Home / Technical Articles / Safety Clearance Recommendations for Transformer
Safety Clearance Recommendations for Transformer (on photo 10/0.4 kV transformer substation by FIMA)
Clearance Tables
  1. Clearance from Outdoor Liquid Insulated Transformers to Buildings (NEC)
  2. Clearance between Two Outdoor Liquid Insulated Transformers (NEC)
  3. Dry Type Transformer in Indoor Installation (NES 420.21)
  4. Dry Type Transformer in Outdoor Installation (NES 420.22)
  5. Non Flammable Liquid-Insulated Transformer in Indoor Installation (NES 420.21)
  6. Oil Insulated Transformer in Indoor Installation (NES 420.25)
  7. Transformer Clearance from Building (IEEE Stand.)
  8. Transformer Clearance Specifications (Stand. Georgia Power Company)
  9. Clearance of Transformer-Cable-Overhead Line (Stand. Georgia Power Company)
LiquidLiquid Volume (m3)Fire Resistant Wall Non-Combustible WallCombustible WallVertical Distance
Less FlammableNA0.9 Meter0.9 Meter0.9 Meter0.9 Meter
<38 m31.5 Meter1.5 Meter7.6 Meter7.6 Meter
>38 m34.6 Meter4.6 Meter15.2 Meter15.2 Meter
Mineral Oil<1.9 m31.5 Meter4.6 Meter7.6 Meter7.6 Meter
1.9 m3 to 19 m34.6 Meter7.6 Meter15.2 Meter15.2 Meter
> 19 m37.6 Meter15.2 Meter30.5 Meter30.5 Meter
Go to Content ↑
LiquidLiquid Volume (m3)Distance
<38 m31.5 Meter
>38 m37.6 Meter
1.9 m3 to 19 m37.6 Meter
> 19 m315.2 Meter
Go to Content ↑
VoltageDistance (min)
Up to 112.5 KVA300 mm (12 in.) from combustible material unless separated from the combustible material by a heat-insulated barrier.
Above 112.5 KVAInstalled in a transformer room of fire-resistant construction.
Above 112.5 KVA with Class 155 Insulationseparated from  a fire-resistant barrier not less than 1.83 m (6 ft) horizontally and 3.7 m (12 ft) vertically
Go to Content ↑
Go to Content ↑
Over 35KVInstalled indoors Vault (Having liquid confinement area and a pressure-relief vent for absorbing any gases generated by arcing inside the tank, the pressure-relief vent shall be connected to a chimney or flue that will carry such gases to an environmentally safe area
Above 112.5 KVA (Class 155 Insulation)separated from a fire-resistant barrier not less than 1.83 m (6 ft) horizontally and 3.7 m (12 ft) vertically
Go to Content ↑
Up to 112.5 KVAInstalled indoors Vault (With construction of reinforced concrete that is not less than 100 mm (4 in.) thick.
Up to 10 KVA & Up to 600VVault shall not be required if suitable arrangements are made to prevent a transformer oil fire from igniting
Up to 75 KVA & Up to 600VVault shall not be required if where the surrounding Structure is classified as fire-resistant construction.
Furnace transformers (Up to 75 kVA)Installed without a vault in a building or room of fire resistant construction
Go to Content ↑
Transformer Clearance from Building (IEEE Stand)
TransformerDistance from Building (min)
Up to 75 KVA3.0 Meter
75 KVA to 333 KVA6.0 Meter
More than 333 KVA9.0 Meter
Go to Content ↑
Transformer Clearance Specifications (Stand: Georgia Power Company)
Description of ClearanceDistance (min)
Clearance in front of the transformer3.0 Meter
Between Two pad mounted transformers (including Cooling fin)2.1  Meter
Between Transformer and Trees, shrubs, vegetation( for unrestricted natural cooling )3.0 Meter
The edge of the concrete transformer pad to nearest the building4.2 Meter
The edge of the concrete transformer pad to nearest  building wall, windows, or other openings3.0 Meter
Clearance from the transformer to edge of (or Canopy) building (3 or less stories)3.0 Meter
Clearance in front of the transformer doors and on the left side of the transformer, looking at it from the front (For operation of protective and switching devices on the unit)3.0 Meter
Gas service meter relief vents.0.9 Meter
Fire sprinkler values, standpipes and fire hydrants1.8 Meter
The water’s edge of a swimming pool or any body of water.4.5 Meter
Facilities used to dispense hazardous liquids or gases6.0 Meter
Facilities used to store hazardous liquids or gases3.0 Meter
Clear vehicle passageway at all times, immediately adjacent of Transformer3.6 Meter
Fire safety clearances can be reduced by building a suitable masonry fire barrier wall (2.7 Meter wide and 4.5 Meter Tall) 0.9 Meter from the back or side of the Pad Mounted Transformer  to the side of the combustible wall
Front of the transformer must face away from the building.
Go to Content ↑
Clearance of Transformer-Cable-Overhead Line (Stand: Georgia Power Company)
Description of ClearanceHorizontal Distance (mm)
to pad-mounted transformersto buried HV cableto overhead HV Line
Fuel tanks7.5 Meter1.5 Meter7.5 Meter
Granaries6.0 Meter0.6 Meter15 Meter
Homes6.0 Meter0.6 Meter15 Meter
Barns, sheds, garages6.0 Meter0.6 Meter15 Meter
Water wells1.5 Meter1.5 Meter15 Meter
Antennas3.0 Meter0.6 MeterHeight of Antenna + 3.0 Meter
Go to Content ↑
Jignesh Parmar
28 Comments
  1. Faseeh Shan
    Jan 23, 2020
    What should be the safe distance of a transformer from the Control system(PLC) Cabinet. So that it may not effect(4 to 20mAmp) Control signals
  2. Joseph
    Dec 05, 2019
    what are the pros/cons in stacking indoor transformers?
  3. TODARMAL Panwar
    Apr 02, 2019
    Sir contractor 440 volt transformers installed closer to my house please suggest me how distance between home and transformers
  4. P RAGHAVEDRARAO
    Mar 15, 2019
    UP TO WHAT CAPACITY FIRE PROTECTION WALL REQUIRED FOR OIL FILLED POWER TRANSFORMERS
  5. Bappadityo Goswami
    Dec 28, 2018
    Dear Sir,
    Please provide the NEC reference Number regarding minimum distance between two outdoor transformer?
  6. Prasenjit Sardar
    Oct 13, 2017
    I live in an apartment and from the electric office a transformer is being planted very near my building and outside my window. So , in this circumstance what should I do and what should be the check points and for complain where sholud I lodge them? Please help. Awaiting your early response.
    • AMITABHA GUHA
      Feb 04, 2018
      Mr. Prasenjit Sardar, I have an exactly similar problem. Have you got answer to your problem from any source ? If yes, please let me know the details as it will help me a lot. I am particularly interested to know what should be the minimum distance they should maintain from building line / property line for a 6 KV / 430 V transformer ?
  7. Abhijit Bhavsar
    Feb 24, 2017
    Dear Sir,
    We are installing Dry type transformer of capacity 2750 KVA (11KV/433 V) inside the container with DNV certified 2.7.2 Pressurized container as the area is hazardous area Please suggest what should be the minimum distance of the transformer from the walls of the container. the walls of the container is of class A60. Also suggest the distance between two transformer as we are placing 2 transformer on the same offshore platform.
  8. Mostafa elsissy
    Aug 21, 2016
    What is the max # of transformer can be located in one room with respect to fire/safety
  9. Mustafa Elsissy
    Aug 01, 2016
    Thanks for the valuable information and my comment is what is the fire min separation distance between TRFS located inside closed space?
  10. choi
    Jan 23, 2016
    Thanks for the useful article.
    Could you let me know “NES”??
    In the middle of the article, there is “NES 420.22 -Dry type transformaer”.
    Is this the first letter of National Electric Safety Code? or Something?
    I would really appreciate your help.
  11. Alex
    Jan 07, 2016
    I would use both measurement units, Imperial and metric?
    Also you should have referenced NFPA 850, UL and FM global.
    Thanks,
    A.
  12. David
    Dec 02, 2015
    For tables 1 and 2, where exactly is this table referencing in the NEC? I’ve scoured all over article 450 and I don’t see anything with specific distances.
  13. Sanjiv Batra
    May 13, 2015
    Hello,
    Two days back punjab state elect. Board put on of tranceformer in front of my residental plot. The clearence from my plot to tranceformer pole is about 6 inches. I was planning to start construction this month. I want that traceformer should be fitted on some where else. Please can you advise how i can proceed. Do you have legal information about this issue. Even i planned to sale this plot but no one like to buy this plot.
  14. folskan
    Dec 16, 2013
    gracias desde honduras
  15. SANATH JAMES
    Dec 24, 2012
    This is a very useful web site providing and sharing the design standards pertaining to electrical engineering. Recommeded for all serious electrical engineers.