Directional earth fault protection

This technical article continues the series of articles dedicated to mastering single line and wiring diagrams of medium voltage switchgear. This time, the subject is the principle, and realization of earth fault protection applied to the same example switchgear used in the previous article. The focus of this article will be on directional earth fault.

Mastering single line and wiring diagrams: MV earth fault protection
Mastering single line and wiring diagrams: MV earth fault protection

If you didn’t read the previous article in this series, you can find it here.

There are numerous variations of MV switchgear topology, measurement, and control logic. However, there are also some basic rules related to these aspects which may be frequently seen in practice, with the purpose of increased safety and reliability during operation. Within this article, the real example of MV switchgear with two main busbar sections will be described.

Most of the attention will be given to concrete practical solutions related to some protection and measuring issues. This subject will be illustrated by use of adequate single line and wiring diagrams.


Example of MV switchgear

Switchgear which is the subject of this example is installed inside MV/LV substation, and serving for power supply of new factory of construction steel products. There are eight MV/LV power transformers in total, with rated power of 3.5 MVA each.

Table 1 – Main technical characteristics of MV switchgear

Construction:Metal enclosed
Installation type:Indoor
Isolation type:Air insulated (isolation medium inside cubicles)
Protection degree:IP 3X
Ambient temperature:−5 … +40 °C
Number of cubicles:14
Rated voltage:24 kV (*)
Operating voltage:20 kV (*)
Rated lightning withstand voltage:125 kV, 1.2/50 µs
Rated power frequency withstand voltage:50 kV, 1 min.
Rated current of main busbars:1250 A
Rated short time withstand current:20 kA × 2 s
Rated peak withstand current:50 kA
Arc test current:21 kA × 1 s (**)
Internal arc classification (IAC):AFLR (**)
Rated voltage of control and signal circuits:110 VDC

(*) Rated voltage of the switchgear is the upper limit of phase to phase RMS value which switchgear is capable to withstand continuously. Operating voltage is rated (expected) phase to phase value during operation. This value is usually allowed to vary within ±10% limits or less.

For MV applications, rated voltage of the switchgear is 20% greater than rated operating voltage. Values of lightning and power frequency withstand voltage are also related to these values, according to IEC standard.

(**) IAC parameter defines from which sides MV switchgear is safely accessible during internal fault followed by presence of electric arc. This parameter depends on arc test current value, dimensions of room inside of which MV switchgear is installed, and technical measures taken for dissipation of heat and pressure caused by arc.

In this case, so called gas duct is used for that purpose. Meaning of IAC designation is as follows:

  • A – MV switchgear may be accessed by instructed (technical) personnel
  • FLR – MV switchgear may be safely accessed from front (F), lateral (L) and rear (R) side
Block diagram of MV switchgear
Figure 1 – Block diagram of MV switchgear

Block diagram of MV switchgear can be seen in Figure 1. It can be supplied from two independent sources (substation 110/20 kV and substation F), that is why two incoming cubicles (1J07 and 1J10) are used. These two incoming cubicles cannot be active (closed) at the same time, i.e. parallel operation of two incoming lines is forbidden.

There are eight transformer cubicles (1J02 – 1J06 and 1J11 – 1J13), bus section cubicle (1J08), bus riser cubicle (1J09) and two spare/measurement cubicles (1J01 and 1J14).

Circuit breaker is used as major switching and protection device inside every cubicle. This is practically mandatory if selectivity and more complex protection functions need to be achieved inside larger MV supply system.


Principle and realization of earth fault protection

Every cubicle which contains the circuit breaker, except the one inside bus section cubicle (1J08), is equipped with protection relay and two types of current transformer: one for overcurrent protection, and other for earth fault protection. Incoming cubicles (1J07 and 1J10) are also equipped with current transformers for measuring. Voltage transformers are placed inside cubicles (1J01) and (1J14), at the end of both busbar sections.

Why there are exactly two voltage transformers for the whole switchgear?

In general, for MV applications, one voltage transformer per each section of mutually connected busbars is used. In our case, the switchgear can be supplied from two separate sources (substation 110/20kV and substation F) with bus section circuit breaker open.

Membership Upgrade Required

This content is not available in your premium membership plan. Please upgrade your plan in order to access this content. You can choose an annually based Basic, Pro, or Enterprise membership plan. Subscribe and enjoy studying specialized technical articles, online video courses, electrical engineering guides, and papers.

With EEP’s premium membership, you get additional essence that enhances your knowledge and experience in low- medium- and high-voltage engineering fields.

Good to know: – Save 50% on all video courses with Enterprise plan.

Upgrade

Already a member? Log in here

Premium Membership

Get access to premium HV/MV/LV technical articles, electrical engineering guides, research studies and much more! It helps you to shape up your technical skills in your everyday life as an electrical engineer.
More Information
Miodrag Kokotovic - Author at EEP-Electrical Engineering Portal

Miodrag Kokotovic

Graduated from Faculty of Electrical Engineering, within University of Belgrade, in the field of electrical power systems. Expert in electrical part of tender preparation, design, procurement, construction and commissioning of treatment plants and pumping stations, electrical power quality and energy management.
Profile: Miodrag Kokotovic

Leave a Comment

Tell us what you're thinking. We care about your opinion! Please keep in mind that comments are moderated and rel="nofollow" is in use. So, please do not use a spammy keyword or a domain as your name, or it will be deleted. Let's have a professional and meaningful conversation instead. Thanks for dropping by!