LV design mistakes & consequences

To provide the end user with a safe, effective, and reliable solution, a designer must steer clear of numerous blunders and misconceptions when creating a low voltage distribution design. Although there are many misconceptions about electrical designs, the ones I’ll mention in this article are frequent and likely to occur because of costs and a failure to adhere to the rules and regulations.

Ten biggest mistakes and misconceptions in the design of low voltage distribution systems
Ten biggest mistakes and misconceptions in the design of low voltage distribution systems (photo credit: blumenbecker.com)

Therefore, in this article, you will learn how to avoid such mistakes using the proper cost-saving technique without deviating from the standards and codes. Moreover, we will also understand the importance of using some design programs that will improve the quality of the electrical design, such as the lux calculation program DIALux, which contributes to the design of efficient distribution of light fixtures evenly.

Also, I will discuss the consequences of these mistakes and the appropriate solutions to correct them. The article is enhanced with video-based lessons to clarify how to avoid some design mistakes and explains further essential aspects of the design.

After you learn about common mistakes in the low voltage design, you may want to learn more about how to design a complete low voltage distribution design project from scratch by enrolling in my course bundle “Electrical Low Voltage System Distribution Design” video-based course and coursebook through the following link.

Table of Contents:

  1. Wrong Selection of Electrical Rooms
  2. Missing Spare Circuits in Distribution Board (DB) Schedules
  3. Unbalancing Loads in DB Schedules
  4. Random Distribution of Light Fixtures
  5. Ignoring Furniture Layout during the distribution of power sockets
  6. Ignoring Spare Space for Cable Trays & Trunks
  7. Not Using Panels Technical Sheets as Reference
  8. Disregarding Cost Saving in the Design
  9. Ignoring Roof Isolators for Outdoor Units
  10. Ignoring to specify Cable Type in the Design

1. Wrong Selection of Electrical Rooms

The selection of electrical rooms for any project must be made in the early stages of the design, specifically when the architect of the project designs the architectural layout. Selection of the suitable location of electrical rooms is a critical task and must be done considering different aspects of the design. For example, easing the cable routing will contribute to saving costs.

There are some questions that, if answered, will contribute to the selection of the most appropriate location for an electrical room:

  1. Can the selected room accommodate the number of panels and electrical boards?
  2. Is the room located nearby a hazardous area where fire or explosion may occur?
  3. Is the main electrical room located nearby the transformer room?
  4. Is the room located in an area that could serve the entire floor without obstructions?
Of course, answering these questions will undoubtedly contribute to selecting the best location for an electrical room. However, there is a leading primary feature that an electrical designer must consider before answering the above questions:

To ensure that the chosen electrical room location could serve other electrical rooms of the project with a straight pathway without changing its routing.

Therefore, an electrical designer must look at the staircases and elevator shafts and select the adjacent rooms. Choosing an electrical room adjacent to the stairs on the ground floor of the building, for instance, will guarantee the selection of other electrical rooms on the upper floors of a building to be at the same location.

This will result in an easing of the cable routing between distribution panels throughout all the floors of the building.

Figure 1 – Electrical distribution panels installed in an electrical room

Electrical distribution panels installed in an electrical room
Figure 1 – Electrical distribution panels installed in an electrical room

On the contrary, some electrical designs do not provide convenient locations for electrical rooms, like selecting the room nearby a wet area which might expose the electrical panels to direct contact with water causing hazardous situations. Additionally, electrical rooms may be located under staircases which does not provide enough space to accommodate future panels, and the accessibility for maintenance becomes problematic.

A project may include one or more main panels that serve several sub-main panels located on each floor to feed distribution boards at each level. Selecting an electrical room beside a staircase or elevator shaft, always continuous up to the roof floor, will be the easiest and shortest way to connect cables between panels.

Therefore, when electrical rooms are selected to be adjacent to the staircases, an electrical designer has to coordinate with the architectural and civil project teams to design an opening at each room’s roof to provide a way to connect the rooms of the entire building.

The electrical name of this opening is a “riser,” which is an opening in the concrete slab to provide a continuous way for electrical feeders to all building floors.

Figure 2 – Electrical riser for cable trays and trunkings

Electrical riser for cable trays and trunkings
Figure 2 – Electrical riser for cable trays and trunkings

Figure 3 – Electrical riser design drawing

Electrical riser design drawing
Figure 3 – Electrical riser design drawing

Go back to the Contents Table ↑


2. Missing Spare Circuits in DB Schedules

One of the biggest mistakes that electrical designers must avoid is not adding spare circuits to Distribution Board (DB) schedules. The probability of adding loads at any time is always potential. Therefore, instead of adding a new distribution board to feed the additional load, having spare circuit breakers will ease this process.

The recommendation for spare circuits is 25% of the total loads. For example, a three-phase DB schedule 12-way type would have four ways as a spare. Four ways of spares mean the user can connect up to 12 additional single-phase loads. Each way represents three circuits R, Y, and B, meaning the user can connect both single and three phases according to the connected load type.

Adding spares means that during site installation of the distribution board, technicians shall install spare circuit breakers that are not connected to any load. However, circuit breakers may also not be installed and left as blanks because the end-user might want to add a specific type that might not match the additionally installed circuit breakers for all the spares.

For example, a three-phase circuit breaker is required instead of a single-phase ELCB instead of MCB, etc. As a result, electrical designers could  indicate the additional 25% circuits as “spares” and “spaces” for practical purposes during the addition of loads to the connected DB.

The below figure shows a 12-way DB schedule with an additional 25% of spares and spaces.

Figure 4 – Distribution board (DB) schedule spares and spaces (click to zoom)

Distribution board (DB) schedule spares and spaces
Figure 4 – Distribution board (DB) schedule spares and spaces

You will notice that the additional “spare” circuit breaker is indicated with its rating ampere because they will have to be installed inside the DB during execution stages at the site. Note that “spaces” are just left as blanks to indicate that no breaker is needed to be installed and it is left for the end user’s decision according to the connection type of load.

The below figure shows what spaces of a DB look like after being covered with dummy lids for safety and not to allow dust and insects to enter the DB.

Figure 5 – Blank cover used in distribution board for space circuits

Blank cover used in distribution board for space circuits
Figure 5 – Blank cover used in distribution board for space circuits

Go back to the Contents Table ↑


3. Unbalancing Loads in DB Schedules

In a three-phase system, it is crucial not to ignore the balancing of loads. This mistake will affect the whole system’s efficiency and might cause severe consequences, as explained in the following lines. So, after defining the loads and adding them to the DB schedule to obtain the demand and total connected load in a three-phase system, it is imperative to balance the loads.

In other words, in a three-phase system, there are Red, Yellow, and Blue phases that are connected to single and three-phase loads and are distributed between them.

Membership Upgrade Required

This content is not available in your premium membership plan. Please upgrade your plan in order to access this content. You can choose an annually based Basic, Pro, or Enterprise membership plan. Subscribe and enjoy studying specialized technical articles, online video courses, electrical engineering guides, and papers.

With EEP’s premium membership, you get additional essence that enhances your knowledge and experience in low- medium- and high-voltage engineering fields.

Time Limited! – Save 15% on PRO Membership Plan with coupon CTS15

Upgrade

Already a member? Log in here

Premium Membership

Get access to premium HV/MV/LV technical articles, electrical engineering guides, research studies and much more! It helps you to shape up your technical skills in your everyday life as an electrical engineer.
More Information
Mohammed Ayman - Author at EEP-Electrical Engineering Portal

Mohammed Ayman

I earned my degree from Eastern Mediterranean University (Turkey, North Cyprus) in B.S Electrical & Electronic Engineering; shortly after, I began my career as an electrical site engineer in a mega-scale project in Qatar which allowed me to monitor and supervise electrical site installations. I indulged in the design field of the electrical low voltage distribution systems and have accomplished more than 10 projects with the compliance of the national codes & international standards.
Profile: Mohammed Ayman

Leave a Comment

Tell us what you're thinking. We care about your opinion! Please keep in mind that comments are moderated and rel="nofollow" is in use. So, please do not use a spammy keyword or a domain as your name, or it will be deleted. Let's have a professional and meaningful conversation instead. Thanks for dropping by!

Learn How to Design Power Systems

Learn to design LV/MV/HV power systems through professional video courses. Lifetime access. Enjoy learning!

EEP Hand-Crafted Video Courses

Check more than a hundred hand-crafted video courses and learn from experienced engineers. Lifetime access included.
Experience matters. Premium membership gives you an opportunity to study specialized technical articles, online video courses, electrical engineering guides, and papers written by experienced electrical engineers.
This whitepaper by OMICRON explores the fundamental shift in substation automation testing from hardware-dependent setups to virtualized, software-defined verification.