Rated switching sequence according to IEC, O – t – CO – t’ – CO. (cf. opposite diagram):
O – Represents opening operation
CO – Represents closing operation followed immediately by an opening operation
Three rated operating sequences exist:
- Slow: O – 3 min – CO – 3 min – CO
- Fast 1: O – 0.3 s – CO – 3 min – CO
- Fast 2: O – 0.3 s – CO – 15 s – CO
NOTE: Other sequences can be requested from manufacturer.
Close/Open cycle
Assumption: O order as soon as the circuit breaker is closed
Automatic reclosing cycle
Assumption: C order as soon as the circuit breaker is open, (with time delay to achieve 0.3 s or 15 s or 3 min).
SOURCE: Schneider Electric – Medium Voltage Technical Guide
Please can you share with me the short circuit calculation guide for the protection relays
Hello Sir!
Please explain Auxiliary Contacts State (OW-OD-C) what mean by (OW, OD).
Also help how ti analysis of timing graph of High voltage Breakers.
Thanks!
Hello Sir,
We have this rated operating sequence O-0.3s-CO-3min-CO VCB but our available unit have this rated operating sequence O-0.3s-CO-15s-CO.
Is it OK to use?
Please help.
I suppose,
Requirement is O-0.3s-CO-3min-CO. And available VCB is O-0.3s-CO-15s-CO.
15s VCB is suitable for autoreclosing application while 3 min VCB can’t.
Although 15s VCB can be used in place of 3 min VCB with suitable delay timer in circuit of breaker.
I hope it is the answer of your question.
Kamal
The article is quite not clear, i want a detailed explanation on this and where could i find articles or features or details about VCB’s. pls help
Try here: http://bit.ly/ZfTVfx Scroll down to title ‘Operating sequences and requirements’.
Hope this helps!