CYBER WEEK OFFER 💥 Save 20% on PRO Membership Plan and Video Courses with the coupon CYM23 (Expires in 2 days).
Home / Technical Articles / SF6 or Vacuum MV Circuit Breaker In Specific Switching Applications
Matching the MV circuit breaker to the task
Many years of experience in developing both SF6 and vacuum medium-voltage circuit breakers has yielded up ample evidence that neither of the two technologies is generally better than the other, and especially that they are complementary from the application point of view.
SF6 or Vacuum MV Circuit Breaker In Specific Switching Applications (on photo: ABB retrofit solution)
Economical factors, user preferences, national ‘traditions’, competence and special switching requirements are the decision-drivers that favor one or the other technology.
Typical of such special applications is the switching of:
  1. Overhead lines and cables
  2. Dry-type transformers
  3. Small-size motors
  4. Capacitors
  5. Arc furnaces,
  6. Shunt reactors and
  7. Railway traction systems.
The need for ‘frequent switching’ or ‘soft switching’ can be an additional element influencing the choice. In such cases, a comprehensive study of the planned installation may be needed to find the best answer.
When applied to the onerous duty of switching and protecting overhead line distribution networks, in which the fault currents are distributed over the whole current range, both technologies provide adequate margins over and above the maximum required by the relevant standards and in normal service practice.
Medium voltage recloser
Go back to Special Applications ↑
2. Transformers
Modern vacuum MV circuit breakers as well as SF6 circuit breakers are suitable for switching the magnetizing currents of unloaded transformers with overvoltages lower than 3.0 pu. In special cases, for instance when vacuum circuit-breakers are used for switching dry-type transformers in industrial installations, the use of surge arresters is to be recommended.
MV cubicle with SF6 circuit breaker - Transformer function
MV cubicle with SF6 circuit breaker – Transformer function (photo credit: demitas.com.tr)
3. Small-Size Motors
When choosing MV circuit breaker for motor-switching duty, attention should be paid to the problems of overvoltages during operation.
The target limit for overvoltages of less than 2.5 pu is obtainable with both technologies. Where vacuum MV circuit breakers are used for switching small motors (starting currents less than 600 A), measures may be necessary to limit overvoltages due to multiple re-ignitions.
However, the probability of this phenomenon arising is low.
Reconditioned General Electric 5 KV LimitAmp Motor Control Center
Reconditioned General Electric 5 KV LimitAmp Motor Control Center with a PowerVac 1200 amp Main Vacuum Circuit Breaker, 4 each 400 amp FVNR Vacuum Starters and 1 each 700 amp Vacuum Circuit Breaker; Credit: atlaselectricinc.com
4. Capacitor banks
Both technologies are suitable for restrike-free switching of capacitor banks. When capacitors must be switched back-to-back, reactors may be necessary to limit the inrush currents. The synchronous control of MV circuit breakers is an effective solution to this problem.
SF6 is specifically recommended for applications with rated voltages higher than 27 kV.
Metal enclosed medium-voltage capacitors and filters
Metal enclosed medium-voltage capacitors and filters (photo credit: ABB)
5. Arc furnaces
Arc furnace switching is often characterized by frequent operation at high current values and short intervals. Vacuum circuit breakers are particularly suited to these service conditions.
Furnace switchgear SIMELTCIS SIVAC-X
Furnace switchgear SIMELTCIS SIVAC-X – Adapted to the extreme requirements of ultra high-power arc furnaces (credit: SIEMENS)
6. Shunt reactors
SF6 circuit breakers are suitable for switching with overvoltages generally lower than 2.5 pu. Where vacuum circuit breakers are employed, it may be necessary under certain circumstances to take additional measures to limit overvoltages.
Shunt reactor
Shunt reactor (photo credit: TRENCH)
7. Railway traction
In principle, both interrupting technologies are well suited for this duty. However, in the case of low-frequency applications (eg, 16.67 Hz), vacuum circuit breakers are to be recommended.
ABB's Unigear medium voltage switchgeara
ABB’s Unigear medium voltage switchgeara (photo credit: sahkopena.fi)
Reference // SF6 or Vacuum MV Circuit Breaker? – Guenter Leonhardt, Mauro Marchi, Giandomenico Rivetti at ABB (Download)
8 Comments
  1. TAHSEEN ISSA BAHAR
    Jun 25, 2023
    Calculations are the best solution for every system and it`s very necessary .
  2. Gustavo
    Jun 11, 2023
    SF6 for circuit breakers is like mineral oil for transformers
    They are stilll KV full range
  3. Madhusudhan .G.Pathak
    Jun 05, 2020
    Thank you sir ji for the update learnt more sir ji thanks
  4. Mark McCloy
    Mar 16, 2017
    From 0kV thru 800kV; SF6 is the ONLY insulating/interrupting medium that CAN be utilized for circuit breakers, save air-blast, magnetic design.
    Great subject and good coverage, Ed, nice job!
    SF6 is an inert gas, heavier than air and naturally dissipates the arc in a manner that allows the energy to be extinguished “softly” alleviating any potential “chopping” effect and capacitance build-up. Furthermore, it can insulate as well as contribute to arc extinguishing. GIS’ design are 92% smaller than traditional, “open-air” substation designs. That savings in real estate cannot be ignored. SF6 is here to stay and has many applications in electrical apparatus and systems, besides inflating tennis balls and gym shoes.
    • Mark McCloy
      Mar 17, 2017
      Furthermore, regarding Capacitor Switching, we have witnessed a 900A; 46kV; 21KA C&L, Pole-Switch; SF6 conduct 19,871 Operations before failure on a full voltage, 9600KVAR, back-to-back switching Fault Test. Very Impressive.
  5. Tanveer shaikh
    Mar 16, 2017
    Iam Elelctrician in Mumbai Maharashtra india
  6. Chris
    Oct 14, 2015
    The Rise, Risks & Safe Detection Of SF6 Gas. 50 years ago ABB pioneered GIS technology. – See more at: http://www.cablejoints.co.uk/blog/article/sf6-gas-detector-crowcon-fgas#sthash.xIembbJL.dpuf
  7. busiku hankondo
    Sep 15, 2015
    Thank you so much for the updates. Learnt more
Leave a Reply to Mark McCloy
  −  one  =  eight
