Search

Premium Membership ♕

Join EEP PREMIUM today to unlock professional articles, specialized guides, and 50% discount on academy courses (lifetime access included)

Home / Technical Articles / The Most Important Post-Installation Tests of a Gas-Insulated Substation (GIS)

Estimated Study Time: 25 minutes

GIS Post-Installation Tests

This technical article explains some of the recommended and most important tests that MUST be performed on the Gas-Insulated Substation after the installation. Such tests are visual inspections, testing for control of cables, bus leakage and gas quality checks, main circuit resistance measurement, mechanical switching checks, interlocking checks, grounding measurements, and instrument transformer tests.

The Most Important Post-Installation Tests of a Gas-Insulated Substation (GIS)
The Most Important Post-Installation Tests of a Gas-Insulated Substation - GIS (photo credit: Tamil Vendhan via Linkedin)

From the safety point of view, the testing & commissioning of distribution and transmission plants is often done under hazardous conditions. The risk of accidents must always be taken into consideration and the testing & commissioning personnel have to be fully aware of the dangers that exist and should know how to conduct their work to avoid such hazards.

The testing & commissioning of plant quite often has to be accomplished within a very short space of time and with many people from different companies involved.

There are two potential reasons for accidents which testing & commissioning personnel must take into consideration:

  1. Stressful situations where action goes before methodic thinking.
  2. Stressful situation during the energizing sequence etc. when one party is unaware of the actions taken by the other.

The testing & commissioning personnel must never allow themself to be influenced by customer demands (economic pressure) etc. which can jeopardize the safety of personnel.

During all energizing procedures, all orders and instructions regarding operations, connections, temporary earthing etc. are to be given by the person (customer/consulting engineer) responsible for the operation of the plant. All contacts between the latter person and Manufacturer testing & commissioning personnel are, during the energizing sequence, to be made via one person only (the chief commissioning engineer) to prevent fatal misunderstanding.

Directives regarding the taking of measurements and any required fault-finding procedures in energized equipment, are to be given by Manufacturer’s chief commissioning engineer in order to minimize the risk of accidents which can occur when uncertainty arise as to who does what.

All personnel in the vicinity of the plant must be fully informed of the risks, which are present when auxiliary circuits of the plant are energized.

Ok, let’s dive into the details!

Table of Contents:

  1. A MUST Construction Visual Inspections
  2. Checking Control Cables and Wirings
  3. Bus Gas Leak Checks
  4. Gas Density Monitor and Local Alarm Tests
  5. Primary Circuit Resistance
  6. SF6 Gas Quality Tests
  7. Circuit Breaker Tests:
    1. Mechanism Stroke, Wipe Measurement
    2. Open/Close Operation Including Anti-pumping
    3. Breaker Travel and Timing Test
    4. Low Gas Tripping and Block Close Operations
  8. Ground and Disconnect Switch and Circuit Breaker Interlock Tests
  9. High-Voltage Bus and Equipment Conditioning Tests
  10. Instrument Transformer Tests
  11. Other GIS Tests/Records:
    1. AC Station Service Measurements, Heater & Control Cabinet Light Operations
    2. Final Circuit Breaker Counter Readings
    3. Turnover Gas Zone Density Readings
  12. Attachments (DWG) 🔗 AutoCAD Drawings of Switching Single-Line Diagram and Interlocking Table for 380kV GIS Switchgear

1. A MUST Construction Visual Inspections

These tasks MUST include:

  1. Check all bonding and grounding conductors are installed, connected, and tight.
  2. Check the condition of the gas valves for normal operations.
  3. Inspect the appearance and condition of the primary GIS, for example, damaged paint, construction scraps, tight structure support connections, viewport covers, and so on.
  4. Cleanliness of the circuit breaker cabinet, disconnect and ground switches, and marshaling and local control cabinets.
  5. Equipment labeling including nameplates and device identification plates.
  6. Overall job site appearance and cleanliness.
  7. Condition of safety equipment, including fire extinguishers, first aid kits, and eyewashes.

Figure 1 – Sulfur Dioxide (SO2) Testing for SF6 Gas Quality

Sulfur Dioxide (SO2) Testing for SF6 Gas Quality
Figure 1 – Sulfur Dioxide (SO2) Testing for SF6 Gas Quality

Go back to Content Table ↑


2. Checking Control Cables and Wirings

Typically control cable tests are in two categories. First, the insulation integrity is tested using a 1000 volt source (Megger), which may be manual or motorized. The owner or manufacturer should be consulted for a site-specific procedure; however, the objective is to confirm that individual conductors are insulated from each other and the cable shield, if one is present.

The cable jacket integrity is also tested. The objective is to detect missing or damaged insulation. Successful tests should show high resistive readings.

The second category is a point-to-point continuity test to verify that the conductors are landed on the correct terminals. Installation personnel isolate the connections using slide links and then verify, using sound powered phones, buzzers, or similar equipment, that the connection is correct.

The installation crew should maintain records of the insulation tests and the point-to-point wiring checks. It is also a generally accepted procedure to trace the various protection, control, interlocking circuits, etc. during the point to point checks, and “yellow line” the associated electrical wiring or schematic drawings as the checks are made to verify the secondary circuit integrity.

Figure 2 – Here we see the control cabinet of a GIS substation bay protection cabinet. This particular cabinet is equipped with an IEC61850 protection network.

Here we see the control cabinet of a marine substation bay protection cabinet
Figure 2 – Here we see the control cabinet of a GIS substation bay protection cabinet. This particular cabinet is equipped with an IEC61850 protection network.

Go back to Content Table ↑


3. Bus Gas Leak Checks

Once the various GIS compartments have been processed and gas-filled, a second leak check may be recommended by the manufacturers, particularly for long bus runs. Each flange is covered by plastic and sealed with duct tape. A small stone is placed in the bottom of the plastic “bag.” This plastic “enclosure” remains for 12 to 24 hours.

An SF6 detection device is then inserted into the bag. If there are gas leaks, as SF6 is heavier than air, it will settle to the bottom of the plastic bag (see Figure 3) and activate the detector.

Figure 4 shows example of using SF6 gas detector.

Figure 3 – Flange gas leakage test

Flange gas leakage test
Figure 3 – Flange gas leakage test

Figure 4 – Gas zone leakage detectors

SF6 Gas Insulated Switchgear Gas Leak Check
Figure 4 – SF6 Gas Insulated Switchgear Gas Leak Check

Go back to Content Table ↑


4. Gas Density Monitor and Local Alarm Tests

This test involves keeping the gas density monitor wired but isolated electrically with open terminal block slide links or a similar switch mechanism, before mechanically isolating the density switch using appropriate valves. Bleed a small amount of gas off and using an ohmmeter at the terminal block, observe and record the alarm point.

Two-way radio or a similar communication may be required for large installations. In a similar manner slowly introduce some gas and as the pressure rises, observe the density switch reset point.

The test purpose is to verify the final wiring and actual alarm points.

Go back to Content Table ↑


5. Primary Circuit Resistance

Generally this test requires a 100 A DC μΩ meter with independent voltage and current sources. Tests are conducted on an assembled GIS section as specified by the manufacturer, isolating the circuit using a ground switch and removing its grounding strap.

The various GIS switches in the test circuit are configured to meet the measurement requirements, and with the current lead connected to the “floating” ground strap and the μΩ meter voltage lead connected to the ground switch enclosure, 100 A are injected into the circuit. The readings obtained are compared to engineering calculations, which may include a tolerance specification.

An acceptable field measurement agrees with the engineered calculation.

Suggested Guide (PDF) – Electrical Testing and Commissioning Handbook

Electrical Testing and Commissioning Handbook

Go back to Content Table ↑


6. SF6 Gas Quality Tests

Once the gas compartments are processed and filled to the correct pressure/density, gas purity tests are conducted (see Figures 5 and 6). These tests require a small amount of gas and identify the level of moisture present and the purity of the SF6. For new GIS equipment installations acceptable values are moisture levels in the 150 ppm to 300 ppm range and gas purity in the 99.5% range.

Some manufacturers decrease the acceptable parameters in older or reprocessed gas to 500 ppm moisture with a gas purity of 98%. These values should be recorded for maintenance baseline use when gas quality measurements are made in the future.

A table similar to Figure 5 should be prepared to record the individual gas zone SF6 moisture content and purity for future maintenance baseline comparison purposes.

Figure 5 – SF6 project gas inventory

SF6 project gas inventory
Figure 5 – SF6 project gas inventory

Pure SF6 serves as the typical filling in GIS; nevertheless, gas compartments can get contaminated with water vapor (H2O) over time due to absorption and desorption from interior materials. Although water vapor and SF6 typically do not interact, under high-energy discharge conditions, hydrogen and oxygen dissociated from water vapor will react with sulfur and fluorine from SF6, resulting in the formation of breakdown by-products.

These comprise sulfur dioxide (SO2) and hydrofluoric acid (HF), which are corrosive to the inside components of gas compartments.

SF6 with minimal water vapor content substantially diminishes the likelihood of generating these corrosive chemicals, therefore rendering precise and consistent measurement data an essential component of any GIS preventative maintenance program.

Figure 6 – SF6 Gas Analyzer

SF6 Gas Analyzer
Figure 6 – SF6 Gas Analyzer

Go back to Content Table ↑


7. Circuit Breaker Tests

Caution: before proceeding with any breaker operations tests, any closing or tripping prevention pins or lock devices should be identified. Depending on the test, the pins or lock devices may or may not be required.

The breaker operating pressures should also be verified to confirm and the circuit breaker is at full operating levels.


7.1 Mechanism Stroke, Wipe Measurement

These tests are generally performed at the factory and verified in the field to ensure that shipping or the installation procedure has not damaged the breaker mechanism or caused it to deviate from acceptable tolerance levels.

Manufacturers should provide the measurement technique and acceptable limits for both the stroke and main contact wipe.

This set of measurements is usually done when operating the circuit breaker manually (see Figure 7).

Figure 7 – Circuit breaker stroke measurement

GIS circuit breaker stroke testing
Figure 7 – GIS circuit breaker stroke testing

Go back to Content Table ↑


7.2 Open/Close Operation Including Anti-pumping

This test will confirm whether the circuit breaker properly opens and closes. One manual test is performed and then the necessary open and close operations at the operating control voltage, as identified in the specification, for example, open and close “X” times in a specified time.

The objective is to observe whether the lights and indicators work properly and the owner’s specification requirements are met.

Watch Video – Circuit Breaker motion measurement on a B65-145 GIS

The anti-pumping test involves closing and opening the breaker with a continuous signal on the close coil. If the anti-pumping circuit is properly functioning, the breaker should not re-close until the close coil is de-energized.

Go back to Content Table ↑


7.3 Breaker Travel and Timing Test

These tests are to confirm the dynamic operating performance of the breaker by measuring the operating times on a per pole basis and identifying any discrepancies or deviations with the phases. Manufacturers will typically provide the timing range and the maximum phase discrepancy limit. Any readings outside the manufacturer’s stated values should be investigated and adjustments made as necessary.

Figure 8 is typical instrumentation used to check circuit breaker contact timing.

Figure 8 – Circuit breaker time and travel analyser with DualGround™ testing by Megger

Circuit breaker time and travel analyser with DualGround™ testing by Megger
Figure 8 – Circuit breaker time and travel analyser with DualGround™ testing by Megger

Go back to Content Table ↑


7.4 Low Gas Tripping and Block Close Operations

This test is on the circuit breaker gas system to prove whether gas leakage detection (multiple alarm levels) is operational and the control limits, for example, serious loss of gas, will block close and prevent the breaker operation.

The manufacturer usually confirms that the tests are acceptable before a circuit breaker is placed in service.

Go back to Content Table ↑


8. Ground and Disconnect Switch and Circuit Breaker Interlock Tests

GIS equipment is generally provided with interlocks to prevent incorrect operations; for example, most disconnects are not designed for load break operation and similarly ground switches cannot be closed without interconnected circuit breakers and disconnects open.

The manufacturer’s interlock logic diagram should be reviewed to verify the various open and close combinations and confirm that incorrect operations are blocked. These interlock schemes should also be checked for correct integration into the owner’s protection and switching logic.

Figure 9 – Logic Table for Interlocking Circuit Breakers in the AC Supply Panel

Logic Table for Interlocking Circuit Breakers in the AC Supply Panel
Figure 9 – Logic Table for Interlocking Circuit Breakers in the AC Supply Panel

Go back to Content Table ↑


9. High Voltage Bus and Equipment Conditioning Tests

Before the GIS installations are placed in service, a high voltage conditioning test is performed with momentary voltages in excess of the equipment rated line-to-ground voltages. The objectives of the test are: to identify any abnormalities in the bus (loose hardware, tools, cleaning material inadvertently left in the bus) that could compromise the internal electrical clearances, identify excessive moisture levels and move conductive and semi-conductive materials to low stress areas or particle traps to prevent insulation flashovers.

The test voltage levels and time durations vary between manufacturers and are based upon the equipment voltage class, but for illustration purposes on a 362 kV class, 1050 BIL installation the test levels may be as shown in Table 12.

Table 1 – Test levels

StepStep (kV)Time (s)
110020
212515
317510
42252
52751
63001
73251
83501
94001

The high voltage test on site is usually done by a resonance test procedure. The inductance of the test transformer and the capacitance of the GIS are chosen in such a way that they form a resonance circuit in the range of 50–100 Hz.

This allows much smaller test equipment, which is shown in Figure 10.

Figure 10 – Variable Frequency high-voltage AC Resonant Test System

Variable Frequency high-voltage AC Resonant Test System
Figure 10 – Variable Frequency high-voltage AC Resonant Test System

The benefits of using a series resonant test is the inherently limited fault current available, compared to a fault energy present when the GIS equipment is connected to the transmission system. A typical test on 362 kV equipment will take approximately an hour. A three person team is recommended including a safety observer, a timer, and the test set operator.

The substation or switchyard low voltage (120/208 v, 220 v, 380 v, 277/440 v) station service connections and capacity should be identified early in the project. If insufficient capacity is available for the test set, a small portable generator may be required.

The GIS can be tested in multiple ways. To expedite the process, one methodology is to test large bus sections at once, taking into consideration the test set capacity. The disadvantage of this approach is that if a discrepancy is identified, the test section will need to be sectionalized into smaller increments to isolate the problem area. A second approach is to begin with smaller test sections, but this will require more test time.

During normal tests at the higher voltages, corona may be heard around the test set wire connected to the GIS bushing. The test fails, if the required voltages cannot be attained or the test set trips off before the peak voltage level is reached. Please note that if new GIS equipment is retrofitted to older designs and both sections must be tested concurrently, it may be prudent to reduce the test levels to avoid problems with the older equipment.

After a test failure, given the low energy involved using the test set, repeat tests can be performed to help isolate the problem. If possible the test section should be reduced with portions of bus systematically removed from the test, until the problem section is located. It may also be helpful to locate individuals at points along a bus to help locate the “ping” or audio noise that may occur when a flashover (test set trips) occurs inside the bus.

Personnel should be positioned in safe locations, well clear of the test set and its connections.

Watch Video – 560kVA 280kV AC Resonance Test Set Wiring Video

Go back to Content Table ↑


10. Instrument Transformer Tests

Current and voltage transformer tests include polarity, ratio, and current transformer saturation curves. These tests require voltage and current injection and are equivalent to testing conducted on similar air insulated equipment.

The results are compared to the manufacturer’s published data.

Further Study – Comprehensive Guide to Secondary Injection Testing of the Current Transformers (Part 1)

Comprehensive Guide to Secondary Injection Testing of the Current Transformers (Part 1)

Further Study – Comprehensive Guide to Secondary Injection Testing of the Current Transformers (Part 2)

Comprehensive Guide to Secondary Injection Testing of the Current Transformers (Part 2)

Go back to Content Table ↑


11. Other Tests/Records

11.1 AC Station Service Measurements, Heater & Control Cabinet Light Operations

This work involves checking the heater circuits for current with a clamp-on ammeter, observing correct light operations using a door or manual switch, confirming all power receptacles are operational, and checking for tight connections.

Ground fault protection should be provided for receptacles particularly if the local control or marshalling cabinet is located outdoors. Three phase 60 or 100 A disconnects with independent power sources located on the exterior of the local control or marshalling cabinets may also be convenient to connect welders or gas cart/processing equipment.

The equipment and control cabinet heater test results MUST be recorded. The circuit breaker and other heaters in the GIS primary circuit are critical, particularly in cold climates to prevent SF6 liquefying and loss of gas density. Heaters may also be required at transition points between heated indoor locations and outdoors.

Thermostatic control settings (if used) should also be verified and the levels recorded.

Figure 11 – AC control circuits: heater circuit, AC load circuit, and lighting circuit (click to zoom)

AC control circuits: heater circuit, AC load circuit, and lighting circuit
Figure 11 – AC control circuits: heater circuit, AC load circuit, and lighting circuit

Figure 12 – GIS local control cabinet

GIS local control cabinet
Figure 12 – GIS local control cabinet

Go back to Content Table ↑


11.2 Final Circuit Breaker Counter Readings

Before equipment is made available for owner operations personnel, all circuit breaker counters are recorded and the values entered in the commissioning records.

Go back to Content Table ↑


11.3 Turnover Gas Zone Density Readings

In a similar manner, all gas zone pressures are recorded including circuit breakers on a compartment, per phase if an iso-phase bus is installed. The bus temperature is also recorded and the pressure reading temperature-compensated.

The value obtained is compared to the engineered nominal value with acceptable readings are within the engineered value.

Please note that some owners/operators may prefer gas density gages with numerical readings. In other designs a color coded gage may be acceptable with the gage needle in the green area on the gage face indicating satisfactory, the yellow area indicating caution or investigation of a potential leakage situation and the red area requiring immediate action and potentially a significant problem.

The gas density gauge design should be discussed during the initial engineering discussions.

Further Study – Primary injection testing and CTs commissioning in power substations

Primary injection testing and CTs commissioning in power substations (for true engineers)

Go back to Content Table ↑


12. Attachments (DWG): AutoCAD Drawings of Switching Single-Line Diagram and Interlocking Table for 380kV GIS Switchgear

Download Attachments: AutoCAD Drawings of Switching Single-Line Diagram and Interlocking Table for 380kV GIS Switchgear (for premium members only):

Membership Upgrade Required

This content is not available in your premium membership plan. Please upgrade your plan in order to access this content. You can choose an annually based Basic, Pro, or Enterprise membership plan. Subscribe and enjoy studying specialized technical articles, online video courses, electrical engineering guides, and papers.
With EEP's premium membership, you get additional essence that enhances your knowledge and experience in low- medium- and high-voltage engineering fields.
Good to know: - Save 50% on all video courses with Enterprise plan.
Upgrade
Already a member? Log in here

Go back to Content Table ↑

Sources:

  1. Gas-Insulated Substations by Hermann Koch

Premium Membership

Get access to premium HV/MV/LV technical articles, electrical engineering guides, research studies and much more! It helps you to shape up your technical skills in your everyday life as an electrical engineer.
More Information
Edvard Csanyi - Author at EEP-Electrical Engineering Portal

Edvard Csanyi

Hi, I'm an electrical engineer, programmer and founder of EEP - Electrical Engineering Portal. I worked twelve years at Schneider Electric in the position of technical support for low- and medium-voltage projects and the design of busbar trunking systems.

I'm highly specialized in the design of LV/MV switchgear and low-voltage, high-power busbar trunking (<6300A) in substations, commercial buildings and industry facilities. I'm also a professional in AutoCAD programming.

Profile: Edvard Csanyi

Leave a Comment

Tell us what you're thinking. We care about your opinion! Please keep in mind that comments are moderated and rel="nofollow" is in use. So, please do not use a spammy keyword or a domain as your name, or it will be deleted. Let's have a professional and meaningful conversation instead. Thanks for dropping by!

Learn How to Design Power Systems

Learn to design LV/MV/HV power systems through professional video courses. Lifetime access. Enjoy learning!

EEP Hand-Crafted Video Courses

Check more than a hundred hand-crafted video courses and learn from experienced engineers. Lifetime access included.
Experience matters. Premium membership gives you an opportunity to study specialized technical articles, online video courses, electrical engineering guides, and papers written by experienced electrical engineers.
Whitepaper: How to Improve Risk Decisions for Power Systems - Prioritizing vulnerabilities with full operational context