Transformer oil & fortune telling

Insulation medium is an indispensable part of a power transformer, and the interesting thing about it is that it can drop dead at any time. Most of the time, this doesn’t happen, but… This article presents the transformer oil features by which one must abide. These features are examined according to standards to ensure the oil’s integrity. Transformer-impregnated paper is the determining factor in transformer age, so it is discussed extensively.

The art of predicting the fate of a power transformer by looking into a cup of oil
The art of predicting the fate of a power transformer by looking into a cup of oil

The importance of insulation was increased over the years due to the increase in the voltage rating of transformers. Within the last decades, although research on transformer insulation and diagnosis methods have been improved so much, the insulation of HV transformers remained more or less unchanged, and for EHV and UHV transformers, the oil–paper insulation is dominant.

Transformer oil has elements indicative of the transformer’s overall health. For example, a DGA transformer oil test shows levels of gases like acetylene and ethylene rising above a safe limit. This indicates the aging of the transformer.

Other crucial transformer oil tests are the Power/Dissipation factor and Oil breakdown voltage which indicate the dielectric strength and power factor of the transformer oil. Any deviation from ideal values is an alarming sign that the transformer needs attention to mitigate the risk of failure.

Transformer oil can be categorized into three types: Mineral oil, Silicone-based oil, and Bio-based oil. Owing to the excellent cooling and insulating property of mineral oils, these have been the most used transformer oil for many years. However, as years and research progressed, the shortcoming of mineral oils started to gain attention. Poor biodegradability, potential flammability, and low moisture tolerance are the most important concerns.

However, it is a topic for another day to discuss the suitability of these oil types.

Transformer oil failure modes are many, but they can be summarized as: moisture presence in oil, oil aging, paper aging, and corrosive sulfur. The DGA sampling frequency is mandated by the detected failure mode and its severity. For instance, a high moisture concentration needs a closer and shorter sampling than paper aging problem.

Dissolved gas analysis (DGA) is an effective tool to assess transformer healthiness by monitoring key gases that have their corresponding failure modes.

Among different DGA analyses, two methods were explained-namely, IEEE C57.104 and Rogers method. The article offers five case studies along with their sample reports to have a sense of result interpretation.

Table of Contents:

  1. Mineral Insulating Oil
    1. Transformer Oil Feature
  2. Chemical Indicators
    1. Insulation Paper Life Determination
    2. Degree of Polymerization (DP)
      1. Relationship between Furans and DP
      2. CO2 and CO
  3. Dissolved Gas Analysis (DGA)
    1. DGA Data Interpretation
      1. Data Quality Review
    2. Context of Data Interpretation
    3. Fault Type Identified from DGA Results
      1. Rogers Ratios Method
      2. Duval Triangle 1
  4. Case Studies:
    1. Case #1: oil analysis and DGA results
    2. Case #2: transformer out of service
    3. Case #3: interesting situation after detanking the transformer
    4. Case #4: partial discharge presence
    5. Case #5: two faults developed

1. Mineral Insulating Oil

Transformer oil is a mineral-insulating oil used in transformers and similar electrical appliances. Mineral insulating oil is obtained through refining, reforming, or mixing petroleum products with other hydrocarbons and additives. Additives are the chemicals added to the mineral oil to improve its specifications.

For example, antioxidants, metal passivators, electrostatic charging tendency depressants, gas absorbers, pour point represents, anti-foam compounds, and refining processes improvers are some additives.

The definition of these chemicals will be presented in the following:

  1. Antioxidant additives: compounds added to mineral insulators to improve oxidation stability, including inhibitors, peroxide decomposers, and metal passivators
  2. Inhibitors: an antioxidant additive containing various phenolic compounds including DBPC1 and DBP2 as described in IEC 60666.
  3. Other antioxidants: includes other antioxidant additives including sulfur or phosphorus compounds
  4. Metal passivators: metal passivator agents are essentially added as electrostatic charging reducers, but may also improve oxidation stability
Generally, mineral insulation oil used in the equipment is classified according to the presence of additives into three types including oil with inhibitors, oil without inhibitors, and oil with very low levels of inhibitors. The standard IEC 60666 governs the inhibitors’ concentration. The total inhibitor content is less than 0.01% in oil without inhibitors according to the standard IEC 60666.

Oil with a meager amount of inhibitor contains inhibitors less than 0.08% in accordance with IEC 60666. Finally, the oil containing inhibitors is mineral oil with a minimum of 0.08% and a maximum of 0.4% of inhibitors.

Moreover, the transformer oil type is divided into three groups based on the antioxidant additives. The first group contains no antioxidants, indicated by the letter “U”. The second group contains a meager amount of antioxidant additives and is indicated by the letter “T”. The third group also contains antioxidants represented by the letter “I”.

Suggested Reading – Do Not Energize Oil-Filled Transformer Just Like That!

Do Not Energize Oil-Filled Transformer Without Performing These 15 Tests and Checks!

Go back to the Contents Table ↑


1.1. Transformer Oil Feature

The characteristics of transformer oil must be in accordance with the specifications in IEC 60296. The details of these specifications can be found in the IEC 60296, and their list is as follows:

  • Viscosity
  • Pout point
  • Water content
  • Breakdown voltage
  • Dielectric dissipation factor
  • Appearance
  • Acidity
  • Interfacial tension
  • Sulphur content
  • Corrosive Sulphur
  • Oxidation stability
  • Flash point
  • Tendency to absorb gases
  • Density
  • Polycyclic aromatic content (PCA)
  • Polychlorinated biphenyl content (PCB)
  • 2-Furfural content
  • Particle content
  • DBDS content
  • Gases in oil

The oil tests could be classified into three types: routine tests, complementary tests, and special tests. The routine tests aim to evaluate basic characteristics that identify the oil proprieties, such as colour, moisture, dielectric breakdown voltage, etc. The complementary tests provide more insight of the oil status, especially if there is any anomaly in the routine tests.

The special tests give an overall view of the transformer oil in terms of physical and chemical properties. This classification is portrayed in Figure 1.

Figure 1 – Oil test types

Oil test types
Figure 1 – Oil test types

Go back to the Contents Table ↑


2. Chemical Indicators

The useful life of the transformers is based on the life of its insulation system, the combination of cellulose and oil. In practice, some transformers even more than 50 years in power networks are constantly being used. The lifetime of an insulating system of a transformer is the lifetime of the paper used because the oil can be cleaned or even replaced during the lifespan of the transformer, but the paper is fixed from the beginning and is not repaired or replaced.

Therefore, the end of the transformer paper life is the end of its transformer life. It should be noted, however, that the oil status of a transformer plays a significant role in the aging process of cellulose.

To estimate the remaining life of the transformer (cellulose insulation), a chemical indicator called the Degree of Polymerization (DP) is used which will be further elaborated. Measuring this indicator directly requires the transformer paper sampling and for an in-service transformer, this is impossible.

As a result, different chemical indicators are used today to indirectly estimate the degree of polymerization with the values of these indicators.

Might be Interesting – A study of lifetime management of generator transformers

A study of lifetime management of generator step-up power transformers

Go back to the Contents Table ↑


2.1. Insulation Paper Life Determination

To determine the end of the paper life, a set of physical quantities must be measured, and then, based on the measurement results, a decision could be made about the end of the paper life. These quantities can be considered as mechanical properties such as elongation, pressure bearing, strength, and wear resistance or electrical properties such as dielectric strength, or chemical properties including the degree of polymerization.

The end of paper life can be a precise amount of these quantities or a percentage of paper loss. At first, it might seem that the paper’s dielectric strength is the best value.

That being said, it was proved that if the paper was not exposed to mechanical stress, the dielectric strength of the paper would decay very slowly.

Go back to the Contents Table ↑


2.2. Degree of Polymerization (DP)

The DP is measured according to IEC 60450. Hence, not only cellulose but also hemicellulose and lignin are broken down. Therefore, DP is a sum total value. In the explanation of DP, it can be said that in the polymer or cellulose molecule, there are long chains that contain rings or glucose monomers and the number of rings in each string reaches 1000–1400.

The average number of glucose rings in a molecule or cellulose polymer is the DP.

The mechanical strength of cellulose depends on the strength between cellulose fibers and their length. If the force between the cellulose chains decreases, while reducing the mechanical strength of the paper, the DP of the paper will decrease. For a new transformer, the DP value is between 1000 and 1200 and when this number drops to 150–200, the cellulosic insulation quality is drastically reduced.

Cellulose is constantly affected by the heat generated by the active part of the transformer, the moisture content, the oxygen concentration in oil, acids produced in the oil, and other factors such as metal catalysts which generally cause cellulose decomposition, degradation, and deterioration. Insulation decomposition is a chemical phenomenon.

Figure 2 – Transformer paper insulating aging

Paper insulating aging
Figure 2 – Paper insulating aging

Three mechanisms of degradation hydrolysis, pyrolysis, and oxidation act simultaneously. Hydrolysis is the decomposition of a chemical compound by reaction with water. On the other hand, pyrolysis and oxidation are the decomposition processes resulting from heating and interacting with oxygen, respectively.

The cellulose paper degradation results in water, acid, furans, carbon oxides, and hydrocarbons. Many mechanisms have been proposed for the thermal degradation of cellulose based on which of the pyrolysis or hydrolysis processes are dominant. In the hydrolysis and pyrolysis processes, furans, especially 2-furfural will be produced.

Basically, water and carbon oxides are the main products of cellulose degradation and furans are the second products, and acids and other products are among other products.

The approach of identification of the paper status in accordance with paper colour. An inverse relationship exists between the paper colour and the DP number. Figure 2 illustrates this relationship in which dark-coloured paper has low DP number. The lower the DP number is, the more degraded the paper is.

As seen in Figure 3 paper deteriorates over time and weakens the insulation system against thermal, mechanical and electrical stresses.

Cellulose is constantly affected by the heat generated by the active part of the transformer, the moisture content, the oxygen concentration in oil, acids produced in the oil and other factors such as metal catalysts which generally cause cellulose decomposition, degradation and deterioration.

Figure 3 – Cellulose ageing and destruction in an old transformer

Cellulose ageing and destruction in an old transformer
Figure 3 – Cellulose ageing and destruction in an old transformer (photo credit: I.A.R. Gray; Transformer Chemistry Services)

Go back to the Contents Table ↑


2.2.1. Relationship between Furans and DP

Furans are the main products of cellulose degradation and decomposition inside the transformers. For analyzing the paper, furans analysis is a very convenient method compared to paper sampling. It was found that the 2-furfural concentration in oil and the DP value are interrelated logarithmically in the case of the paper degradation process.

Fault assessment is determined by the method depicted in Figure 4 adapted from “An Introduction to the Half-Century Transformer by the Transformer Maintenance Institute, S.D.Myers Co., 2002”.

The furan test (2-furfural) confirms the remaining life of the insulation paper of the transformer.

Membership Upgrade Required

This content is not available in your premium membership plan. Please upgrade your plan in order to access this content. You can choose an annually based Basic, Pro, or Enterprise membership plan. Subscribe and enjoy studying specialized technical articles, online video courses, electrical engineering guides, and papers.

With EEP’s premium membership, you get additional essence that enhances your knowledge and experience in low- medium- and high-voltage engineering fields.

Good to know: – Save 50% on all video courses with Enterprise plan.

Upgrade

Already a member? Log in here

Premium Membership

Get access to premium HV/MV/LV technical articles, electrical engineering guides, research studies and much more! It helps you to shape up your technical skills in your everyday life as an electrical engineer.
More Information
Salem Alshahrani - Author at EEP-Electrical Engineering Portal

Salem Alshahrani

Electrical engineer (BEE & Meng). Specialized in substation design, especially in LV/MV switchgears and transformers. Passionate in power system planning, analysis, and stability studies.

Profile: Salem Alshahrani

Leave a Comment

Tell us what you're thinking. We care about your opinion! Please keep in mind that comments are moderated and rel="nofollow" is in use. So, please do not use a spammy keyword or a domain as your name, or it will be deleted. Let's have a professional and meaningful conversation instead. Thanks for dropping by!

Learn How to Design Power Systems

Learn to design LV/MV/HV power systems through professional video courses. Lifetime access. Enjoy learning!

EEP Hand-Crafted Video Courses

Check more than a hundred hand-crafted video courses and learn from experienced engineers. Lifetime access included.
Experience matters. Premium membership gives you an opportunity to study specialized technical articles, online video courses, electrical engineering guides, and papers written by experienced electrical engineers.
Whitepaper: How to Improve Risk Decisions for Power Systems - Prioritizing vulnerabilities with full operational context