Home / Technical Articles / MV network diagrams for feeding secondary switchboards and MV/LV transformers
MV network diagrams
Let’s take a look at the main MV network diagrams and structures used to feed secondary switchboards and MV/LV transformers. The complexity of the diagrams differs, depending on the level of power supply security required. Note that there are many other variations of presented medium voltage network diagrams, we shall focus on the five most common.
MV network diagrams for feeding secondary switchboards and MV/LV transformers (photo credit: Leonhard Weiss)
The following MV network supply arrangements are the ones most commonly adopted.
  1. Single fed radial network
  2. Dual fed radial network with no coupler
  3. Dual fed radial network with coupler
  4. Loop systems:
    1. Open loop
    2. Closed loop
  5. MV parallel feeder
MV single fed radial network
Figure 1 – MV single fed radial network
Network characteristics:
  • The main switchboard is fed by 2 sources with coupler.
  • Switchboards 1 and 2 are fed by a single source, and there is no emergency back-up supply.
This structure should be used when service continuity is not a vital requirement and it is often adopted for cement works networks.
Go back to contents ↑
MV dual fed radial network with no coupler
Figure 2 – MV dual fed radial network with no coupler
  • The main switchboard is fed by two sources with coupler.
  • Switchboards 1 and 2 are fed by two sources with no coupler, the one backing up the other.
  • Service continuity is good. The fact that there is no source coupler for switchboards 1 and 2 means that the network is less flexible to use.
MV dual fed radial network with coupler
Figure 3 – MV dual fed radial network with coupler
  • Switchboards 1 and 2 are fed by 2 sources with coupler. During normal operation, the bus coupler circuit-breakers are open.
  • Each bus section can be backed up and fed by one or other of the sources.
This structure should be used when good service continuity is required and it is often adopted in the iron and steel and petrochemical industries.
4. Loop system
This system should be used for widespread networks with large future extensions. There are two types depending on whether the loop is open or closed during normal operation.
Open loop (see Figure 1-20a)
MV open loop system
Figure 4 – MV open loop system
  • The loop heads in A and B are fitted with circuit-breakers.
  • Switchboards 1, 2 and 3 are fitted with switches.
  • During normal operation, the loop is open (in the figure it is normally open at switchboard 2).
  • The switchboards can be fed by one or other of the sources.
  • Reconfiguration of the loop enables the supply to be restored upon occurrence of a fault or loss of a source.
    (The loop heads at A1 and B1 are fitted with circuit-breakers, and phase and earth fault protection devices. The substations are fitted with switches. Fault detectors are installed on each switch. They indicate the passage of a fault current.)
This reconfiguration causes a power cut of several seconds if an automatic loop reconfiguration control has been installed. The cut lasts for at least several minutes or dozens of minutes if the loop reconfiguration is carried out manually by operators.
Closed loop
MV closed loop system
Figure 5 – MV closed loop system
  • All the loop switching devices are circuit-breakers.
  • During normal operation, the loop is closed.
  • The protection system ensures against power cuts caused by a fault.
    (Each link end is fitted with a circuit-breaker. During normal operation, the loop is closed. The protection systems will allow power cuts to be avoided when a fault occurs.).
This system is more efficient than the open loop system because it avoids power cuts. However, it is more costly since it requires circuit-breakers in each switchboard and a complex protection system.
MV parallel feeder
MV parallel feeder network
Figure 6 – MV parallel feeder network
  • Switchboards 1, 2 and 3 can be backed up and fed by one or other of the sources independently.
This structure should be used for widespread networks with limited future extensions and that require good supply continuity.
Reference // Protection of Electrical Networks by Christophe Prévé
  1. Bezabih Tegegn
    Oct 21, 2019
    thanks bro for all
  2. NguyenCao Ky
    Oct 21, 2019
    Thanks so much
  3. José Aular
    Oct 20, 2019
    Excellent!. Thank you
  4. Leone Takeshi Uema
    Apr 02, 2018
    Gostei da apresentação, gostaria de receber mais matérias sobre assuntos Tecnco.
  5. ADOLFO PONCE DE LEON
    Aug 04, 2017
    edvard I was paid to develo procedures e . specially years ago when it was protected . interesting that I am not copmpemsaed for comtributig to your site. on the subject matter.
    very clever. God speed.
Leave a Reply to José Aular
4  ×    =  sixteen