Distance relays are one of the most important protection elements in a transmission line.

Principles and Characteristics of Distance Protection
Principles and Characteristics of Distance Protection

These  relays may sometimes be set based in percentages of the line impedances, for example a  typical setting for zone 1 is 80% of the impedance of the line in order to not reach the remote  end, the zone 2 can be set at 120% of the impedance of the line in order to dependably  overreach the line, Zone 3 sometimes are disabled or set to cover an adjacent line.

Distance relays characteristics may be Mho, Quadrilateral, Offset Mho, etc. In the case of the  quadrilateral characteristic or long reaching mho characteristics, additional care may be  required to remain secure during heavy load.

In the case of parallel lines, the mutual coupling of these lines can cause distance relays to  under reach and over reach. For this reason the relay setting must consider this effect, some  relays have algorithms to compensate, but it is necessary to use the current of the parallel line  which adds complexity to the installation.

In some countries there criteria that a distance protection can not reach fault in other voltage  levels, because fault clearing times in sub transmission levels may be slower than fault clearing  times at the transmission level.

The problem of combining fast fault clearance with selective tripping of plant is a key aim for the protection of power systems.

To meet these requirements, high-speed protection systems for transmission and primary distribution circuits that are suitable for use with the automatic reclosure of circuit breakers are under continuous development and are very widely applied.

Distance protection, in its basic form, is a non-unit system of protection offering considerable economic and technical advantages.

Unlike phase and neutral overcurrent protection, the key advantage of distance protection is that its fault coverage of the protected circuit is virtually independent of source impedance variations.

Advantages of distance over overcurrent protection
Figure 1 – Advantages of distance over overcurrent protection

Distance protection is comparatively simple to apply and it can be fast in operation for faults located along most of a protected circuit. It can also provide both primary and remote back-up functions in a single scheme. It can easily be adapted to create a unit protection scheme when applied with a signalling channel.

In this form it is eminently suitable for application with high-speed auto- reclosing, for the protection of critical transmission lines.


Principles of Distance Relays

Since the impedance of a transmission line is proportional to its length, for distance measurement it is appropriate to use a relay capable of measuring the impedance of a line up to a predetermined point (the reach point).

Such a relay is described as a distance relay and is designed to operate only for faults occurring between the relay location and the selected reach point, thus giving discrimination for faults that may occur in different line sections.

The basic principle of distance protection involves the division of the voltage at the relaying point by the measured current. The apparent impedance so calculated is compared with the reach point impedance. If the measured impedance is less than the reach point impedance, it is assumed that a fault exists on the line between the relay and the reach point.

The reach point of a relay is the point along the line impedance locus that is intersected by the boundary characteristic of the relay.

Since this is dependent on the ratio of voltage and current and the phase angle between them, it may be plotted on an R/X diagram. The loci of power system impedances as seen by the relay during faults, power swings and load variations may be plotted on the same diagram and in this manner the performance of the relay in the presence of system faults and disturbances may be studied.


Relay performance

Distance relay performance is defined in terms of reach accuracy and operating time. Reach accuracy is a comparison of the actual ohmic reach of the relay under practical conditions with the relay setting value in ohms.

Reach accuracy particularly depends on the level of voltage presented to the relay under fault conditions.

The impedance measuring techniques employed in particular relay designs also have an impact. Operating times can vary with fault current, with fault position relative to the relay setting, and with the point on the voltage wave at which the fault occurs.

Depending on the measuring techniques employed in a particular relay design, measuring signal transient errors, such as those produced by Capacitor Voltage Transformers or saturating CT’s, can also adversely delay relay operation for faults close to the reach point. It is usual for electromechanical and static distance relays to claim both maximum and minimum operating times.

However, for modern digital or numerical distance relays, the variation between these is small over a wide range of system operating conditions and fault positions.


Distance Relay Characteristics

Some numerical relays measure the absolute fault impedance and then determine whether operation is required according to impedance boundaries defined on the R/X diagram.

Traditional distance relays and numerical relays that emulate the impedance elements of traditional relays do not measure absolute impedance. They compare the measured fault voltage with a replica voltage derived from the fault current and the zone impedance setting to determine whether the fault is within zone or out-of-zone. Distance relay impedance comparators or algorithms which emulate traditional comparators are classified according to their polar characteristics, the number of signal inputs they have, and the method by which signal comparisons are made.

The common types compare either the relative amplitude or phase of two input quantities to obtain operating characteristics that are either straight lines or circles when plotted on an R/X diagram. At each stage of distance relay design evolution, the development of impedance operating characteristic shapes and sophistication has been governed by the technology available and the acceptable cost.

Since many traditional relays are still in service and since some numerical relays emulate the techniques of the traditional relays, a brief review of impedance comparators is justified.


Example of Modern Distance Protection Relay

SIPROTEC 7SA522 protection relay - Single line diagram
SIPROTEC 7SA522 protection relay – Single line diagram (provides full-scheme distance protection and incorporates all functions usually required for the protection of a power line)

This particulary relay has following ANSI protection functions:

ANSIDescriptionANSIDescription
21/21NDistance protection50HSSwitch-onto-fault protection
FLFault locator50BFBreaker failure protection
50N/51N; 67NDirectional ground-fault protection59/27Overvoltage/undervoltage protection
50/51/67Backup overcurrent protection81O/UOver/underfrequency protection
50 STUBSTUB-bus overcurrent stage25Synchro-check
68/68TPower swing detection/tripping79Auto-reclosure
85/21Teleprotection for distance protection74TCTrip circuit supervision
27WIWeak-infeed protection86Lockout (CLOSE command – interlocking)
85/67NTeleprotection for ground-fault protection

Distance Protection Theory (VIDEO)


Resource: Network protection and automation guide – Areva; SIPROTEC47SA522 – Distance Protection Relay for Transmission Lines; An Example Distance Protection Application with Complicating Factors by Yofre Jacome and Charles F Henville

Premium Membership

Get access to premium HV/MV/LV technical articles, electrical engineering guides, research studies and much more! It helps you to shape up your technical skills in your everyday life as an electrical engineer.
More Information
author-pic

Edvard Csanyi

Electrical engineer, programmer and founder of EEP. Highly specialized for design of LV/MV switchgears and LV high power busbar trunking (<6300A) in power substations, commercial buildings and industry facilities. Professional in AutoCAD programming.

18 Comments


  1. Tanka B Wakhley
    Sep 21, 2023

    What does STUB stands for?


  2. Mohamed Sallieu Bah
    Nov 06, 2022

    Nominal voltage is 154 kV, the distance of the overhead line is 60i the characteristic of the line is r=0.125 ohm/km ve x=0.270 ohm/km. A three-phase line is protected with a distance relay which is supplied from 150/5A CT and 154/0.1 kV VT. If the measured value is 0.25 ohm when a fault occurs, What is the distance of fault point from the head of the line?

    Hello everyone, can someone help me out on how to solve this problem? thanks.


  3. Yusuf
    Jun 02, 2021

    Even in case of the faults in protected line for that short section of 4%. For adjacent line it will be in reverse zone (Z4) & time delay for Z4 will be intentionaly high. so Z2 will surely clear that primary protected line.


  4. S.VASUDEVAN
    Jun 11, 2020

    In most of text books Zone 2 setting of distance relay and by author is recommended 120% of line impedance. Zone 1 is set at 80% expecting errors in CT/VT/Relay error/Impedance variations is 20%. If so with 120% line impedance setting fault coverage will be 96% to 144% and the over reaching zone 2 trips for fault in protected line close to remote substation < 4% line length or on bus at remote s/s. Right setting will be 130% protected line impedance for Zone2 coverage 104% to 156% line covering remote bus also which is a must as back up protection. S.Vasudevan 9840229620 Ex. Site Manager ABB/Sweden for Kuwait projects.


  5. Afomia Aalze
    Feb 11, 2020

    Very Helpful, thank you.


  6. Riad Yalda
    Apr 03, 2019

    Hi!
    Can you explain the economical and environmental effects or goals of distance protection? please


  7. shingirai tomu
    Mar 31, 2019

    please send me updates


  8. Relay article very useful.
    Mar 11, 2019

    113, Chitnisnagar, Umrer road, Nagpur-440024.


  9. ziad
    Mar 02, 2019

    Hi .. Can you explain the topic of Extensive Relay Protection using the microprocessor?I need this topic as fast as possible …. Thank you


  10. sreelekshmi
    Feb 22, 2017

    what is the advantages and disadvantages of distance relay


  11. whodoes
    Mar 07, 2016

    What are the advantages of distance relays over overcurrent relays?


  12. Kalyanasis Pal
    Feb 06, 2016

    Sir I want to know in detail about STUB protection.


  13. Adnan
    Feb 05, 2016

    Very useful information. Sir plz tell how can we learn and read switch board drawings. And motor control center


  14. b.d.borule
    Sep 28, 2015

    respected sir,
    is there any effect of ungrounded ct star point on distance shown by relay


  15. Emmanuel
    May 25, 2015

    Congratulations for a short presentation of the matter.
    I suggest including some features I consider important for fully understanding of the distance protection aplications, such as:
    – tied lines infeed for lines with ties;
    – arc fault detection;
    – week infeed;
    – signaling for pilot applications;
    – close-up faults;
    – the use of the reverse zone for busbar fault protection
    These are what I have in mind at the moment.


    • Edvard
      May 25, 2015

      Thanks Emmanuel, I agree with you for adding.


  16. s.muthukumar
    May 16, 2015

    very useful to me.


  17. AHMED SALIM KURDI
    May 07, 2015

    I’ةm very interest for above

Leave a Reply to Relay article very useful.

Tell us what you're thinking. We care about your opinion! Please keep in mind that comments are moderated and rel="nofollow" is in use. So, please do not use a spammy keyword or a domain as your name, or it will be deleted. Let's have a professional and meaningful conversation instead. Thanks for dropping by!

eight  +    =  eighteen

Learn How to Design Power Systems

Learn to design LV/MV/HV power systems through professional video courses. Lifetime access. Enjoy learning!

Subscribe to Weekly Newsletter

Subscribe to our Weekly Digest newsletter and receive free updates on new technical articles, video courses and guides (PDF).
EEP Academy Courses - A hand crafted cutting-edge electrical engineering knowledge