Home / Technical Articles / Rogowski Coil Construction
How it’s build?
Figure 1 shows the construction of a Rogowski coil, an air-core current transformer that is especially well suited to measuring ripple currents in the presence of a DC component or measuring pulsed currents.
Rogowski Coils For Precision Measurements and Protection
The raw output is proportional to the derivative of the current, and the current can be recovered by an integrator or a low-pass filter.
The output voltage is given by:
Output voltage formula
Rogowski coil construction
Figure 1 – Rogowski coil construction
n is the number of turns
A is the cross sectional area of the toroid
s is the centerline circumference
The coil is wound on an air-core form of suitable size for the current conductor. The winding should be applied in evenly spaced turns in one direction only-not back and forth-so that capacitive effects are minimized.
The far end of the winding should be brought back around the circumference of the coil to eliminate the turn formed by the winding itself. The winding must generally be shielded, since the output voltage is relatively low. The shield should be applied so that it does not form a shorted turn through the opening, and the coil should be equipped with an integral shielded output lead with the ground side connected to the coil shield.
Output from the Rogowski coil can either be integrated with a passive network as an R/C low-pass filter or with an operational amplifier.
The advantage of the R/C network is that no power is required for operation. The disadvantages are that it cannot be gated and that the output voltage becomes very low if low-frequency response is required.
Although a toroidal form is shown in the sketch, Rogowski coils are commercially available that are wound in the form of a very long, flexible solenoid that can be wrapped around a conductor and then secured mechanically.
Rogowski coils are largely unaffected by stray fields that have a constant amplitude across the coil. A field gradient across the coil, however, will introduce a spurious output if the field is time varying.
It is good practice to make the coil as small as possible within the electrical and physical constraints of the equipment.
The Rogowski coil can be calibrated from a 50/60-Hz current assuming, of course, that the bandpass of the filter or integrator extends down to those frequencies.
Resource: Electronics Design : A Practitioner’s Guide – eith H. Sueker
  1. Jay Reed
    Jul 23, 2020
    Hello, I’m interested in setting up a Rogowski interfaced to a small Tektronix oscilloscope to display the inrush current when a 60 Hertz Neon sign transformer charges an empty capacitor. Can you offer any design or advice. Thank you, Jay
  2. Denis Zandona
    Mar 17, 2018
    Good morning, Mr. Edvard,
    I read your article and it’s very interesting. Could you tell me more about the construction of rogowsky coils? For example, could you tell me how to control the cross-talk and how to make the linear rogowsky coils at different currents?
    Best regards
  3. José Santana
    Feb 24, 2013
    Hi
    I like so much read every week your technical articles, as well as the electrical softwares.
    Many thanks for your contribution.
    JP
Leave a Reply to Denis Zandona
ninety  ⁄    =  fifteen
