Home / Technical Articles / My worst experience in testing and commissioning power transformers

Estimated Study Time: 29 minutes

Transformer commissioning

This technical article discusses a comprehensive approach to conduct transformer commissioning successfully. The set of standards employed, test classes, and test sequence shall be identified beforehand. The pre-commissioning phase is vital in finding any issues prior to engaging in the commissioning process.

My worst experience in testing and commissioning power transformers
My worst experience in testing and commissioning power transformers

Delays are expected during the commissioning phase due to many reasons, but this can be enhanced substantially by imposing a systematic procedure. Moreover, few case studies are briefly discussed to shed light on some common problems that are likely to be encountered during the commissioning.

Some of these cases could have been avoided by following simple visual inspection, so it cannot be emphasized much to follow a well-written procedure.

Reliable and secure electric power delivery is dependent on power transformers’ reliability that is enhanced significantly by sound test plans. These test plans shall be prepared by both manufacturers and end-users to develop thorough and effective plans and specifications. The plan and specifications developers must account for several factors like anticipated environmental conditions, grounding types, exposure to lightning, and switching transient conditions.

The nominal rating specifications are not the only specifications that should be included, but also special ratings like impedance, sound level, or otherwise shall be considered in the test plan and formulated in the specifications.

It is vital to select the set of test plans and specifications of correct test levels that suit the transformer application so as to have an overall reliable power system.

Transformers are subjected to a number of test plans in order to achieve:

  • Compliance with user specifications
  • Quality and reliability assessment
  • Design calculation verification
  • Compliance with applicable industry standard

Table of Contents:

  1. ANSI standards for power transformers
  2. Classification of Tests
  3. Sequence of Tests
  4. Transformer Pre-Commissioning
  5. Transformer Commissioning:
    1. Sweep Frequency Response Analysis (SFRA)
    2. Dielectric Response Frequency (DFR)
    3. Transformer Differential Protection
  6. Case Studies
    1. Oil Analysis and Insulators
    2. Oil Level Problem
    3. Problems in Transformer Differential Protection
  7. Attachment (PDF) 🔗 Standards used for power transformers (PDF)

1. ANSI standards for power transformers

ANSI standards for power transformers are provided in the C57 series of standards. Power transformers, as well as distribution transformers general requirements, are given in the following two standards:

  1. IEEE C57.12.00: IEEE Standard General Requirements for Liquid-Immersed Distribution, Power, and Regulating Transformers
  2. IEEE C57.12.90: IEEE Standard Test Code for Liquid-Immersed Distribution, Power, and Regulating Transformers; and Guide for Short-Circuit  Testing of Distribution and Power Transformers (ANSI)

There are several other standards in the ANSI C57 series for transformers that cover certain specific products and special applications. They also include guides, recommended practices, and tutorials. Indeed, these documents are of great importance for readers who need detailed information on power and distribution transformers testing.

The standards mentioned above are very important references because they serve as an effective communication medium between manufacturers and users. They identify critical features, provide minimum requirements for safe and reliable operation, and serve as valuable references of technical information.

Factory Acceptance Test(FAT) for 2 unit transformer 132kV 90MVA & 2 unit 33kV 30MVA
Figure 0 – Factory Acceptance Test(FAT) for 2 unit transformer 132kV 90MVA & 2 unit 33kV 30MVA (photo credit: Abang Abdul Rahman via Twitter)

Go back to Contents Table ↑


2. Classification of Tests

Power transformers tests are classified according to ANSI and IEEE standards into routine tests, design tests, and other tests. Other tests are applied to ensure the transformer quality measures throughout the transformer production cycle stages. Power transformer test categories are listed in Table 1.

Table 1 – Transformer test categories

No.Transients
1Lightning impulse:
– Full wave
– Chopped wave
– Steep wave
2Switching impulse

No.Low (Power) Frequency
1Applied voltage
2Single-phase induced
3Three-phase induced
4Partial discharge

No.Tests of Performance Characteristics
1No-load loss
2Excitation current %
3Load loss
4Impedance %
5Zero-sequence impedance
6Ratio test
7Short-circuit test

No.Thermal Tests
1Winding resistance
2Heat run test:
– Oil rise
– Winding rise
– Hottest-spot rise
3Overload heat run
4Gas in oil
5Thermal scan

No.Other Transformer Tests
1Insulation capacitance and dissipation factor
2Sound-level tests
310-kV excitation current Megger
4Core ground
5Electrical center
6Recurrent surge
7Dew point
8Core loss before impulse
9Control-circuit test
10Test on a series transformer
11LTC tests
12Preliminary ratio tests
13Test on bushing CT
14Oil preservation system

The stage at which these tests are performed differ; some tests are applied before assembling the core and coil inside the tank, and some tests are performed after fully assembling the transformer and make it ready for final testing. This final testing term is not really final testing, as additional tests are performed just before shipment besides commissioning tests at customer sites.

NOTE! In all of these tests, the test levels and the accept/reject criteria are of prime importance in the jointly developed test plan between the manufacturer and the transformer client.

Go back to Contents Table ↑


3. Sequence of Tests

The standardized documents specify the sequence in which these tests are performed. An example of a test sequence is as in Table 2 below.

Table 2 – Transformer sequence of tests

No.Tests Before Tanking
1Preliminary ratio, polarity, & connection of the transformer windings
2Core insulation tests
3Ratio and polarity tests of bushing-current transformers

No.Tests After Tanking (Final Tests)
1Final ratio, polarity, and phase rotation
2Insulation capacitance and dissipation factor
3Insulation resistance
4Control-wiring tests
5Lightning-voltage impulse tests
6Applied-voltage tests
7Induced-voltage tests & partial-discharge measurements
8No-load-loss & excitation-current measurements
9Winding-resistance measurements
10Load-loss & impedance-voltage measurements
11Temperature-rise tests (heat runs)
12Tests on gauges, accessories, LTCs, etc.
13Sound-level tests
14Other tests as required

No.Tests Before Shipment
1Dew point of gas
2Core-ground Megger Excitation-frequency response test

No.Commissioning Tests
1Ratio, polarity, & phase rotation
2Capacitance, insulation dissipation factor, & Megger tests
3LTC control settings check
4Test on transformer oil
5Excitation-frequency response test
6Space above the oil in the transformer tank

Go back to Contents Table ↑


4. Transformer Pre-Commissioning

The commissioning stage is anteceded by the pre-commissioning stage to prove that new transformers have been properly shipped and correctly erected and installed.

Generally, all electrical equipment types must be tested in the factory to generate the so-called Site Acceptance Test (SAT). The pre-commissioning testing is conducted to prove that:

  1. No equipment was subjected to any damage during transportation
  2. All equipment types have been installed correctly
  3. Equipment is working in harmony with other equipment as per specifications
  4. Protection and control schemes function in accordance with relevant specifications
  5. Equipment is adjusted as per approved settings
  6. Safe installation to energize equipment (very important!)
The pre-commissioning procedure could be divided into three phases: before, during, and after the pre-commissioning tests. Also, some mechanical and electrical checks should be done before the commissioning phase starts. It is not uncommon to find that at many stages during the commissioning phase the contractor is not ready and then the commissioning team has to wait for some test results that might have been missed or ignored.

A procedure is required to check the complete readiness of the contractor prior to the pre-commissioning tests and to prepare for the commissioning tests.

This procedure has to outline the project (transformer) readiness for the commissioning tests, the contractor is fully equipped and ready from all aspects to conduct the commissioning tests, and the time of witnessing the pre-commissioning tests is at minimum duration with high-quality performance.

Transformer pre-commissioning tests and after-receipt checks you MUST perform

A joint inspection that involves the contractor and the client is mandated, and the elements of such an inspection could be viewed in Figure 1.

Moreover, the procedure shall describe at least the following:

  1. Project management structure and responsibilities
  2. Documents needed to commence the commissioning phase
  3. Site instruction records issuance
  4. Safety coordination & meeting
  5. Technical problem reporting
  6. Time and quality management
  7. Uncontrollable project delay form
  8. Readiness of energization report
  9. Final pre-commissioning reporting and contractor evaluation
  10. Fault report
  11. Implementation & improvement

It is quite necessary to prescribe a joint procedure with the contractor to facilitate the commissioning process. Besides the procedure described above, some documents must be submitted before proceeding to the transformer commissioning phase, especially for power transformers. These documents in conjunction with the agreed-upon procedure minimize the possibility of having some inspection activities gone unnoticed.

The documents include the following: wiring diagram, outline diagram, schematic diagram, transport diagram and documents, transformer specifications, technical documentation from suppliers (bushings, tap-changer, cooler, etc.), transformer oil datasheet, SAT report, operation and maintenance manuals, troubleshooting guide, commissioning test list, and hand-over protocol.

Rarely do you find an organization that utilizes these instructions fully since it is time-consuming and many contractors do not abide by such a procedure!

This might be true for small projects and transformers, but it pays off for complicated projects and large power transformers. A simple risk assessment tool could be used to show the impact of having a messy commissioning process to justify formulating a thorough and detailed pre-commissioning/commissioning procedure.

Membership Upgrade Required

This content is not available in your premium membership plan. Please upgrade your plan in order to access this content. You can choose an annually based Basic, Pro, or Enterprise membership plan. Subscribe and enjoy studying specialized technical articles, online video courses, electrical engineering guides, and papers.

With EEP’s premium membership, you get additional essence that enhances your knowledge and experience in low- medium- and high-voltage engineering fields.

Good to know: – Save 50% on all video courses with Enterprise plan.

Upgrade

Already a member? Log in here

Premium Membership

Get access to premium HV/MV/LV technical articles, electrical engineering guides, research studies and much more! It helps you to shape up your technical skills in your everyday life as an electrical engineer.
More Information
Salem Alshahrani - Author at EEP-Electrical Engineering Portal

Salem Alshahrani

Electrical engineer (BEE & Meng). Specialized in substation design, especially in LV/MV switchgears and transformers. Passionate in power system planning, analysis, and stability studies.

Profile: Salem Alshahrani

Leave a Comment

Tell us what you're thinking. We care about your opinion! Please keep in mind that comments are moderated and rel="nofollow" is in use. So, please do not use a spammy keyword or a domain as your name, or it will be deleted. Let's have a professional and meaningful conversation instead. Thanks for dropping by!