Home / Technical Articles / Sizing and protection of the neutral conductor (2)
Sizing and protection of the neutral conductor (photo credit: diy.stackexchange.com)
Continued from the first part – Sizing and Protection of the Neutral Conductor (1)
Protection of the neutral conductor
Protection against overload
If the neutral conductor is correctly sized (including harmonics), no specific protection of the neutral conductor is required because it is protected by the phase protection.
However, in practice, if the c.s.a. of the neutral conductor is lower than the phase c.s.a, a neutral overload protection must be installed.
Protection against short-circuit
If the c.s.a. of the neutral conductor is lower than the c.s.a. of the phase conductor, the neutral conductor must be protected against short-circuit. If the c.s.a. of the neutral conductor is equal or greater than the c.s.a. of the phase conductor, no specific protection of the neutral conductor is required because it is protected by the phase protection.
Breaking of the neutral conductor (Fig. 1)
The need to break or not the neutral conductor is related to the protection against indirect contact.
In TN-C scheme
The neutral conductor must not be open-circuited under any circumstances since it constitutes a PE as well as a neutral conductor.
In TT, TN-S and IT schemes
In the event of a fault, the circuit-breaker will open all poles, including the neutral pole, i.e. the circuit-breaker is omnipolar.
The action can only be achieved with fuses in an indirect way, in which the operation of one or more fuses triggers a mechanical trip-out of all poles of an associated series-connected load-break switch.
Isolation of the neutral conductor (Fig. 1)
It is considered to be the good practice that every circuit be provided with the means for its isolation.
Fig. 1 – Neutral conductor appearances
The various situations in which the neutral conductor may appear
Figure 1 – The various situations in which the neutral conductor may appear
A
Authorized for TT or TN-S systems if a RCD is installed at the origin of the circuit or upstream of it, and if no artificial neutral is distributed downstream of its location
B
The neutral overcurrent protection is not necessary:
  • If the neutral conductor is protected against short-circuits by a device placed upstream, or,
  • If the circuit is protected by a RCD which sensitivity is less than 15% of the neutral admissible current.
Reference // Electrical Installation Guide 2010 – Schneider Electric
  1. NOEL.GSANTOS
    Nov 08, 2018
    CAN YOU PLEASE COMPARE THIS TO NATIONAL ELECTRICAL CODE OF USA. THE NEUTRAL IS NOT PROTECTED. IN YOUR OPINION WHOSE CODE IS THE BEST? THANKS.
  2. Ahmad Ramzy
    May 13, 2014
    This is a wonderful website, articles are very useful and subjects are often discussed.Thank you
    A.Ramzy
  3. SANJEEV SHARMA
    Oct 04, 2012
    sir last day leave a comment but no any responce. pls ans my question.
Leave a Reply to Ahmad Ramzy
two  +  5  =
