Home / Technical Articles / The essentials of an automatic changeover systems in medium voltage networks
Automatic transfer switch (ATS)
In medium voltage distribution networks, it is important to maintain a high level of reliability. Industry relies on the continuous operation of critical plant, which requires no or little disruption to the electrical supply. There are various methods for building redundancy of supply into a system.
The most commonly used methods are a dual transformer fed supply and/or a standby generator sized to keep critical plant online. Automatic changeover systems are designed to monitor and maintain continuous supply.
Today’s technology allows the supervision and control of an entire distribution system from a single controller, referred to as an automatic transfer switch (ATS) or automatic changeover unit (ACU). Although there are a wide range of products available, they all have the same primary function.
The equipment monitors 3-phase voltages on all power sources. Power supply sources are often prioritized and if any phase voltage on the primary power source falls outside a predetermined range for a specific amount of time, the power source is switched over to a back-up supply. Once the primary power source is re-established, the power source is switched back to the primary power source.
In medium voltage systems, switching is performed using either contactors or circuit breakers. Most ATS controllers can control both types of switching devices.
Automatic changeover systems range from simple main/standby set-ups to highly complex distribution systems and this is where the selection of an appropriate ATS controller is important. Systems can be operated in automatic or
manual mode.
  • In AUTO mode, supervision and power source switching is carried out entirely by the ATS controller.
  • In MANUAL mode, power source switching is carried out by manual selection via the ATS controller.
NOTE! For safety reasons, manual mode cannot be used in certain network configurations.
Table of contents:
ATS Switching Devices
Typical Circuit Breaker Control
This information focuses on the double command operated (DCO) method of circuit breaker control. DCO control uses normally-open momentary contacts (ie pushbuttons) or a bistable relay to operate the shunt closing and opening coils. Some circuit breakers use voltage fed open and close command signals while others use volt-free signals.
Medium voltage circuit breakers can be vacuum or gas (SF6) insulated, with magnetic or motor charged spring operation.
Here are some examples of various double command operated (DCO) control methods:
Wiring diagram #1
Motor operated circuit breaker using voltage fed open and close command signals via momentary contact pushbuttons
Figure 1 – MV circuit breaker control diagram: Motor operated circuit breaker using voltage fed open and close command signals via momentary contact pushbuttons
  1. Auxiliary supply
  2. Motor (spring charge)
  3. Close shunt coil
  4. Open shunt coil
  5. Circuit breaker controller
  6. External trip contact (eg. from motor protection relay)
Wiring diagram #2
Magnetic operated circuit breaker using volt-free open and close command signals via bistable relay contacts
Figure 2 – MV circuit breaker control diagram: Magnetic operated circuit breaker using volt-free open and close command signals via bistable relay contacts
  1. Auxiliary supply
  2. Circuit breaker control (open/close)
  3. Circuit breaker controller
  4. External trip contact (eg from motor protection relay)
  1. Control supply
  2. Command inputs (common, close, open)
Go back to Table of Contents ↑
Typical Contactor Control
Medium voltage contactors genarlly have two methods of control:
  1. Single command operated control (SCO) – this requires a permanent signal to close and maintain the contactor in the closed position. Removal of the control signal will open the contactor.
  2. Double command operated control (DCO) – this requires two separate momentary contacts; one for the close command and one for the open command. The DCO control method typically uses normally open, spring return pushbuttons for both the open and close commands.
Typically, command signals require an external voltage source and the contactor controller itself requires a separate auxiliary voltage source. Depending on the contactor make and model, electrical options are available.
Some examples are shown in Table 1 below:
Table 1 – Electrical options of a contactor and their descriptions
Electrical optionDescription
Undervoltage shunt tripOnly used with DCO control.
Lock-out solenoidNeeds to be externally energised before contactor main poles can be electrically operated.
Racking solenoidNeeds to be externally energised before a withdrawable contactor can be moved between the test and service positions.
Auxiliary contactsIndicate the electrical state of the main contactor poles.
Racking contactsIndicate whether a withdrawable contactor is in the service or test position.
Fuse blow indicator contactsIndicate fuse condition. Operated by striker pin and only available on contactors with integral medium voltage fuses
The following examples show typical contactor control circuits:
Wiring diagram #1
Single command operated contactor control (typical)
Figure 3 – MV contactor control diagram: Single command operated contactor control (typical)
  1. Auxiliary supply
  2. Contactor controller
  3. Control signal (maintained)
  1. Control supply
  2. Command input
Wiring diagram #2
Double command operated contactor control (typical)
Figure 4 – MV contactor control diagram: Double command operated contactor control (typical)
  1. Auxiliary supply
  3. External trip contact (eg. from motor protection relay)
  1. Control supply
  2. Close input
  3. Open input
Operating modes in automatic changeover systems
The following are examples of common operating modes in automatic changeover systems. Most ATS controllers can be programmed to operate in any one of these modes.
N1+N2 mode
N1+N2 operating mode in automatic changeover systems
Figure 5 – N1+N2 operating mode in automatic changeover systems
AUTO mode with line priority:
N1 is the prioritized power source and, if healthy, will always supply the receiving network (DB). If N1 is lost, the controller switches over to power source N2. The controller switches back to N1 once it has been re-established.
AUTO mode without line priority:
The first power source verified as healthy will supply the receiving network (DB). If this power source is lost, the other power source will be selected and remain as the supply as long as it is healthy.
If both power sources are lost, both sources N1 and N2 are isolated from the receiving network (DB).
MANUAL mode:
Select N1 or N2 as the power source.
N1+G mode
N1+G operating mode in automatic changeover systems
Figure 6 – N1+G operating mode in automatic changeover systems
AUTO mode:
N1 is the prioritized power source and, if healthy, will always supply the receiving network (DB). If power source N1 is lost, the controller commands the standby generator to start. Once the generator is at correct voltage and frequency, power source G is switched in to supply the receiving network (DB). The controller switches back to N1 once it has been re-established.
MANUAL mode:
Select N1 or G as the power source.
N1+N2+N3 mode
N1+N2+N3 operating mode in automatic changeover systems
Figure 7 – N1+N2+N3 operating mode in automatic changeover systems
N1 is the prioritized power source and, if healthy, will always supply the receiving network (DB). If N1 is lost, the controller switches over to power source N2. If power source N2 is lost, the controller switches over to power source N3.
The first power source verified as healthy will supply the receiving network (DB). If this power source is lost, the next healthy power source is selected and will remain as the supply as long as it is healthy. The order of power source selection is normally predetermined, eg N1 then N2 then N3.
MANUAL mode:
Select N1 or N2 or N3 as the power source.
N1+N2+G mode
N1+N2+G operating mode in automatic changeover systems
Figure 8 – N1+N2+G operating mode in automatic changeover systems
If both power sources N1 and N2 are lost, the controller commands the standby generator to start. Once the generator is at correct voltage and frequency, power source G is switched in to supply the receiving network (DB). The controller switches back to the first re-established power source N1 or N2.
MANUAL mode:
Select N1 or N2 or G as the power source
N1+N2+S mode
N1+N2+S operating mode in automatic changeover systems
Figure 9 – N1+N2+S operating mode in automatic changeover systems
AUTO mode:
Providing power sources N1 and N2 are healthy, N1 will supply network DB1 and N2 will supply network DB2. Bus coupler S will remain open.
If power source N1 is lost, this supply is isolated and bus coupler S is closed. Power source N2 now supplies networks DB1 and DB2. Once power source N1 is re-established, bus coupler S is opened and N1 will supply network DB1 and N2 will supply network DB2.
If power source N2 is lost, this supply is isolated and bus coupler S is closed. Power source N1 now supplies networks DB1 and DB2. Once power source N2 is re-established, bus coupler S is opened and N1 will supply network DB1 and N2 will supply network DB2.
MANUAL mode:
Select N1 and N2 as power sources with bus coupler S open. Select power source N1 with bus coupler S closed and power source N2 isolated. Select power source N2 with bus coupler S closed and power source N1 isolated.
Source: Medium voltage guide by Aucom
  1. Afam-Anadu, Uche
    Jan 28, 2024
    I want practical knowledge on the following areas:
    1. Electrical Power Supply and Distribution for both commercial buildings and industrial installations
    2. Practical knowledge in Industrial Automation & programming
    3. Practical knowledge in Industrial Instrumentation
    Please kindly advise how EEP can be of help
  2. Sabry Abbas
    Mar 10, 2023
    Need to make interlock between two incoming feeders, always one in service and when the power is lost automatically transfer to other supply feeder, this foe 22 kv
  3. Victor
    Nov 12, 2020
    I love the Explanation,I wish you could help me with more practicals
    Thanks.
  4. Amos
    Oct 30, 2020
    Hello IAM studying electrical engineering
    Power option so I need to get in contact with an engineer to guide me in what is expected thanks
  5. Thomas
    Nov 04, 2019
    The way we have explained good
    I need more practical I want you to
    Train me
Leave a Reply to Sabry Abbas
seventy three  −    =  sixty eight
