Home / Technical Articles / The fundamentals of protection relay co-ordination and time/current grading principles
The importance of overcurrent protection
Transmission and distribution systems are exposed to overcurrent flow into their elements. In an electric power system, overcurrent or excess current is a situation where a larger than intended electric current exists through a conductor, leading to excessive generation of heat, and the risk of fire or damage to equipment.
The fundamentals of protection relay co-ordination and time/current grading principles (photo credit: JAL International)
Possible causes for overcurrent include short circuits, excessive load, transformer inrush current, motor starting, incorrect design, or a ground fault.
Therefore, for normal system conditions, some tools such as demand – side management, load shedding, and soft motor starting can be applied to avoid overloads.
In addition, distribution systems are equipped with protective relays that initiate action to enable switching equipment to respond only to abnormal system conditions. The relay is connected to the circuit to be protected via CTs and VTs according to the required protection function.
In order for the relay to operate, it needs to be energized. This energy can be provided by battery sets (mostly) or by the monitored circuit itself.
This article deals with co-ordination between protection relays in general and  principles of Time/Current grading used to achieve correct relay co-ordination.
  1. Co-ordination procedure
  2. Principles of Time/Current grading
    1. Discrimination by Time
    2. Discrimination by Current
    3. Discrimination by both Time and Current
Correct overcurrent relay application requires knowledge of the fault current that can flow in each part of the network. Since large-scale tests are normally impracticable, system analysis must be used.
The data required for a relay setting study are:
  1. Single-line diagram of the power system involved, showing the type and rating of the protection devices and their associated current transformers.
  2. The impedances in ohms, per cent or per unit, of all power transformers, rotating machine and feeder circuits.
  3. The maximum and minimum values of short circuit currents that are expected to flow through each protection device.
  4. The maximum load current through protection devices.
  5. The starting current requirements of motors and the starting and locked rotor/stalling times of induction motors.
  6. The transformer inrush, thermal withstand and damage characteristics.
  7. Decrement curves showing the rate of decay of the fault current supplied by the generators.
  8. Performance curves of the current transformers.
The relay settings are first determined to give the shortest operating times at maximum fault levels and then checked to see if operation will also be satisfactory at the minimum fault current expected.
It is always advisable to plot the curves of relays and other protection devices, such as fuses, that are to operate in series, on a common scale. It is usually more convenient to use a scale corresponding to the current expected at the lowest voltage base, or to use the predominant voltage base.
The alternatives are a common MVA base or a separate current scale for each system voltage.
The basic rules for correct relay co-ordination can generally be stated as follows:
RULE #1
Whenever possible, use relays with the same operating characteristic in series with each other.
RULE #2
Make sure that the relay farthest from the source has current settings equal to or less than the relays behind it, that is, that the primary current required to operate the relay in front is always equal to or less than the primary current required to operate the relay behind it.
Among the various possible methods used to achieve correct relay co-ordination are those using either time or overcurrent, or a combination of both. The common aim of all three methods is to give correct discrimination.
That is to say, each one must isolate only the faulty section of the power system network, leaving the rest of the system undisturbed.
2.1 Discrimination by Time
In this method, an appropriate time setting is given to each of the relays controlling the circuit breakers in a power system to ensure that the breaker nearest to the fault opens first.
A simple radial distribution system is shown in Figure 1, to illustrate the principle.
Radial system with time discrimination
Figure 1 – Radial system with time discrimination
Overcurrent protection is provided at B, C, D and E, that is, at the infeed end of each section of the power system.
Each protection unit comprises a definite-time delay overcurrent relay in which the operation of the current sensitive element simply initiates the time delay element. Provided the setting of the current element is below the fault current value, this element plays no part in the achievement of discrimination.
For this reason, the relay is sometimes described as an ‘independent definite-time delay relay’, since its operating time is for practical purposes independent of the level of overcurrent.
It is the time delay element, therefore, which provides the means of discrimination. The relay at B is set at the shortest time delay possible to allow the fuse to blow for a fault at A on the secondary side of the transformer. After the time delay has expired, the relay output contact closes to trip the circuit breaker. The relay at C has a time delay setting equal to t1 seconds, and similarly for the relays at D and E.
If a fault occurs at F, the relay at B will operate in t seconds and the subsequent operation of the circuit breaker at B will clear the fault before the relays at C, D and E have time to operate.
The time interval t1 between each relay time setting must be long enough to ensure that the upstream relays do not operate before the circuit breaker at the fault location has tripped and cleared the fault.
The main disadvantage of this method of discrimination is that the longest fault clearance time occurs for faults in the section closest to the power source, where the fault level (MVA) is highest.
2.2 Discrimination by Current
Discrimination by current relies on the fact that the fault current varies with the position of the fault because of the difference in impedance values between the source and the fault.
Hence, typically, the relays controlling the various circuit breakers are set to operate at suitably tapered values of current such that only the relay nearest to the fault trips its breaker.
Figure 2 illustrates the method.
Radial system with current discrimination
Figure 2 – Radial system with current discrimination
For a fault at F1, the system short-circuit current is given by:
I = 6350 / (ZS + ZL1) A
where:
  • ZS = source impedance = 112 / 250 = 0.485 Ω
  • ZL1 = cable impedance between C and B = 0.24 Ω
Hence,
I = 6350 / 0.725 = 8800 A
So, a relay controlling the circuit breaker at C and set to operate at a fault current of 8800A would in theory protect the whole of the cable section between C and B.
Points affecting this method
However, there are two important practical points that affect this method of co-ordination:
Point #1 – It is not practical to distinguish between a fault at F1 and a fault at F2, since the distance between these points may be only a few metres, corresponding to a change in fault current of approximately 0.1%.
Point #2 – In practice, there would be variations in the source fault level, typically from 250MVA to 130MVA.
At this lower fault level the fault current would not exceed 6800A, even for a cable fault close to C. A relay set at 8800A would not protect any part of the cable section concerned.
Discrimination by current is therefore not a practical proposition for correct grading between the circuit breakers at C and B. However, the problem changes appreciably when there is significant impedance between the two circuit breakers concerned.
Consider the grading required between the circuit breakers at C and A in Figure 2. Assuming a fault at F4, the short-circuit current is given by:
I = 6350 / (ZS + ZL1 + ZL2 + ZT)
where:
  • ZL2 = cable impedance between B and 4MVA transformer = 0.04 Ω
  • ZT = transformer impedance = 0.07 × (112/4) = 2.12 Ω
Hence,
I = 6350 / 2.885 = 2200 A
For this reason, a relay controlling the circuit breaker at B and set to operate at a current of 2200A plus a safety margin would not operate for a fault at F4 and would thus discriminate with the relay at A.
Assuming a safety margin of 20% to allow for relay errors and a further 10% for variations in the system impedance values, it is reasonable to choose a relay setting of 1.3 x 2200A, that is, 2860A, for the relay at B.
Now, assuming a fault at F3, at the end of the 11kV cable feeding the 4MVA transformer, the short-circuit current is given by:
I = 6350 / (ZS + ZL1 + ZL2)
Thus, assuming a 250MVA source fault level:
I = 6350 / (0.485 + 0.24 + 0.04) = 8300A
Alternatively, assuming a source fault level of 130MVA:
I = 6350 / (0.93 + 0.214 + 0.04) = 5250A
For either value of source level, the relay at B would operate correctly for faults anywhere on the 11kV cable feeding the transformer.
2.3 Discrimination by both Time and Current
Each of the two methods described above has a fundamental disadvantage. In the case of discrimination by time alone, the disadvantage is due to the fact that the more severe faults are cleared in the longest operating time.
On the other hand, discrimination by current can be applied only where there is appreciable impedance between the two circuit breakers concerned.
It is because of the limitations imposed by the independent use of either time or current co-ordination that the inverse time overcurrent relay characteristic has evolved.
With this characteristic, the time of operation is inversely proportional to the fault current level and the actual characteristic is a function of both ‘time’ and ‘current’ settings.
Figure 3 shows the characteristics of two relays given different current/time settings.
Relay characteristics for different settings
Figure 3 – Relay characteristics for different settings
For a large variation in fault current between the two ends of the feeder, faster operating times can be achieved by the relays nearest to the source, where the fault level is the highest.
So, by using both functions the disadvantages of grading by time or current alone are overcome!
Variations of current/time tripping characteristics of IDMT relays will be discussed in some of the coming technical articles.
References //
  • Network Protection & Automation Guide by Alstom Grid
  • The Basics Of Overcurrent Protection – Seminar Paper by Genc Baruti
23 Comments
  1. wael ibrahim
    Jun 29, 2023
    it is very helpful but with more practical examples detailed will be great
    thanks a lot
  2. Sabu A K
    Nov 18, 2022
    Thank you very much sir .
    Good.
  3. Chioma
    Oct 18, 2021
    Thank you Edvard. You have always made what seems difficult simpler.
  4. B S Kolaki
    Jul 11, 2021
    Nice
  5. Gaby
    Jul 05, 2020
    Hello how is the cable impedance of 0.24 between C & B obtained? is it a given quantity or calculated
  6. Dr Joe Oni
    May 09, 2020
    I have benefited immensely from the articles promoted in this portal. As a Power System Engineer and a professor in this discipline, I encourage technical articles on smart grid and security.
    • Anil Paul Jacob
      Jul 03, 2020
      Dear Dr
      Seen your message kindly give your email in reply. anil paul 2k at gmail dot com is my id. (no space) I am in the same field from India I got some doubts in power need to communicate.
  7. Cheran
    Oct 04, 2019
    I need to know the PROCEDURE FOR RELAY SETTING or Steps for Relay setting?
    • Jimuel
      Jul 10, 2020
      You can check the videos of ETIP or Electrical Technology and Industrial Practice. By the way, I am not here to promote anything but to help you in your concern.
      The video discusses the step by step procedures on setting a relay.
  8. Ali Akbar
    Sep 05, 2019
    I want to know about the relays and the relay settings.
  9. Sateesh
    Jul 24, 2019
    Thanks very much for explaining in simplest possible way.
  10. Pasha
    Jul 23, 2019
    Mr Edward,
    May I request you to explain the role and importance of grounding grid in a substation and what is the relation with the relay picking the fault current and the grounding grid / system in a substation.
    Does the relay work if the grounding grid is open and the risers to the equipment( the circuit breaker ) are disconnected from the grounding grid.?
    Please explain clearly the relation between the grounding grid and the relay function.
  11. Milind Vyas
    Jul 13, 2019
    “In practice, there would be variations in the source fault level, typically from 250MVA to 130MVA” can you please explain as the source is of 250MVA how can it go down to 130 MVA.
  12. Mahmud suleiman
    Mar 21, 2019
    Pls i want to have more inside on transformer excitation test
  13. R H Magem
    Aug 26, 2018
    Your portal is very educating
  14. İRFAN SELVİ
    Aug 16, 2018
    Hello Edward
    Which brand(s) and model do you recommend
  15. senthil kumar.V
    Aug 14, 2018
    hi .,
    6350 is 11KV / root 3., I = V/Z
  16. Jürgen Verpaele
    Aug 14, 2018
    Hello,
    You talk about:
    “The time interval t1 between each relay time setting must be long enough to ensure that the upstream relays do not operate before the circuit breaker at the fault location has tripped and cleared the fault.”
    Are there some typical time values for this? Or how can this be selected?
      It depends on many things in your network. The best would be to perform a protection study using some testing device and its protection relay software (OMICRON for example) and see the results.
    • Amir
      Jul 24, 2019
      Hello,
      You can find your answer in IEEE 242 (Buff Book)- Chapter 15.
      the CTI (Current Time Interval) is between 0.2 to 0.4 sec and totally depends on systems you are working on.
  17. Madhav
    Aug 14, 2018
    Hello Edvard,
    No where in this article you have mentioned as to how the figure 6350 is arrived in the calculation of fault current… I wonder how and why?
    • Heidar Ghamsarian
      Aug 16, 2018
      LL=11000 so that LN=11000/square root3=6350 volt
  18. wagner jirschik
    Aug 13, 2018
    Hi, thank you for the explantion.
Leave a Reply to Heidar Ghamsarian
fifty two  +    =  fifty nine
