Home / Technical Articles / The essentials of overcurrent protection you are not allowed to forget (types and principles)
Back to how it works…
Relay protection is nowadays completely digitalized and very sophisticated; there is no doubt about that. But, do electrical engineers really understand what they do when setting parameters and navigate through endless menus on a relay? Most engineers do know, of course, but the memory naturally fades over time, and it’s a good thing to refresh the basics you learned many years ago.
Overcurrent protection is often confused with overload protection which is related to the thermal capability of circuits. Overcurrent protection is primarily provided for the correct clearance of faults. Very often, engineers adopt settings that make some compromise in order to cover both of these protection objectives.
Overcurrent protection in low- and medium voltage networks can be achieved by the use of fuses, by direct-acting trip mechanisms on circuit breakers or by protection relays.
This technical article covers the essentials of overcurrent protection principles and rules.
  1. Types of overcurrent system
    1. Overcurrent and earth-fault protection systems
    2. Grading of current settings
    3. Grading of time settings: the definite-time system
    4. Grading by both time and current: inverse-time overcurrent systems
      1. Fuses
      2. Delayed action a.c. trip coils
      3. Fuse shunted a.c. trip coils
      4. Inverse-time relays
  2. Selection of overcurrent protection settings
    1. Data needed for system analysis
Where a source of electrical energy feeds directly to a single load, a little complication in the circuit protection is required beyond the provision of an overcurrent device that is suitable in operating characteristics for the load in question, i.e. appropriate current setting possibly with a time-lag to permit harmless short time overloads to be supplied.
Development of the power system to one such as is shown in Figure 1, in which the power source A feeds through a number of substations B, C, D, and E, from each of the busbars of which load is taken necessitates a more selective treatment.
It is usually not good enough to shut down the whole system for every fault along the line. The system requires discriminative protection designed to disconnect the minimum amount of circuit and load that will isolate the fault.
Circuit breakers are installed at the feeding end of each line section and a graded scheme of protection is applied.
Figure 1 – Radial distribution system
Go back to Contents Table ↑
1.1 Overcurrent and earth-fault protection systems
Overcurrent protection involves the inclusion of a suitable device in each phase since the object is to detect faults that may affect only one or two phases. Where relays are used, they will usually be energized via current-transformers, which latter are included in the above statement.
Typical arrangements are shown in Figure 2 below.
The magnitude of an inter-phase fault current will normally be governed by the known impedances of the power plant and transmission lines; such currents are usually large.
Figure 2 – Types of overcurrent protection
Phase-to-earth fault current may be limited also by such features as:
  1. the method of earthing the system neutral
  2. the characteristics of certain types of plant, e.g. faults on delta-connected transformer windings
  3. resistance in the earth path.
In consequence, earth-fault current may be of low or moderate value and also often rather uncertain in magnitude particularly on account of item (c) above.
The protection is often required to have a high sensitivity to earth faults, i.e. earth-fault settings are often required to be lower than system rating. Response to an earth fault at a lower current value than system rating or loading is achieved by the residual connection shown in Figure 3.
Three current transformers, one in each phase, have their secondary windings connected in parallel, and the group connected to a protective device, either a circuit-breaker tripping coil or a relay.
Figure 3 – Residual circuit and earth-fault relay
With normal load current, the output of such a group is zero, and this is also the case with a system phase-to-phase short circuit. Only when current flows to earth is there a residual component that will then energize the protective device. Since the protection is not energized by a three-phase load current, the setting can be low, giving the desired sensitive response to earth-fault current.
Phase-fault and earth-fault protection can be combined, as shown in Figure 4. The protection scheme, involving equipment at a series of substations, can be graded in various ways, the significance of which is examined below.
Figure 4 – Combined phase and earth-fault protection
1.2 Grading of current settings
If protection is given to the system shown in Figure 1 by simple instantaneous tripping devices, set so that those furthest from the power source operate with the lowest current values and progressively higher settings apply to each stage back towards the source, then if the current were to increase through the range of settings, the device with the lowest setting of those affected would operate first and disconnect the overload at the nearest point.
Faults, however, rarely occur in this way: a short circuit on the system will immediately establish a large current of many times the trip settings likely to be adopted and would cause all the tripping devices to operate simultaneously.
The position would appear to be better when the feeder sections have sufficient impedance to cause the prospective short-circuit current to vary substantially over the length of the radial system, as indicated in Figure 5 below.
One might attempt to set the circuit breaker trips to just operate with the expected fault current at the end of the associated feeder section, but this would not be successful since:
Reason #1 – It is not practicable to distinguish in magnitude between faults at F1 and F2, since these two points may, in the limit, be separated by no more than the path through the circuit breaker. The fault current at the alternative fault locations will then differ by only an insignificant amount (e.g. 0.1% or less) necessitating an unrealistic setting accuracy.
Reason #2 – In the diagram, the fault current at F1 is given as 8800 A when the source busbar fault rating is 250MVA. In practice the source fault power may vary over a range of almost 2:1 by, for example, the switching out of one of two supply transformers; in some cases a bigger range is possible.
A minimum source power of 130 MVA may be assumed for illustration in this example, for which the corresponding fault current at F1 would be only 5400 A and for a fault close up to Station A the current would be 6850 A. A trip set at 8800 A would therefore not protect any of the relevant cable under the reduced infeed conditions.
It is, therefore, clear that discrimination by current setting is not in general feasible.
Figure 5 – Radial system with variation in fault current due to feeder impedance
A single exception to the above deduction occurs when there is a lumped impedance in the system. Where, as in the last section of Figure 5, the line feeds a transformer directly, without other interconnections, there will be a significant difference in the fault current flowing in the feeder for faults, respectively, on the primary and on the secondary side of the transformer.
In many cases, it is possible to choose a current setting that will inhibit operation for all secondary-side faults, while ensuring operation for all primary side faults under all anticipated infeed conditions. The transformer is not necessarily adequately protected by such high set protection.
In special cases, instantaneous relays with high settings are used as a supplementary feature to other protection systems.
1.3 Grading of time settings: the definite-time system
The problem discussed in the preceding Section is resolved by arranging for the equipment which trips the circuit breaker most remote from the power source, to operate in the shortest time, each successive circuit breaker back towards the supply station being tripped in progressively longer times; the time interval between any two adjacent circuit breakers is known as the ‘grading margin‘.
In this arrangement, instantaneous overcurrent relays are used in the role of starters or fault detectors. They could, in principle, have identical settings but are better with graded current settings increasing towards the supply station.
All settings are subject to tolerance. If all relays were given the same nominal setting, some would in fact operate at a lower current value than others. If the current were to be raised into the tolerance band, the relay with the lowest operating current would operate first. This relay might be located at the supply end of the feeder and would shut down the entire system.
These fault-detector relays initiate the operation of d.c. definite time relays, which are set to provide the required time grading. This system is therefore known as ‘definite-time overcurrent protection‘.
Referring to the radial system of Figure 1, busbar E feeds separate circuits through fuses. A relay at D might have an instantaneous operation with a high current setting which will not permit operation with a fault at E. Alternatively, if this is not feasible on account of the range of possible current, a lower current setting, but one above the maximum load current, may be used with a time setting chosen to discriminate with the fuse blowing.
Usually, a time lag of 0.2 s is sufficient, although it is desirable to check the suitability of this value for a fault current equivalent to the overcurrent element setting.
The relay at C may be set to operate in 0-5 s longer than that at D, i.e. in 0.7 s, and those at B and A will be progressively slower by the same amount, giving an operating time for relay A of 1.7 s.
Since the timing is not related to fault current but is based only on position, the difficulty that was discussed for current grading does not exist here. A fault at any point will be removed by tripping the nearest circuit breaker on the supply side, which will occur before any of the others which carry the fault current have time to operate. The minimum amount of power system is thereby isolated, although, for a fault on any but the last section, some disconnection of unfaulted sections and loss of load is inevitable.
The only disadvantage with this method of discrimination is that faults close to the power source, which will cause the largest fault current is cleared in the longest time.
At substations B, C, and D, loads are connected through transformers. The time setting on these circuits is selected in the same way as that at D on the feed to E and should never be greater than that on the outgoing feeder from the same busbars.
1.4 Grading by both time and current: inverse-time overcurrent systems
The disadvantage of the definite time system mentioned above is reduced by the use of protective devices with an inverse time-current characteristic in a graded system. Figure 6 shows two time-current curves in which the operating time is in inverse ratio to the excess of current above setting.
An exact inverse ratio has been used in this diagram in order that it may be seen that the effects obtained in the grading are general and not related to any specific device other than that the device has an inverse type of characteristic.
Figure 6 – Principle of inverse time-grading
The two curves correspond to protective devices having the same current setting, whilst curve A shows twice the operating time as does curve B for any current value. The current scale is in multiples of setting current.
Two sections of a radial system A-B- etc. protected at A and B by the corresponding devices are shown with a fault in alternative positions immediately after stations A and B. Fault F1 following station B produces 5 times setting current in both devices which tend to operate in 0.5 and 1.0 s, respectively. There is therefore a ‘grading margin’ of 0.5 s whereby the fault can be expected to be cleared at B and protective device A will reset without completing its full operation.
Alternatively, if fault F2 occurred, the fault current through A is now 8.5 times the setting, and device A will operate in 0.59 s which is a little slower than device B with close-up fault F1.
Had the current step been greater, the best operation of A might have been even faster than that for B, although such a gain in speed is unusual in practice. This gain can be made at every stage of grading for a multisection feeder so that the tripping time, for a fault close up to the power source, maybe very much shorter than would have been possible with a definite-time system.
Inverse-time overcurrent systems include:
  1. Fuses
  4. Inverse-time relays.
1.4.1 Fuses
The fuse, the first protective device, is inverse-time graded protection. Although fuses are graded by the use of different current ratings in series, discriminative operation with large fault currents is obtained because the fuses then operate at different times.
This continues to be effective even when the clearance times are very short because the fuse constitutes both the measuring system and the circuit breaker, whereas, with a relay system, a fixed time margin must be provided to allow for circuit-breaker clearance time.
Suggested reading – Dos and don’ts in operating circuit breakers, relays, disconnectors & fuses
Dos and don’ts in operating LV/MV circuit breakers, relays, disconnectors and fuses
1.4.2 Delayed action trip coils
Grading can be achieved by fitting delaying devices direct to the circuit-breaker trip mechanism. Dash-pots have been used for this purpose but unfortunately, these devices are not sufficiently accurate or consistent to permit more than relatively crude grading.
1.4.3 Fuse-shunted trip coils
This form of protection consists of an a.c. trip coil on the circuit breaker, shunted by a fuse. The circuits for overcurrent and combined overcurrent and earth fault are shown in Figure 7.
The resistance of the fuse and its connections is low compared with the impedance of the trip coil, and consequently, the majority of the current, supplied by the current transformer, passes through the fuse. If the current is high enough when a fault occurs, the fuse blows, and the current is then transferred to the trip coil.
Figure 7 – Arrangements for fuse-shunted trip coils
The time taken, from the instant when the fault occurs, for the circuit breaker to trip is thus mainly dependent on the time/current characteristics of the fuse.
Some error is introduced by the current which is shunted from the fuse through the trip coil, but this can be made small. The coil and its associated circuit should have an impedance of many times that of the smallest fuse that is to be used. The impedance of the coil must be low enough, however, to not unduly overburden the current transformer, when the fuse blows.
It is now standard practice to employ 2 A trip coils with current transformers of 5 A secondary rating and to use 2.5, 5.0, 7.5 or 10 A fuses as required. The rating of a time-limit, the fuse is generally specified in terms of the minimum current required to cause the fuse to blow, whereas, in the usual application of a fuse, its rating is the maximum current which can be carried continuously without deterioration.
In the design of the circuit, the fuses should be connected directly, not through isolating plugs, to the current transformers, to avoid the inclusion of additional resistance in the fuse circuit.
Figure 8 – Time/fusing current characteristics of time-limit fuses
Figure 8 shows typical time/current characteristics for time-limit fuses. It will be noted that the difference in operating time between any two ratings of fuse decreases as the current increases. These differences constitute the discrimination time. Unlike main fuse protection, this margin must not be reduced to a very low value, since it must cover the tripping time of the circuit breaker. Thus for a 0.5 s margin the fault current must not exceed a certain limit.
For example, for a current of 37 A, there is 0.5 s between the time for blowing a 5 A and a 7.5 A fuse. If these fuses were used in conjunction with 300/5 A current transformers, for the protection of two sections of a radial feeder, the maximum fault current at the beginning of the second section, that is at the sending end of the second feeder, must not exceed:
37 x 300 / 5 = 2220A
If the maximum fault current at this location could be higher, it would be necessary to use a larger rating for the first section fuse. It would then be necessary to decide whether this is admissible under considerations of minimum fault current, or of desired overload protection.
Figure 9 – Application of time-limit fuses
As an example in the application of this form of protection, Figure 9 shows a radial feeder, using graded time-limit fuses, and shows in graphical form the characteristics of the fuses and the discrimination obtained. The current scale of primary current allows for the current-transformer ratios, in this case uniformly of 300/5 A.
In practice, the limits imposed by the maximum permissible fault currents preclude a more extensive use of this form of protection. In addition, the fuses have not proved to be entirely satisfactory; their characteristics can be changed by through-fault current and also by aging.
In view of this, all fuses that have carried fault current even if apparently sound should be replaced with new fuse links.
1.4.4 Inverse-time overcurrent relays
Relays designed to provide an inverse characteristic are both more reliable and provide more scope for precise grading than the above techniques. The relays are adjustable over a wide range in setting current and operating time.
Typical current-time characteristics are shown in Figure 10. Curve A is the most commonly used characteristic and is standardized by BS 142: Parts 1-4.
Figure 10 – Typical time curves for IDMTL relays
It will be noted that the curve, although nominally inversive, departs from an exact ratio at each end due to the effects of mechanical restraint and saturation of the electromagnet. Steeper characteristics curves B and C are known as ‘very inverse’ and ‘extremely inverse’ characteristics, respectively, and have special applications.
It will be observed that the characteristic curves are plotted with an abscissa of ‘plug setting multiplier’. Relays can have many different settings for which there are as many time-current curves. This cumbersome state of affairs is simplified by realizing that a relay of a given type always has the same ampere-turn loading of its winding at setting and for each operating time point, the coil turns to be in inverse ratio to the setting.
It follows that a curve plotted in terms of multiples of setting current is applicable to all relays of that type and at all plug settings. Taking into account the current transformer with which the relay is used we can write:
plug setting multiplier (p.s.m.) = primary current / primary setting current
The ordinate is the operating time scale for maximum disc movement. Restricting the movement by setting forward the backstop proportionately reduces the operating time, the ratio of such reduction applying at all current levels and hence being known as the time multiplier setting (t.m.s.). When the curve is plotted with logarithmic scales, the effect is to displace the basic curve downwards, maintaining the original curve shape. Because of certain small errors in the constancy of the time multiplier over the current range, a family of curves with t.m.s, from 0.1 to 1.0 is sometimes given by the relay manufacturer.
The principle of grading is generally similar to that of the definite-time system. For any fault, the relays in a series system are graded so that the one nearest to the fault trips the associated breaker before the others have time to operate.
A grading margin of 0.4 or 0.5 s is usually sufficient.
2.  Selection of overcurrent settings
It will be clear from the generalized discussion above that a knowledge of the fault current that can flow is essential for correct relay application. Since large-scale power-system tests are normally impracticable, fault currents must be calculated.
It is first necessary to collect system data and then to calculate maximum and minimum fault currents for each stage of grading. Time-grading calculations are made using the maximum value of fault current; the grading margin will be increased with lower currents so that discrimination, if correct at the highest current, is ensured for all lower values.
Minimum fault currents (i.e. short-circuit current with a minimum amount of feeding plant or circuit connections) are determined in order to check that current settings are satisfactory to ensure that correct operation will occur.
2.1 Data needed for system analysis
Some or all of the following data may be needed:
  1. A single-line diagram of the power system, showing the type of all protective devices and the ratio of all protective current transformers.
  2. The impedances in ohms, percent or per unit, of all power transformers, rotating machines, and feeder circuits.
  3. It is generally sufficient to use machine transient reactance, and to use the symmetrical current value; subtransient effects and offset are usually of too short duration to affect time-graded protection.
  4. The starting current requirements of large motors and the starting and stalling times of induction motors may be of importance.
  5. The maximum peak load current is expected to flow through protective devices. ‘Peak load’ in this context includes all short-time overloads due to motor starting or other causes; it does not refer to the peak of the current waveform.
  6. Decrement curves showing the rate of decay of the fault current supplied by generators.
  7. Excitation curves of the current transformers and details of secondary winding resistance, lead burden, and other connected burdens.
Not all the above data is necessary in every case; with discretion, some items may be deemed to be irrelevant.
The maximum and minimum values of short-circuit currents that are expected to flow through each protective device are calculated. Three-phase short-circuit calculations are adequate for phase-fault studies and are relatively simple.
Earth-fault current and its distribution through the system should also be examined. This will be necessary if the system is earthed through a limiting impedance, in cases of multiple solid earthing, and also if the ratio of phase-fault current to overcurrent setting is not large.
Earth-fault calculations will be required whenever earth-fault relays are used but should be made also in the above cases, even if only overcurrent elements are included since in any case earth faults will have to be covered by the protection.
Suggested reading – A real-life case study of relay coordination (step by step tutorial with analysis)
Source: Power system protection by The Institution of Electrical Engineers
  1. Guillermo Hernandez
    Feb 19, 2023
    Thanks. Very good lesson
  2. Win Naing Lwin
    Dec 03, 2022
  3. Syed Muzaffar Ahmad
    Jun 13, 2022
    Please have article on wirring diagrams.of 33 kv breakers and C&R panels.
  4. Syed Muzaffar Ahmad
    Jun 13, 2022
    For me very helpful article
  5. GIRMA wolde
    Jan 24, 2022
    go head its very important lessen
Leave a Reply to Syed Muzaffar Ahmad