Get access to premium HV/MV/LV technical articles, technical guides & papers. Apply a 20% discount code: 99AF8 for a 1-year plan!
Formulas
For each system parameter, per-unit value is equal to the actual value divided by a base value:
Epu = E / Ebase
Ipu = I / Ibase
Zpu = Z / Zbase
Select rated values as base values, usually rated power in MVA and rated phase voltage in kV:
Sbase = Srated = Ö3ElineIline
Ebase = Ephase = Eline/ Ö3
The base values for line current in kA and per-phase star impedance in ohms/phase are:
Ibase = Sbase / 3Ebase ( = Sbase / Ö3Eline)
Zbase = Ebase / Ibase = 3Ebase2 / Sbase ( = Eline2 / Sbase)
Note that selecting the base values for any two of Sbase, Ebase, Ibase or Zbase fixes the base values of all four. Note also that Ohm’s Law is satisfied by each of the sets of actual, base and per-unit values for voltage, current and impedance.
Transformers
The primary and secondary MVA ratings of a transformer are equal, but the voltages and currents in the primary (subscript 1) and the secondary (subscript 2) are usually different:
Ö3E1lineI1line = S = Ö3E2lineI2line
Converting to base (per-phase star) values:
3E1baseI1base = Sbase = 3E2baseI2base
E1base / E2base = I2base / I1base
Z1base / Z2base = (E1base / E2base)2
The impedance Z21pu referred to the primary side, equivalent to an impedance Z2pu on the secondary side, is:
Z21pu = Z2pu(E1base / E2base)2
The impedance Z12pu referred to the secondary side, equivalent to an impedance Z1pu on the primary side, is:
Z12pu = Z1pu(E2base / E1base)2
Note that per-unit and percentage values are related by:
Zpu = Z% / 100
NOTATION
The symbol font is used for some notation and formulae. If the Greek symbols for alpha beta delta do not appear here [ a b d ] the symbol font needs to be installed for correct display of notation and formulae.
B
C
E
f
G
h
I
j
L
P
Q
susceptance
capacitance
voltage source
frequency
conductance
h-operator
current
j-operator
inductance
active power
reactive power
[siemens, S]
[farads, F]
[volts, V]
[hertz, Hz]
[siemens, S]
[1Ð120°]
[amps, A]
[1Ð90°]
[henrys, H]
[watts, W]
[VAreactive, VArs]
Q
R
S
t
V
W
X
Y
Z
f
w
quality factor
resistance
apparent power
time
voltage drop
energy
reactance
admittance
impedance
phase angle
angular frequency
[number]
[ohms, W]
[volt-amps, VA]
[seconds, s]
[volts, V]
[joules, J]
[ohms, W]
[siemens, S]
[ohms, W]
[degrees, °]
[rad/sec]
Get email alert whenever we publish new electrical guides and articles.
New Online Training Courses
World class online training for electrical engineers and industrial electricians.