Home / Technical Articles / Meggering (insulation resistance testing) of dry-type power transformer
MEGGER - Insulation resistance test device
The insulation resistance test (meggering) is of value for future comparison and also for determining if the transformer is to be subjected to the applied voltage test.The winding insulation resistance test is a DC high voltage test used to determine the dryness of winding insulation system. The test measures the insulation resistance from individual windings to ground and/or between individual windings.
The measurement values are subject to wide variation in design, temperature, dryness and cleanliness of the parts. This makes it difficult to set minimum acceptable insulation resistance values that are realistic for wide variety of insulation systems that are in use and performing satisfactorily. If a transformer is known to be wet or if it has been subjected to unusually damp conditions, it should be dried before the application of the applied voltage test.
Low readings can sometimes be brought up by cleaning or drying the apparatus. The insulation resistance test should be performed at a transformer temperature as close as possible or at 20 °C. Test conducted at other temperature should be corrected 20°C with the use of temperature correcting factor.
The test equipment is calibrated to read in Megohm and commonly know as a HV Megger. Typical maximum test set voltage values may be 1kV, 5kV or 15kV. The 30kV Megger is also available.
Duration of the test voltage shall be 1 minute. In the absence of manufacture’s recommended values, the following readings may be used. Refer to Table 1.
Table 1Transformer Insulation Resistance Acceptance Testing
Winding Insulation Class, kVInsulation Resistance, MΩ*
1.2600
2.51000
5.01500
8.72000
153000
* Normally dried transformers may be expected to have readings 5 to 10 times the above minimum values.
Important Notes:
  1. Table 1 was sourced from IEEE C57-94-1982 Recommended Practice for Installation, Operation and Maintenance of Dry-type General Purpose Distribution and Power Transformer. Table 6 differs from NETA Table 100.5 figures for transformer Insulation Resistance Acceptance Testing values. There is no industry consensus for satisfactory values.
  2. Other references noted a general rule of thumb for acceptable insulation values at 1MΩ per 1kV of nameplate rating plus 1MΩ.
  3. Under no condition should the test be made while the transformer is under vacuum.
  4. The significance of values of insulation resistance test requires some interpretation depending on design, dryness and cleanliness of the insulation involved. It is recommended that the insulation resistance values be measured during periodic maintenance shutdown and trended. Large variation in the trended values should be investigated for cause.
  5. Insulation resistance may vary with applied voltage and any comparison should be made with the same measurements at the same voltage and as close as possible to the same equipment temperature and humidity as practically possible.
Insulation Resistance Test Procedure:
  1. Isolate the equipment, apply working grounds to all incoming and outgoing cables and disconnect all incoming and outgoing cables from the transformer bushing terminals connections. Disconnected cables should have sufficient clearance from the switchgear terminals greater that the phase spacing distance. Use nylon rope to hold cable away from incoming and outgoing terminals as required.
  2. Ensure the transformer tank and core is grounded.
  3. Disconnect all lightning arresters, fan system, meter or low voltage control systems that are connected to the transformer winding.
  4. Short circuit all winding terminals of the same voltage level together.
  5. Perform a 1 minute resistance measurements between each winding group to the other windings and ground.
  6. Remove all shorting leads after completion of all test.
Table 2Insulation Resistance Test Connections for Two Winding Transformer
Test No.Single-phase transformerThree-phase transformer
1High voltage winding to low voltage winding and groundHigh voltage winding to low voltage winding and ground
2High voltage winding to low voltage windingHigh voltage winding to low voltage winding
3High Voltage winding to groundHigh voltage winding to ground with low voltage winding to guard
4Low Voltage winding to high voltage winding and groundLow voltage winding to high voltage winding and ground
5Low voltage winding to groundLow voltage winding to ground and high voltage winding to guard
Resource: Substation Commisioning Course – Module for Dry-type power transformer by R. Lee
13 Comments
  1. Lawrence Rammego
    Nov 16, 2022
    Hi
    A transformer megger reading is 602Mega Ohms at 42 degrees celcius, 20MVA, 88;22KV is the meggaaer results acceptable
  2. Oacar
    Oct 10, 2019
    Not that it really matters but picture shows a microohm meter and not a insulation resistance tester…
  3. Mosayeb Moradi
    Nov 16, 2018
    Hi
    I am hope to be good
    when I have seen this site, I am very happy, because subjects of this site are useful and applicable
    good luck
  4. Concordio Tanedo
    Mar 08, 2018
    What is the ideal or acceptable values in Ductor Testing of a busbar connections is it in micro ohms or milli ohms?
  5. Concordio Tanedo
    Feb 26, 2018
    What is the ideal dc voltage sitting in Megohm testers for 15kVA, 460/230v transformer and what is the acceptable megohm result?
    • Romelito Agan
      Aug 25, 2021
      Per NETA standard, 1kV dc test voltage and minimum reading should be 500 MOhm. Also, if ambient temperature is not 20 deg C, correction factor needs to be applied in getting the right IR reading.
  6. Giorgos
    Dec 18, 2016
    Is there a way to measure the ir of thansformer without removing the hv and lv cables from the bushings??
  7. Youssef Adel
    Feb 15, 2016
    First of all thanks for your shared information and for your efforts but i have a question
    is tests ( 1&3) and (4&5) are the same?
  8. James
    Feb 03, 2015
    What are the minimum and maximum resistive values for a 315kva and 500kva transformer?
  9. Deng Makur
    Dec 21, 2014
    so technically informative and knowledge updating site
  10. Jose
    Apr 06, 2014
    Is it good not if we dont short circuited the winding terminals of the transformer if we are doing insulation testing? Need help pls. Thank you
    • Florentino
      Oct 10, 2019
      The test Voltage all over the winding must be the same, tha is the importance of the shortcircuit. If you don’t make this conection you can have 10 kV in one point and 7 kV in the other side of the winding, to give you and example. Good luck!
  11. Bhushan
    Jan 18, 2014
    GOOD INFORMATION
Leave a Reply to Concordio Tanedo
sixteen  +    =  twenty four