Earth-fault protection

Purpose of the measurement

The zero-sequence impedance is usually measured for all star-connected windings of the transformer. The measurement is carried out by supplying a current of rated frequency between the parallell connected phase terminals and the neutral terminal.

Testing of Power Transformer – Measurement of Zero-Sequence Impedance
Testing of Power Transformer – Measurement of Zero-Sequence Impedance (on photo: preparing the 400 kV transformer for the test field inside the ABB’s factory)

The zero-sequence impedance per phase is three times the impedance measured in this way. The zero-sequence is needed for earth-fault protection and earth-fault current calculations.


Measuring circuit and performance of measurement

Circuit for zero-sequence impedance measurement in shown below, where:

  • G1 = supply generator
  • T1 = transformer to be tested
  • T2 = voltage transformer
  • T3 = current transformer
  • P2 = voltmeter
  • P3 = ammeter
  • I = test current
Figure 1 - Circuit for zero-sequence impedance measurement
Figure 1 – Circuit for zero-sequence impedance measurement

The zero-sequence impedance is dependent on the current flowing through the winding. Usually the value corresponding to rated current IN is stated. This implies that the measurement is carried out with a test current of 3 x IN.

However, this is not always possible in practice since the current must be limited to avoid excessive temperature of metallic constructional parts.

The zero-sequence impedance is measured as function of test current, and when necessary the final result is obtained by extrapolation.

Test Result

The zero-sequence impedance is usually given as a percentage of the rated phase impedance.

When the transformer has a three-limb core and no delta-connecter windings, the zero-sequence impedance is about 30…60 %. When the transformer has a delta-connected winding, the zero-sequence impedance is 0.8…1.0 times the corresponding short-circuit impedance.

In the test report the zero-sequence impedance values at the principal and extreme tappings are stated.

Reference: Testing power transformers – ABB

Premium Membership

Get access to premium HV/MV/LV technical articles, electrical engineering guides, research studies and much more! It helps you to shape up your technical skills in your everyday life as an electrical engineer.
More Information
Edvard Csanyi - Author at EEP-Electrical Engineering Portal

Edvard Csanyi

Hi, I'm an electrical engineer, programmer and founder of EEP - Electrical Engineering Portal. I worked twelve years at Schneider Electric in the position of technical support for low- and medium-voltage projects and the design of busbar trunking systems.

I'm highly specialized in the design of LV/MV switchgear and low-voltage, high-power busbar trunking (<6300A) in substations, commercial buildings and industry facilities. I'm also a professional in AutoCAD programming.

Profile: Edvard Csanyi

18 Comments


  1. Prashant Ramdas Vanavale
    Jun 08, 2022

    I have 22/11 kv, 10 MVA Dyn11,transformer while magnetic balance testing the middle phase readings are abnormal can anyone suggest the remedies for achieving the MBT.


    • Franco
      May 06, 2023

      What do you mean with “abnormal reading”. You should never expect equal readings in the 3 phases


  2. Murray Newman
    Feb 18, 2022

    A 5 MVA, 66/11kV, YNzn11 transformer nameplate shows an ‘Impedance Voltage’ of 7.18%.
    Would this value be determined by short-circuiting the secondary ( z ) phase terminals and increasing the primary side ( Y ) phase-phase voltage until rated current flows in the shorted secondary ? The dataplate does not show a value for zero sequence impedance.
    How would the zero sequence impedance be measured ? Star points earthed / unearthed ?
    Would the measurements be different when the primary terminals are shorted be different from when the secondary terminals are shorted ?


  3. sureshkumar
    Nov 20, 2021

    Zero Sequence Impedance test for Three/ Two winding Transformer Star(Py) -Star(Sy) – Delta ( Teritary Winding) to Find out parameter of H,L,&T and convert to 100MVA Rating.This calculation is very useful for Transformer HV SBEF protection Settings.


  4. H.Talukdar
    Jul 13, 2019

    If a three winding Y-Y transformer is kept idly charged ( secondary open ), it is seen that considerably high zero sequence current flows in the transformer, whenever there appears some unbalance voltage due to fault in the system. Can some one explain why ?


    • Shyamkant P. Vasekar
      Nov 29, 2024

      Tranformer tank as secondary of the transformer core and draws much more current from primary under unbalanced voltage condition due to fault.


  5. Moamen Ragab
    Oct 26, 2018

    Dear Edvard,
    It’s nice to be here and read this great article, and I have two questions.
    first one is, if the star connected side is the LV side can I make this test?
    second one is, if the transformer is star/star connection should I make the test for two HV/LV sides?
    Thanks and Regards.


  6. Niaz
    May 23, 2017

    Helo,

    ..i have noticed that, in our 333MVA unit main transformer, YND11 , 400/15 KV, neutral point is solidly earthed.. do you know why? Cause, 15KV generator is high impedance grounded.. but 400 KV transformer also should have impedance grounded.. why it is solidly grounded?


    • KC Sharma
      Jul 18, 2020

      To limit the fault current on application / consumer side, high impedance is provided so that protection can be achieved and damage can be minimized during fault condition.

      Regarding 400kV side, being Extra High Tension voltage, higher sensitivity of ground fault current is considered, second, Solid grounding system does not allow neutral shift which may increase 1.732 time voltage of other phases during ground fault. this may further lead to damages of equipment.


  7. Azizul islam
    Jan 25, 2017

    good


  8. smisencontrols
    Jul 10, 2015

    Top Manufacturer of 3 phase control transformers in Maharashtra
    I’m new on this community,
    and this is my very first post.
    I really appreciate your hard work .
    Thank you for this
    Information.


  9. smisencontrols
    Jul 10, 2015

    Control Power Transformers Mumbai India
    I’m new on this community,
    and this is my very first post.
    I really appreciate your hard work .
    Thank you for this
    Information.


  10. smisencontrols
    Mar 27, 2015

    Top Manufacturer of Single phase control transformers in Mumbai
    This is something I really wanted to read-up on, plus you gave some extra links for further reading.

    Thanks for the resources!


  11. smisencontrols
    Mar 17, 2015

    Top Manufacturer of 3 phase control transformers in Mumbai
    your article is very useful
    I really appreciate your work.
    thank you for this information.


  12. Ananthapadmanaban
    Aug 19, 2014

    Electrical and Electronic engineer in thirst of learning about power systems


  13. Venkat Iyer
    Aug 06, 2014

    Great …. What is the mehodology of earthing to be adopted when substations are located on different floors in a high rise building? If earthing system is TT, what are earthing conductors can be grouped like HT panel body, Transformer body, LV panel body, neutral side of transformer etc.

    Would be grateful if you could throw some lights with some supporting documents.

    I am located in Mumbai, India.

    Thanks and Regards,
    Venkat Iyer


  14. KarSho
    Aug 05, 2014

    Simply Thanks…


  15. pavan
    Jul 28, 2014

    Explain with motor traction

Leave a Comment

Tell us what you're thinking. We care about your opinion! Please keep in mind that comments are moderated and rel="nofollow" is in use. So, please do not use a spammy keyword or a domain as your name, or it will be deleted. Let's have a professional and meaningful conversation instead. Thanks for dropping by!

Learn How to Design Power Systems

Learn to design LV/MV/HV power systems through professional video courses. Lifetime access. Enjoy learning!

EEP Hand-Crafted Video Courses

Check more than a hundred hand-crafted video courses and learn from experienced engineers. Lifetime access included.
Experience matters. Premium membership gives you an opportunity to study specialized technical articles, online video courses, electrical engineering guides, and papers written by experienced electrical engineers.
This whitepaper by OMICRON explores the fundamental shift in substation automation testing from hardware-dependent setups to virtualized, software-defined verification.