Substation Control and Protection

Relay protection and the whole bunch of protection system engineering around the substation are quite interesting from the point of view of creativity. The Control and Protection System technology in a substation is very important because it watches over, protects, and manages the flow of electricity. Because substations are getting more complicated, more power is being sent, and fault currents are getting higher, which means that control and safety equipment has to work better.

Practical Design Rules for Protection System Engineers
Practical Design Rules for Protection System Engineers

The main goals are to have the lowest possible life cycle costs and the most reliable service available. To get total reliability, it’s also important that the system is flexible and easy to manage.

To get low life cycle costs, it’s important to pick the right main equipment, whether to use AIS, GIS, or hybrid switchgear, the switching arrangement, the transformer size, and other things. Then decisions are made about the control and protection equipment, such as whether to use traditional or computerized control equipment, single or redundant protection systems, the design and voltage of the battery system, the type of battery to use, and so on.

When making decisions, it’s important to think about how things will likely go in the future. Any changes made later will always cost a lot more than a choice made at the start that took future needs into account.

Some general rules for Engineering of Protection System are given in this scientific article. These could be improved by the utility if it thought it was important based on its own needs and ways of doing things. SCADA systems control and watch, send signals, and record events most of the time these days. This article doesn’t talk about how to design a SCADA system.

Table of Contents:

  1. Engineering Of Protection System:
    1. Redundancy (Two Groups of Protection Systems)
    2. Instrument Transformer Circuits
    3. Physical Location of Relay Protection Panels
    4. Exchange of Information Between Two Subsystems:
      1. Start and Block of Auto-Reclose
      2. Start of Breaker Failure Protection
    5. Arrangement of Trip Circuits
    6. Trip Unit
    7. Direct Trip of Remote End Breaker
    8. Trip Circuit Supervision
    9. Cabling
    10. Capacitive Discharges
    11. Alarming and Testing
    12. Design Of Fault Clearing System
  2. DC Distribution (Auxiliary Power System):
    1. DC Distribution to Different Equipment
    2. DC Supervision
  3. Design Of Control and Protection Panel:
    1. Terminals Inside a Panel
  4. Fault Signaling
  5. Interlocking
  6. Documentation
  7. BONUS! Download Guide for the Operation and Maintenance of Power Plant Equipment (PDF)

1. Engineering Of Protection System

1.1 Redundancy (Two Groups of Protection Systems)

In cases when there are two sets of direct current (DC) sources, the relays are electrically and physically split into two groups in order to achieve redundancy and facilitate the removal of a protection for maintenance purposes while the protected equipment is in operation. The process of grouping is implemented to the maximum extent feasible, ensuring that each group is capable of autonomously performing protective functions with almost equal redundancy.

The establishment of interconnection between these two groups is generally not recommended. Nevertheless, if it is absolutely essential, the level of linkage should be limited to the absolute minimum.

A common technique employed in redundant systems is:

  1. The utilization of redundant batteries is recommended.
  2. Two sets of safeguards are employed, each with the ability to fully execute the protective function.
  3. The objective is to achieve maximum physical segregation between the two groups.
  4. The instrument transformers employ distinct cores for the two protection groups.
  5. Due to budgetary considerations, the circuit breakers are not duplicated. The utilization of duplicated trip coils is observed.
  6. Cables should be arranged in distinct cable ducts or layers to the greatest extent feasible.
The absence of duplicate circuit breakers results in the failure of a breaker to function, hence preventing the resolution of the fault. To rectify the deficiencies, it is necessary for the adjacent circuit breakers to be operated instead. In situations where the failure of “remote” protection relays to detect faults necessitates local backup, the inclusion of a breaker failure relay becomes imperative.

The breaker failure relay quantifies the residual fault current that remains flowing through the breaker following the anticipated tripping event, and subsequently triggers the tripping of all neighboring circuit breakers.

Figure 1 – Redundant power supplies within the central and bay units of the decentralized busbar protection

Redundant power supplies within the central and bay units of the decentralized BBP
Figure 1 – Redundant power supplies within the central and bay units of the decentralized busbar protection

Figure 2 – Busbar protection power supply using two batteries and an auxiliary relay to commute between batteries

Decentralized BBP power supply using two batteries and an auxiliary relay to commute between batteries
Figure 2 – Busbar protection power supply using two batteries and an auxiliary relay to commute between batteries

Go back to Content Table ↑


1.2 Instrument Transformer Circuits

In most cases, instrument transformers are not duplicated, but rather equipped with different cores to accommodate the two sub-systems. Various cores are interconnected with redundant protective methods. It is advisable to refrain from using a single current transformer core to supply power to both sub-systems. It is necessary to supply each Busbar protection with power from a separate CT core.

To mitigate the potential for open circuits at the terminating point or within the terminal itself, it is advisable to refrain from utilizing any current loop that supplies many panels. This precaution is particularly crucial when the loop is equipped with a disconnectable connection. Typically, both subsystems are linked to the identical CT junction box.

Therefore, it is typically not feasible to achieve physical isolation within distinct CT junction boxes. Nevertheless, it is necessary to transmit distinct cores of the CT using separate wires.

It is customary to have distinct secondary windings for the two sub-systems in voltage transformer circuits. In certain instances where two windings are unavailable, such as at lower voltage levels, it is advisable to employ distinct fuse groups within the marshalling box to divide the circuits. The high availability of voltage transformers renders this option generally acceptable.

Figure 3 – Dedicated current transformer wiring panel in air insulated substation

Dedicated current transformer wiring panel in air insulated substation
Figure 3 – Dedicated current transformer wiring panel in air insulated substation

Go back to Content Table ↑


1.3 Physical Location of Panels

The physical placement of the protection relays and auxiliary relays in the panels is crucial when utilizing sub-divided systems. It is recommended to employ distinct panels for the protection equipment of group A and group B. The rationale behind implementing physical split-up is to mitigate any issues that may arise from a singular incident, such as a cable fire or mechanical damage in a panel, affecting both sets of protective measures.

Additionally, it facilitates the ability to work on one group while the other group is engaged in service.

Nevertheless, in certain instances where the sub-systems occupy little space, it is deemed permissible to house the equipment for both sub-systems within a single panel. There is a little likelihood of cable fire or any other mechanical damage that may impact the two systems within the same panel. The issue of circuit mix-up resulting from errors during the processes of erection, commissioning, or maintenance necessitates careful consideration and the implementation of preventive measures.

Based on what has already been said, it may be concluded that a crucial aspect of panel design involves the explicit indication of the object to which it pertains. When employing sub-divided systems, it is imperative to explicitly specify the sub-system to which it belongs. This encompasses the implementation of distinct equipment segregation and explicit labeling of various portions, as well as the segregation of components between sub-systems or objects. The process of separation within the panel involves the physical segregation of terminal groups to accommodate the various protected devices within the panel.

Any equipment employed in the protective system, as well as additional supplementary relays linked to the identical battery system or fuse groups, must be consolidated and unambiguously designated. The equipment responsible for closing, interlocking, and other related functions is situated within the protection panel.

Figure 4 – Relay protection panel

Relay protection panel
Figure 4 – Relay protection panel

Go back to Content Table ↑


1.4 Exchange of Information Between Two Subsystems

One of the primary principles employed in the utilization of sub-divided systems is to prevent signal exchange between the two systems. To the greatest extent feasible, sub-systems should function entirely autonomously from one another. This provides the utmost level of security during maintenance and other related activities, encompassing both human and equipment failures.

Nevertheless, in the majority of instances, certain signals are necessary to be transmitted to another sub-system. The signals that are most frequently encountered are:


1.4.1 Start and Block of Auto-Recloser

The duplication of auto-recloser is typically avoided due to speed limitations associated with two units, as well as the absence of significant consequences resulting from a failure to autoreclose.

The sub-systems involved in the initiation and termination of the autoreclose function engage in the exchange of various signals.

Further Study – Auto-reclose schemes for re-energising the line after a fault trip

Auto-reclose schemes for re-energising the line after a fault trip


1.4.2 Start of Breaker Failure Protection

The Breaker failure relay/function (BFR) isn’t duplicated in redundant systems, just like the Auto-recloser function. However, the rationale behind this is entirely different. The Breaker failure function necessitates stringent security measures to prevent unnecessary trippings and duplication, resulting in enhanced dependability but a deterioration in security.

Given the statistically low risk of breaker failure, prioritizing security is of greater significance.

The provision of the BFR function is limited to a single system, often within the Group A protection system. It is now usual practice to provide DC changeover to the BFR relay when using a single BFR, as this enhances reliability and availability. When the breaker failure function is repeated, such as when duplicate busbar protection is employed, it is important to acknowledge the associated security issues.

The transmission of data between the systems must be managed with meticulous attention to avoid issues, such as when maintenance is performed on one of the systems. Interface relays should be positioned either internally or externally, ideally in a distinct and clearly marked section within one of the panels only.

In order to facilitate the identification and disconnection of the appropriate terminals during the separation of sub-systems, it is imperative that the terminals are prominently displayed within the panel.

Figure 5 – Functional diagram of a Breaker Failure Relay

Functional diagram of a Breaker Failure Relay
Figure 5 – Functional diagram of a Breaker Failure Relay

Go back to Content Table ↑


1.5 Arrangement of Trip Circuits

The trip circuits are a significant component of the protective system. The occurrence of a trip circuit failure will inevitably result in the failure to activate the circuit breaker. As previously stated, the breaker is not duplicated due to cost considerations. The only practical way to enhance reliability is by incorporating two trip coils on the breaker.

This approach aims to mitigate operational failure issues related to DC supply, wiring, and trip coils in CBs. However, it does not provide any benefits in terms of mechanical issues within the CB operating mechanism.

Membership Upgrade Required

This content is not available in your premium membership plan. Please upgrade your plan in order to access this content. You can choose an annually based Basic, Pro, or Enterprise membership plan. Subscribe and enjoy studying specialized technical articles, online video courses, electrical engineering guides, and papers.

With EEP’s premium membership, you get additional essence that enhances your knowledge and experience in low- medium- and high-voltage engineering fields.

Time Limited! – Save 15% on PRO Membership Plan with coupon CTS15

Upgrade

Already a member? Log in here

Premium Membership

Get access to premium HV/MV/LV technical articles, electrical engineering guides, research studies and much more! It helps you to shape up your technical skills in your everyday life as an electrical engineer.
More Information
Edvard Csanyi - Author at EEP-Electrical Engineering Portal

Edvard Csanyi

Hi, I'm an electrical engineer, programmer and founder of EEP - Electrical Engineering Portal. I worked twelve years at Schneider Electric in the position of technical support for low- and medium-voltage projects and the design of busbar trunking systems.

I'm highly specialized in the design of LV/MV switchgear and low-voltage, high-power busbar trunking (<6300A) in substations, commercial buildings and industry facilities. I'm also a professional in AutoCAD programming.

Profile: Edvard Csanyi

Leave a Comment

Tell us what you're thinking. We care about your opinion! Please keep in mind that comments are moderated and rel="nofollow" is in use. So, please do not use a spammy keyword or a domain as your name, or it will be deleted. Let's have a professional and meaningful conversation instead. Thanks for dropping by!

Learn How to Design Power Systems

Learn to design LV/MV/HV power systems through professional video courses. Lifetime access. Enjoy learning!

EEP Hand-Crafted Video Courses

Check more than a hundred hand-crafted video courses and learn from experienced engineers. Lifetime access included.
Experience matters. Premium membership gives you an opportunity to study specialized technical articles, online video courses, electrical engineering guides, and papers written by experienced electrical engineers.
This whitepaper by OMICRON explores the fundamental shift in substation automation testing from hardware-dependent setups to virtualized, software-defined verification.