Home / Technical Articles / Protective relay – The brain that detects abnormal system conditions
Protective relay in MV applications
For medium voltage circuit breaker applications, protective relay serve as the “brain” that detects abnormal system conditions and direct the circuit breaker to operate. They also serve to provide specialized protection in low voltage power circuit breaker applications for functions not available in the circuit breaker trip units.
Protective Relay - The Brain That Detects Abnormal System Conditions
Protective Relay - The Brain That Detects Abnormal System Conditions (on photo: Jenkintown substation and setting of protection relays parameters; credit: septa.org)
Most modern protective relays are solid-state electronic or microprocessor-based devices, although older electromechanical devices are still available and still work!
Microprocessor-based or solid-state electronic relays offer more flexibility and functionality than electromechanical relays, including the ability to interface with common communications protocols such as MODBUS for integration into a SCADA environment.
Figure 1 - Microprocessor-based protective relay
Figure 1 – Microprocessor-based protective relay (on photo: SIPROTEC 5; credit: digitalsubstation.ru)
However, they do require “reliable” control power to maintain operation during abnormal system conditions. This reliable control power is most often provided by a DC battery system, although AC UPS-based systems are also encountered.
Electromechanical relays are typically single-phase devices. Solid-state electronic relays are typically available in single-phase or three-phase versions. Microprocessor-based relays are typically three-phase devices.
While electromechanical and solid-state electronic relays typically incorporate one relay function per device, microprocessor-based relays usually encompass many functions in one device. This makes a single microprocessor-based relay capable of performing the same functions that would require several electromechanical or solid-state relays.
This functionality usually makes microprocessor-based relays the best choice for new installations.
Generally, protective relay is not rated for direct connection to the power system where they are applied. For this reason, instrument transformers are used to reduce the currents and voltages to the levels for which the relays are designed. Instrument transformers generally fall into one of two broad categories:
  1. Current Transformers (CTs) and
  2. Voltage Transformers (VTs)
The loads on instrument transformers, such as relays and meters, are known as burdens to distinguish them from power system loads.
Medium voltage cubicle compartments showing positions of protection relay 'SEPAM', CTs and VTs (on photo: Schneider Electric's MV switchgear 'MCSET')
Medium voltage cubicle compartments showing positions of protection relay ‘SEPAM’, CTs and VTs (on photo: Schneider Electric’s MV switchgear ‘MCSET’)
Current transformers (CTs)
A current transformer consists of a coil toroidally-wound around a ferromagnetic core. The conductor for which the current is to be measured is passed through the center of the toroid. The magnetic field generated by the current through the conductor causes current to flow in the coil.
In essence, a CT may be thought of as a conventional transformer with one primary turn.
Current transformers in the United States typically have 5A rated secondaries, with primary ratings from 10-40,000 A and larger. For relaying applications in industrial facilities, CT ratios are typically 50:5-4000:5.
The classification system consists of a letter and a number. The letter may be C, designating that the percent ratio correction may be calculated, or T, denoting that the ratio correction has been determined by test.
MV Current Transformers
MV Current Transformers (photo credit: naswgr.net)
The number denotes the voltage that the CT can deliver to a “standard burden” at 20 times the rated secondary current without exceeding 10% ratio error. As a more accurate alternative, manufacturer-published CT excitation curves may be used to determine the current transformer accuracy.
For relaying application, the issue at hand is the performance of the protective relay during worst-case short-circuit conditions, when the CT secondary currents are the largest and may cause the secondary voltage to exceed the CTs rating due to the voltage developed across the relay input coil.
Current transformer scheme
Figure 2 – Current transformer scheme
This condition will cause the CT to saturate, significantly changing the ratio and thus the accuracy of the measurement. For cases of severe CT saturation the protective relay may respond in an unpredictable manner, such as not operating or producing “chatter” of its output contacts.
CTs where the power conductor passes through the window formed by the toroidal CT winding are known as window-type CTs. CTs which are designed with an integral bus bar running through device are known as bus-bar type CTs. Other designs, such as wound primary CTs for metering applications and non-saturating air-core CTs, are available.
Go back to Instrument Transformers ↑
Voltage transformers (VTs)
Voltage transformers (VTs) are used to step the power system voltage down to a level that the protective relay can utilize. The operation of voltage transformers is essentially the same as for conventional power transformers discussed in section 2 of this guide, except that the design has been optimized for accuracy. Like current transformers, voltage transformers are assigned accuracy classes by IEEE Std. C57.13.
VT accuracy classes are designated W, X,M Y, Z, and ZZ in order of increasing burden requirements.
Voltage instrument supporting transformer
Protective relays are classified by function. To make circuit representations easier, each function has been defined and assigned a number by IEEE Std. C37.2. The IEEE standard function numbers are given in Table 1.
Table 2 gives the commonly-used suffix letters to further designate protective functions. These designations can be combined in various ways. For example, 87T denotes a transformer differential relay, 51N denotes a residual ground time-overcurrent relay, 87B denotes a bus differential relay, etc.
Table 1 – Commonly used protective relay device function numbers
Relay device function number (ANSI Code)Protection function
21Distance
25Synchronizing
27Undervoltage
32Directional Power
40Loss of Excitation (field)
46Phase balance (current balance, negative sequence current)
47Phase-Sequence Voltage (reverse phase voltage)
49Thermal (generally thermal overload)
50Instantaneous Overcurrent
51Time-overcurrent
59Overvoltage
60Voltage balance (between two circuits)
67Directional Overcurrent
81Frequency (over and underfrequency)
86Lockout
87Differential
Table 2 – Commonly used suffix letters applied to protective relay function numbers
Suffix LetterRelay Application
AAlarm only
BBus protection
GGround fault protection [relay current transformer (CT) in a system neutral circuit] or generator protection]
GSGround-fault protection (relay CT is toroidal or ground sensor)
LLine Protection
MMotor Protection
NGround fault protection (relay coil connected in residual CT circuit)
TTransformer protection
VVoltage
Reference // System Protection by Bill Brown, P.E., Square D Engineering Services
6 Comments
  1. Mumba mulenga
    Jun 29, 2021
    This is a very good and interesting team, would like to join.
    Any access?
  2. Shivram tayshete
    Nov 14, 2020
    Please send all new information of any type relay
  3. Bouhamida Kamel
    Jun 29, 2019
    Tres Bon article
  4. Antonio Buccieri
    Aug 14, 2017
    I love this job
    If possible I will do again
  5. pedro
    Jul 07, 2017
    Mr Edvard thanks for the information is very good
  6. JOSE MONTALVAN
    Dec 16, 2015
    Very good article congratulations Eng. Edvard.
Leave a Reply to Antonio Buccieri
  +  twenty eight  =  thirty eight