3. Selection of Switching Devices
Switching devices are selected both according to their ratings and according to the switching duties to be performed, which also includes the switching rates.
  1. Selection according to ratings
  2. Selection according to endurance and switching rates
    1. Switches (general, sf6, air-break, vacuum)
    2. Circuit Breakers
    3. Disconnectors
    4. Earthing Switches
    5. Contactors
3.1 Selection according to ratings
The system conditions, that is, the properties of the primary circuit, determine the required parameters.
The most important of these are:
Rated voltage
The upper limit of the system voltage the device is designed for. Because all high voltage switching devices are zero-current interrupters, except for some for fuses the system voltage is the most important dimensioning criterion.
It determines the dielectric stress of the switching device by means of the transient recovery voltage and the recovery voltage, especially while switching off.
Rated insulation level
The dielectric strength from phase to earth, between phases and across the open contact gap, or across the isolating distance. The dielectric strength is the capability of an electrical component to withstand all voltages with a specific time sequence up to the magnitude of the corresponding withstand voltages.
These can be operating voltages or higher frequency voltages caused by switching operations, earth faults (internal overvoltages) or lightning strikes (external overvoltages). The dielectric strength is verified by a lightning impulse withstand voltage test with the standard impulse wave of 1.2/50μs and a power frequency withstand voltage test (50Hz/1min).
Rated normal current
The current that the main circuit of a device can continuously carry under defined conditions. The temperature increase of components – especially contacts must not exceed defined values.
Permissible temperature increases always refer to the ambient air temperature. If a device is mounted in an enclosure, it may be advisable to load it below its full rated current, depending on the quality of heat dissipation.
Rated peak withstand current
The peak value of the major loop of the short circuit current during a compensation process after the beginning of the current flow, which the device can carry in closed state.
It is a measure for the electrodynamic (mechanical) load of an electrical component. For devices with full making capacity, this value is not relevant.
Rated short circuit making current
The peak value of the making current in case of short circuit at the terminals of the switching device. This stress is greater than that of the rated peak withstand current, because dynamic forces may work against the contact movement.
Rated breaking current
The load breaking current in normal operation. For devices with full breaking capacity and without a critical current range, this value is not relevant.
Rated short circuit breaking current
The root – mean – square value of the breaking current in case of short circuit at the terminals of the switching device.
3.2 Selection according to endurance and switching rates
If several devices satisfy the electrical requirements and no additional criteria have to be taken into account, the required switching rate can be used as an additional selection criterion.
Table 1 through table 5 show the endurance of the switching devices, providing a recommendation for their appropriate use. The respective device standards distinguish between classes of mechanical (M) and electrical (E) endurance, whereby they can also be used together on the same switching device.
Go to Content ↑
Switches:
Standard IEC 62271 – 103/VDE 0671 – 103 only specifies classes for the so called general-purpose switches. There are also ‘special switches’ and ‘switches for limited applications’.
Important note:
Disconnectors up to 52kV may only switch negligible currents up to 500mA (e.g., voltage transformer), or larger currents only when there is an insignificant voltage difference (e.g., during busbar transfer when the bus coupler is closed).
General–purpose switches
General-purpose switches must be able to break different types of operating currents (load currents, ring currents, currents of unloaded transformers, charging currents of unloaded cables and overhead lines), as well as to make on short circuit currents.
General-purpose switches that are intended for use in systems with isolated neutral or with earth fault compensation must also be able to switch under earth fault conditions.
SF6 (Sulfur hexafluoride) switches
SF6 switches are appropriate when the switching rate is not more than once a month. These switches are usually classified as E3 with regard to their electrical endurance.
Air-break or hard-gas switches
Air-break or hard-gas switches are appropriate when the switching rate is not more than once a year. These switches are simpler and usually belong to the E1 class. There are also E2 versions available.
Vacuum switches
The switching capacity of vacuum switches is significantly higher than that of the M2/E2 classes. Vacuum switches are used for special tasks: mostly in industrial power supply systems, or when the switching rate is at least once a week.
Table 1 - Classes for switches
Go to Content ↑
Circuit breakers
VD4 medium voltage circuit breaker - ABB
Whereas the number of mechanical operating cycles is specifically stated in the M classes, the circuit breaker standard IEC 62271-100/VDE 0671-100 does not define the electrical endurance of the E classes by specific numbers of operating cycles; the standard remains very vague on this.
The test duties of the short circuit type tests provide an orientation as to what is meant by ‘normal electrical endurance’ and ‘extended electrical endurance’. The number of make and break operations (Close, Open) is specified in Table 2.
Modern vacuum circuit breakers can generally make and break the rated normal current up to the number of mechanical operating cycles.
The switching rate is not a determining selection criterion, because circuit breakers are always used where short – circuit breaking capacity is required to protect equipment.
Table 2 - Classes for circuit breakers
Go to Content ↑
Disconnectors
Disconnectors do not have any switching capacity (switches for limited applications must only control some of the switching duties of a general-purpose switch). Switches for special applications are provided for switching duties such as switching of single capacitor banks, switching of ring circuits formed by transformers connected in parallel, or switching of motors in normal and locked condition.
Therefore, classes are only specified for the number of mechanical operating cycles.
Table 3 - Endurance classes for disconnectors
Go to Content ↑
Earthing switches
With earthing switches, the E classes designate the short circuit making capacity (earthing on applied voltage). E0 corresponds to a normal earthing switch; switches of the E1 and E2 classes are also called make-proof or high-speed earthing switches.
The standard does not specify how often an earthing switch can be actuated purely mechanically; there are no M classes for these switches.
Table 4 - Endurance classes for earthing switches
Go to Content ↑
Contactors
Toshiba vacuum contactors, 400A
Toshiba vacuum contactors, 400A. Current limiting, high interrupting power fuses.
The standard has not specified any endurance classes for conductors yet. Commonly used conductors today have a mechanical and electrical endurance in the range of 250,000 to 1,000,000 operating cycles.
They are used wherever switching operations are performed very frequently, e.g., more than once per hour.
Table 5 - Classes for contactors
Go to Content ↑
References: SIEMENS Power Engineerind Guide – ‘Switchgear and Substations’
Emmanouil Angeladas
Bachelor in Electrical Engineering from Technological Educational Institute of Piraeus, Hellas. Electrical engineer working at Center of Renewable Energy Sources. I work in the field of maintenance, functional test and installation of measuring systems, including wind potential measurements in areas where wind turbines will be installed. I'm highly interested in HVDC systems, Fuel Cells technology and Microgrids.
  1. Abdelmoneim
    Feb 14, 2022
  2. Oumarou Farouk
    May 02, 2021
    is it real that endurance class E 2 is notpossible for circuit breakers above 52 kV
  3. Imran
    Apr 09, 2021
    Hi, Is there any calculations to show if a CB is rated for E1,E2 or E3, what is the number of operations that the CB can clear on rated current(100%load)?
  4. P.SitaRamaRao
    Feb 03, 2020
    This is an excellent site giving ample details about power
  5. Tarif Singh
    Apr 25, 2018
    Hi need to know what is the procedure to do high voltage test at 52kV DC between the phases
    And what is the standard for the same