Home / Technical Articles / Few Tips For Correct Protection Against Indirect Contact In TT System
Earth fault in a TT system
An earth fault in a TT system originates the circuit represented in Figure 1. The fault current flows through the secondary winding of the transformer, the line conductor, the fault resistance, the protective conductor, and the earth electrode resistances (RA, of the user’s plant, and RB, of the neutral).
Few Tips For Correct Protection Against Indirect Contact In TT System (photo credit: faisaljassim.ae)
According to IEC 60364-4 prescriptions, the protective devices MUST be coordinated with the earthing arrangement in order to rapidly disconnect the supply if the touch voltage reaches harmful values for the human body.
In TT systems the neutral and the exposed conductive parts are connected to earth electrodes electrically independent (Figure 1). Therefore the earth fault current returns to the power supply node through the soil.
Figure 1 – Earth fault in a TT system
Before describing such prescriptions, it is useful to know the different circuit types described in the above mentioned Standard. In particular, in a plant, the circuits can be divided into:
  1. Final circuit
    It is a circuit which usually supplies equipment (for example an aspirator, a bridge crane, etc.)
  2. Distribution circuit
    It is a circuit which supplies a distribution board to which other final circuits are connected.
Example of protection solution for earth fault in a TT system
Figure 2 – Example of protection solution for earth fault in a TT system
In a TT system, to achieve a correct protection against indirect contact through the automatic disconnection of the circuit, it is necessary to respect one of the following conditions (in compliance with IEC 60364-4):
  1. Protection by means of residual current devices (RCD)
  2. Protection by means of overcurrent protective devices
  3. Protection against indirect contact by means of circuit breakers equipped with electronic releases
At the end of this technical article, we’ll see the example of the LV circuit breaker settings (Tmax 250A equipped with an electronic release) and also a few words for final conclusions.
By assuming 50V as limit voltage (standard environments), to achieve protection against indirect contact by means of residual current devices it is necessary to satisfy the following condition:
RA · I∆n ≤ 50V then: RA ≤ 50V / I∆n
where:
  • RA is the total resistance (in ohm) of the earth electrode and of the protective conductor of the exposed conductive parts;
  • I∆n is the rated residual operating current of the residual current circuit-breaker.
As regards the disconnection times, the Standard distinguishes two possibilities:
Final circuits with rated currents not exceeding 32A:
In this case it is necessary that the above mentioned condition with the times shown in Table 1 (values referred to fault currents significantly higher than the rated residual current of the residual current circuit breakers typically 5·I∆n) is fulfilled;
Distribution circuit or final circuit with rated currents exceeding 32A:
In this case it is necessary that the above mentioned condition is fulfilled with a time not exceeding 1s (conventional time).
Table 1: Maximum disconnection times for final circuits not exceeding 32A
50V < U≤ 120V130V < U≤ 230V230V < U≤ 400VU> 400V
Systema.c.d.c.a.c.d.c.a.c.d.c.a.c.d.c.
TT0.3Note 10.20.40.070.20.040.1
Uo is the nominal a.c. or d.c. line to earth voltage.
Where in TT systems the disconnection is achivied by an overcurrent protective device and the protective equipotential bonding is connected with all extraneous-conductive-parts within the installation, the maximum disconnection times applicable to TN systems may be used.
  • NOTE 1 // Disconnection may be required for reasons other than protection against electric shock.
  • NOTE 2 // Where compliance with the above mentioned requirement is provided by an RCD, the disconnecting times in accordance with the table above relate to prospective residual currents significantly higher than the rated residual operating current of the RCD (typically 5·I∆n).
From the above, it is evident that the value of the resistance RA of the earthing arrangement results to be different by using residual current circuit-breakers with different sensitivity, since the current quantity at the denominator in the above mentioned relationship is different.
In fact, by using a residual current device with 30mA sensitivity, an earthing resistance value lower than
RA ≤ 50 / 0.03 = 1666.6 Ω
shall be obtained, whereas with a less sensitive residual current device (for example with 300mA sensitivity) an earthing resistance value lower than:
RA ≤ 50 / 0.3 = 166.6 Ω
shall be obtained.
As shown in the example, thanks to a more sensitive residual current device, from a practical point of view it will be easier to realize an earthing system coordinated with the characteristics of the device itself. The Table 2 shows the maximum values of earth resistance which can be obtained with residual current devices and making reference to a common environment (50V):
I∆n [A]RA [Ω]
0.015000
0.031666
0.1500
0.3166
0.5100
316
105
301.6
Operating principle of residual current devices
The operating principle of residual current devices consists in the detection of an earth fault current by means of a toroidal transformer which encloses all the live conductors, included the neutral, if distributed. In absence of an earth fault the vectorial sum of the currents I is equal to zero.
In case of an earth fault, if the value of I exceeds the value of the trip threshold, called I∆n, the circuit at the secondary of the toroid sends a command signal to a dedicated opening device causing the circuit-breaker tripping.
In addition to the coordination with the earthing arrangement, to select the rated operating residual current I∆n, also the total leakage current of the installation under normal operating conditions shall be taken into consideration and, in order to avoid unwanted trips, such current shall not exceed 0.5 × I∆n.
Go back to conditions ↑
The choice of the automatic device for the protection against phase-to-earth faults and indirect contact shall be carried out by coordinating properly the disconnection times with the impedance of the fault loop. As a consequence, it is necessary to fulfill the following condition:
Zs · Ia ≤ U0
where:
  • Zs is the impedance (in ohms) of the fault loop comprising
    – the source;
    – the line conductor up to the point of the fault;
    – the protective conductor of the exposed-conductive-parts;
    – the earthing conductor;
    – the earth electrode of the installation;
    – the earth electrode of the source;
  • Ia is the disconnection current in the times shown in Table 1 for final circuits with currents not exceeding 32A or within 1 second for distribution circuits and for final circuits with currents exceeding 32A;
  • U0 is the nominal a.c. r.m.s. voltage to earth (V).
The choice of the automatic device shall be made by coordinating properly the disconnection times with the impedance of the fault loop.
The relationship Zs · Ia ≤ U0 may be expressed as :
Ia ≤ U0 / Zs = IkL-to earth
where IkL-to earth is the phase-to-earth fault current. Therefore, it is possible to state that the protection against indirect contact is veri ed when the tripping current Ia of the protective device (within the times shown in Table 1 or within 1s) is lower than the phase-to-earth fault current IkL-to earth at the exposed-conductive-part to be protected.
It is to underline that in TT distribution systems the use of a residual current device allows to have an earthing arrangement with an earth resistance value which can be easily obtained, whereas the use of automatic circuit- breakers is possible only in case of low earth resistance values RA (very difficult to be obtained in practice).
Besides, in such circumstances, it could be very difficult to calculate the impedance of the fault loop (Zs), because the earthing resistance of the neutral cannot be considered negligible (in fact it could reach values of the same quantity of the earth resistance).
As previously indicated, the earth fault currents in TT systems have low values and consequently providing this protection by using thermomagnetic/electronic releases with phase protections within the times required by the Standard might be difficult or even impossible.
In such cases it is possible to use advanced electronic releases providing protection function G, which improves the protection conditions with earth fault currents not particularly high.
It is important to remember that this protection can evaluate the vectorial sum of the currents owing through the live conductors (between the three phases and the neutral). In a sound circuit this sum is equal to zero, but in the presence of an earth fault, part of the fault current shall return to the supply source through the protective conductor and the ground, without affecting the line conductors.
If this current is higher than the value set for protection G, the circuit breaker shall trip in the time set on the electronic release.
By using function G, the condition to be fulfilled to obtain protection against indirect contact becomes:
Zs · I4 ≤ U0
where I4 is the value in amperes of the setting of the protection function against earth fault. Since this value can be set from 0.2 to 1 for In, it is easy to realize how, by using function G, it is possible to provide protection against indirect contact for high impedance values of the fault loop and therefore low earth fault currents.
Example with CB settings
The following example (Figure 2) shows the possible settings of the LV circuit breaker Tmax T4N250 In250A equipped with an electronic release type PR222DS/P LSIG.
Electronic release type PR222DS/P LSIG
Electronic release type PR222DS/P LSIG (photo credit: ABB)
An example:
By using protection function G set at 0.20×In (see Figure 2), the current value over which tripping is obtained within 1s is 60A (value including the upper tolerance). The value of the phase-to-earth fault current (100A) results to be higher than the trip value within 1 second. Therefore protection against indirect current is achieved.
If protection function G were not used, the phase protections would not sense the current of 100A, since the setting of these functions is too high in comparison with the fault currents under consideration.
Settings of the LV circuit breaker Tmax T4N250 In250A
Figure 2 – Settings of the LV circuit breaker Tmax T4N250 In250A
Conclusions
To sum up, in TT systems, the Standard IEC 60364 permits the use of:
1 // Residual current devices complying with the condition RA· I∆n≤ 50V, within the disconnection times reported in Table 1 for final circuits with currents lower than 32A, or within 1s for distribution circuits or final circuits with rated currents exceeding 32A.
2 // automatic protective devices against overcurrents fulfilling the condition Zs · Ia≤ U0 within the disconnection times reported in Table 1 for final circuits with currents lower than 32A, or within 1s for distribution circuits or final circuits with rated currents exceeding 32A.
If automatic disconnection cannot be obtained in compliance with the disconnection times of the table or within the conventional time, it shall be necessary to provide supplementary equipotential bonding connected to earth
However the use of supplementary protective bonding does not exclude the need to disconnect the supply for other reasons, for example protection against fire, thermal stresses in equipment, etc.
Reference // Distribution systems and protection against indirect contact and earth fault by ABB
  1. habib
    Feb 26, 2018
    Hi, Edvard,
    If we have TNS-C system what was the protection required for N-current and G.F we required both separately. .
Leave a Reply to habib
nine  +  1  =
Learn to Design Power Systems
Subscribe to Newsletter
