tan powder. Toxic gases are also formed which have the characteristic odor of rotten eggs. Do not breathe the vapors remaining in a circuit breaker where arcing or corona dis­charges have occurred in the gas.
Evacuate the faulted SF6 gas from the circuit breaker and flush with fresh air before working on the circuit breaker.
c) Physical Properties
SF6 is one of the heaviest known gases with a den­sity about five times the density of air under similar conditions. SF6 shows little change in vapor pressure over a wide temperature range and is a soft gas in that it is more compressible dynamically than air.
The heat trans­fer coefficient of SF6 is greater than air and its cooling characteristics by convection are about 1.6 times air.
d) Dielectric Strength
SF6 has a di­electric strength about three times that of air at one atmosphere pressure for a given electrode spacing. The dielectric strength increases with increasing pressure; and at three atmospheres, the dielectric strength is roughly equivalent to transformer oil. The heaters for SF6 in circuit breakers are required to keep the gas from liquefying because, as the gas liquifies, the pressure drops, lowering the dielectric strength.
The exact dielectric strength, as compared to air, varies with electrical configuration, electrode spacing, and electrode configuration.
e) Arc Quenching
SF6 is approxi­mately 100 times more effective than air in quenching spurious arcing. SF6 also has a high thermal heat capacity that can absorb the energy of the arc without much of a temperature rise.
f) Electrical Arc Breakdown
Because of the arc-quenching ability of SF6, corona and arcing in SF6 does not occur until way past the voltage level of onset of corona and arcing in air. SF6 will slowly decompose when ex­posed to continuous corona.
All SF6 breakdown or arc products are toxic. Normal circuit breaker operation produces small quantities of arc products during current interruption which normally recombine to SF6.
Arc products which do not recombine, or which combine with any oxygen or moisture present, are normally re­moved by the molecular sieve filter material within the circuit breaker.
Handling Nonfaulted SF6
The procedures for handling nonfaulted SF6 are well covered in manufacturer’s instruction books. These procedures normally consist of removing the SF6 from the circuit breaker, filtering and storing it in a gas cart as a liquid, and transferring it back to the circuit breaker after the circuit breaker maintenance has been performed.
No special dress or precautions are required when handling nonfaulted SF6.
Handling Faulted SF6
Toxicity
FAULTED SF6 GAS – Faulted SF6 gas smells like rotten eggs and can cause nausea and minor irritation of the eyes and upper respiratory tract. Normally, faulted SF6 gas is so foul smelling no one can stand exposure long enough at a concentration high enough to cause permanent damage.
SOLID ARC PRODUCTS – Solid arc products are toxic and are a white or off-white, ashlike powder. Contact with the skin may cause an irritation or possible painful fluoride burn. If solid arc products come in contact with the skin, wash immediately with a large amount of water. If water is not available, vacuum off arc products with a vacuum cleaner.
Clothing and safety equipment requirements
When handling and re­ moving solid arc products from faulted SF6, the following clothing and safety equipment should be worn:
COVERALLS – Coveralls must be worn when removing solid arc products. Coveralls are not required after all solid arc products are cleaned up. Disposable coveralls are recommended for use when removing solid arc products; however, regular coveralls can be worn if disposable ones are not available, provided they are washed at the end of each day.
HOODS – Hoods must be worn when removing solid arc products from inside a faulted dead-tank circuit breaker.
GLOVES – Gloves must be worn when solid arc products are hah-died. Inexpensive, disposable gloves are recommended. Non-disposable gloves must be washed in water and allowed to drip-dry after use.
BOOTS – Slip-on boots, non-disposable or plastic disposable, must be worn by employees who enter eternally faulted dead-tank circuit breakers. Slip-on boots are not required after the removal of solid arc products and vacuuming. Nondisposable boots must be washed in water and dried after use.
SAFETY GLASSES – Safety glasses are recommended when handling solid arc products if a full face respirator is not worn.
RESPIRATOR – A cartridge, dust-type respirator is required when entering an internally faulted dead-tank circuit breaker. The respirator will remove solid arc products from air breathed, but it does not supply oxygen so it must only be used when there is sufficient oxygen to support life. The filter and cartridge should be changed when an odor is sensed through the respirator.
The use of respirators is optional for work on circuit breakers whose in­ terrupter units are not large enough for a man to enter and the units are well ventilated.
Air-line-type respirators should be used when the cartridge type is ineffective due to providing too short a work time before the cartridge becomes contaminated and an odor is sensed.
When an air-line respirator is used, a minimum of two working respirators must be available on the job before any employee is allowed to enter the circuit breaker tank.
Disposal of waste
All materials used in the cleanup operation for large quantities of SF6 arc products shall be placed in a 55­ gal drum and disposed of as hazardous waste.
The following items should be disposed of:
  • All solid arc products
  • All disposable protective clothing
  • All cleaning rags
  • Filters from respirators
  • Molecular sieve from breaker and gas cart
  • Vacuum filter element
15 Comments
  1. Ramaz Baramidze
    Oct 13, 2021
    Can you send me maintenance schedule of sf6 circuit breakers: HGI 2; HD4/C-17-06-25? Intervals (periods) and short explanations of actions
    Best regards
    Ramaz
  2. ROHIT GAUATM
    Mar 20, 2020
    What is the maintanance schedule of sf6 circuit breaker ? @advard sir
  3. Ganesh
    Nov 27, 2019
    Please can i get safeties of high voltage switch board
  4. Paulson
    Mar 27, 2019
    What are the check list for refilling of SF6 , can we do it in LIVE panel.
  5. goutham
    Oct 10, 2018
    sir, we are using sf6 cb with 5.465kg/cm3. what will happen if the density increases
  6. Deedar ali
    Feb 04, 2017
    Dear sir, last week we have faced a problem at 132/11kv grid station, our SF6 breaker tripped on trafo differential relay fault. on checking on differential relay there were no fault shown, only fault shown on annunciator and trafo tripped, on physically checking of grid trafo there were no abnormality shown. so we did not find the reason of tripping , please advice.
    • Paulson
      Mar 27, 2019
      check your surge arrestor
  7. Mujeeb Raza
    Oct 10, 2014
    What is meant by live tank and dead tank circuit breakers ?
    • Paulson
      Mar 27, 2019
      simply say – DEAD tank means the contacts are inside a box which are conneted through bushings to the live line
      LIVE tank- contacts are inside the bushes itself
  8. ABHAYA MISHRA
    Sep 18, 2014
    What is the frequency of sf6 breaker 145 kV for crm checking
    • Christian Coppolecchia
      May 17, 2016
      In my experiance a weekly check is recommended. A visual check is enough on the pressure level indicator to be sure that there aren’t leakage. Moreover, if the breaker is close to the sea (aggressive enviromental) a visual check on the connections should be better. During rain season, is important to verify, if the umidity is going inside the pressure indicator. If it happens a false allarm is possible.
  9. ABHAYA MISHRA
    Sep 18, 2014
    While one no. 145 kV breaker sf6 type in operation for capacitor power factor application, it got blasted off though pressure noted ok 2 hours before. What could be the reason.
  10. Patrick Bheki Maseko
    Feb 20, 2014
    I try to search your contact number but I cun’t please send me to my email [email protected] I want to ask about servicecing the sf6 breackers s1-145 , tapchanger20mva 88kw/11kv and inspacting or service a transformer I’m in South Africa, piet retief Mpumalanga My contuct no is 0782409543 please send your details as possible thanks
  11. Max
    Jan 10, 2011
    Edvard.
    I’m interested in using gis. If u can help by some information please contact me with email – [email protected]
    National Technical Centre of Energy, Ukraine, Kiev
      Max, I tried to send you email, but I’m getting return message error.
Leave a Reply to Christian Coppolecchia
sixty  ⁄    =  fifteen
