Search

Premium Membership ♕

Join EEP PREMIUM today to unlock specialized LV/MV/HV technical articles & expert guides. Apply coupon CTS15 to get 15% off the PRO plan.

Home / Technical Articles / Hands on schemes: Mechanical and electrical interlocking of feeders (to prevent parallel operation)

Estimated Study Time: 24 minutes

Mechanical and electrical interlocks

An industrial load with a connected load need above 2000 kVA usually requires multiple feeding transformers to restrict the system’s fault level. The fault level of an electrical network indicates the supply source’s capacity to withstand a faulty circuit, expressed in kVA or MVA.

Interlocking of feeders to prevent parallel operation
Interlocking of feeders to prevent parallel operation

Electrical network may also have a standby emergency supply source. The two feeding transformers, while electrically similar and capable of parallel operation, are not intended to operate in parallel to restrict the fault level.

The emergency source, due to different electrical parameters, SHOULD NOT oerate in parallel with either of the two incoming sources.

To ensure mandatory safety by preventing parallel operation, it is imperative to implement a mechanical or electrical interlock, or both, between all incoming feeders.

This article discusses schemes that provide the necessary safety interlocks.

Table of Contents:

    1. Schemes with more than one source of supply
    2. Mechanical interlocking schemes:
      1. Use of switchgear castell locks
      2. Scheme with two sources of supplies
      3. Scheme with two sources of supplies and a bus coupler
      4. Scheme with three sources of supplies and two bus couplers
    3. Electrical interlocking schemes (when the iInterrupters are manually operated):
      1. Scheme with two sources of supplies
      2. Scheme with two sources of supplies and a bus coupler
      3. Scheme with three sources of supplies and two bus couplers
      4. Electrical interlocking schemes when the interrupters are also electrically operated
        1. Limit switch (LS)
        2. Closing coil (CC)
        3. Breaker control switch (CS)
    4. Attachment (PDF) 🔗 Download ‘The Basic Power Substation Theory For Students’

1. Schemes with more than one source of supply

When there are more than one sources of supply, it is advisable to distribute the loads also in as many sections as the incomers, and offer a tie-circuit between every two sections, to achieve additional flexibility. Now fault on one segment or source of supply will not result in power failure to the entire system.

Figures 1 and 2 depict this type of distribution. Current limiting fuses must be installed at both ends of potential/control transformers.

It is important to note that for big industrial and other LV loads, it is common practice to select multiple transformers with lower ratings to meet the needed load rather than a single transformer with greater capacity. Similarly, when more than one transformer is utilized to serve an important industrial load, the load must be distributed in as many sections as there are transformers.

Parallel operation of any two transformers must be avoided, even if they are compatible and have the same power source. Otherwise, the impedances of all transformers operating in parallel would drop in parallel. It reduces the effective impedance of the faulty circuit and increases the system fault level. The use of current limiting reactors on LV systems is not encouraged due to the reactor’s relatively large losses in comparison to the power it handles.

Figures 1 and 2 depict a few typical but widely used distribution networks.

Figure 1 – Interlocking requirements for two-feeders system

Interlocking requirements
Figure 1 – Interlocking requirements

Figure 2 – Interlocking requirements for a three-feeders system

Interlocking requirements for a three-feeders system
Figure 2 – Interlocking requirements for a three-feeders system

Go back to Content Table ↑


2. Mechanical interlocking schemes

2.1 Use of switchgear castell locks

Different figure locks such as A – , – B and AB are used with a common master key. See Figure 3. The master key can unlock all locks A – , – B or AB because it has grooves for both A and B but will be locked with the lock that it unlocks.

For the removal of the key, the lock must first be locked. Only then can the key be used for the other locks, so accomplishing the required interlocking. The lock secures the lever of the interrupter’s closing mechanism, blocking its closure.

Lock AB can be unlocked by either of the keys A – or – B. The number of locks will be the same as the number of interrupting devices, but the keys will be less and will be for only as many interrupting devices as are permitted to be switched at a time (generally equal to the number of supply sources).

Figure 3 – Switchgear Castell locks

Switchgear Castell locks
Figure 3 – Switchgear Castell locks

Go back to Content Table ↑


2.2 Scheme with two sources of supplie

The two incomers (I/C), fed from two different sources, can be fitted with two locks A – and – B , and one master key AB . This key will permit the switching of only one incomer at a time.

See Figure 4.

Figure 4 – Two sources of supply

Two sources of supply
Figure 4 – Two sources of supply

Go back to Content Table ↑


2.3 Scheme with two sources of supplies and a bus coupler

The two incomers (I/C) and the coupler can be fitted with three locks, A –, – B and AB and two keys A – and – B : locks A – and – B for the incomers and AB for the coupler. The key A – can operate I/C-1 or the coupler and key – B can operate I/C-2 or the coupler.

Thus, only two of the three interrupting devices, I/C-1 and coupler, I/C-2 and coupler, or I/C-1 and I/C-2 can be switched at a time to achieve the required interlocking.

See Figure 5.

Figure 5 – Two sources of supply and a bus coupler

Two sources of supply and a bus coupler
Figure 5 – Two sources of supply and a bus coupler

Go back to Content Table ↑


2.4 Scheme with three sources of supplies and two bus couplers

The three incomers and two couplers can be fitted with five locks, A – , – B , C – . AB and CB and three keys A – , – B , and C – .

Figures 4, 5, and 6 are mechanical interlocking schemes.

The interlocking is achieved as follows:

  • Key A – can allow switching of I/C-1 or coupler 1
  • Key B – can allow switching of I/C-2, coupler 1 or coupler 2 and
  • Key C  – can allow switching of I/C-3 or coupler 2
Consequently, just three of the five interrupting devices may be switched simultaneously as necessary, without causing a parallel operation between any two incoming sources.

For a larger number of supply sources, each having two interrupting devices, one as incomer and the other as coupler, two more locks, i.e. – D and CD and one key, i.e. – D may be added for each extra source and so on.

See Figure 6.

Figure 6 – Three sources of supply and two bus couplers

Three sources of supply and two bus couplers
Figure 6 – Three sources of supply and two bus couplers

Important Note!

The mechanical interlocking system is typically needed for manually operated interrupting devices that lack electrically operated tripping mechanisms, such as under-voltage (U/V) or shunt trip (S/T) releases. A switch or switch fuse unit (SFU or FSU) is a device that lacks an electrically driven tripping mechanism.

Occasionally, manually operated breakers or MCCBs equipped with an under-voltage or shunt trip require a mechanical interlocking scheme, however this is not the preferable approach when an electrical interlocking scheme is feasible.

When a breaker, including an MCCB, is equipped with an electrical closing mechanism with a motor or solenoid, mechanical interlocking is NOT recommended as it makes the electrical closing redundant!

Good Reading – Tricks in designing and analyzing schematics and diagrams of high voltage substations

Tricks in designing and analyzing schematics and diagrams of high voltage substations

Go back to Content Table ↑


3. Electrical interlocking schemes (when the interrupters are manually operated)

The most effective approach for achieving interlocking between several supply sources is exclusively through electrical systems, whenever feasible. They are failsafe and can also be controlled remotely. Mechanical interlocking schemes are typically employed for smaller installations when, due to lower ratings or price limitations, a breaker is not installed, hence restricting the implementation of an electrical interlocking scheme.

The electrical interlocking should ideally be implemented by shunt trip releases. It must have a different AC and DC source for control supply, ensuring that the operation of the system is autonomous from the primary supply source.

Consequently, interlocking via under-voltage (U/V) releases is definetely not recommended as its operation relies on the supply situation at hand.

An under-voltage release is typically designed to trip the interrupting device when the power supply is interrupted, rather than for any other control schemes.

The systems are logical and straightforward, intended to ensure that no two supply sources can be switched in parallel. The scheme prohibits switching an interrupter that might couse it to operate in parallel with another, unless the first source is opened first. This is shown in the following interlocking schemes.

Suggested Study – A Guide to the Logic Behind the GIS Operation Interlocks

A Guide to the Logic Behind the GIS Operation Interlocks

Go back to Content Table ↑


3.1 Scheme with two sources of supplies

The NO (normally open) contact of I/C-1 (52i) is wired in the trip circuit of I/C-2 (52 ii) and vice versa. As soon as an interrupter is closed, the tripping circuit of the other gets ready to trip. See Figure 7.

Important Note!

The function of a shunt trip coil is to trip an interrupter. It releases the interrupter’s closing lever and trips it as soon as its coil is energized. The coil is rated for a short-time, since it is in the circuit for a very short-period only when it is required to trip the interrupter.

To ensure that it does not continue to remain energized after carrying out its function, the interrupter’s ‘NO’ contacts are also wired in series with the coil as shown.

The coil becomes de-energized as soon as the interrupter trips. Normally two NO contacts of the interrupter are wired in series, as standard practice, by the interrupter (breaker or MCCB) manufacturers to share the arc energy on a trip and enhance contact life, particularly when the control supply is d.c. which normally is the case.

Figure 7 – Electrical interlocking scheme for manually operated breakers for two sources of supplies

Electrical interlocking scheme for manually operated breakers for two sources of supplies
Figure 7 – Electrical interlocking scheme for manually operated breakers for two sources of supplies

* Note: Normally 2NOs of the interrupters are wired in series to share the arc energy and enhance the contact life.

Legends details:

  • Sw – 1: Control supply ON/OFF switch
  • F1 – F2: Control fuses
  • ST1, ST2: Shunt trip coils of breakers
  • I/C: 1, 2 or 52(i, ii): Incoming sources of supplies

Go back to Content Table ↑


3.2 Scheme with two sources of supplies and a bus coupler

The logic is the same as above. In the trip circuit of each interrupter is wired the NO contacts of the other two interrupters. Obviously only two of the three interrupters can be switched at a time.

See Figure 8.

Figure 8 – Electrical interlocking scheme for manually operated breakers for two sources of supplies and a bus coupler

Electrical interlocking scheme for manually operated breakers for two sources of supplies and a bus coupler
Figure 8 – Electrical interlocking scheme for manually operated breakers for two sources of supplies and a bus coupler

* Note: Normally 2NOs of the interrupters are wired in series to share the arc energy and enhance the contact life.

Legends details:

  • Sw – 1: Control supply ON/OFF switch
  • F1 – F2: Control fuses
  • ST1, ST2, ST3: Shunt trip coils of breakers
  • I/C – 1, 2 or 52(i, ii): Incoming sources of supplies
  • B/C – 1 or 52(iii): Bus coupler

Go back to Content Table ↑


3.3 Scheme with three sources of supplies and two bus couplers

The scheme is now more complicated but the following logical approach will make it simple. See Figure 9.

(a) When I/C-1 (52i) is required to be switched

  1. (i) Interlocking with I/C-2 (52ii): I/C-2 (52ii) and B/C-1 (52 iv) should not be in a closed position at one time.
  2. (ii) Interlocking with I/C-3 (52iii): I/C-3 (52iii), B/C-1 (52iv) and B/C-2 (52v) should not all be in a closed position at one time. Refer to the control scheme for I/C-1 (52i).

(b) When I/C-2 (52ii) is required to be switched

  1. Interlocking with I/C-1 (52i): I/C-1 (52i) and B/C-1 (52iv) should not both be in a closed position at one time.
  2. Interlocking with I/C-3 (52iii): I/C-3 (52iii) and B/C-2 (52v) should not both be in a closed position at one time. Refer to the control scheme for I/C-2 (52ii).

(c) When I/C-3 (52iii) is required to be switched

  1. Interlocking with I/C-2 (52ii): I/C-2 (52ii) and B/C-2 (52v), should not both be in a closed position at one time.
  2. Interlocking with I/C-1 (52i): I/C-1 (52i), B/C-1 (52iv) and B/C-2 (52v) should not all be in a closed position at one time. Refer to the control scheme for I/C-3 (52iii).

(d) When B/C-1 (52iv) is required to be switched

  1. Interlocking with I/C-1 (52i) and I/C-2 (52ii): These should not be in a closed position at one time.
  2. Interlocking with I/C-1 (52i) and I/C–3 (52iii): I/C-1 (52i), B/C-2 (52v) and I/C-3 (52iii) should not all be in a closed position at one time. Refer to the control scheme for B/C-1 (52iv).

(e) When B/C-2 is required to be switched

  1. Interlocking with I/C-2 (52ii) and I/C-3 (52iii): Both should not be in a closed position at one time.
  2. Interlocking with I/C-1 (52i) and I/C-3 (52iii): I/C-1 (52i), B/C-1 (52iv) and I/C-3 (52iii) should not all be in a closed position at a time. Refer to the control scheme for B/C-2 (52v).

Figure 9 – Electrical interlocking scheme for manually operated breakers for three sources of supplies and two bus couplers

Electrical interlocking scheme for manually operated breakers for three sources of supplies and two bus couplers
Figure 9 – Electrical interlocking scheme for manually operated breakers for three sources of supplies and two bus couplers

* Note! Normally 2NOs of the interrupters are wired in series to share the arc energy and enhance the contact life.

Legends details:

  • Sw – 1: Control supply ON/OFF switch
  • F1 – F2: Control fuses
  • ST1, ST2, ST 3, ST4 and ST5: Shunt trip coils of breakers
  • I/C-1,2,3 or 52(i,ii,iii): Incoming sources of supplies
  • B/C-1,2 or 52(iv,v): Bus couplers.

Go back to Content Table ↑


3.4 Electrical interlocking schemes

When the interrupters are also electrically operated

Motor-operated interrupting devices are applied when the system requires remote-controlled power switching, like for an auto-reclosing scheme. With the addition of a circuit for the motor spring charging mechanism and the interrupter’s closing coil, the electrical interlocking schemes essentially stay the same. See the Figure 10.

Brief details of the electrical closing features are as follows.

Spring charging motor mechanism

The purpose of the motor is to charge the closing spring that closes the interrupter, independently of the speed and operation of the motor or of the operator when closed manually. (The interrupter can be closed manually or electrically when the spring is fully charged.)

As soon as the spring is discharged, the motor recharges it automatically to prepare it for the next operation. The motor may be fed through the same source as for the main control scheme or another source, depending upon the system design. But the source must be reliable and independent of the main power supply as far as possible (such as through a battery).

Important Note! Small interrupters and MCCBs particularly may be electrically operated through a solenoid valve.

Figure 10 – Control scheme for two electrically operated breakers and two sources of supplies

Control scheme for two electrically operated breakers and two sources of supplies
Figure 10 – Control scheme for two electrically operated breakers and two sources of supplies

Go back to Content Table ↑


3.4.1 Limit switch (LS)

The spring charging mechanism is fitted with a limit switch, having generally 2NO and 2NC change-over contacts. The 2NC contacts are wired in series with the motor to allow it to charge the spring mechanism immediately on discharge of the spring, to prepare it for the next operation.

As soon as the spring is fully charged, the NC contacts change over to NO and cut off the supply to the motor terminals. See Figure 11 below.

The 2NO contacts of the limit switch are wired in series with the closing coil of the interrupter. As soon as the spring is fully charged these contacts change over to NC and the closing coil circuit gets ready to close.

Further Study – Mastering switchgear control circuits – AC/DC circuits and circuit breaker closing circuit

Mastering switchgear control circuits – AC/DC circuits and circuit breaker closing circuit

Go back to Content Table ↑


3.4.2 Closing coil (CC)

The charged closing spring may be released manually or electrically by energizing a closing coil as shown in the above Figure 10.

Figure 11 – Control scheme for two electrically operated breakers, a bus coupler and two sources of supplies

Control scheme for two electrically operated breakers, a bus coupler and two sources of supplies
Figure 11 – Control scheme for two electrically operated breakers, a bus coupler and two sources of supplies

Go back to Content Table ↑


3.4.3 Breaker control switch (CS)

To close or trip the interrupter locally or remotely a breaker control switch is also wired with the closing and the shunt trip coils of the interrupter, as shown in Figure 10. The switch is a spring return type to ensure that it resumes its original (neutral) position as soon as it has carried out its job of closing or opening the interrupter.

With the above features in mind, the control logic for the various interlocking schemes becomes simple as shown in Figures 10, 11 and 12:

  • Two sources of supplies: Figure 10.
  • Two sources of supplies and a bus coupler: Figure 11.
  • Three sources of supplies and two bus couplers: Figure 12.

Figure 12 – Control scheme for three electrically operated breakers, two bus couplers and three sources of supplies

Control scheme for three electrically operated breakers, two bus couplers and three sources of supplies
Figure 12 – Control scheme for three electrically operated breakers, two bus couplers and three sources of supplies

Go back to Content Table ↑


4. Attachment (PDF)

The Basic Power Substation Theory For Students

Download: The Basic Power Substation Theory For Students (for premium members only):

Membership Upgrade Required

This content is not available in your premium membership plan. Please upgrade your plan in order to access this content. You can choose an annually based Basic, Pro, or Enterprise membership plan. Subscribe and enjoy studying specialized technical articles, online video courses, electrical engineering guides, and papers.
With EEP's premium membership, you get additional essence that enhances your knowledge and experience in low- medium- and high-voltage engineering fields.
Time Limited! - Save 15% on PRO Membership Plan with coupon CTS15
Upgrade
Already a member? Log in here

Go back to Content Table ↑

Source: Switchgear and controlgear assemblies by K.C. Agrawal

Premium Membership

Get access to premium HV/MV/LV technical articles, electrical engineering guides, research studies and much more! It helps you to shape up your technical skills in your everyday life as an electrical engineer.
More Information
Edvard Csanyi - Author at EEP-Electrical Engineering Portal

Edvard Csanyi

Hi, I'm an electrical engineer, programmer and founder of EEP - Electrical Engineering Portal. I worked twelve years at Schneider Electric in the position of technical support for low- and medium-voltage projects and the design of busbar trunking systems.

I'm highly specialized in the design of LV/MV switchgear and low-voltage, high-power busbar trunking (<6300A) in substations, commercial buildings and industry facilities. I'm also a professional in AutoCAD programming.

Profile: Edvard Csanyi

One Comment


  1. Shivakumar G
    Apr 13, 2026

    HI,
    i need two incomer and one bus coupler controller circuit drawing .

Leave a Comment

Tell us what you're thinking. We care about your opinion! Please keep in mind that comments are moderated and rel="nofollow" is in use. So, please do not use a spammy keyword or a domain as your name, or it will be deleted. Let's have a professional and meaningful conversation instead. Thanks for dropping by!

Learn How to Design Power Systems

Learn to design LV/MV/HV power systems through professional video courses. Lifetime access. Enjoy learning!

EEP Hand-Crafted Video Courses

Check more than a hundred hand-crafted video courses and learn from experienced engineers. Lifetime access included.
Experience matters. Premium membership gives you an opportunity to study specialized technical articles, online video courses, electrical engineering guides, and papers written by experienced electrical engineers.