What’s the catch: The microshock

This technical article analyzes the safety requirements against indirect contact employed in particularly special medical locations (e.g., hospitals, medical, and dental practices, etc.), where environmental conditions may increase the risk of indirect contact and therefore the electroshock, precisely microshock.

The ground is not just ground! At least not in hospitals, medical, and dental practices
The ground is not just ground! At least not in hospitals, medical, and dental practices

Generally speaking, special locations and installations are locations where the presence of water or moisture decreases the resistance-to-ground of the person’s body by lowering his/her skin resistance. Special locations in terms of safety requirements against indirect contact are also wet locations where the humidity can increase the failure rate of equipment by compromising the integrity of its basic insulation.

In medical locations (e.g., hospitals, medical, and dental practices, etc.), patients are exposed to increased hazard of electric shock due to their particular conditions. Patients, in fact, may be unconscious, or anaesthetized and, therefore, unable to let-go of an energized part.

In addition, patients may be connected to medical equipment either through applied parts to the skin (e.g., sensors, electrodes, etc.), often locally treated to lower its resistance, and/or through the introduction of catheters directly into their body’s organs (e.g., the heart).

The use of conductive intracardiac probes, electrically connecting the heart to medical equipment, makes the patient extremely vulnerable to electric currents, because it lowers the threshold of danger. In fact, in a catheterized patient subject to touch voltages, leakage, or fault, currents will entirely flow through patient’s heart and leave the body via the catheter.

In these conditions, the current is no longer limited by the body resistance-to-ground, because this resistance does not form part with the fault-loop. Patients become particularly susceptible to the adverse effects of electricity, and currents of magnitude of a few tens of microamperes can trigger ventricular fibrillation.

This phenomenon is defined as microshock.

Table of Contents:

  1. High Protective Conductor Currents
  2. Leakage Currents
  3. Local Equipotential Earthing Connection
  4. Electrical Separation
    1. Interruption of the Protective Conductor in Separated Systems

1. High Protective Conductor Currents

Medical electronics equipment may be sensitive to electromagnetic interferences irradiated by “disturbing” loads. For this reason, radio frequency input filters constituted by capacitors connected between supply conductors and enclosures of equipment are employed to enhance the electronic systems’ immunity.

Such filters may cause continuous leakage currents through the protective conductors in excess of 3.5 A. See Figure 1.

Figure 1 – Earth leakage currents due to radio frequency filters

Earth leakage currents due to radio frequency filters
Figure 1 – Earth leakage currents due to radio frequency filters

IEC 60950-13 limits the maximum value of leakage currents of Class I, stationary, or pluggable, equipment to 5% of the input current. The presence of high currents on protective conductors might cause nuisance trippings of RCDs, when their residual settings are exceeded even in the absence of ground faults.

Serious hazard is caused by the accidental loss of the protective conductor serving the equipment.

See Figure 2.

Figure 2 – Hazardous situation caused by the accidental loss of the PE

Hazardous situation caused by the accidental loss of the PE
Figure 2 – Hazardous situation caused by the accidental loss of the PE

The leakage current, in fact, will circulate through the person’s body if she/he comes into contact with the enclosure. Thus, for safety reasons, the bonding of high leakage current equipment must be assured by enhancing the reliability of the PE. This can be obtained by doubling its cross-sectional area, with respect to minimum permissible values, by using more than one PE conductor in parallel, and/or monitoring its electrical continuity.

If the leakage current exceeds 3.5 A, the aforementioned IEC standard requires a warning label to be affixed adjacent to the equipment power connection, indicating the necessity of connecting the protective conductor before switching on the supply.

To prevent electrical noise from interfering with sensitive electronic equipment, manufacturers may require a dedicated grounding system. An erroneous interpretation of this condition may lead the designer to install in the same building one separate ground for the high-frequency electronic apparatus and one for the 50/60-Hz equipment.

See Figure 3.

Figure 3 – Grounding electrodes for sensitive 50/60-Hz electronic equipment

Distinct grounding electrodes for sensitive electronic equipment and for 50/60-Hz equipment
Figure 3 – Distinct grounding electrodes for sensitive electronic equipment and for 50/60-Hz equipment

The above arrangement is extremely unsafe and must be avoided, because it does not assure equal potential between equipment under fault conditions. In the case of ground faults on either exposed conductive part, persons in simultaneous contact with both pieces of equipment are subject to the whole earth potential.

Each exposed conductive part becomes, in fact, an extraneous conductive part to the other one. In addition, separate earthing points, possibly energized at different potentials under fault conditions, can cause circulation of ground currents, and be the source of the electrical noise one wants to eliminate.

Another issue pertaining to continuous high leakage currents may be the inevitable nuisance trippings of protective residual current devices. In this situation, the general protection provided by RCDs becomes ineffective, circumstance extremely dangerous in TT systems. The solution to this problem might be to supply the “offender” equipment with a dedicated RCD with residual operating threshold set to a sufficiently high value.

Alternatively, a separation transformer with RCDs on the primary side can be used to supply the load, as RCDs would not sense any leakage currents on its secondary side.

Suggested Reading – Current sensors as the eyes of RCD & tips for their correct installation

Current sensors as the eyes of RCD and tips for their correct installation

Go back to the Contents Table ↑


2. Leakage Currents

Ordinary Class I equipment, medical or not, during its use may leak current through the insulation, and into the protective conductor. As discussed in previous Section 1, in the case of interruption of the protective conductor, the leakage current may circulate through the persons in contact with the enclosure.

For ordinary equipment (i.e., equipment having low protective conductor currents), the magnitude of such current is so low that it does not constitute a hazard for persons.

In medical locations, though, the interruption of the PE, defined as single fault condition, is very dangerous because the same low amount of  leakage current flowing through the catatherized patient, defined as patient leakage current IP, can cause the microshock.

In Figure 4, it is shown how in a single fault condition, the patient leakage current IP can directly circulate through his/her heart due to contacts with any Class I equipment (Ien) and/or due to applied parts to the body (Iap).

In the above situation, the person is at great risk of microshock, as the patient current may exceed the fibrillation threshold.

Figure 4 – Patient leakage current caused by the interruption of the PE

Patient leakage current caused by the interruption of the PE
Figure 4 – Patient leakage current caused by the interruption of the PE

Go back to the Contents Table ↑


3. Local Equipotential Earthing Connection

In addition to the “chronic” problem of leakage currents from regularly operating Class I equipment emphasized by the interruption of their protective conductors, the safety of the patient can also be endangered by actual ground faults.

Figure 5 exemplifies a ground fault in TT systems because of the failure of an electrical component in the patient vicinity. The patient vicinity is defined as the space with enclosures likely to be touched by the patient, which extends 1.83 m beyond the perimeter of the bed and 2.29 m above the floor.

In the above situation, a potential difference VA, caused by the voltage drop on the protective conductor of resistance RPEA, appears between the two pieces of equipment the patient may be in simultaneous contact with by touch and via catheters.

Figure 5 – Hazardous condition in the presence of a sound PE

Hazardous condition in the presence of a sound PE
Figure 5 – Hazardous condition in the presence of a sound PE

The reduction of such voltage drop can be obtained by connecting together all the exposed conductive parts (ECPs) and the extraneous conductive parts (EXCPs) to a local equipotential earthing bus located within the patient vicinity (see Figure 6).

This supplementary equipotential bonding connection lowers the resistance of the protective conductor serving the faulty exposed conductive part, ECP (i.e., RPEA1 < RPEA), thereby decreasing the touch voltage (i.e., VA1 < VA).

It is important to note that due to the patient’s enhanced sensitivity to electric currents, extraneous conductive parts (EXCPs) in medical locations need to be redefined, with respect to the standard definition that we gave in ordinary locations. In medical locations, in fact, IEC standards assume the threshold of 25 V as the maximum permissible touch voltage, and a lethal current for catheterized patients of 50 A.

In these assumptions, the resulting resistance-to-ground of any metal part in the patient vicinity must exceed 500 kΩ in order not to be an extraneous conductive parts (EXCPs), and therefore, not bonded to the local earthing bus.

Figure 6 – A local equipotential earthing bus reduces the voltage drop on the PE

A local equipotential earthing bus reduces the voltage drop on the PE
Figure 6 – A local equipotential earthing bus reduces the voltage drop on the PE

Go back to the Contents Table ↑


4. Electrical Separation

The local supplementary bonding connection, even though within the patient vicinity, cannot always sufficiently decrease the resistance of the PE and therefore limit the touch voltage to safe values. This is true especially in TN systems, where the ground-fault current may be rather high and so may the voltage drop on the PEs.

In non-fault conditions, instead, currents leaking from pieces of equipment connected to the same local earthing bus are virtually identical and in phase, and cause almost identical voltage drops over their PE, thereby determining no appreciable potential differences.

To improve the protection against indirect contact under fault conditions, in addition to the local equipotential earthing bus, an isolating transformer supplying the circuits in the patient vicinity may be adopted (see Figure 7).

First faults occurring in electrically separated systems, cause the flow of capacitive currents IG of low magnitude (i.e., order of milliamperes) through the PEs. As a consequence, the touch voltage the patient might be exposed to is well within safe limits.

Problems may arise at the occurrence of a subsequent second fault involving the other pole in another piece of equipment in contact with the patient. In that case, the resulting short circuit current circulating through the protective conductors might cause dangerous potential differences between the faulty exposed conductive parts, even in the presence of the supplementary equipotential bonding.

For this reason, in medical locations, the first fault must be promptly traced by means of an insulation-monitoring device and then cleared.

Figure 7 – Isolating transformer supplying the circuits in the patient vicinity

Isolating transformer supplying the circuits in the patient vicinity
Figure 7 – Isolating transformer supplying the circuits in the patient vicinity

The earthing connection of the enclosures of the separated system, shown in Figure 7, makes this system resemble the IT system. In the patient vicinity, in fact, there may be small equipment, not supplied by the isolating transformer, requiring the ground connection available at the local earthing bus.

The above arrangement is a violation of the general rule, which prohibits the exposed conductive parts of separated systems to share the earth with nonseparated systems (prohibition also applicable to Class II equipment).

As you can see, this rule intends to prevent enclosures of separated systems from becoming dangerously “live” due to potentials transferred by means of earthing connections.

In the presence of the supplementary equipotential bonding in medical locations, this risk is, indeed, very low and deemed acceptable. In fact, even if the earthing bus attains a certain potential under fault conditions, all the ECPs in the patient vicinity will simultaneously reach this same value, as Figure 7 shows; ergo, no potential differences can appear among them and the patient is safe.

As a consequence, the grounding connection in separated systems adopted in medical locations is deemed safe in the presence of the local equipotential bonding.

Suggested course – Learn AC Distribution Panel Drawings: Single-Line Diagrams, Wirings, and Interlocking Schematics

Learn AC Distribution Panel Drawings: Single-Line Diagrams, Wirings, and Interlocking Schematics

Go back to the Contents Table ↑


4.1 Interruption of the Protective Conductor in Separated Systems

The interruption of the PE is dangerous even in separated systems because the resulting capacitive current through the patient may exceed the fibrillation limits (Figure 8).

Let Z1, Z2, Z3, and Z4 be the capacitive impedances-to-ground of supply and equipment, as indicated in Figure 8. Upon loss of the protective conductor, the leakage current impressed by pole D through Z4 will reclose toward pole A by circulating through the patient.

Figure 8 – Separated system with interrupted PE

Separated system with interrupted PE
Figure 8 – Separated system with interrupted PE

The above impedances are connected in a “bridge” configuration across whose diagonal BC patients may find themselves linked (Figure 9).

Figure 9 – The patient may be connected across the impedance bridge’s diagonal

The patient may be connected across the impedance bridge’s diagonal
Figure 9 – The patient may be connected across the impedance bridge’s diagonal

If the impedance bridge is balanced, that is, Z1×Z4 = Z2×Z3, the patient is safe, as VBC = IP = 0. If the bridge is not balanced, the patient current IP can be obtained by deducing the Thevenin equivalent circuit as seen at the points B and C.

See Figure 10.

Figure 10 – Thevenin equivalent circuit as seen at the points B and C of the bridge

Thevenin equivalent circuit as seen at the points B and C of the bridge
Figure 10 – Thevenin equivalent circuit as seen at the points B and C of the bridge

The equivalent Thevenin voltage Vth is calculated by applying Kirchhoff’s second law to the loop DBAD and the voltage divider rule (Equation 1):

Voltage divider rule

The Thevenin impedance Zth is given by:

Thevenin impedance Zth

Thus, the patient current IP is:

Patient current formulae

where RB is the patient’s body resistance.

In balance conditions of the bridge (i.e., Z1×Z4 = Z2×Z3), it appears clear from Eq. (15.2) that Vth equals zero; therefore, the patient is safe even if the protective conductor of the medical equipment is interrupted.

In practice, the balance condition is rather challenging to both achieve and maintain in time. Although results have been achieved in manufacturing separation transformers with identical capacitance-to-ground, that is, Z1 = Z2, it is rather difficult to obtain medical equipment with symmetrical impedance-to-ground, that is, Z3 ≠ Z3.

Thus, designers cannot rely upon balanced bridges to achieve safety in medical locations.

Suggested Course – Transformer Differential Protection Course: Understanding Schematics, Relay Settings and Testing

Transformer Differential Protection Course: Understanding Schematics, Relay Settings and Testing

Go back to the Contents Table ↑


Source: Electrical Safety of LV Systems by Dr. Massimo A. G. Mitolo

Premium Membership

Get access to premium HV/MV/LV technical articles, electrical engineering guides, research studies and much more! It helps you to shape up your technical skills in your everyday life as an electrical engineer.
More Information
Edvard Csanyi - Author at EEP-Electrical Engineering Portal

Edvard Csanyi

Hi, I'm an electrical engineer, programmer and founder of EEP - Electrical Engineering Portal. I worked twelve years at Schneider Electric in the position of technical support for low- and medium-voltage projects and the design of busbar trunking systems.

I'm highly specialized in the design of LV/MV switchgear and low-voltage, high-power busbar trunking (<6300A) in substations, commercial buildings and industry facilities. I'm also a professional in AutoCAD programming.

Profile: Edvard Csanyi

One Comment


  1. Che Wan Zainul
    Nov 22, 2022

    I feel many thanks.
    Professional reading to enhance and expand my knowledge and understanding of topics, themes and research.
    You went to extraordinary lengths explanation to understand.

    Terima Kasih

Leave a Comment

Tell us what you're thinking. We care about your opinion! Please keep in mind that comments are moderated and rel="nofollow" is in use. So, please do not use a spammy keyword or a domain as your name, or it will be deleted. Let's have a professional and meaningful conversation instead. Thanks for dropping by!

Learn How to Design Power Systems

Learn to design LV/MV/HV power systems through professional video courses. Lifetime access. Enjoy learning!

EEP Hand-Crafted Video Courses

Check more than a hundred hand-crafted video courses and learn from experienced engineers. Lifetime access included.
Experience matters. Premium membership gives you an opportunity to study specialized technical articles, online video courses, electrical engineering guides, and papers written by experienced electrical engineers.
Whitepaper: How to Improve Risk Decisions for Power Systems - Prioritizing vulnerabilities with full operational context