Search

Premium Membership ♕

Join EEP PREMIUM today to unlock professional articles, specialized guides, and 50% discount on academy courses (lifetime access included)

Home / Technical Articles / Schematics Analysis of 13.8kV 100MVA Transformer Feeder

Estimated Study Time: 51 minutes

Metal-Clad Switchgear Schematics

This technical article provides a detailed analysis of the schematic drawings for a 13.8kV, 100MVA Transformer Feeder. The source material for this analysis is attached drawing document (PDF), detailing an ABB UNIGEAR-ZS1 metal-clad switchgear panel designated as =H.1.

Schematics Analysis of 13.8kV 100MVA Transformer Feeder
Schematics Analysis of 13.8kV 100MVA Transformer Feeder

The analysis starts with an overview of the Single Line Diagram (SLD) and physical panel specifications. From there, we will explain the mechanical and electrical operations of the vacuum circuit breaker, tracing the precise pathways of its charging motor, safety interlocks, and redundant trip coils.

The discussion will examine the distinct roles of the multi-core Current Transformers (CTs) and Voltage Transformers (VTs), explaining how they feed high-impedance differential schemes, precise metering instruments, and primary feeder protection relays.

We will also explain the schematics of digital protection relay ABB REF 615, its binary input matrix, analog mappings, and critical circuit breaker failure (CBF) lockout logic. Furthermore, the analysis will navigate through auxiliary systems, including mechanical earthing switches and load-dependent cooling circuits.

To provide maximum practical value for field engineers and technical reviewers, we will conclude by identifying, analyzing, and resolving specific documentation inconsistencies hidden within the attached engineering drawings.

Here is the download link for the complete PDF document with drawings (256 pages). Open it up, so you can follow the discussion.
Schematics (PDF, 14.0 MB)

Table of Contents:

  1. An Overview of 13.8kV Metal-Clad Swichgear:
    1. Switchgear Specifications and Ratings
    2. The Single Line Diagram (SLD)
    3. Physical Layout and Compartments
  2. The Vacuum Circuit Breaker +A-Q0:
    1. Breaker Specifications
    2. Breaker Operating Mechanism and Control Coils
  3. Current Transformer (CT) Arrangement:
    1. Upper CTs (+B-CT): High-Impedance Differential Protection:
      1. Tracing the Upper CT Core 1 Wiring
    2. Lower CTs (+C-CT): Metering and Feeder Protection:
      1. Lower CT Core 1: Metering (Class 0.2Fs5)
      2. Lower CT Core 2: Primary Feeder Protection (Class 5P20)
      3. Lower CT Core 3: Busbar Differential Protection (Class PX)
  4. Voltage Transformer (VT) Arrangement and Distribution:
    1. VT Specifications
    2. VT Secondary Distribution and Protection:
      1. Winding 1 Distribution (Sheets 21 and 22)
      2. Winding 2 Distribution and Fuse Supervision
  5. Protection and Control: ABB REF 615:
    1. Digital Communications and IEC 61850
    2. Analog Inputs
    3. Binary Inputs and Output (I/O) Mapping
  6. Tripping and Closing Circuits:
    1. Trip Circuits 1 and 2 (Sheets 31 and 32)
    2. Circuit Breaker Failure (CBF) Lockout Scheme (Sheet 34)
    3. The Closing Circuit and Permissive Interlocking (Sheet 33)
  7. Digital Metering and Local Indication
  8. Auxiliary Systems: Cooling, Heating & Earthing:
    1. Forced Air Cooling Circuit (Sheet 25)
    2. Environmental Heating and Safe Earthing (Sheets 24 and 26)
  9. Schematic Inconsistencies:
    1. Circuit Breaker Ampacity Rating Mismatch
    2. Circuit Breaker Part Number Typographical Error
    3. Binary Input Mapping “As-Built” Discrepancy
  10. Summary Notes
  11. Attachment (PDF) 🔗 Download ‘Low Voltage Design Handbook: From Principles to Application’

1. An Overview of 13.8kV Metal-Clad Swichgear

1.1 Switchgear Specifications and Ratings

The electrical parameters of the switchgear are established on the Rating Plate detailed on Sheet 1 (Row B, Column 4-7). The panel is engineered to operate at a nominal service voltage of 13.8kV, sitting within a maximum rated voltage envelope of 17.5kV.

The rated insulation level, expressed as Basic Insulation Level (BIL), is 17.5/38/95 kV, indicating the root-mean-square (RMS) withstand voltage and the peak lightning impulse withstand voltage, respectively. The system operates at a frequency of 60Hz.

To accommodate the power transfer required by a 100MVA transformer at 13.8kV, both the main busbars and the tee-off connections are rated for a normal continuous current of 3600A. Handling this current safely requires thermal management, which is addressed through forced cooling systems within the physical cubicle.

The short-time withstand current (the fault current the busbars can physically and thermally endure without failure) is rated at 25kA for a duration of 3 seconds.

Furthermore, the peak withstand current, which accounts for the mechanical stresses generated by the asymmetrical peak of the first half-cycle of a fault, is rated at 65kA.

Figure 1 – Switchgear rating plate (Sheet 1)

Switchgear rating plate (Sheet 1)
Figure 1 – Switchgear rating plate (Sheet 1)

Go back to Content Table ↑


1.2 The Single Line Diagram (SLD)

The Single Line Diagram, located on Sheet 11, serves as the feeder’s power flow and protection arrangement. Power decreases from the 3600A main busbar through various components we’ll mention now.

Immediately below the busbar connection, the Upper Current Transformers +B-CT are positioned. These CTs are dedicated exclusively to providing primary current data to the external transformer differential protection schemes.

Below the upper CTs sits the primary interrupting device, the Vacuum Circuit Breaker +A-Q0. This 3600A breaker is the critical actuator for all protection logic, designed to sever the circuit instantly upon receiving a trip command.

On the load side of the circuit breaker, the Lower Current Transformers +C-CT are installed. These lower CTs are multi-core devices, supplying analog current signals to the digital metering devices, the primary ABB REF 615 feeder protection relay, and the busbar differential protection scheme.

Further down the load side, the Voltage Transformers +C-VT are tapped off the main copper conductors. Protected by primary fuses, these VTs step the 13.8kV potential down to a safe 120V secondary voltage for metering and distance/voltage protection references.

Finally, at the very bottom of the SLD, the Earthing Switch +C-Q2 provides a mechanical means to ground the outgoing cable section, ensuring a zero-potential environment for maintenance personnel.

Figure 2 – Transformer feeder SLD

Transformer feeder SLD
Figure 2 – Transformer feeder SLD

Go back to Content Table ↑


1.3 Physical Layout and Compartments

The switchgear physical layout is illustrated in the Cubicle Assembly drawing on Sheet 12. The ABB UNIGEAR-ZS1 is a highly compartmentalized, metal-clad design. Segregating the components into grounded metal compartments ensures that a failure (such as an internal arc fault) in one section does not propagate to destroy the entire switchgear.

As shown on the sectional side view (Sheet 12, Row C, Column 3), the switchgear is divided into four main zones. The Busbar Compartment is located at the top rear, housing the 2×120×100mm copper busbars.

The Circuit Breaker (CB) Compartment is positioned in the middle front, containing the withdrawable vacuum circuit breaker. The Cable Compartment occupies the bottom rear, providing space for the Lower CTs, VTs, Earthing Switch, and the terminations for eight power cables per phase.

Finally, the Low Voltage (LV) Compartment sits at the top front, securely isolated from the high voltage zones, housing the delicate protective relays, terminal blocks, and control wiring.

Figure 3 – Transformer feeder assembly

Transformer feeder assembly
Figure 3 – Transformer feeder assembly

Go back to Content Table ↑


2. The Vacuum Circuit Breaker (+A-Q0)

The central switching mechanism responsible for energizing the feeder and clearing faults is the Vacuum Circuit Breaker, designated as +A-Q0. The detailed specifications for this critical component are located in the Apparatus List on Sheet 3 (Row A, Column 5).


2.1 Breaker Specifications

The device is specified as an ABB Vacuum Circuit Breaker, Type VD4/P17.32.25p275. It utilizes an embedded pole design, where the vacuum interrupter is encapsulated within epoxy resin. This encapsulation protects the fragile vacuum bottle from environmental contaminants, dust, moisture, and external mechanical impacts, ensuring long-term dielectric integrity.

The operating cycle defined by IEC standards for this breaker is O-0.3sec-CO-15Secs-CO. This notation dictates the breaker’s duty cycle during an autoreclosing sequence.

It signifies that the breaker can Open (O) to clear a fault, wait for a dead time of 0.3 seconds to allow a transient fault (like a lightning strike) to clear, and then perform a Close-Open (CO) operation.

If the fault persists, it will wait 15 seconds before attempting one final Close-Open (CO) sequence. If the fault is still present, the breaker will lock out.

Figure 4 – Medium voltage draw-out vacuum circuit breaker, type VD4

Medium voltage draw-out vacuum circuit breaker, type VD4
Figure 4 – Medium voltage draw-out vacuum circuit breaker, type VD4

Go back to Content Table ↑


2.2 Breaker Operating Mechanism and Control Coils

The mechanical operation of the VD4 breaker is driven by a strong spring mechanism. The energy required to close the breaker against the immense electromagnetic forces of a short circuit is stored in this spring. The charging of the spring is controlled by a 125 VDC charging motor -MS.

To ensure unparalleled reliability, the breaker features a suite of 125 VDC control coils, interconnected via a 58-Pole Plug -XB detailed on Sheet 46. These coils execute the commands from the protection relays and safety interlocks:

First Shunt Release OFF (-MO1) – This is the primary tripping coil. Energizing this coil releases the mechanical latch holding the breaker closed.

Second Shunt Release OFF (-MO2) – Complete redundancy is mandatory in protection engineering. -MO2 is an entirely separate coil acting on the same mechanical trip latch. If -MO1 burns out or its wiring fails, -MO2 ensures the breaker can still clear a catastrophic fault.

Shunt Release ON (-MC) – This is the closing coil. When energized, it unlatches the charged closing spring, slamming the vacuum contacts together.

Truck Blocking Coil (-RL2) – This electromechanical lock prevents the breaker truck from being physically racked into or out of the ‘Service’ position unless specific safety conditions are met (e.g., the breaker must be OPEN).

Closing Blocking Coil (-RL1) – This coil acts as a definitive veto over the closing circuit. If -RL1 is not energized (indicating a blocked state), the mechanical closing linkage is disabled, rendering the -MC coil ineffective even if it receives an electrical command.

Furthermore, the breaker contains an internal Anti-Pumping facility. If a continuous mechanical or electrical “CLOSE” command is applied simultaneously with a “TRIP” command, the breaker will open to clear the fault but will mathematically refuse to re-close until the initial “CLOSE” command is entirely removed and re-applied.

This prevents the breaker from continuously “pumping” (opening and closing rapidly), which would destroy the vacuum bottles within seconds.

Figure 5 – Circuit breaker VD4 internal wiring

Circuit breaker VD4 internal wiring
Figure 5 – Circuit breaker VD4 internal wiring

Go back to Content Table ↑


3. Current Transformer (CT) Arrangement

Current Transformers are the sensory organs of the switchgear, stepping down primary currents (up to 25,000A during a fault) to safe, standardized secondary levels (1 Ampere) that delicate microprocessor relays and meters can analyze.

The accuracy and saturation characteristics of these CTs dictate the entire success of the protection scheme. The schematics distinguish between Upper CTs +B-CT and Lower CTs +C-CT.


3.1 Upper CTs (+B-CT): High-Impedance Differential Protection

The Upper CTs +B-CT1, +B-CT2, and +B-CT3 are located in the busbar compartment and are dedicated to the external transformer differential protection schemes. They are defined in the Apparatus List on Sheet 3 (Rows B, C, D; Column 5).

These CTs contain two identical protection cores, both specified as 3600/1A, Class PX. The selection of Class PX is highly deliberate. Standard protection CTs (like Class 5P20) are defined by their composite error at a specific multiple of their rated current.

However, in high-impedance differential protection, it is absolutely critical that the CTs on both sides of the protected zone (the transformer in this case) behave identically during external faults. If one CT saturates slightly before the other, the resulting “spill current” will flow into the differential relay, causing a catastrophic false trip, taking the transformer offline for a fault that wasn’t inside its zone.

To eliminate this, Class PX CTs are strictly defined by their internal physical and magnetic characteristics.


3.1.1 Tracing the Upper CT Core 1 Wiring

The schematic routing for the Upper CT Core 1 is explicitly detailed on Sheet 15. This core is designated to feed the Transformer Differential Protection Relay 87T1 (IED1), which resides in a remote relay panel.

Following the wiring standard defined on Sheet 1 (PVC insulated H07VK – 2.5 mm2 Yellow color for CT circuits), the Red (R) phase current originates at terminal 1S1 of +B-CT1 (Sheet 15, Row B, Column 1). This wire is routed directly to pin 1 of the disconnecting terminal block -X21 (Sheet 15, Row B, Column 4).

Disconnecting terminal blocks are vital; they allow technicians to isolate the CT circuit or inject test currents without physically unscrewing wires from the CT itself.

Similarly, the Yellow (Y) phase originates at terminal 1S1 of +B-CT2 and routes to -X21 pin 3. The Blue (B) phase originates at 1S1 of +B-CT3 and routes to -X21 pin 5. To complete the circuit, the return path (Neutral) must be formed. This is achieved by physically bridging the 1S2 terminals of all three CTs together.

This common neutral wire is routed to -X21 pin 7.

Importantly, a CT secondary circuit must be grounded at one, and exactly one, point. Grounding ensures the circuit does not float to a high voltage via capacitive coupling with the primary busbar. However, grounding at multiple points would create a parallel path for ground fault currents, distorting the differential reading.

On Sheet 15 (Row D, Column 4), the neutral path is solidly grounded at the local panel via the earth stud -EARTH1.

The wiring for Upper CT Core 2 is identical in topology, utilizing terminals 2S1 and 2S2, and is detailed on Sheet 16. It routes through terminal block -X22 to feed the redundant 87T2 differential relay (IED2).

Figure 6 -Upper CT Core 1 Wiring

Upper CT Core 1 Wiring
Figure 6 – Upper CT Core 1 Wiring

Go back to Content Table ↑


3.2 Lower CTs (+C-CT): Metering and Feeder Protection

Positioned below the circuit breaker in the cable compartment, the Lower CTs +C-CT1, +C-CT2, and +C-CT3 monitor the current flowing directly to the load cables.

These are multi-core devices, engineered to serve three distinct functions simultaneously. The specifications are located on Sheet 4 (Rows A, B, C; Column 5).


3.2.1 Lower CT Core 1: Metering (Class 0.2Fs5)

Core 1 is a 3600/1A core dedicated to revenue and operational metering. It is classified as 0.2Fs5 with a 15 VA burden. The “0.2” indicates an extremely high accuracy class, guaranteeing a maximum measurement error of just 0.2% under normal operating conditions.

This precision is required for accurate power billing and SCADA monitoring.

The “Fs5” designation represents an Instrument Security Factor of 5. Metering instruments contain delicate electronics that would be instantly vaporized by the secondary currents generated during a 25kA primary short circuit. An Fs5 core is intentionally manufactured with a limited cross-sectional magnetic iron area.

If the primary current exceeds 5 times the nominal rating (18,000A), the magnetic iron physically saturates. Once saturated, magnetic flux cannot increase, and the secondary current is strictly capped, creating a physical shield that protects the downstream +D-DM and +D-DA meters.

The schematic routing for Core 1 begins on Sheet 17. Terminals 1S1 and 1S2 from all three phases are routed to the disconnecting block -X11. From there, the wiring transitions to Sheet 18, entering the test switch +D1-TSM. The test switch allows technicians to safely short-circuit the CT secondaries, because an open-circuited CT under load will generate dangerous kilovolt potentials.

After passing through the test switch, the current loops in series through the Digital Multifunction Meter +D-DM and the Digital Ammeter +D-DA.

Figure 7 – Lower CT Core 1: Metering (Class 0.2Fs5)

Lower CT Core 1: Metering (Class 0.2Fs5)
Figure 7 – Lower CT Core 1: Metering (Class 0.2Fs5)

Figure 8 – Lower CT Core 1: Metering (Class 0.2Fs5) – continued

Lower CT Core 1: Metering (Class 0.2Fs5) - continued
Figure 8 – Lower CT Core 1: Metering (Class 0.2Fs5) – continued

Go back to Content Table ↑


3.2.2 Lower CT Core 2: REF 615 Protection (Class 5P20)

Core 2 is a 3600/1A core designed for the primary overcurrent and earth fault protection of the feeder, supervised by the REF 615 relay. It is classified as 5P20 with a 30 VA burden. In stark contrast to the metering core, a protection core must absolutely never saturate during a fault.

If a protection CT saturates, the secondary waveform becomes clipped and distorted, causing the protective relay to calculate an artificially low fault current. This can lead to delays in tripping, resulting in equipment damage.

And now a little bit of theory! The “5P20” classification guarantees a composite error of less than 5% when the CT is subjected to 20 times its rated primary current (the Accuracy Limit Factor). This ensures the REF 615 relay receives a perfectly proportional analog waveform even during a severe 25kA short circuit, allowing the microprocessor to calculate precise fault clearance timings.

The wiring for Core 2 is shown on Sheet 19. Terminals 2S1 and 2S2 route to disconnecting block -X12 (Row B, Column 4). The phases pass through the REF 615 test switch +D1-TS1 at pins 1A/2A, 3A/4A, and 5A/6A. Exiting the test switch, they terminate directly at the heavy-duty analog current inputs of the REF 615 relay +D-F1.

The Red phase lands on pins X120:7/8, the Yellow phase on X120:9/10, and the Blue phase on X120:11/12 (Sheet 19, Row B, Column 6).

Figure 9 – Lower CT Core 2: REF 615 Protection (Class 5P20)

Lower CT Core 2: REF 615 Protection (Class 5P20)
Figure 9 – Lower CT Core 2: REF 615 Protection (Class 5P20)

Go back to Content Table ↑


3.2.3 Lower CT Core 3: Busbar Differential Protection (Class PX)

Core 3 is a 3600/1A Class PX core, utilizing identical parameters to the Upper CTs (Vkp ≥ 800 V, Rct ≤ 18 Ω). This core forms the boundary for the main 13.8kV Busbar Differential Protection scheme (87B).

By summing the currents entering the busbar (from the transformer) and subtracting the currents leaving the busbar (via the feeders), the 87B relay can instantly detect a busbar short circuit. Traced on Sheet 20, terminals 3S1 and 3S2 map to terminal block -X13, then bridge across to the inter-panel feed-through block -X87 (Row A/B, Column 5) to connect with the central 87B relay panel.

The local neutral is established and grounded via -EARTH8.

Membership Upgrade Required

This content is not available in your premium membership plan. Please upgrade your plan in order to access this content. You can choose an annually based Basic, Pro, or Enterprise membership plan. Subscribe and enjoy studying specialized technical articles, online video courses, electrical engineering guides, and papers.

With EEP’s premium membership, you get additional essence that enhances your knowledge and experience in low- medium- and high-voltage engineering fields.

Good to know: – Save 50% on all video courses with Enterprise plan.

Upgrade

Already a member? Log in here

Premium Membership

Get access to premium HV/MV/LV technical articles, electrical engineering guides, research studies and much more! It helps you to shape up your technical skills in your everyday life as an electrical engineer.
More Information
Edvard Csanyi - Author at EEP-Electrical Engineering Portal

Edvard Csanyi

Hi, I'm an electrical engineer, programmer and founder of EEP - Electrical Engineering Portal. I worked twelve years at Schneider Electric in the position of technical support for low- and medium-voltage projects and the design of busbar trunking systems.

I'm highly specialized in the design of LV/MV switchgear and low-voltage, high-power busbar trunking (<6300A) in substations, commercial buildings and industry facilities. I'm also a professional in AutoCAD programming.

Profile: Edvard Csanyi

Leave a Comment

Tell us what you're thinking. We care about your opinion! Please keep in mind that comments are moderated and rel="nofollow" is in use. So, please do not use a spammy keyword or a domain as your name, or it will be deleted. Let's have a professional and meaningful conversation instead. Thanks for dropping by!

Learn How to Design Power Systems

Learn to design LV/MV/HV power systems through professional video courses. Lifetime access. Enjoy learning!

EEP Hand-Crafted Video Courses

Check more than a hundred hand-crafted video courses and learn from experienced engineers. Lifetime access included.
Experience matters. Premium membership gives you an opportunity to study specialized technical articles, online video courses, electrical engineering guides, and papers written by experienced electrical engineers.
Whitepaper: How to Improve Risk Decisions for Power Systems - Prioritizing vulnerabilities with full operational context