Safety in the first place
There are at least two safety requirements that medium-voltage switchgear MUST fulfil: an interlocking system and an arc protection system. Yes, these two systems are crucial in terms of safety because they protect not only the operator and other substation personnel but also the equipment in the substation itself.
There are hundreds and hundreds of incidents worldwide that usually involve wrong breaker manipulation that leads to catastrophic consequences and injuries.
This article sheds some light on the most common interlocking and arc protection systems installed in a medium voltage switchgear.
1. Switchgear Interlocking Systems
Interlocking between different switchgear apparatus and enclosure access covers and doors enhances personnel safety, as well as improving operational convenience. If a switching device can cause serious damage in an incorrect position, this must also have a locking facility.
Interlocks consists of the rules. Interlocks MUST ensure that the disconnector cannot be moved or operated unless the circuit breaker is open. Interlocks shall ensure that the circuit breaker cannot be closed unless the disconnector is fully in the ‘closed‘, ‘isolated‘ or ‘earth‘ position.
Interlocking uses electrical and mechanical methods or a combination of both. IEC 62271-200 states mandatory rules for switchgear interlocking:
For metal-enclosed switchgear with removable switching apparatus:
Rule #1 – Switching device must be in the open position before it can be withdrawn.
Rule #2 – Switching device can only be operated in the positive service or test position.
Rule #3 – Switching device cannot be closed unless the auxiliary control circuits required to open the switch are connected. Auxiliary control circuits cannot be disconnected with the switching device closed in the service position.
For metal-enclosed switchgear with disconnectors:
Rule #1 – Disconnector cannot be operated under conditions other than those for which it is intended to be used.
Rule #2 – Disconnector cannot be operated unless the main switching device is open.
Rule #3 – Operation of a main switching device is prevented unless its associated disconnector is in a positive service, test or earth position.
Rule #4 – Disconnectors providing isolation for maintenance and servicing must have a locking facility.
1.1 Interlocking Methods
The illustration in Figure 1 shows a common switchgear arrangement for a medium voltage power distribution system. This switchgear arrangement uses three separate interlocking methods which are marked with 1, 2 and 3 in the red squares.
Let ‘s now start with describing of each scheme.
Figure 1 – Typical MV power distribution switchgear arrangement with interlocks
- Q-IL – Circuit breaker (left incomer)
- E-IL – Earth switch (left incomer)
- TXR_L – Supply transformer (left bus)
- Q-IR – Circuit breaker (right incomer)
- E-IR – Earth switch (right incomer)
- TXR_R – Supply transformer (right bus)
- Q-BC – Circuit breaker (bus coupler)
- Q-FL – Circuit breaker (left feeder)
- E-FL – Earth switch (left feeder)
- Q-FR – Circuit breaker (right feeder)
- E-FR – Earth switch (right feeder)
Interlock Scheme #1
Two Incomers and Bus Coupler Interlocking
The two incomers and the bus coupler circuit breakers use a standard “2 out of 3” interlocking system to prevent a parallel feed from the two incomers onto a common bus. Interlocking allows the following conditions:
Condition #1 – The two incomer circuit breakers closed (Q-1L and Q-1R) with the bus coupler circuit breaker open (Q-BC).
Condition #2 – Left incomer and bus coupler circuit breakers closed (Q-IL and Q-BC) with right incomer circuit breaker open (Q-IR).
Condition #3 – Right incomer and bus coupler circuit breakers closed (Q-IR and Q-BC) with left incomer circuit breaker open (Q-IL).
Typically, these interlocking conditions are met using both electrical and mechanical method.
Electrical Interlocking
Normally closed auxiliary contacts from the two incomers and the bus coupler circuit breakers are used to electrically interlock the close command of each circuit breaker.
Left incomer circuit breaker (Q-IL) has a normally closed auxiliary contact from the right incomer circuit breaker (Q-IR) and a normally closed contact from the bus coupler circuit breaker (Q-BC) connected in parallel to allow a close command.
Right incomer circuit breaker (Q-IR) has a normally closed auxiliary contact from the left incomer circuit breaker (Q-IL) and a normally closed contact from the bus coupler circuit breaker (Q-BC) connected in parallel to allow a close command.
Bus coupler circuit breaker (Q-BC) has a normally closed auxiliary contact from the left incomer circuit breaker (Q-IL) and a normally closed contact from the right incomer circuit breaker (Q-IR) connected in parallel to allow a close command.
This control method only allows for any two circuit breakers to be closed at the same time.
Figure 2 – Interlock scheme #1: Two incomers and bus coupler interlocking
Mechanical Interlocking
Mechanical locks must be used to prevent unauthorized access to areas of the switchgear panel that contain live components. Unless all live parts have been rendered safe – either by a clearly applied earth connection or by being positively disconnected and screened from the other live parts – access to such parts is not possible.
To guarantee effective and comprehensive protection against malfunction, mechanical interlocks must be supplied. Mechanical interlocks must be built and engineered to ensure reliable fail-safe performance.
In our case, interlocking uses a key system which includes three identical locks and two identical keys. Both incomer and the bus coupler circuit breakers (Q-IL, Q-IR, Q-BC) require an interlock key to be inserted into the circuit breaker body, and the circuit breaker racked into the service position, before the circuit breaker can be closed. This interlock key can only be removed when the circuit breaker is open and in the racked-out test position.
When the circuit breaker is in service, the interlock key is not accessible.
If one of the incomer supplies is lost, the associated circuit breaker is opened and racked-out to the test position. The interlock key can be moved to the bus coupler circuit breaker, allowing it to be racked into the service position and closed. When normal supply resumes, the bus coupler circuit breaker has to be opened before the revived incomer circuit breaker can be closed using the interlock key retrieved from the bus coupler circuit breaker.
This key interlock system only allows for any two circuit breakers to be closed at the same time.
Further Study – Learn how to interpret interlocking schemes between MV cubicles
Learn how to interpret interlocking schemes between MV cubicles (single line and wiring diagrams)
Interlock Scheme #2
Incomer Circuit Breaker and Earth Switch Interlocking
The incomer circuit breaker (Q-IL or Q-IR) and earth switch (E-IL or E-IR) are mechanically interlocked to prevent both being closed at the same time. The earth switch can only be closed once the circuit breaker is open and racked-out to the test position. The circuit breaker can only be racked-in for closing, once the earth switch is open.
An additional level of interlocking is required. The incomer earth switch cannot be mechanically operated until power is removed from the incoming supply. This prevents closing the earth switch onto a live supply.
This interlocking is achieved in one of two ways: