Calculate size of each part of DOL motor starter for the system voltage 415V, 5HP three phase house hold application induction motor, code A, motor efficiency 80%, motor RPM 750, power factor 0.8 and overload relay of starter is put before motor.
Basic Calculation of Motor Torque and Current
- Motor Rated Torque (Full Load Torque) = 5252xHPxRPM
- Motor Rated Torque (Full Load Torque) = 5252x5x750 = 35 lb-ft.
- Motor Rated Torque (Full Load Torque) = 9500xKWxRPM
- Motor Rated Torque (Full Load Torque) = 9500x(5×0.746)x750 = 47 Nm
- If Motor Capacity is less than 30 KW than Motor Starting Torque is 3xMotor Full Load Current or 2X Motor Full Load Current.
- Motor Starting Torque = 3xMotor Full Load Current.
- Motor Starting Torque = 3×47 = 142Nm.
- Motor Lock Rotor Current = 1000xHPx figure from below Chart/1.732×415
Locked Rotor Current
Code | Min. | Max. |
A | 1 | 3.14 |
B | 3.15 | 3.54 |
C | 3.55 | 3.99 |
D | 4 | 4.49 |
E | 4.5 | 4.99 |
F | 5 | 2.59 |
G | 2.6 | 6.29 |
H | 6.3 | 7.09 |
I | 7.1 | 7.99 |
K | 8 | 8.99 |
L | 9 | 9.99 |
M | 10 | 11.19 |
N | 11.2 | 12.49 |
P | 12.5 | 13.99 |
R | 14 | 15.99 |
S | 16 | 17.99 |
T | 18 | 19.99 |
U | 20 | 22.39 |
V | 22.4 |
- As per above chart Minimum Locked Rotor Current = 1000x5x1/1.732×415 = 7 Amp
- Maximum Locked Rotor Current = 1000x5x3.14/1.732×415 = 22 Amp.
- Motor Full Load Current (Line) = KWx1000/1.732×415
- Motor Full Load Current (Line) = (5×0.746)x1000/1.732×415 = 6 Amp.
- Motor Full Load Current (Phase) = Motor Full Load Current (Line)/1.732
- Motor Full Load Current (Phase) = 6/1.732 =4Amp
- Motor Starting Current = 6 to 7xFull Load Current.
- Motor Starting Current (Line) = 7×6 = 45 Amp
1. Size of Fuse
Fuse as per NEC 430-52
Type of Motor | Time Delay Fuse | Non-Time Delay Fuse |
Single Phase | 300% | 175% |
3 Phase | 300% | 175% |
Synchronous | 300% | 175% |
Wound Rotor | 150% | 150% |
Direct Current | 150% | 150% |
- Maximum Size of Time Delay Fuse = 300% x Full Load Line Current.
- Maximum Size of Time Delay Fuse = 300%x6 = 19 Amp.
- Maximum Size of Non Time Delay Fuse = 1.75% x Full Load Line Current.
- Maximum Size of Non Time Delay Fuse = 1.75%6 = 11 Amp.
2. Size of Circuit Breaker
Circuit Breaker as per NEC 430-52
Type of Motor | Instantaneous Trip | Inverse Time |
Single Phase | 800% | 250% |
3 Phase | 800% | 250% |
Synchronous | 800% | 250% |
Wound Rotor | 800% | 150% |
Direct Current | 200% | 150% |
- Maximum Size of Instantaneous Trip Circuit Breaker = 800% x Full Load Line Current.
- Maximum Size of Instantaneous Trip Circuit Breaker = 800%x6 = 52 Amp.
- Maximum Size of Inverse Trip Circuit Breaker = 250% x Full Load Line Current.
- Maximum Size of Inverse Trip Circuit Breaker = 250%x6 = 16 Amp.
3. Thermal Overload Relay
Thermal Overload Relay (Phase):
- Min. Thermal Overload Relay setting = 70%x Full Load Current(Phase)
- Min. Thermal Overload Relay setting = 70%x4 = 3 Amp
- Max. Thermal Overload Relay setting = 120%x Full Load Current(Phase)
- Max. Thermal Overload Relay setting = 120%x4 = 4 Amp
- Thermal Overload Relay setting = 100% x Full Load Current (Line).
- Thermal Overload Relay setting = 100%x6 = 6 Amp
4. Size and Type of Contactor
Application | Contactor | Making Cap |
Non-Inductive or Slightly Inductive ,Resistive Load | AC1 | 1.5 |
Slip Ring Motor | AC2 | 4 |
Squirrel Cage Motor | AC3 | 10 |
Rapid Start / Stop | AC4 | 12 |
Switching of Electrical Discharge Lamp | AC5a | 3 |
Switching of Electrical Incandescent Lamp | AC5b | 1.5 |
Switching of Transformer | AC6a | 12 |
Switching of Capacitor Bank | AC6b | 12 |
Slightly Inductive Load in Household or same type load | AC7a | 1.5 |
Motor Load in Household Application | AC7b | 8 |
Hermetic refrigerant Compressor Motor with Manual O/L Reset | AC8a | 6 |
Hermetic refrigerant Compressor Motor with Auto O/L Reset | AC8b | 6 |
Control of Restive & Solid State Load with opto coupler Isolation | AC12 | 6 |
Control of Restive Load and Solid State with T/C Isolation | AC13 | 10 |
Control of Small Electro Magnetic Load ( <72VA) | AC14 | 6 |
Control of Small Electro Magnetic Load ( >72VA) | AC15 | 10 |
As per above chart:
- Type of Contactor = AC7b
- Size of Main Contactor = 100%X Full Load Current (Line).
- Size of Main Contactor = 100%x6 = 6 Amp.
- Making/Breaking Capacity of Contactor = Value above Chart x Full Load Current (Line).
- Making/Breaking Capacity of Contactor = 8×6 = 52 Amp.
Dear Gents
Please support me to select fuse size for 3 phase motor with LRA 11.4 A V=400, inpout power 1.21Kw, current = 2.3A and how to calculat it?, fause PH (3N)
how we select aa magnetic contactor wth respect to motor
Dear Sir/Mam ,
I have completed bachelor’s degree in Electrical & Electronics engineering branch in 2014 . I have 6months experience in designing electrical panels ( APFC, MCC & PCC panels)& switchgears and software skills in electrical autocad.
Can you please suggest doing PLC, SCADA automation course will hike up my career or not
to get a higher package. If yes please do suggest Institutes for the same
Sanjul
The starting current is 45A , maximum size of none time delay fuse is 11A ,
Why it will not blow?
Why Code F minimum locked rotor current =5A , maximum locked rotor current =2.59A
Motor starting torque=3 times of motor full load torque or current
3 times or 2 times it is very big difference
i want to know how many torque of 15 kw motor
How will you calculate the contactor, circuit breaker, thermal overload and size of power cable and control cable for DOL starter when u are give a 3KW induction motor. Thank u.
what are the basis for above calculations?
What is the basis of above calculation….
Provide International Standard for Calculation….
1.Can we say what is the no load current for a motor if it’s full load current,voltage,power ,power factor are known
5252x5x750 = 35 lb-ft. ????
9500x(5×0.746)x750 = 47 Nm ???????
It should be:
5252×5/750 = 35 lb-ft.
9500x(5×0.746)/750 = 47 Nm
Yes u r right
From where you got multiplying factor, Is there any std/ ref in IS, IEC.etc.
Why the power factor is not included in the calculation although it has been give in the details?
p.f is taken in the calculation, but it is missing in the formula
great sir,can u describe about selection of transformer according to connected load, necessary erection steps for transformer erection